      A few questions:

      Do we still have a line length limit? Object model fetches such as 'heat.heaters[tools[state.currentTool].heaters[0]].current' burn through characters quite quickly.

      How are line numbers counted when I get a syntax error? The line number given by RRF does not match the error location. Should it be file-linenumber, or are things like empty lines and comment lines skipped?

      About the maximum stack depth: how deep is it? It is tempting to split code to separate macros, just like you would normally do with functions. This does increase nesting depth though.

      I do not really want to bother you guys with this yet since I have to carefully check the hotend heating before complaining, but I see 'maximum excursion' heater faults when I do not expect them, such as soon after programming a lower temperature for an active heater. Did anything change in RC2 regarding heater fault detection?

      dc42undefined 1 Reply Last reply Reply Quote 0
      • dc42undefined
        dc42 administrators @DaBit
        last edited by

        @DaBit said in New firmware 3.01-RC2 available:

        Do we still have a line length limit? Object model fetches such as 'heat.heaters[tools[state.currentTool].heaters[0]].current' burn through characters quite quickly.

        Yes, 160 characters, not counting leading spaces/tabs.

        How are line numbers counted when I get a syntax error? The line number given by RRF does not match the error location. Should it be file-linenumber, or are things like empty lines and comment lines skipped?

        It should be line number within the file, with 1 being the first line. If you think it doesn't match, please submit a simple example that reproduces the issue. The column number (if given) is generally the number of the character after the item that caused the problem.

        About the maximum stack depth: how deep is it? It is tempting to split code to separate macros, just like you would normally do with functions. This does increase nesting depth though.

        5 at present, but it will be increased to 7 in the next release or RC.

        I do not really want to bother you guys with this yet since I have to carefully check the hotend heating before complaining, but I see 'maximum excursion' heater faults when I do not expect them, such as soon after programming a lower temperature for an active heater. Did anything change in RC2 regarding heater fault detection?

        Not intentionally. Again, if you can reproduce a problem, please post a demo file.

        Duet WiFi hardware designer and firmware engineer
        Please do not ask me for Duet support via PM or email, use the forum
        http://www.escher3d.com, https://miscsolutions.wordpress.com

        1 Reply Last reply Reply Quote 0
        • DaBitundefined
          DaBit
          last edited by DaBit

          @dc42 said in New firmware 3.01-RC2 available:

          Not intentionally. Again, if you can reproduce a problem, please post a demo file.

          With heater 1/tool 0 active and heater 2/tool 1 standby, executing a 'G10 P1 S250 R200' at the console triggers an 'Error: Heating fault on heater 2, temperature excursion exceeded 15.0°C' after a few seconds.

          'M109 T1 S200' works. 'G10 P0 S250 R200' works. Machine homed or not does not change the behaviour.

          If I execute a T1 so T0 is put in standby and T1 is made active, the behaviour reverses. 'G10 P0 S250 R200' triggers an error, 'G10 P1 S250 R200' works as expected.

          For this test I made sure there were no active M570 commands in the config.

          Heaters/tools sections of the config.g:

          ; Heaters
          M308 S0 P"bedtemp" Y"thermistor" T100000 B4092         ; configure sensor 0 as thermistor on pin bedtemp
          M950 H0 C"bedheat" T0 Q5                               ; create bed heater output on bedheat and map it to sensor 0
          M143 H0 S140                                           ; set temperature limit for heater 0 to 140C
          M307 H0 A486.1 C2320.7 D16.5 S1.00 V24.0 B0	       ; PID-parameters for heated bed
          M308 S1 P"spi.cs1" Y"rtd-max31865"
          M950 H1 C"e0heat" T1 Q50                               ; create nozzle heater output on e0heat and map it to sensor 1
          M143 H1 S290                                           ; set temperature limit for heater 1 to 290C
          M307 H1 A675.5 C232.3 D2.8 S1.00 V23.7 B0
          M308 S2 P"e1temp" Y"thermistor" T100000 B4725 C7.06e-8 ; configure sensor 2 as thermistor on pin e1temp
          M950 H2 C"e1heat" T2 Q50                               ; create nozzle heater output on e1heat and map it to sensor 2
          M143 H2 S290                                           ; set temperature limit for heater 2 to 290C
          M307 H2 A650.8 C253.7 D3.6 S1.00 V23.8 B0			   ; PID parameters for heater 1
          
