    • dc42undefined
      dc42 administrators
      last edited by

      Thanks for the clarification. Yes I could make M80 blocking for a while until VIN is satisfactory. However, an alternative is for you to add a G4 dwell command immediately after the M80 command to delay for a short while.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      1 Reply Last reply Reply Quote 0
      • DocTruckerundefined
        DocTrucker
        last edited by

        The use of G4 is a good idea to let the power levels settle a little.

        From what I understand there is a feature in the system to drop the signal to the power supply if there is a heater fault detected. Is that on as default? If so setting the heater bed or cartridge heater to 5-10°C above ambient and a wait for temperature would be another way of achieving this with the current firmware release. I'd shy away from doing this with the hot end as I wouldn't want to unnecessarily age the polymer in the hot end and it's the heater more likely to go badly wrong of there is a failure of some description.

        I'm going to start having a read through the firmware source code with a view to better understanding it soon. Small chunks at a time relevant to current issues at the time should help and reduce the quantity of my questions! I appreciate the time you take to respond to these and similar questions that I've posted on Reprap forum (post there when I think the issues may be less specific to the duet), thanks! I'm rarely comfortable working from a crib sheet with little knowledge of how things are working outside of the prescribed path. It makes me a frustrating employee for routine tasks but I'd like to think better for R&D!

        Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

        1 Reply Last reply Reply Quote 0
        • dc42undefined
          dc42 administrators
          last edited by

          There is no facility yet to turn off the power supply when a heater fault is detected. It's on the list to add when we have implemented logging, so that the cause of the power going off can be determined subsequently.

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          1 Reply Last reply Reply Quote 0
          • DocTruckerundefined
            DocTrucker
            last edited by

            Just seen this. Really can't get used to the forum needing you to press subscribe again after each new post!

            Link to "Control of Actions after Heater Fault" repeat request

            I'll reference this thread by web link. In a nut shell for safety sake I think there should be an option to call M81 after heater fault as a higher priority than logging. You've got some really nice features for detecting when the heater is going out of control but the current actions of heater fault offers no protection against failed close circuit mosfet or SSR. Addtional thermal fuses and snap switches are an additional point of failure that would rarely (if ever) be tested.

            I'll add any further comments about the M81 action on fault to the "Control of Actions after Heater Fault…" thread.

            Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

            1 Reply Last reply Reply Quote 0
            • dc42undefined
              dc42 administrators
              last edited by

              @DocTrucker:

              Really can't get used to the forum needing you to press subscribe again after each new post!

              Does checking "Automatically subscribe to every thread you comment in" in your user settings not cover that?

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              1 Reply Last reply Reply Quote 0
              • DocTruckerundefined
                DocTrucker
                last edited by

                Mine is ticked.

                Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                1 Reply Last reply Reply Quote 0
                • DeltaConundefined
                  DeltaCon
                  last edited by

                  I do not have a PSU that can be switched electronically. Is there an not too difficult relay kind of trick to add this feature to PSU's that don't have it? Seems a meaningful addition to be able to shutdown PSU after say 15 minutes of ending a print, or when the HE reaches < 50C after ending a print.

                  If you think trial and error is dangerous, try routine. That's even more so!

                  1 Reply Last reply Reply Quote 0
                  • dc42undefined
                    dc42 administrators
                    last edited by

                    You can use the PS_ON output to control an SSR that is connected in series with the mains input to the PSU.

                    Duet WiFi hardware designer and firmware engineer
                    Please do not ask me for Duet support via PM or email, use the forum
                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                    1 Reply Last reply Reply Quote 0
                    • DocTruckerundefined
                      DocTrucker
                      last edited by

                      You can use the pin to ground a 5V coil relay that's got 5v on the other side of it. I didn't looking in to it too closely but you could probably pull the 5V from the board to go to the other side of the relay coil. You'll need to add a flywheel / flyback diode to the relay too in order to protect the board.

                      I use that relay to kill the mains power to the power supply that I'm using to feed V-IN and the heaters.

                      Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                      1 Reply Last reply Reply Quote 0
                      • DocTruckerundefined
                        DocTrucker
                        last edited by

                        Don't bother using an SSR. They fail closed circuit. Relay + diode much better.

                        Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                        1 Reply Last reply Reply Quote 0
                        • DjDemonDundefined
                          DjDemonD
                          last edited by

                          @peridot:

                          Currently I put M80 in my start-of-print G-codes and M81 in my end-of-print G-codes, which mostly handles the problem: I have to manually turn the power on if I want to tinker with the machine (e.g. run probe tests) and I have to manually turn the power off if I cancel a print and then give up (rather than trying again until it succeeds). This is slightly complicated by the fact that I don't ever want to turn the power off when the hot end is too hot, but I have a "cool down and shut off" macro which does an okay job.

                          I don't use PSon and PSoff currently, but I think I might for safety from now on, probably via a relay.

