    Auto Delta Calibration Odd Behavior
    2.1k
      dc42 administrators @bricor
      @bricor said in Auto Delta Calibration Odd Behavior:
      Calibrated 7 factors using 7 points, deviation before 0.249 after 1.257
      I agree, that's very odd behaviour! Auto calibration is saying that it made matters worse.
      Please restart the Duet, connect a PC running Pronterface/YAT/etc. via USB, send M111 S1 P4 to enable Move debugging, then run auto calibration. Report the debug output from the PC here.
      • bricorundefined
        bricor
        I'll setup terminal and get back to you.
        I deleted config-overide rebooted and ran auto calibrate again
        This is the result
        Calibrated 7 factors using 7 points, deviation before 1.030 after nan
        One more tidbit, I was successful performing multiple Auto Calibrations using a BLTouch clone. I stopped using it since it had inconsistent results, (thats why I bought the DUET IR)
        I believe I was on 2.02RC2 but not sure.
          I have one other report of auto calibration producing 'nan' values. I believe these are generated when one or more probe points are not reachable using the current M665 parameters (even when one set of arms becomes horizontal), typically because the delta radius has been set incorrectly, or simply because when the bed.g file was generated, the probing radius was set too high (taking account of any XY offset of the Z probe). The debug data may confirm that.
          • bricorundefined
            bricor
            When you said ". Report the debug output from the PC here" is that from terminal?
            YAT is not displaying much.
            Debugging enabled for modules: Move(4)<LF>Debugging disabled for modules: Platform(0) Network(1) Webserver(2) GCodes(3) Heat(5) DDA(6) Roland(7) Scanner(8) PrintMonitor(9) Storage(10) PortControl(11) DuetExpansion(12) FilamentSensors(13) WiFi(14) Display(15)<LF>ok<LF>RepRapFirmware for Duet 2 WiFi/Ethernet Version 2.02RC4(RTOS) dated 2018-11-18b5<LF><LF>Executing config.g...HTTP is enabled on port 80<LF>FTP is disabled<LF>TELNET is disabled<LF>Warning: Macro file config-override.g not found.<LF><LF>Done!<LF>RepRapFirmware for Duet 2 WiFi/Ethernet is up and running.<LF>WiFi module started<LF>WiFi module is conne
            I've been successful with the Delta Parameters that I've been using for some time. They deviate only slightly from manual calibration.
            I tried a new bed.g probing set using 80mm probing radius. same result.
            The IR Board is positioned Y-21 (21mm In front of the nozzle, with z tower to the rear). (hopefully I have that correct)
              When you run auto calibration, it should produced a lot more output.
              • bricorundefined
                bricor
                is there a parameter setting in YAT?
                I've tried multiple times same result.
                • bricorundefined
                  bricor
                  I swapped IR boards (Since I don't know what else to try and I have a spare), same results.
                  I did manage to get the diag info using Pronterface
                  Connecting...
                  Printer is now online.
                  M111 S1 P4
                  SENDING:M111 S1 P4
                  Z probe offsets: -1.484 -0.935 -1.135 -0.586 -0.154 -0.354 0.486, mean -0.595, deviation from mean 0.612
                  Stops X0.000 Y0.000 Z0.000 height 316.200 diagonal 268.000 radius 138.000 xcorr 0.00 ycorr 0.00 zcorr 0.00 xtilt 0.000% ytilt 0.000%
                  Derivative matrix
                  0.0609 0.0609 0.8782 0.2582 0.0758 -0.0758 -1.0797
                  0.0686 0.7233 0.2080 0.4208 -0.0460 -0.1226 -1.1212
                  0.7234 0.0686 0.2080 0.4208 0.1226 0.0460 -1.1212
