• Tags
  • Documentation
  • Order
  • Register
  • Login
Duet3D Logo Duet3D
  • Tags
  • Documentation
  • Order
  • Register
  • Login

Thermocouple wiring which already includes amplification circuit

Scheduled Pinned Locked Moved
Duet Hardware and wiring
3
20
924
Loading More Posts
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • undefined
    VirtualBrown @dc42
    last edited by 10 May 2022, 22:17

    @dc42 thanks, plug into the duet thermocouple board, or straight into the main board?

    undefined 1 Reply Last reply 11 May 2022, 05:44 Reply Quote 0
    • undefined
      dc42 administrators @VirtualBrown
      last edited by 11 May 2022, 05:44

      @virtualbrown said in Thermocouple wiring which already includes amplification circuit:

      @dc42 thanks, plug into the duet thermocouple board, or straight into the main board?

      Straight into the main board.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      undefined 1 Reply Last reply 23 May 2022, 13:03 Reply Quote 0
      • undefined
        VirtualBrown @dc42
        last edited by 23 May 2022, 13:03

        @dc42 So, I've finally got (almost) everything installed and wired up. I went for a Duet 3 Mini, not a Duet 2 in the end. I have the amplified thermocouple plugged into TEMP1 on the board and am noticing the hot end temp reading in the web interface is reading about 90 DegC at room temperature. That is from being configured in the reprap configurator with the default values and the same as the bed thermistor (which is giving accurate readings).

        First of all is that the correct method of wiring? And is there a method you'd suggest or a starting point to tune in the sensor to give accurate readings?

        undefined 1 Reply Last reply 23 May 2022, 13:16 Reply Quote 0
        • undefined
          dc42 administrators @VirtualBrown
          last edited by 23 May 2022, 13:16

          @virtualbrown you need to configure it as a linear analog sensor instead. Assuming that it's sensor 1, use this command instead of the existing M308 S1 command in config.g:

          M308 S1 Y"linear-analog" Bxxx Cyyy

          You will need to replace xxx and yyy by suitable numbers that depend on the amplifier characteristics, and calibrate them by subjecting the thermocouple to two known temperatures, for example ice water at 0C and boiling water at 100C.

          If you can take a higher resolution photo of the components so that I can read the numbers on the resistors and preferably also the marking on the chip, then I may be able to work out one or both of those values.

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          undefined 2 Replies Last reply 24 May 2022, 12:40 Reply Quote 0
          • undefined
            VirtualBrown @dc42
            last edited by 24 May 2022, 12:40

            @dc42 thanks, I’ll try that later today. I have managed to fish that circuit board out, here are some photos.

            alt text

            alt text

            alt text

            alt text

            alt text

            So looking at the underside of the daughter board the thermocouple is the three left most pins on the 5 pin connector. The left most pin is a bit of a mystery to me as I loose it’s path here. That’s the white braided wire in the 4th photo.

            Hopefully they’ve uploaded in a high enough res to see all the marking and tracks. I’ve included a pic of the main board so you can see if there’s anything of interest on the way to the processor. The thermocouple pins are the second pair down the column of the 20 pin connector in the bottom right.

            Let me know if there’s anything else which could help.

            1 Reply Last reply Reply Quote 0
            • undefined
              VirtualBrown @dc42
              last edited by 24 May 2022, 17:35

              @dc42 reading about the chip which seems to be an Analog Devices AD8495, I’m probably missing the 5 V supply to this daughter board which would explain the 2 ways on the ribbon cable which are connected together on the old motherboard before I loose track of them. Where on the Duet 3 Mini would be best to take a 5V supply?

              I was planning on adding some LEDs in the future so would like to leave the NEOPIXEL socket free.

              undefined 1 Reply Last reply 24 May 2022, 21:10 Reply Quote 0
              • undefined
                Phaedrux Moderator
                last edited by 24 May 2022, 20:33

                Perhaps the paneldue connector if you're not using one.

                https://docs.duet3d.com/duet_boards/duet_3_mini_5_plus/duet_3_mini_5+_wiring_v0.5_v1.0_v1.01.png

                Z-Bot CoreXY Build | Thingiverse Profile

                1 Reply Last reply Reply Quote 0
                • undefined
                  dc42 administrators @VirtualBrown
                  last edited by 24 May 2022, 21:10

                  @virtualbrown all the 5-pin IO connectors on the Duet 3 Mini have 5V.

