    for debug issues i suggest to split (if possible)
    heater issues from termistor issues

    by the way is there any theoretical or practical chance that smatreffector (broken or crazy) is causing heater faults?

    undefined 1 Reply Last reply 8 Jul 2018, 11:20 Reply Quote 0
    • undefined
      dc42 administrators @c310
      last edited by 8 Jul 2018, 11:20

      @c310 said in Heater Fault debug facility:

      for debug issues i suggest to split (if possible)
      heater issues from termistor issues

      The firmware can't always tell the difference. For example, if the temperature rises too slowly when heating is commanded, it could be caused by either a thermistor fault or a heater fault.

      by the way is there any theoretical or practical chance that smatreffector (broken or crazy) is causing heater faults?

      Yes, if the heater or thermistor connector isn't properly soldered.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      1 Reply Last reply Reply Quote 0
      • undefined
        Barracuda72
        last edited by 8 Jul 2018, 11:27

        1. What would help a lot would be a screenshot of the moment when the error occurs. For example, if the temperature drops by 30° within a second in the event of an error, it cannot be a Heater error, but must be a problem with the thermistor. because NO heatbed can drop 30° in that time. If theres a heater prob, the temp would fall more slowly.

        2. a menue point in the right mouse menue on the bed and tool heater to reset it would be nice.

        1 Reply Last reply Reply Quote 0
        • undefined
          c310
          last edited by c310 7 Sept 2018, 10:39 9 Jul 2018, 10:37

          in last case fault was issued by high temperature i think. pt100 is up to 500 degrees
          but RRF M143 command limits temp to 262 degrees and i was trying to print at 290.

          when tool was hot, and no print job - no errors so far. once i start print - heater fault immediately.
          i think it is RRF bug. it should not allow 290 deg 🙂 in such a config.

          to find the issue i removed all cables from the duet board, and connected heater and PT100 directly without heatsink ... took me 2 hrs to find 🙂

          i have added that to wiki on heater fault troubleshooting

          1 Reply Last reply Reply Quote 0
          • undefined
            r3cvr
            last edited by 9 Jul 2018, 18:25

            With default settings, I was getting a heater fault whenever the model fan came on, as it would cause a dip in extruder temperature until the PID caught up. Had to greatly relax the fault detection. Should detect on temperature direction instead of anomaly from set temp?

            undefined undefined 2 Replies Last reply 10 Jul 2018, 07:15 Reply Quote 0
            • undefined
              dc42 administrators @r3cvr
              last edited by 10 Jul 2018, 07:15

              @r3cvr said in Heater Fault debug facility:

              With default settings, I was getting a heater fault whenever the model fan came on, as it would cause a dip in extruder temperature until the PID caught up. Had to greatly relax the fault detection. Should detect on temperature direction instead of anomaly from set temp?

              A falling temperature may be caused by the heater or the thermistor falling out of the heater block. Either could cause a fire.

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              undefined 1 Reply Last reply 11 Jul 2018, 02:34 Reply Quote 1
              • undefined
                dragonn @r3cvr
                last edited by 10 Jul 2018, 07:53

                @r3cvr and what is wrong with that? One step of setting up a new printer is always do a PID tune.

                1 Reply Last reply Reply Quote 0
                • undefined
                  r3cvr @dc42
                  last edited by 11 Jul 2018, 02:34

                  @dc42 said in Heater Fault debug facility:

                  A falling temperature may be caused by the heater or the thermistor falling out of the heater block. Either could cause a fire.

                  But false positives lead to effectively disabling the feature?

                  Is there any way to measure the resistance/power consumption of the heater? Could try and use the resistance as a secondary temp measurement and set thresholds for disabling. I'm assuming most heaters have some positive coefficient of resistance.

                  @dragonn said in Heater Fault debug facility:

                  @r3cvr and what is wrong with that? One step of setting up a new printer is always do a PID tune.

                  Print fails with no extrusion after heater fault shuts down heater. That's how my first dozen or so print attempts on DuetWifi went. I actually have several PID tunes, done at different model fan settings. No surprise it comes up with different parameters. Doesn't help this issue that much.

                  undefined undefined 2 Replies Last reply 11 Jul 2018, 05:48 Reply Quote 0
                  • undefined
                    dragonn @r3cvr
                    last edited by 11 Jul 2018, 05:48

                    @r3cvr They are no "false positives" when dealing with "thermal runaway". If it triggers then is something wrong with you hardware setup. It can by that you part cooling fan is to strong, it can be that you part cooling tunnel is wrong and blows on the heater block.

                    First of all, I suggest isolating you block, even warping it with kapton tape helps much. And E3D silicon socks are just amazing.

                    Don't blame software for problems with you hardware. 99% of users don't have any problems with current thermal runaway implementation in DuetWifi.

                    1 Reply Last reply Reply Quote 0
                    • undefined
                      dc42 administrators @r3cvr
                      last edited by 11 Jul 2018, 15:31

                      @r3cvr said in Heater Fault debug facility:

                      Is there any way to measure the resistance/power consumption of the heater? Could try and use the resistance as a secondary temp measurement and set thresholds for disabling. I'm assuming most heaters have some positive coefficient of resistance.

                      Heaters usually use nichrome wire, which has a very low temperature coefficient of resistance, making it hard to use the element as a temperature sensor.

                      Duet WiFi hardware designer and firmware engineer
                      Please do not ask me for Duet support via PM or email, use the forum
                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                      1 Reply Last reply Reply Quote 0
                      13 out of 13
                      • First post
                        13/13
                        Last post
                      Unless otherwise noted, all forum content is licensed under CC-BY-SA