      Dear community.

      We are trying to get the chamber heater running. Therefor we set up our system as follows:
      Our chamber heater is assigned to heater H6.
      M141 H6 ; Define heater h6 as chamber heater
      M301 H6 P-1 ; Disable PID settings to use bang-bang
      M307 H6 B1 ; To ensure bang-bang is enabled for heater h6

      From our point of view no further changes are required.
      Nevertheless we still receive the error below after a few seconds

      Error: Heating fault on heater 6, temperature rising much more slowly than the expected 1.7°C/sec

      Therefor we adapted the parameters to:
      M307 H6 B1 A5 D300 C600
      If our understanding is correct this should lead to a temperature curve that reaches a delta of 5 degrees after approx. an hour.

      Are we on the wrong track? Please give instructions.

      Thank you in advance!

      3dWare

      1 Reply Last reply Reply Quote 0
      • 3dwareundefined
        3dware
        last edited by

        Brief update: Removing the A Parameter from the M307 results in:
        M307 H6 B1 D300 C600

        Now the heater is ramping up properly without an error message.
        Since the C parameter is limited to 999 I assume the heater will throw an error if the set temperature is not reached after approx. 120 min. Is that correct? Is there a way to disable the temerature check?

        1 Reply Last reply Reply Quote 0
        • dc42undefined
          dc42 administrators
          last edited by dc42

          The A parameter is approximately the expected eventual temperature rise when the heater is run at full power. The C parameter is the time for the temperature to fall by 63% of the final temperature drop when the heater is turned off. The time that the heater takes to raise the temperature by 63% of the eventual temperature rise should be approximately the same.

          Using those definitions, do you think your chamber heater has a time constant (C parameter) greater than 999 seconds?

          There is no timeout during heating, except when tuning.

          HTH David

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          1 Reply Last reply Reply Quote 0
          • 3dwareundefined
            3dware
            last edited by

            Thank you for the quick reply. We applied the parameter and will see how it works in an longtime test.. Since the room temperature can only been held to the desired value whie the bed heater is running in some cases the value will not be reached.