                  Duet WiFi hardware designer and firmware engineer
                  Please do not ask me for Duet support via PM or email, use the forum
                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                  undefined 2 Replies Last reply 25 May 2022, 18:06 Reply Quote 0
                  • undefined
                    VirtualBrown @dc42
                    last edited by 25 May 2022, 18:06

                    @dc42 thanks, any idea on those values for Bxxx and Cyyy?

                    1 Reply Last reply Reply Quote 0
                    • undefined
                      VirtualBrown @dc42
                      last edited by 25 May 2022, 18:59

                      @dc42 i get an error: VSSA fault when connecting that wire to 5 V so that much not be correct.

                      Struggling to work it out as the extruder temperature reading doesn’t respond to heat in the extruder, so something must be missing.

                      undefined 1 Reply Last reply 25 May 2022, 20:04 Reply Quote 0
                      • undefined
                        dc42 administrators @VirtualBrown
                        last edited by 25 May 2022, 20:04

                        @virtualbrown said in Thermocouple wiring which already includes amplification circuit:

                        @dc42 i get an error: VSSA fault when connecting that wire to 5 V so that much not be correct.

                        That error suggests that you have connected the VSSA pin of the TEMP connector you are using to 5V.

                        Duet WiFi hardware designer and firmware engineer
                        Please do not ask me for Duet support via PM or email, use the forum
                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                        undefined 1 Reply Last reply 25 May 2022, 20:13 Reply Quote 0
                        • undefined
                          VirtualBrown @dc42
                          last edited by VirtualBrown 25 May 2022, 20:13

                          @dc42 so there are 4 ways of the ribbon cable used for the temperature sensor. 2 of which are connected together, so we have 3 discrete connections. Any idea which is which? Do the photos above shed any light?

                          undefined 1 Reply Last reply 25 May 2022, 20:18 Reply Quote 0
                          • undefined
                            dc42 administrators @VirtualBrown
                            last edited by dc42 25 May 2022, 20:18

                            @virtualbrown from the amplifier there will be a +5V connection, a ground connection, and an output connection. Connect the 5V and ground connections to 5V and GND respectively on an IO_ connector. Connect the amplifier output to the THERM pin (not the VSSA pin) of a temperature input connector.

                            Duet WiFi hardware designer and firmware engineer
                            Please do not ask me for Duet support via PM or email, use the forum
                            http://www.escher3d.com, https://miscsolutions.wordpress.com

                            undefined 1 Reply Last reply 25 May 2022, 20:25 Reply Quote 0
                            • undefined
                              dc42 administrators @dc42
                              last edited by 25 May 2022, 20:25

                              PS - I think the correct parameters for the M308 command to configure the linear analog sensor are 0 for the lower limit and 330 for the upper limit.

                              Duet WiFi hardware designer and firmware engineer
                              Please do not ask me for Duet support via PM or email, use the forum
                              http://www.escher3d.com, https://miscsolutions.wordpress.com

                              undefined 1 Reply Last reply 25 May 2022, 20:56 Reply Quote 0
                              • undefined
                                VirtualBrown @dc42
                                last edited by 25 May 2022, 20:56

                                @dc42 she lives!!

                                Now I just need to fine tune those B and C values. I’ve got a multimeter thermocouple attached to the heater block. Is there a methodical approach to adjusting each value?

                                Its currently saying 19 degC when the multimeter says 33.

                                undefined 1 Reply Last reply 26 May 2022, 05:46 Reply Quote 0
                                • undefined
                                  dc42 administrators @VirtualBrown
                                  last edited by dc42 26 May 2022, 05:46

                                  @virtualbrown the B value affects the reading when the thermocouple temperature is close to zero, and the C value when it is much higher. So I suggest you adjust B to get a good reading at room temperature, then adjust C to get a good reading at printing temperature. You may need to repeat this a few times.

                                  Alternatively, use your multimeter to measure the output of the amplifier at room temperature and at printing temperature. Then extrapolate those values to calculate the temperature at zero output and the temperature at 3.3V output.

                                  Duet WiFi hardware designer and firmware engineer
                                  Please do not ask me for Duet support via PM or email, use the forum
                                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                                  undefined 1 Reply Last reply 26 May 2022, 09:33 Reply Quote 0
                                  • undefined
                                    VirtualBrown @dc42
                                    last edited by 26 May 2022, 09:33

                                    @dc42 I found B0 and C500 work well.

                                    Thank very much for all your help on this!

                                    1 Reply Last reply Reply Quote 0
                                    • NeoDueundefined NeoDue referenced this topic 15 May 2023, 01:30
                                    • First post
                                      Last post
                                    Unless otherwise noted, all forum content is licensed under CC-BY-SA