                  0.1587 0.1587 0.6825 0.4700 0.1002 -0.1002 -1.1347
                  0.1665 0.5013 0.3320 0.5574 -0.0318 -0.0898 -1.1556
                  0.5014 0.1665 0.3320 0.5575 0.0898 0.0318 -1.1556
                  0.2726 0.2726 0.4548 0.5849 0.0537 -0.0536 -1.1627
                  Normal matrix
                  0.9104 0.3694 0.6723 0.9555 0.1605 -0.0093 -2.2227 1.1394
                  0.3694 0.9102 0.6722 0.9553 0.0093 -0.1604 -2.2224 0.9413
                  0.6723 0.6722 1.7508 1.3588 0.1946 -0.1946 -3.4851 2.0816
                  0.9555 0.9553 1.3588 1.6054 0.1627 -0.1626 -3.7242 1.5288
                  0.1605 0.0093 0.1946 0.1627 0.0449 -0.0017 -0.4110 0.2683
                  -0.0093 -0.1604 -0.1946 -0.1626 -0.0017 0.0449 0.4108 -0.2102
                  -2.2227 -2.2224 -3.4851 -3.7242 -0.4110 0.4108 8.9900 -4.6103
                  Solved matrix
                  -2.2227 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 3316.2751
                  0.0000 -0.5408 0.0000 0.0000 0.0000 0.0000 0.0000 806.0934
                  0.0000 0.0000 0.6967 0.0000 0.0000 0.0000 0.0000 -1038.0209
                  0.0000 0.0000 0.0000 0.0510 0.0000 0.0000 0.0000 -19.4663
                  0.0000 0.0000 0.0000 0.0000 0.0019 0.0000 0.0000 -0.0262
                  0.0000 0.0000 0.0000 0.0000 0.0000 0.0015 0.0000 0.0314
                  0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 -0.0001
                  Solution: -1491.9964 -1490.4760 -1489.9205 -381.8478 -13.8789 21.5039 -1475.2585
                  Residuals: 0.0000 0.0000 0.0000 -0.0000 -0.0000 -0.0000 0.0000
                  Expected probe error: -2425.4219 -2439.0444 -2440.5215 -2440.8616 -2443.4946 -2443.7583 -2444.4780
                  Derivative matrix
                  -0.1685 -0.2423 1.4087 0.2783 -0.2399 0.3497 0.9692
                  0.1227 0.9259 -0.0500 -0.0684 -0.0488 0.0836 1.0065
                  0.8765 0.1062 0.0171 -0.0848 -0.0232 0.0336 1.0089
                  0.0531 0.0055 0.9418 -0.0299 0.0421 -0.0043 1.0028
                  0.2051 0.5981 0.1959 -0.1746 -0.0110 -0.0555 1.0175
                  0.5792 0.1904 0.2301 -0.1782 0.0708 0.0018 1.0175
                  0.2802 0.2667 0.4523 -0.1825 0.0793 -0.0757 1.0187
                  Normal matrix
                  1.2705 0.5555 0.1217 -0.3214 0.0773 -0.0510 1.9811 4760.7002
                  0.5555 1.3925 -0.0991 -0.3269 0.0388 -0.0568 1.8837 4522.1376
                  0.1217 -0.0991 3.1700 0.2081 -0.2462 0.4403 3.1708 7781.6607
                  -0.3214 -0.3269 0.2081 0.1858 -0.0879 0.1121 -0.4595 -1079.9139
                  0.0773 0.0388 -0.2462 -0.0879 0.0737 -0.0942 -0.1211 -314.5505
                  -0.0510 -0.0568 0.4403 0.1121 -0.0942 0.1393 0.3210 807.4441
                  1.9811 1.8837 3.1708 -0.4595 -0.1211 0.3210 7.0841 17178.3176
                  Solved matrix
                  1.9811 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 2443.6416
                  0.0000 0.8643 0.0000 0.0000 0.0000 0.0000 0.0000 1067.7703
                  0.0000 0.0000 2.7297 0.0000 0.0000 0.0000 0.0000 3374.5799
                  0.0000 0.0000 0.0000 0.0632 0.0000 0.0000 0.0000 5.3086
                  0.0000 0.0000 0.0000 0.0000 0.0047 0.0000 0.0000 0.0108
                  0.0000 0.0000 0.0000 0.0000 0.0000 -0.0074 0.0000 -0.0401
                  0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 -0.0000 -0.0013
                  Solution: 1233.4769 1235.3774 1236.2498 83.9775 2.3079 5.3981 1203.3699
                  Residuals: 2423.9380 2438.1091 2439.3862 2440.2751 2443.3408 2443.4045 2444.9639
                  Expected probe error: nan nan nan nan nan nan nan
                  Stops X-2.756 Y0.664 Z2.092 height nan diagonal -3.889 radius -159.870 xcorr -11.57 ycorr 26.90 zcorr 0.00 xtilt 0.000% ytilt 0.000%
                  Disconnected.