                          However I do use it with another printer which runs from an xbox PSU.

                          In Marlin I get around the hotend cooling problem, by using M109 R40, then M81 in my end gcode, or on Duet you might also put it in your cancel.g. The firmware then waits for hotend temp to drop to below glass transition temp for any material (40, 50 would do but you might get heat creep after power off) before shutting off the power.

                          Does M109 behave in this way in RRF?

                          Simon. Precision Piezo Z-Probe Technology
                          www.precisionpiezo.co.uk
                          PT1000 cartridge sensors NOW IN, just attach to your Duet board directly!

                          1 Reply Last reply Reply Quote 0
                          • dc42undefined
                            dc42 administrators
                            last edited by

                            @DocTrucker:

                            Don't bother using an SSR. They fail closed circuit. Relay + diode much better.

                            They only fail closed circuit if you overload them, and most of them can tolerate very large current surges. A mechanical relay can also fail closed circuit under overload, because the contacts get welded together.

                            Whatever solution you choose, test it regularly by using it as your standard method of powering the printer off.

                            Duet WiFi hardware designer and firmware engineer
                            Please do not ask me for Duet support via PM or email, use the forum
                            http://www.escher3d.com, https://miscsolutions.wordpress.com

                            1 Reply Last reply Reply Quote 0
                            • DocTruckerundefined
                              DocTrucker
                              last edited by

                              SSR would not be trusted in a safety interlock circuit as far as I'm aware. Solid state devices are more sensitive to very temporary voltage spikes. Simple contact overload is preventable by fuse, as you've mentioned elsewhere mosfets are a great protection device for fuses. They certainly weren't trusted by the contractors developing the the safeties on MCPs/MTT/Renishaw's selective laser melting machine while I was involved or service people I recently contracted to swap out some mercury contactors on a polymer chip drier.

                              Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                              1 Reply Last reply Reply Quote 0
                              • DocTruckerundefined
                                DocTrucker
                                last edited by

                                This is straight from the Duet wiki page. That page is also what gave me the impression the M81 on heater fault was already available.

                                "If your power supply supports the PS_ON pin, then the firmware can use it to shut down the whole 12/24V circuit, leaving only the low-power 5V circuit. If you have an ATX power supply, then this is simply a matter of connecting the appropriate pin."

                                "The manufacturers of these parts warn that they can fail as a short, that is, supplying full power to the attached device regardless of the input signal, and they advise against building devices whose only off switch is an SSR in case this occurs. For a heated bed powered this way, it may be a good idea to add either an appropriate thermal cutoff to the bed (see below) or an electromechanical relay attached to PS_ON (so that the MCU can shut down the heater)."

                                This is direct from Omron's pdf that Duet's wiki refers too:

                                "Therefore, for fail-safe operation of control circuits that use SSRs, do not use circuits that shut OFF the load power supply only with an SSR, but rather also use circuits with a contactor or breaker that shuts off the load when the SSR fails. In particular, it may not be possible to ensure safety if the SSRs are used outside the rated ranges. Therefore, always use the SSRs within the ratings. When using an SSR, always design the system to ensure safety and prevent human accidents, fires, and social harm in the event of SSR failure."

                                Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                                1 Reply Last reply Reply Quote 0
                                • DeltaConundefined
                                  DeltaCon
                                  last edited by

                                  There is a lot to consider I see…
                                  Waht do we think about this:
                                  http://3dmodularsystems.com/en/upgrades/282-pson-kit-auto-power-off-your-reprap-3d-printers.html
                                  Seems a cheap solution, but I would want to add 1 or 2 temp fuses, under the bed and perhaps on the HE. Would I use normally closed fuses between the PS_ON signal and the input side if the relay?

                                  If you think trial and error is dangerous, try routine. That's even more so!

                                  1 Reply Last reply Reply Quote 0
                                  • dc42undefined
                                    dc42 administrators
                                    last edited by

                                    @DocTrucker:

                                    This is straight from the Duet wiki page. That page is also what gave me the impression the M81 on heater fault was already available.

                                    "If your power supply supports the PS_ON pin, then the firmware can use it to shut down the whole 12/24V circuit, leaving only the low-power 5V circuit. If you have an ATX power supply, then this is simply a matter of connecting the appropriate pin."

                                    "The manufacturers of these parts warn that they can fail as a short, that is, supplying full power to the attached device regardless of the input signal, and they advise against building devices whose only off switch is an SSR in case this occurs. For a heated bed powered this way, it may be a good idea to add either an appropriate thermal cutoff to the bed (see below) or an electromechanical relay attached to PS_ON (so that the MCU can shut down the heater)."

                                    This is direct from Omron's pdf that Duet's wiki refers too:

                                    "Therefore, for fail-safe operation of control circuits that use SSRs, do not use circuits that shut OFF the load power supply only with an SSR, but rather also use circuits with a contactor or breaker that shuts off the load when the SSR fails. In particular, it may not be possible to ensure safety if the SSRs are used outside the rated ranges. Therefore, always use the SSRs within the ratings. When using an SSR, always design the system to ensure safety and prevent human accidents, fires, and social harm in the event of SSR failure."