          ; Auxiliary temp sensors
          M308 S3 P"mcu-temp" Y"mcu-temp" A"mcu-temp"				; MCU temp
          M308 S4 P"e0temp" Y"thermistor" A"Chamber" T100000 B4725 C7.06e-8 ; configure sensor 3 (chamber temp) as thermistor on pin e0temp
          
          ; Tools
          M563 P0 S"Extruder 0" D0 H1 F0                         ; define tool 0
          G10 P0 X0 Y0 Z0                                        ; set tool 0 axis offsets
          G10 P0 R0 S0                                           ; set initial tool 0 active and standby temperatures to 0C
          M563 P1 S"Extruder 1" D1 H2 F0                         ; define tool 1
          G10 P1 X19.88 Y0.1 Z0                                   ; set tool 1 axis offsets
          G10 P1 R0 S0                                           ; set initial tool 1 active and standby temperatures to 0C
          M104 S0 T0					       ; make sure the heater is not 'off'
          M104 S0 T1					       ; make sure the heater is not 'off'
          
          dc42undefined 1 Reply Last reply Reply Quote 0
          • dc42undefined
            dc42 administrators @DaBit
            last edited by

            @DaBit said in New firmware 3.01-RC2 available:

            @dc42 said in New firmware 3.01-RC2 available:

            Not intentionally. Again, if you can reproduce a problem, please post a demo file.

            With heater 1/tool 0 active and heater 2/tool 1 standby, executing a 'G10 P1 S250 R200' at the console triggers an 'Error: Heating fault on heater 2, temperature excursion exceeded 15.0°C' after a few seconds.
            'M109 T1 S200' works. 'G10 P0 S250 R200' works. Machine homed or not does not change the behaviour.
            If I execute a T1 so T0 is put in standby and T1 is made active, the behaviour reverses. 'G10 P0 S250 R200' triggers an error, 'G10 P1 S250 R200' works as expected.

            I confirm this was an unintended change in 3.01-RC2. Please can you check that the new binary at https://www.dropbox.com/sh/3azy1njy3ayjsbp/AACquxr2m00eV568RZg5QG5wa?dl=0 corrects it. This binary also has the maximum stack depth increased to 7.

            Duet WiFi hardware designer and firmware engineer
            Please do not ask me for Duet support via PM or email, use the forum
            http://www.escher3d.com, https://miscsolutions.wordpress.com

            1 Reply Last reply Reply Quote 1
            • DaBitundefined
              DaBit
              last edited by

              I can confirm that the issue is resolved.
              Thanks for the exceptionally quick response, once again!

              I will check the error line numbers later, with this firmware.

              dc42undefined 1 Reply Last reply Reply Quote 0
              • dc42undefined
                dc42 administrators @DaBit
                last edited by

                @DaBit said in New firmware 3.01-RC2 available:

                I can confirm that the issue is resolved.
                Thanks for the exceptionally quick response, once again!

                I will check the error line numbers later, with this firmware.

                I haven't changed the line numbering in this build, so I expect the issue is unchanged. Please supply a test file to reproduce it.

                Duet WiFi hardware designer and firmware engineer
                Please do not ask me for Duet support via PM or email, use the forum
                http://www.escher3d.com, https://miscsolutions.wordpress.com

                1 Reply Last reply Reply Quote 0
                • smoki3undefined
                  smoki3
                  last edited by

                  Is it actually possible to define more than one probe?

