      I agree, very strange. Typical causes of this type of problem would be:

      • Endstops pulling the input low enough to light the LED, but not low enough to register as a low input to the processor. But in that case, M119 wouldn't show the endstops as triggered when you test them.
      • X and Y endstop connections swapped
      • Axis movement incorrect (easy to do on a CoreXY machine), for example G1 H1 X-395 is actually moving the Y axis, or is moving X away from the endstop switch.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      NL61undefined 1 Reply Last reply Reply Quote 0
      • NL61undefined
        NL61 @dc42
        last edited by

        @dc42
        thanks for answering,
        I tried M119 serveral times for each axis, it always shows if triggered or not.
        the endstops are not swapped and the movement goes to the correct direction.

        dc42undefined 1 Reply Last reply Reply Quote 0
        • deckingmanundefined
          deckingman
          last edited by

          One thing that keeps leaping out at me from the config.g file, is the steps per mm for X and Y but I don't see what this would have bearing on the end stop triggering. But with a 16 tooth pulley, 2mm pitch, and 0.9 degree motors, the value is around 80 so having the steps per mm set to 32 would imply something like a 50 tooth pulley which is pretty huge. 32 steps @16x micro stepping is 2 full steps per mm or 100 mm per motor revolution using 1.8 degree motors.

          Ian
          https://somei3deas.wordpress.com/
          https://www.youtube.com/@deckingman

          1 Reply Last reply Reply Quote 0
          • dc42undefined
            dc42 administrators @NL61
            last edited by dc42

            @NL61 said in H-Bot Endstop problem:

            @dc42
            thanks for answering,
            I tried M119 serveral times for each axis, it always shows if triggered or not.
            the endstops are not swapped and the movement goes to the correct direction.

            1. Can you confirm that the homex.g file looks exactly like the one you posted above when you open it in Duet Web Control?

            2. If you try to home just X (by pressing the Home X button in Duet Web Control, or by sending G28 X), does movement stop if you trigger either the X or Y homing sensors manually?

            Until you have homing working, you may wish to reduce the motor currents.

            Duet WiFi hardware designer and firmware engineer
            Please do not ask me for Duet support via PM or email, use the forum
            http://www.escher3d.com, https://miscsolutions.wordpress.com

            NL61undefined 1 Reply Last reply Reply Quote 0
            • NL61undefined
              NL61 @dc42
              last edited by

              @dc42
              once again the homex.g file:

              ; homex.g
              ; called to home the X axis
              ;
              ; generated by RepRapFirmware Configuration Tool v2.1.2 on Mon Nov 11 2019 14:44:06 GMT+0100 (Mitteleuropäische Normalzeit)
              G91 ; relative positioning
              G1 H2 Z5 F1800 ; lift Z relative to current position
              G1 H1 X-395 F1800 ; move quickly to X axis endstop and stop there (first pass)
              G1 X5 F1800 ; go back a few mm
              G1 S1 X-395 F360 ; move slowly to X axis endstop once more (second pass)
              G1 H2 Z-5 F1800 ; lower Z again
              G90 ; absolute positioning

              I tried to home X and triggered both, X and Y Endstop. No reaction

              1 Reply Last reply Reply Quote 0
              • droftartsundefined
                droftarts administrators
                last edited by

                Could you try swapping your NPN sensor for a microswitch, just to check it's working correctly?

                Ian

                Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                NL61undefined 1 Reply Last reply Reply Quote 0
                • NL61undefined
                  NL61 @droftarts
                  last edited by

                  @droftarts
                  hmm, the micro switch is working in X and Y.
                  The Sensors are MLM8-3002NA NPN, Schließer.
                  24 V and a BAT43 Diode at the signal output.
                  Why does the z-axis work? Its all the same setup.

                  I have to leave now. Thank you all for your answers, if there are any ideas whalt I can di to get those sensors working, I`ll try tomorrow.

                  dc42undefined 1 Reply Last reply Reply Quote 0
                  • dc42undefined
                    dc42 administrators @NL61
                    last edited by

                    Those sensors have a blue wire that must be connected to ground. Where on the Duet have you connected them?