                  • bricorundefined
                    bricor
                    I looked through the diag data and I don't know what I'm looking for and I really can't make sense of any of it.
                    I've tried all that I can, I keep getting erratic results. Really far out numbers.
                    Before:
                    Diagonal 268.000, delta radius 138.000, homed height 316.200, bed radius 110.0, X 0.000°, Y 0.000°, Z 0.000°
                    Calibrated 7 factors using 7 points, deviation before 0.833 after 0.880
                    After:
                    Diagonal 621.396, delta radius 205.951, homed height 316.909, bed radius 110.0, X 5.334°, Y -1.442°, Z 0.000°
                    I'm going to manually calibrate so I can get it back in service.
                      Ah I see the problem. YAT isn't recognising LF as the line ending character, so it's putting everything on one line, and truncating it. In YAT, go to Terminal/Settings/Text Settings and change the EOL sequence to <LF>.
                      • bricorundefined
                        bricor
                        The data looks to be about the same as I posted from Pronterface. You might have missed my posts after the YAT question.
                        M111 S1 P4<CR>
                        ok
                        Z probe offsets: 0.591 1.065 -0.610 1.376 1.659 0.696 2.048, mean 0.975, deviation from mean 0.804
                        Derivative matrix
                        Normal matrix
                        0.9104 0.3694 0.6723 0.9555 0.1605 -0.0093 -2.2227 -1.0699
                        0.3694 0.9102 0.6722 0.9553 0.0093 -0.1604 -2.2224 -2.4886
                        0.6723 0.6722 1.7508 1.3588 0.1946 -0.1946 -3.4851 -3.2662
                        0.9555 0.9553 1.3588 1.6054 0.1627 -0.1626 -3.7242 -3.5016
                        0.1605 0.0093 0.1946 0.1627 0.0449 -0.0017 -0.4110 -0.1787
                        -0.0093 -0.1604 -0.1946 -0.1626 -0.0017 0.0449 0.4108 0.5781
                        -2.2227 -2.2224 -3.4851 -3.7242 -0.4110 0.4108 8.9900 7.8125
                        Solved matrix
                        -2.2227 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 2889.3218
                        0.0000 -0.5408 0.0000 0.0000 0.0000 0.0000 0.0000 703.4698
                        0.0000 0.0000 0.6967 0.0000 0.0000 0.0000 0.0000 -905.9999
                        0.0000 0.0000 0.0000 0.0510 0.0000 0.0000 0.0000 -17.0178
                        0.0000 0.0000 0.0000 0.0000 0.0019 0.0000 0.0000 -0.0241
                        0.0000 0.0000 0.0000 0.0000 0.0000 0.0015 0.0000 0.0292
                        Solution: -1299.9096 -1300.7239 -1300.4244 -333.8168 -12.7325 19.9704 -1285.9941
                        Expected probe error: -2035.5796 -2058.8149 -2060.0117 -2059.7983 -2066.9802 -2067.0186 -2068.2925
                        Derivative matrix
                        -0.2682 -0.3717 1.6391 0.5011 -0.3729 0.5194 0.9479
                        0.0476 1.0614 -0.1086 0.0183 -0.0201 0.0952 0.9979
                        1.0260 0.0049 -0.0323 0.0134 -0.0232 0.0018 0.9985
                        -0.0183 -0.0989 1.1163 0.0616 -0.0140 0.0763 0.9943
                        0.1587 0.6494 0.1935 -0.1501 -0.0122 -0.0500 1.0150
                        0.6519 0.1141 0.2325 -0.1453 0.0732 0.0055 1.0144
                        0.2643 0.2197 0.5164 -0.1654 0.0696 -0.0562 1.0162
                        Normal matrix
                        1.6472 0.3926 -0.1797 -0.2831 0.1397 -0.1535 1.8904 3849.8519
                        0.3926 1.7576 -0.5695 -0.3233 0.1342 -0.1438 1.6117 3267.6931
                        -0.1797 -0.5695 4.3038 0.7395 -0.5734 0.8887 3.4799 7294.1970
                        -0.2831 -0.3233 0.7395 0.3264 -0.2087 0.2828 0.1001 259.6438
                        0.1397 0.1342 -0.5734 -0.2087 0.1506 -0.1996 -0.2781 -607.2070
                        -0.1535 -0.1438 0.8887 0.2828 -0.1996 0.2904 0.5627 1206.0157
                        1.8904 1.6117 3.4799 0.1001 -0.2781 0.5627 6.9720 14385.6735
