    Connect a water flow sensor --> will M591 P7 work in Laser mode?

    Scheduled Pinned Locked Moved Solved
    Laser Cutters
    4
    50
    2.2k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • paulg4hundefined
      paulg4h @cosmowave
      last edited by

      @cosmowave this will not work because as more readings the sum gets as less the chance that the avg value comes close to the low value.

      There should be something like a array with 10 values which are overwritten every 10 readings to get an reliable value.

      cosmowaveundefined 1 Reply Last reply Reply Quote 0
      • cosmowaveundefined
        cosmowave @paulg4h
        last edited by

        @paulg4h Yes... you need more or less 10 readings of the low value. But is your flow detection that much time critical?

        Mankati FSXT+, DeltaTowerV2, E3D MS/TC

        paulg4hundefined 1 Reply Last reply Reply Quote 0
        • paulg4hundefined
          paulg4h @cosmowave
          last edited by

          @cosmowave You add the current value to the sum variable all the time --> so after 100 readings you got the sum of them and calculate the average by the dvision of 100 reading, so the avg value gets higher and higher.

          cosmowaveundefined 1 Reply Last reply Reply Quote 0
          • cosmowaveundefined
            cosmowave @paulg4h
            last edited by

            @paulg4h uups, there is an error in my code!
            you need to reset the counter to 0 in the else construct!

            Mankati FSXT+, DeltaTowerV2, E3D MS/TC

            cosmowaveundefined 1 Reply Last reply Reply Quote 0
            • cosmowaveundefined
              cosmowave @cosmowave
              last edited by

               var.counter
               var.sum
               
              if var.counter < 10
              	set var.sum = {var.sum + "newValue"}
              	set var.counter = var.counter + 1
               
              else 
                      var.counter = 0
              	if {var.sum / var.counter} < 20
              		NO FLOW
              

              Mankati FSXT+, DeltaTowerV2, E3D MS/TC

              cosmowaveundefined 1 Reply Last reply Reply Quote 0
              • cosmowaveundefined
                cosmowave @cosmowave
                last edited by

                @cosmowave once again an error
                The reset should be after the if where you calculate the average!

                Mankati FSXT+, DeltaTowerV2, E3D MS/TC

                cosmowaveundefined 1 Reply Last reply Reply Quote 0
                • cosmowaveundefined
                  cosmowave @cosmowave
                  last edited by

                  var.counter
                  var.sum
                  
                  if var.counter < 10
                     set var.sum = {var.sum + "newValue"}
                     set var.counter = var.counter + 1
                  
                  else 
                     if {var.sum / var.counter} < 20
                     	NO FLOW
                     var.counter = 0
                  

                  Mankati FSXT+, DeltaTowerV2, E3D MS/TC

                  paulg4hundefined 1 Reply Last reply Reply Quote 0
                  • paulg4hundefined
                    paulg4h @cosmowave
                    last edited by paulg4h

                    @cosmowave there is still an issue, the sum value will get higher and higher, so when the flow sensor will return only zero after an hour it takes several runs to get the avg town to trigger the alarm.

                    var val1 = 0
                    var val2 = 0
                    var val3 = 0
                    var val4 = 0
                    var val5 = 0
                    var max= 5
                    var avg = 0
                    var pos = 1
                    var initDone = 0
                    while true
                      G4 S2 ; run every two seconds
                      if pos = 1
                        set val1 = fans[0].rpm
                      if pos = 2
                        set val2 = fans[0].rpm
                      if pos = 3
                        set val3 = fans[0].rpm
                      if pos = 4
                        set val4 = fans[0].rpm
                      if pos = 5
                        set val5 = fans[0].rpm
                     set  pos = pos +1 
                      if pos > max
                        set pos = 1
                        if initDone = 0
                          set initDone = 1
                      set avg = {val1 + val2 + val3 + val4 + val5} / max
                    
                      if initDone > 0
                        if avg < 50
                           M118 S"no water flow"
                           M25
                    

                    This code is not tested jet and far from nice...

                    cosmowaveundefined 1 Reply Last reply Reply Quote 0
                    • cosmowaveundefined
                      cosmowave @paulg4h
                      last edited by

                      @paulg4h yes, you're right. There is again an error! Soory for that!
                      You have to reset the sum too!

                      var.counter
                      var.sum
                       
                      if var.counter < 10
                         set var.sum = {var.sum + "newValue"}
                         set var.counter = var.counter + 1
                       
                      else 
                         if {var.sum / var.counter} < 20
                         	NO FLOW
                         var.counter = 0
                         var.sum = 0
                      

                      Mankati FSXT+, DeltaTowerV2, E3D MS/TC

                      1 Reply Last reply Reply Quote 0
                      • dc42undefined
                        dc42 administrators @paulg4h
                        last edited by dc42

                        @paulg4h said in Connect a water flow sensor --> will M591 P7 work in Laser mode?:

                        How could I use the rpm more reliable to detect water flow, even in DWC the Sensors Fan RPM are shown and jumps between 0 and something between 190 and 210 all the time.

