    [3.4b7+7] Chamber Heater faults

    Scheduled Pinned Locked Moved Solved
    Beta Firmware
    3
    11
    547
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • oozeBotundefined
      oozeBot
      last edited by

      Here is the error logged when it faults:

      Error: Heater 0 fault: temperature rising too slowly: expected -0.00°C/sec measured -0.01°C/sec
      
      1 Reply Last reply Reply Quote 1
      • oozeBotundefined oozeBot marked this topic as a question
      • oozeBotundefined
        oozeBot
        last edited by oozeBot

        As an additional test, we adjusted M307 to the following, but it resulted in the same fault.

        M307 H2 B1 C3600 D350 R0.01
        

        The documentation on the M307 parameters are a bit sparse - if anyone knows something we are missing that might resolve this, please speak up. Maybe our understanding of deadtime is inaccurate?

        Stephen6309undefined 1 Reply Last reply Reply Quote 0
        • Stephen6309undefined
          Stephen6309 @oozeBot
          last edited by

          @oozebot D is the dead time;
          https://duet3d.dozuki.com/Wiki/Tuning_the_heater_temperature_control#Section_Setting_the_model_parameters_manually

          1 Reply Last reply Reply Quote 0
          • oozeBotundefined
            oozeBot
            last edited by oozeBot

            When this was first discovered, our testing determined the maximum D value was around 350. On 3.4b7+1, it accepted D1000. I will test this change as soon as an available printer cools down.

            Current M307 settings:

            Heater 2: heating rate 0.010, cooling rate 0.028, dead time 1000.00, max PWM 1.00, mode bang-bang
            

            edit - adjusting the dead time to 1000 appears to have been helpful. I have now adjusted all our printers to the new settings and will continue testing over the next few days.

            1 Reply Last reply Reply Quote 0
            • oozeBotundefined
              oozeBot
              last edited by oozeBot

              Further testing with the following M307 still results in a chamber heater fault in the 3.4 betas. This was never an issue in 3.3. It appears the current algorithm simply won't let the temperature dip negative, which can and does happen when heating a chamber.

              M307 H2 B1 C3600 D1000 R0.01
              Heater 2: heating rate 0.010, cooling rate 0.028, dead time 1000.00, max PWM 1.00, mode bang-bang
              Predicted max temperature rise 36°C
              
              Error: Heater 0 fault: temperature rising too slowly: expected -0.00°C/sec measured -0.01°C/sec
              
              1 Reply Last reply Reply Quote 0
              • oozeBotundefined
                oozeBot
                last edited by

                @dc42 - I just dug through the recent RRF code changes and see several (hopefully) related modifications that have been made. I am in hopes the information we've provided helped identify the issue. Can you confirm this was targeted in those changes? Thanks

                dc42undefined 1 Reply Last reply Reply Quote 1
                • dc42undefined
                  dc42 administrators @oozeBot
                  last edited by

                  @oozebot the problem was that prior to the 3.4beta series, if the M307 R parameter was low enough then the heater fault detection didn't work at all. So I've been trying to come up with a solution that works for slow heaters; but it's proving difficult. You may find RRF 3.4b7+4 better, and I hope to make that available later today.

                  Duet WiFi hardware designer and firmware engineer
                  Please do not ask me for Duet support via PM or email, use the forum
                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                  oozeBotundefined 1 Reply Last reply Reply Quote 2
                  • oozeBotundefined
                    oozeBot @dc42
                    last edited by

                    @dc42 Thank you. We'll definitely test it right away and report back with our findings.

                    1 Reply Last reply Reply Quote 1
                    • oozeBotundefined
                      oozeBot
                      last edited by oozeBot

                      After spending the weekend on this, I believe we may have been able to stabilize the tuning to stop the heater faults by further raising the C value to 200x the actual time it takes to fully heat our chambers. As mentioned, this was never an issue prior to the 3.4 betas. We understand a defect was addressed to better protect against heater faults, but it feels way to restrictive for chamber heaters.

                      We will continue to test and provide results. If our current settings continue to provide success, I guess we'll consider this resolved, but it does not feel as if we are properly setting the values for how our heaters work. Instead, it feels as if we are working around a software issue.

                      oozeBotundefined 1 Reply Last reply Reply Quote 2
                      • oozeBotundefined
                        oozeBot @oozeBot
                        last edited by

                        @dc42 - After several more days of testing, we are going to mark this as solved, however something still feels wrong as the only way to reliably stop the heater faults was to raise the C value to 200x the actual time it takes to fully heat our chambers. That isn't how the documentation describes the C parameter, but we'll run with it unless we're told additional changes are made in the firmware.

                        1 Reply Last reply Reply Quote 2
                        • oozeBotundefined oozeBot has marked this topic as solved
                        • Phaedruxundefined Phaedrux has marked this topic as unsolved
                        • oozeBotundefined oozeBot has marked this topic as solved
                        • jay_s_ukundefined jay_s_uk referenced this topic
                        • oozeBotundefined oozeBot referenced this topic
                        • oozeBotundefined oozeBot referenced this topic
                        • jay_s_ukundefined jay_s_uk referenced this topic
                        • First post
                          Last post
                        Unless otherwise noted, all forum content is licensed under CC-BY-SA