    Board 3 not found
    Firmware installation
    772
      A Former User
      Usually the length and quality of wiring is negligible in a typical setup, but maybe you can elaborate a little on that just for good measure?
      But more importantly the jumpers are either wrong not clearly illustrated. Board 2 and 3 should not have jumpers behind the RJ11 plugs.
      Important! Just behind the RJ11 connectors is a 4-pin terminal block. On the last board in the CAN chain only (the one with a cable in only one of the RJ11 connectors), two jumpers must be fitted in that block to terminate the CAN bus. Jumpers must not be fitted in expansion boards that are not at the end of the CAN bus.
      https://duet3d.dozuki.com/Wiki/Duet_3_Expansion_Hardware_Overview#Section_CAN
      ahwitmerundefined 2 Replies Last reply Reply Quote 0
      • ahwitmerundefined
        ahwitmer @A Former User
        @bearer
        Thank you for your reply
        Well you are right with regards to the jumper settings, however I did not find any permutation of jumper settings that did work.
        as well as
        gives the same problems
        Error: M115: Response timeout: CAN addr 3, req type 6024, RID=..<LF>ok<LF> on Yat
        and
        warning: lost connection to Duet (Timeout while waiting for transfer ready pin) on RPI interface.
        CoreXYUV
        • ahwitmerundefined
          @bearer I'm using 50 cm ethernet cables between the cards.
          CoreXYUV
            A Former User
            Cables should be fine. Maybe you could wire straight from 6HC motherboard to 3HC expansion board 1 and see if it helps? (I.e. bypass board 2 and board 3, leave the jumper on board 1 in any case)
            Not sure how compatible the different versions are, but maybe its necessary to update the expansion to 3.1.1 before the 6HC motherboard. (You can either try installing the same version on the 6HC motherboard or wait and see if there are any other suggestions like addressing or faulty hardware potentially)
              Your second diagram looks correct to me.
              Your second diagram has the jumpers in the right place, however the board address is set to 4 not 3.
              Are you able to communicate with board 3 at all? Is the red LED on it flashing in sync with the other 3 boards?
              You can send M409 K"boards" to list the boards that have announced themselves to the main board.
              ahwitmerundefined 1 Reply Last reply Reply Quote 0
              • ahwitmerundefined
                ahwitmer @dc42
                @dc42 The led lights between the ethernet connectors are all blinking with the same pace, no difference ever since I switched them on. On board 1 and 2 it shortly stopped while updating.
                I understand what you are saying with the dipswitches, however yesterday, I updated board 1 and 2 successfully (stopping of blinking indicated transfer of firmware)
                Board 3 did not give a reaction at all. This having the dip switches in the shown positions.
                Nevertheless after your message, I changed the position of the dipswitches as indicated below.
                After changing the dipswitches, board 1 is showing version 3.1.1 and to my surprise board 2 is showing an old version 3.0. How can it be... no clue because yesterday it said differently. but let's forget it. Not important.