                        Solved matrix
                        1.8904 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 1050.4940
                        0.0000 1.4229 0.0000 0.0000 0.0000 0.0000 0.0000 788.1418
                        0.0000 0.0000 4.2567 0.0000 0.0000 0.0000 0.0000 2365.7897
                        0.0000 0.0000 0.0000 0.1409 0.0000 0.0000 0.0000 15.9871
                        0.0000 0.0000 0.0000 0.0000 0.0099 0.0000 0.0000 0.1313
                        0.0000 0.0000 0.0000 0.0000 0.0000 0.0095 0.0000 0.0006
                        Solution: 555.6917 553.9042 555.7788 113.4557 13.2953 0.0585 1506.1367
                        Residuals: 2036.1707 2059.8796 2059.4016 2061.1743 2068.6389 2067.7148 2070.3408
                        Expected probe error: -898.2925 -955.3685 -954.5236 -952.5867 -987.6226 -982.6718 -989.0720
                        Stops X1.010 Y-1.592 Z0.582 height -680.433 diagonal 488.143 radius -82.361 xcorr 0.56 ycorr 20.03 zcorr 0.00 xtilt 0.000% ytilt 0.000%
                          The matrix is numerically unstable (the diagonal element of the last row of the solved matrix is showing as zero). Try 6-factor calibration instead of 7. That's S6 on the final G30 command in bed.g instead of S7.
                          • bricorundefined
                            bricor
                            6 Factor seems to have made it work
                            I ran the calibration and it was finally successful running multiple passes. The printer is cold and in need of a full calibration (i gave up last night/early am in the middle of manual calibration) but the results are good.
                            3 passes in a row
                            :17:39 PMM665
                            Diagonal 268.000, delta radius 133.271, homed height 314.718, bed radius 110.0, X 1.334°, Y 0.015°, Z 0.000°
                            12:17:35 PMG32
                            Calibrated 6 factors using 7 points, deviation before 0.041 after 0.017
                            12:16:32 PMG32
                            Calibrated 6 factors using 7 points, deviation before 0.155 after 0.034
                            12:15:38 PMM665
                            Diagonal 268.000, delta radius 132.043, homed height 314.423, bed radius 110.0, X 1.683°, Y -1.559°, Z 0.000°
                            12:15:32 PMG32
                            Calibrated 6 factors using 7 points, deviation before 1.261 after 0.139
                            12:14:35 PMM665
                            4th & 5th pass 10 Point -
                            12:46:03 PMM665
                            Diagonal 268.000, delta radius 132.788, homed height 314.692, bed radius 110.0, X 1.361°, Y 0.113°, Z 0.000°
                            12:43:50 PMG28
                            12:36:22 PMG32
                            Calibrated 6 factors using 10 points, deviation before 0.121 after 0.038
                            12:35:10 PMM665
                            Diagonal 268.000, delta radius 132.290, homed height 314.515, bed radius 110.0, X 1.037°, Y -0.048°, Z 0.000°
                            12:35:04 PMG32
                            Calibrated 6 factors using 10 points, deviation before 1.096 after 0.126
                            YAT diag data (pass 5)
                            M111 S1 P4
                            ok
                            Z probe offsets: -0.087 0.009 0.012 0.002 -0.049 0.050 0.085, mean 0.003, deviation from mean 0.053
                            Stops X1.561 Y-0.472 Z-1.089 height 314.718 diagonal 268.000 radius 133.271 xcorr 1.33 ycorr 0.01 zcorr 0.00 xtilt 0.000% ytilt 0.000%
                            Derivative matrix
                            0.0555 0.0552 0.8892 0.2258 0.0645 -0.0645
                            0.0632 0.7298 0.2071 0.3908 -0.0406 -0.1187
                            0.7304 0.0556 0.2141 0.3907 0.1297 0.0351
                            0.1548 0.1533 0.6919 0.4407 0.0917 -0.0917