                                    If you are looking for a fail-safe solution, you shouldn't rely on the Duet to implement it at all. You should use a simpler system, such as enclosing the entire printer in a fire-resistant box and using a non-resetting thermal cutout at the top of the box to cut the mains supply. Perhaps also a smoke detector that cuts the mains supply.

                                    Duet WiFi hardware designer and firmware engineer
                                    Please do not ask me for Duet support via PM or email, use the forum
                                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                                    1 Reply Last reply Reply Quote 0
                                    • dc42undefined
                                      dc42 administrators
                                      last edited by

                                      @DeltaCon:

                                      There is a lot to consider I see…
                                      Waht do we think about this:
                                      http://3dmodularsystems.com/en/upgrades/282-pson-kit-auto-power-off-your-reprap-3d-printers.html
                                      Seems a cheap solution, but I would want to add 1 or 2 temp fuses, under the bed and perhaps on the HE. I suppose I can use NO thermal fuses parallel to the emergency button?

                                      That's the same arrangement that I have previously (a year or two ago) suggested for providing an auto power off solution.

                                      Duet WiFi hardware designer and firmware engineer
                                      Please do not ask me for Duet support via PM or email, use the forum
                                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                                      1 Reply Last reply Reply Quote 0
                                      • DeltaConundefined
                                        DeltaCon
                                        last edited by

                                        @dc42:

                                        @DeltaCon:

                                        There is a lot to consider I see…
                                        Waht do we think about this:
                                        http://3dmodularsystems.com/en/upgrades/282-pson-kit-auto-power-off-your-reprap-3d-printers.html
                                        Seems a cheap solution, but I would want to add 1 or 2 temp fuses, under the bed and perhaps on the HE. I suppose I can use NO thermal fuses parallel to the emergency button?

                                        That's the same arrangement that I have previously (a year or two ago) suggested for providing an auto power off solution.

                                        Thanks David, You have replied before I edited. Looking back to the schematic I think it is not wise to do anything on the mains side. If I want to add thermal fuses, I think I should do that on the 5V input side, between the PS_On signal and the relay, right?

                                        If you think trial and error is dangerous, try routine. That's even more so!

                                        1 Reply Last reply Reply Quote 0
                                        • DocTruckerundefined
                                          DocTrucker
                                          last edited by

                                          @dc42:

                                          If you are looking for a fail-safe solution, you shouldn't rely on the Duet to implement it at all. You should use a simpler system, such as enclosing the entire printer in a fire-resistant box and using a non-resetting thermal cutout at the top of the box to cut the mains supply. Perhaps also a smoke detector that cuts the mains supply.

                                          Agreed you can't rely on the duet to make the system safe. Safety systems (particually programable ones) are typically seperate from the main control. What I was trying to implement on the back of the wiki page advice is giving the duet the chance to say "help I'm out of control" or to consider the atx-on as a "I'm ok signal" until the signal is no longer to ground.

                                          Your other points are also read from same wiki page. Smoke alarms are after the event and a good last line of defence, particularly if the machine is built into a fire box. I've seached for thermal cutouts but not found much suitable for the hot end. I welcome any supplier advice on that! In addition the thermal fuses and snap switches are can fail badly if they fall from the zone they are monitoring. I considered electrically grounding the whole frame to 0V but aluminium is very quick to oxidise and could easily create a new failure point it the circuit raising more false trips.

                                          The exisiting fault detection for the heater is a great way of detecting failure before it happens, and this is easily tested with something as little as a wrench on the hot end or a block or aluminium on the hotend to push the response of the system out of limits. I've seen it trip a few times, but been able to link it to something daft that I've done. Testing thermal fuses isn't ideal as the snap point isn't exact and would naturally be a safety magin above normal operating temperatures. You either end up adding an external heat source (not necessarily similar to the machine out of control) or trying to push the heaters beyond their intended range just to hit the trip.

                                          I've set up a 24VDC interlock loop to kill mains power to psu for steppers and heaters. At the moment this is just grounded by the 5VDC relay and broken by a big red e-stop button. The intention is to expand it to include other safety measures that are not likely to nusance trip. The interlock loop is based on force guided contact relays whose status will be verified by the user through unused normally closed and open contacts. The relay contacts are quick blow fuse protected to well within there operating range.

                                          SSRs are great to replace electromechanical where high switch rates are required. Other than that the electromechanical are often cheaper with the flyback diode and very robust once the contacts are fuse protected. I originally wanted to move away from relays on my trucks loom, but the additional work needed in transient voltage suppression pushed it well into the relms of too much work.

                                          Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                                          1 Reply Last reply Reply Quote 0