                I changed the dipswitches as per your message and per sketch below. Updated the expansion board firmware as I did yesterday. Next I used the M115 B0 / B1 / B2 / B3 to see the versions on the boards, the following is shown:
                M115 B0
                FIRMWARE_NAME: RepRapFirmware for Duet 3 MB6HC FIRMWARE_VERSION: 3.1.1 ELECTRONICS: Duet 3 MB6HC v0.6 or 1.0 FIRMWARE_DATE: 2020-05-19b2<LF>ok<LF>
                M115 B1
                Board EXP3HC firmware 3.1.0 (2020-05-15b1)<LF>ok<LF>
                M115 B2
                M115 B3
                Error: M115: Response timeout: CAN addr 3, req type 6024, RID=50<LF>ok<LF>
                M115 B4
                Error: M115: Response timeout: CAN addr 4, req type 6024, RID=51<LF>ok<LF>
                M115 B5
                Error: M115: Response timeout: CAN addr 5, req type 6024, RID=52<LF>ok<LF>
                Then I Used the M409 k"boards" as per your message. The following is returned:
                M409 K"boards"
                {"key":"boards","flags":"","result":
                "canAddress":0,
                "firmwareDate":"2020-05-19b2",
                "firmwareFileName":"Duet3Firmware_MB6HC.bin",
                "firmwareName":"RepRapFirmware for Duet 3 MB6HC",
                "firmwareVersion":"3.1.1",
                "iapFileNameSBC":"Duet3_SBCiap_MB6HC.bin",
                "iapFileNameSD":"Duet3_SDiap_MB6HC.bin",
                "mcuTemp":{"current":37.4,"max":37.5,"min":23.5},
                "name":"Duet 3 MB6HC",
                "shortName":"MB6HC",
                "uniqueId":"08DJM-956L2-G43S4-6J1D8-3SJ6M-9B6GG",
                "v12":{"current":11.4,"max":12.0,"min":0.1},
                "vIn":{"current":12.1,"max":12.7,"min":0.1}
                "canAddress":1,
                "firmwareFileName":"Duet3Firmware_EXP3HC.bin",
                "firmwareVersion":"3.1.0 (2020-05-15b1)",
                "mcuTemp":{"current":0,"max":0,"min":0},
                "shortName":"EXP3HC",
                "state":"running",
                "v12":{"current":0,"max":0,"min":0},
                "vIn":{"current":0,"max":0,"min":0}},
                {"canAddress":2,
                "state":"running","v12":{"current":0,"max":0,"min":0},
                {"canAddress":126,
                "state":"running",
                "vIn":{"current":0,"max":0,"min":0}}]
                <LF>ok<LF>
                No clue what happened.
                I used the following configuration:
                CoreXYUV
                  A Former User @ahwitmer
                  @ahwitmer said in Board 3 not found:
                  canAddress":126
                  seems to match https://duet3d.dozuki.com/Wiki/CAN_connection#Section_EXP3HC
                  it'd be easier to follow if you addressed the boards with the same adress as on the labels. in any case 126 / boards 1 needs to be changed methinks.
                  • ahwitmerundefined
                    ahwitmer
                    Thanks for the reference! Allthough I have been reading and searching a lot, I have not seen this document before. Thanks!
                    CoreXYUV
                    • ahwitmerundefined
                      @bearer
                      As I understand the guide, the 3HC expansion boards are set via the dipswitches only. The 126 you get when all switches are off. The other type of boards are factory set to an address, which you can change by sending M952 command.
                      So in my case I have chosen 1,2 and 3 as adress.
                      The system does not seem to be stable, suddenly @ startup I get many errors and after that all my tools are gone and stay gone, this although the .g files are present at the duet.....
                      Back to the drawing board
                      34b7647b-e47c-4c28-a960-8499a54de8d2-image.png M409 K"boards"
                      {"canAddress":0,
                      "mcuTemp":{"current":35.8,"max":35.8,"min":31.6},
                      "v12":{"current":11.4,"max":11.7,"min":0.1},"vIn":{"current":12.1,"max":12.4,"min":0.1}},
                      {"canAddress":1,
                      "state":"running",
                      {"canAddress":2,"
                      "state":"running",
                      {"canAddress":3,
                      "shortName":"EXP3HC","state":"running",
                      "vIn":{"current":0,"max":0,"min":0}}]}
                      <LF>ok<LF>
                      CoreXYUV
                        A Former User
                        if you changed the address to make it clearer, you'd also need to change the config?
                        the pins are references as CanAddress.PinName, so changing the address you need to change the pin references.
                          A Former User
                          you can execute the config file to see any errors; M98 P"config.g"
                          • ahwitmerundefined
                            @bearer I preferred to keep to the convention of card numbering because it is configured like that in my config file to keep the changes limited.
                            CoreXYUV
                            • ahwitmerundefined
                              @bearer I will try that one tonight, thanks!
                              CoreXYUV
                              • ahwitmerundefined
                                ahwitmer
                                @bearer @dc42
                                For some reason the system doesn't seem to be stable.