                        That doesn't sound right. I suspect it is because the RPM is much lower than for a typical fan. If RRF doesn't receive any tacho pulses for a certain period of time, it assumes the fan has stopped and gives a zero reading.

                        I just checked the code: it requires at least 32 tacho pulses over a period not exceeding 3 seconds. It assumes 2 tacho pulses per revolution. So the minimum speed to get a stable reading is 16/3 revs/sec = 320 rpm.

                        I'll make a note to allow a wider range in RRF 3.4.

                        Duet WiFi hardware designer and firmware engineer
                        Please do not ask me for Duet support via PM or email, use the forum
                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                        paulg4hundefined 1 Reply Last reply Reply Quote 1
                        • paulg4hundefined
                          paulg4h @dc42
                          last edited by

                          @dc42 said in Connect a water flow sensor --> will M591 P7 work in Laser mode?:

                          16/3 revs/sec = 320 rpm.

                          Many thank's!

                          cosmowaveundefined 1 Reply Last reply Reply Quote 0
                          • cosmowaveundefined
                            cosmowave @paulg4h
                            last edited by

                            @paulg4h If you can open the sensor, you can try to insert more magnets. Eventually you can reach the desired rpm. But i'm not sure if there is space and if the hall detects proper signal-edges with more magnets...

                            Mankati FSXT+, DeltaTowerV2, E3D MS/TC

                            paulg4hundefined 1 Reply Last reply Reply Quote 0
                            • paulg4hundefined
                              paulg4h @cosmowave
                              last edited by

                              @cosmowave I use your script above with some slightly modification and now it works so far

                              var counter=0
                              var sum=0
                              
                              while true
                                G4 S2
                                if job.duration = null
                                    ; No job ignore sensor reading
                                else
                                    ; Check Water Flow
                                    if var.counter < 10
                                      set var.sum = {var.sum + fans[0].rpm}
                                      set var.counter = var.counter + 1
                                    else 
                                      if {var.sum / var.counter} < 50
                                        ; NO FLOW
                                        var.counter = 0
                                        var.sum = 0
                                        M25
                                        M118 S"No Water flow!" 
                                    
                                    ; Check water temperature
                                    if sensors.analog[0].lastReading > 35
                                       M25
                                       M118 S"Water to hot!"
                              
                              paulg4hundefined 1 Reply Last reply Reply Quote 0
                              • paulg4hundefined
                                paulg4h @paulg4h
                                last edited by paulg4h

                                The Release 3.3 of RRF includes a fix to recognize pulse sensors until 160 rpm instead of 320 rpm minimum
                                https://github.com/Duet3D/RepRapFirmware/wiki/Changelog-RRF-3.x-Beta-&-RC#reprapfirmware-33-post-rc3

                                Many thank's!

                                dc42undefined 2 Replies Last reply Reply Quote 0
                                • dc42undefined
                                  dc42 administrators @paulg4h
                                  last edited by dc42

                                  @paulg4h said in Connect a water flow sensor --> will M591 P7 work in Laser mode?:

                                  The Release 3.3 of RRF includes a fix to recognize pulse sensors until 160 rpm instead of 320 rpm minimum
                                  https://github.com/Duet3D/RepRapFirmware/wiki/Changelog-RRF-3.x-Beta-&-RC#reprapfirmware-33-post-rc3

                                  Many thank's!

                                  @paulg4h You can download preview firmware including that change from https://www.dropbox.com/sh/xfsvscbaab0dtzl/AACCcSeiTNINZL-xbs6IhC4Ja?dl=0. Ignore the .map files.

                                  Duet WiFi hardware designer and firmware engineer
                                  Please do not ask me for Duet support via PM or email, use the forum
                                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                                  1 Reply Last reply Reply Quote 0
                                  • dc42undefined
                                    dc42 administrators @paulg4h
                                    last edited by

                                    @paulg4h is this now working properly for you using firmware 3.3 ?

                                    Duet WiFi hardware designer and firmware engineer
                                    Please do not ask me for Duet support via PM or email, use the forum
                                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                                    paulg4hundefined 1 Reply Last reply Reply Quote 0
                                    • paulg4hundefined
                                      paulg4h @dc42
                                      last edited by

                                      @dc42

                                      Many thank's I updated today and now the RPM of the flow sensor is working perfectly without the variables!

                                      cosmowaveundefined 1 Reply Last reply Reply Quote 0
                                      • cosmowaveundefined
                                        cosmowave @paulg4h
                                        last edited by

                                        @dc42
                                        Is it possible to allow even lower rpm readings? My flowsensor gives 35rpm at minimum...

                                        Mankati FSXT+, DeltaTowerV2, E3D MS/TC

                                        1 Reply Last reply Reply Quote 0