                            0.1632 0.5023 0.3346 0.5294 -0.0308 -0.0862
                            0.5045 0.1570 0.3385 0.5294 0.0899 0.0284
                            0.2711 0.2677 0.4612 0.5571 0.0502 -0.0502
                            Normal matrix
                            0.9191 0.3473 0.6764 0.8954 0.1639 -0.0130 -0.0452
                            0.3473 0.9109 0.6629 0.8851 0.0073 -0.1546 -0.0088
                            0.6764 0.6629 1.7974 1.2836 0.1835 -0.1802 0.0316
                            0.8954 0.8851 1.2836 1.4215 0.1491 -0.1462 -0.0377
                            0.1639 0.0073 0.1835 0.1491 0.0426 -0.0005 -0.0061
                            -0.0130 -0.1546 -0.1802 -0.1462 -0.0005 0.0386 -0.0061
                            Solved matrix
                            0.9191 0.0000 0.0000 0.0000 0.0000 0.0000 0.4568
                            0.0000 0.7797 0.0000 0.0000 0.0000 0.0000 -0.1543
                            0.0000 0.0000 1.0869 0.0000 0.0000 0.0000 0.2634
                            0.0000 0.0000 0.0000 0.0600 0.0000 0.0000 -0.0196
                            0.0000 0.0000 0.0000 0.0000 0.0018 0.0000 -0.0036
                            0.0000 0.0000 0.0000 0.0000 0.0000 0.0014 -0.0013
                            Solution: 0.4969 -0.1979 0.2423 -0.3264 -1.9328 -0.9136
                            Residuals: 0.0055 0.0053 0.0053 -0.0209 -0.0205 -0.0205 0.0458
                            Expected probe error: 0.0164 0.0035 0.0127 -0.0181 -0.0233 -0.0197 0.0442
                            Derivative matrix
                            0.0471 0.0601 0.8929 0.2177 0.0554 -0.0708
                            0.0635 0.7277 0.2088 0.3941 -0.0392 -0.1179
                            0.7340 0.0611 0.2049 0.3846 0.1203 0.0392
                            0.1485 0.1576 0.6939 0.4360 0.0894 -0.0950
                            0.1623 0.5028 0.3349 0.5293 -0.0283 -0.0860
                            0.5054 0.1617 0.3329 0.5259 0.0880 0.0300
                            0.2688 0.2711 0.4601 0.5548 0.0515 -0.0508
                            Normal matrix
                            0.9211 0.3535 0.6551 0.8832 0.1554 -0.0086 -0.0058
                            0.3535 0.9142 0.6744 0.8937 0.0103 -0.1547 0.0015
                            0.6551 0.6744 1.7991 1.2656 0.1715 -0.1879 -0.0113
                            0.8832 0.8937 1.2656 1.4053 0.1417 -0.1461 -0.0038
                            0.1554 0.0103 0.1715 0.1417 0.0383 -0.0006 -0.0019
                            -0.0086 -0.1547 -0.1879 -0.1461 -0.0006 0.0403 0.0002
                            Solved matrix
                            0.9211 0.0000 0.0000 0.0000 0.0000 0.0000 -0.0229
                            0.0000 0.7785 0.0000 0.0000 0.0000 0.0000 -0.0037
                            0.0000 0.0000 1.1034 0.0000 0.0000 0.0000 -0.0206
                            0.0000 0.0000 0.0000 0.0608 0.0000 0.0000 0.0019
                            0.0000 0.0000 0.0000 0.0000 0.0000 0.0014 0.0000
                            Solution: -0.0248 -0.0047 -0.0187 0.0318 0.0189 0.0100
                            Residuals: -0.0980 0.0104 0.0043 -0.0005 -0.0458 0.0496 0.0870
                            Expected probe error: 0.0055 0.0052 0.0053 -0.0209 -0.0205 -0.0205 0.0458
                            Stops X1.869 Y-0.839 Z-1.029 height 314.714 diagonal 268.000 radius 132.977 xcorr -0.58 ycorr -0.89 zcorr 0.00 xtilt 0.000% ytilt 0.000%
                              That's looking much better!
                              • bricorundefined
                                bricor
                                Is the answer to the issue, don't use 7 factor?
                                  Yes, we don't recommend 7-factor calibration unless you can probe a lot of points including some that are between two towers and outside the normal print radius.
                                  • bricorundefined
                                    bricor
                                    Thank you for your help once again. Issue solved.