                                The reponses of the system are not consistent.
                                M98 P"config.g" does some times a lot and some times nothing at all
                                Yesterday, I had no tools, tonight suddenly they are back
                                The command M98 etc resulted in
                                M98 P"config.g"
                                <LF>
                                RepRapFirmware for Duet 3 MB6HC Version 3.1.1 dated 2020-05-19b2 <LF>
                                Ethernet is disabled. <LF>
                                RepRapFirmware for Duet 3 MB6HC is up and running. <LF>
                                Connection to Linux established! <LF>
                                Warning: VIN under-voltage event (0.9V)Lost connection to Linux <LF>
                                Connection to Linux established!<LF>Lost connection to Linux <LF>
                                Warning: 12V under-voltage ok<LF>
                                After that, I only get <LF>ok<LF> restarting sometimes gives the first message sometimes only the last result.
                                The interface is showing at startup: Duet connected
                                then after M98 P"config,g" I get on my interface:
                                Error M574 pin "io1.in" is not free
                                Error M574 pin "io0.in" is not free
                                Warning M307: heater 0 appears to be overpowered, if left at full power its temperature is predicted to reach 365C
                                the M568 command is not longer needed
                                then the last two messages disapear automatically
                                heater o is switched off according to the interface
                                the first message I get from the M98 command, mentions vin undervoltage, could that be the cause of the inconsistent behavior?
                                The RPI has its own power
                                the MB runs on 12V
                                the expansion boards run on 24V
                                CoreXYUV
                                • ahwitmerundefined
                                  ahwitmer
                                  @bearer @dc42
                                  Using the M409 K"boards" results in the info below.
                                  The thing that surprises me that the MB shows values for V12 and Vin
                                  The expansion boards show 0 values. Is that potentially the problem?
                                  M409 K"boards"
                                  {"key":"boards","flags":"","result":[
                                  {"canAddress":0,
                                  "mcuTemp":{"current":36.2,"max":37.0,"min":32.3},
                                  "v12":{"current":11.4,"max":11.9,"min":0.1},
                                  "vIn":{"current":12.1,"max":12.6,"min":0.1}},
                                  {"canAddress":1,
                                  {"canAddress":2,"firmwareFileNa
                                  "state":"running",
                                  {"canAddress":3,"
                                  "state":"running",
                                  CoreXYUV
                                    A Former User
                                    (i'm out of my depth, a long time ago; maybe @Phaedrux or the other wizards can shed some light on it)
                                    ((d'oh, yes, please relabel diagram instead of changing addresses))
                                      Currently, it's normal for VIN and V12 to show zero for the expansion boards in M409, because the expansion boards don't report the voltages. I plan to fix this before firmware 3.2 release. Meanwhile, you can see the actual voltages using M122, for example M122 B1 to show the voltages for the board with CAN address 1.
                                      Feel free to set the CAN addresses 1, 2, 3 of your expansion boards any way you like, but in future please re-label the boards in your diagrams "Expansion board 1" for the board with CAN address 1, similarly for boards 2 and 3. Talking about "Expansion board 1" when that board has CAN address 2 or 3 is very confusing.
                                      Those messages indicate that you have a problem with VIN power to the main board.
                                      • ahwitmerundefined
                                        ahwitmer @dc42
                                        @dc42 I originally misunderstood the settings of the dip-switches. Didn't realize it was a binary setting. Thanks to remarks made by Bearer I got the place where I could find the functioning. Hence the setting of position of the dip-switches did not correspond to the board numbering. Sorry for the confusion.
                                        CoreXYUV
                                          That looks good. Did you sort out the VIN power issue?
                                          • ahwitmerundefined
                                            ahwitmer @dc42
                                            @dc42 I have not been able to reproduce the dialog at all.
                                            I got this result by using M98 P"config.g"
                                            Only answer I get back via the terminal screen is:
                                            ok<LF>
                                            On the screen I get a message M307 on heater 0 being overpowered (this is the bed), although the heater is swiched off.
                                            CoreXYUV