    Reading Sensor Pressure from Analog output
    988
      dc42 administrators @developeralgo222
      @developeralgo222 if you don't need isolation between the sensor and the Duet, just use 2 resistors as a voltage divider.
      A better solution would be to use sensors that provide a digital interface that the Duet can use, for example Modbus RTL via RS485. You cold put all 6 sensors on the same RS485 bus provided that the sensors provide a way to set then all to different slave addresses.
      We have a small number of prototype 2-channel ADC daughter boards designed for reading 0 to 10V signals.
      developeralgo222undefined 1 Reply Last reply Reply Quote 0
      • developeralgo222undefined
        developeralgo222 @dc42
        Managed to mount 12 resistors ( that i had in hand creating 6 Voltage Dividers ( 1.8K & 3.3K ) per connection and it seems to work read the values fine now . Now my issue is how to Calibrate it correctly .
        Sensor Analog ( 1 ~ 5V) ===> Duet Analog ( 0 ~ 3V getting a Max of 3.24V) . Ideally probably i need to use 1.7K resistor so at get 3.3V or 1.6K resistor(assuming leakage or noise) to get 3.33V
        @ 0 kPa on the Sensor ===> Duet reads -22 kPa
        @ 40 kPa on Sensor ===> Duet reads -38 kPa
        @ 55 kPa on Sensor ==> Duet reads -53 kPa
        @ 65 kPa on Sensor ==> Duet reads -63 kPa
        and so on
        Not sure how to calibrate it correctly using U & V values for adjusted reading
        dc42undefined infiniteloopundefined 2 Replies Last reply Reply Quote 0
          @developeralgo222 for a linear analog sensor you should leave U and V as zero. Adjust the B and C parameters to get the correct readings.
          • infiniteloopundefined
            infiniteloop @developeralgo222
            @developeralgo222
            The nominal values of the two resistors are fine. Depending on the resistor’s specs, the effective values may come with enormous tolerances of up to 20%, so in order to get identical readings on all six channels, you should use resistors with a tolerance of 1% (”E96”) or better (”E192”). Alternatively, you can hand-pick resistors with the help of a multimeter.
            Which M308 command do you apply? Is it still this one from your OP:
            M308 S1  P"2.io0.in" Y"linear-analog"  A"VG1"  F0  B0.0  C-101  V0.00 U13.5
            If I understand the ”Analogue Section” from the data sheet you provided in the OP correctly, the output voltage at 0.0 kPa is somewhere between 0.6 and 1V (but not 0V). The resulting range should span about 0.5 to 3.2 V. Assuming that you want the Duet to report negative values, the Bnnn parameter (”The temperature or other value when the ADC output is zero”) should be positive (with U at 13.5, try 22), not 0.0. Similarly, Cnnn (”The temperature or other value when the ADC output is full scale”) should be a bit larger, as the output will rarely reach 3.3V.
            Think of Bnnn / Cnnn as defining an absolute scale (for 0.0 - 3.3 V), the effective readings being a subset (0.5 - 3.2 V) of that range.
            developeralgo222undefined 1 Reply Last reply Reply Quote 1
              developeralgo222 @infiniteloop
              @infiniteloop @dc42
              currently i only have
              M308 S1 P"2.io0.in" Y"linear-analog" A"VG1" F0 B0.0 C-101  V0.0 U0.0
              i am not using U & V as @dc42 mentioned above.
              If i understand what you explained above would this work for the subset range
              i will test it but would this work as my start of testing
              M308 S1 P"2.io0.in" Y"linear-analog" A"VG1" F0 B22  C-123  V0.0 U0.0
              OR
              M308 S1 P"2.io0.in" Y"linear-analog" A"VG1" F0 B22  C-101  V0.0 U0.0
              and also do i need to include U & V values in the M308 command if both the values are at 0.0 ? or i can leave them out and just use B & C values like this and no worry about including U & V on the command
              infiniteloopundefined 1 Reply Last reply Reply Quote 0
                @developeralgo222
                That’s good, @dc42’s post was short but precise.
                Yes, that’s a good starting point. Don’t stick with the idea to define the minimum and/or maximum of absolute values in Bnnn / Cnnn. Instead, adjust these until the result reads 0 for 0 kPa and -101 for 101 kPa. So, if at 0 kPa, you get a value >0, lower B - or, if you read <0, enlarge B. Then, adjust C in the same way. However, you will notice that if you change C, the reading for 0 kPa will also change a bit. So, it's an iterative process with a lot of try and error.
                  @infiniteloop Thanks guys for the help i will test it this weekend
                  • infiniteloopundefined infiniteloop referenced this topic