                    Duet WiFi hardware designer and firmware engineer
                    Please do not ask me for Duet support via PM or email, use the forum
                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                    NL61undefined 1 Reply Last reply Reply Quote 0
                    • NL61undefined
                      NL61 @dc42
                      last edited by

                      @dc42
                      I connected 24V and Ground to the Power Supply.

                      1 Reply Last reply Reply Quote 0
                      • NL61undefined
                        NL61
                        last edited by

                        I did some troubleshooting this morning. I connectet the X-Sensor to the Z-input and could stop the Z-axis with a piece of metal holding it to the X-Sensor. Same with the Y-Sensor. That tells me that the sensors work fine.
                        Then I connectet Z-Motor and Sensor to the Y-connectors on the duet. The LED triggered but the motor did not stop. M119 says Y-Axis homed.
                        Is it possible that there is a problem with the board?
                        Or does anyone have an idea?

                        1 Reply Last reply Reply Quote 0
                        • dc42undefined
                          dc42 administrators
                          last edited by

                          Can you confirm that if you use a microswitch connected to the Y endstop input in place of the inductive sensor, the Y motor does stop when you trigger the microswitch?

                          If that's the case, then one possibility is that ground noise created by running the X and Y motors is affecting the input voltage at the endstop inputs. It may work better if you connect the blue wire to the ground pin on the endstop input, instead of to ground at the PSU.

                          Duet WiFi hardware designer and firmware engineer
                          Please do not ask me for Duet support via PM or email, use the forum
                          http://www.escher3d.com, https://miscsolutions.wordpress.com

                          NL61undefined 1 Reply Last reply Reply Quote 0
                          • NL61undefined
                            NL61 @dc42
                            last edited by

                            @dc42
                            I connected microswitches to X and Y now, so I can run my first print. They are both working.
                            I already connected the ground wire to the input of the endstop but it also didn't work.

                            dc42undefined 1 Reply Last reply Reply Quote 0
                            • dc42undefined
                              dc42 administrators @NL61
                              last edited by

                              @NL61 said in H-Bot Endstop problem:

                              @dc42
                              I connected microswitches to X and Y now, so I can run my first print. They are both working.
                              I already connected the ground wire to the input of the endstop but it also didn't work.

                              If your Duet is revision 1.04, then you might get the inductive sensors working if you remove the diodes and connect the output directly to the endstop input. This disadvantage is that as you are using a 24V supply, if the ground wire to the sensor breaks then that will probably feed enough voltage into the endstop input to blow the indicator LED. The microcontroller itself is protected against excessive input voltage on the version 1.04 Duet.

                              Duet WiFi hardware designer and firmware engineer
                              Please do not ask me for Duet support via PM or email, use the forum
                              http://www.escher3d.com, https://miscsolutions.wordpress.com

                              Vetiundefined NL61undefined 2 Replies Last reply Reply Quote 0
                              • Vetiundefined
                                Veti @dc42
                                last edited by

                                @dc42

                                how does that correspond to the documentation here?
                                https://duet3d.dozuki.com/Wiki/Hardware_Overview

                                The Z probe input improved to tolerate inputs up to 30V.
                                The endstop inputs will tolerate at least 8V.

                                to me, this says do not connect the 24v on the endstops directly.

                                dc42undefined 1 Reply Last reply Reply Quote 0
                                • dc42undefined
                                  dc42 administrators @Veti
                                  last edited by

                                  @Veti said in H-Bot Endstop problem:

                                  @dc42

                                  how does that correspond to the documentation here?
                                  https://duet3d.dozuki.com/Wiki/Hardware_Overview

                                  The Z probe input improved to tolerate inputs up to 30V.
                                  The endstop inputs will tolerate at least 8V.

                                  to me, this says do not connect the 24v on the endstops directly.

                                  An NPN output sensor doesn't apply 24V to the endstop input, except that under fault conditions (ground wire disconnected) then it may apply something approaching 24V.

                                  Duet WiFi hardware designer and firmware engineer
                                  Please do not ask me for Duet support via PM or email, use the forum
                                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                                  1 Reply Last reply Reply Quote 0
                                  • NL61undefined
                                    NL61 @dc42
                                    last edited by

                                    @dc42
                                    I removed the diodes and the NPN Sensors are working properly now.
                                    Thanks all for your help.