                  I tried M558 K1 for G38.x and M585 but it always responds only for my Zprobe

                  dc42undefined 1 Reply Last reply Reply Quote 0
                  • dc42undefined
                    dc42 administrators @smoki3
                    last edited by

                    @smoki3 said in New firmware 3.01-RC2 available:

                    Is it actually possible to define more than one probe?

                    I tried M558 K1 for G38.x and M585 but it always responds only for my Zprobe

                    Currently it's possible to define more than one probe but not to switch between them.

                    Duet WiFi hardware designer and firmware engineer
                    Please do not ask me for Duet support via PM or email, use the forum
                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                    smoki3undefined 1 Reply Last reply Reply Quote 0
                    • smoki3undefined
                      smoki3 @dc42
                      last edited by smoki3

                      @dc42 I don't understand?

                      ; Z-Probe
                      
                      M558 K0 P5 C"^!zprobe.in" H3 F180 T25000	   	; Z probe connected to Z endstop input
                      G31 K0 X0 Y0 Z0.17 P500          	               	; Set Z probe offset + naher ran - weiter weg
                      
                      ; Tool Probe
                      M558 K1 P5 C"!e0stop" H5 F120 T3000  		  	; Tool probe connected to Z endstop input
                      G31 K1 X0 Y0 Z0 P500          	               	; Set Z probe offset + naher ran - weiter weg
                      

                      I defined this one. If I report the probe status with G31 K0 or K1 it always only responds for K0. If I try to use it K1 in G38.2 P1 or in M585 P1 it only react when K0 is trigged and not for K1

                      dc42undefined 1 Reply Last reply Reply Quote 0
                      • dc42undefined
                        dc42 administrators @smoki3
                        last edited by dc42

                        @smoki3 said in New firmware 3.01-RC2 available:

                        If I report the probe status with G31 K0 or K1 it always only responds for K0.

                        I see the problem, which is that there is only one Z probe input filter. So only one Z probe can be type 1,2,3 or 5. Defining two type 8 Z probes works for me. I will add a note to the M558 description.

                        Duet WiFi hardware designer and firmware engineer
                        Please do not ask me for Duet support via PM or email, use the forum
                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                        1 Reply Last reply Reply Quote 1
                        • jay_s_ukundefined
                          jay_s_uk
                          last edited by

                          Running 3.01-RC2 on the expansion board, for me at least, results in none of the motor drivers working.
                          I have had to roll back to 3.0-RC2 to get them to work and to be able to print.

                          Owns various duet boards and is the main wiki maintainer for the Teamgloomy LPC/STM32 port of RRF. Assume I'm running whatever the latest beta/stable build is

                          1 Reply Last reply Reply Quote 0
                          • matej1006undefined
                            matej1006
                            last edited by matej1006

                            Hello @dc42 why my fan rpm on duet web is wrong.it's show number between 25000 and 32000 on my noctua fan which has 100% open PWM 1700RPM.
                            i upgrade my DUET2 Wifi with: Duet2CombinedIAP and Duet2CombinedFirmware

                            Please help

                            dc42undefined 1 Reply Last reply Reply Quote 0
                            • dc42undefined
                              dc42 administrators @matej1006
                              last edited by

                              @matej1006 said in New firmware 3.01-RC2 available:

                              Hello @dc42 why my fan rpm on duet web is wrong.it's show number between 25000 and 32000 on my noctua fan which has 100% open PWM 1700RPM.
                              i upgrade my DUET2 Wifi with: Duet2CombinedIAP and Duet2CombinedFirmware

                              Is it a 4-wire fan, and have you connected it as recommended for 4-wire fans? Was it giving the correct RPM before you upgraded the firmware?

                              If so then my guess is that the tacho input is picking up noise from the PWM input, or from stepper motor cables in the same wiring bundle.

                              Duet WiFi hardware designer and firmware engineer
                              Please do not ask me for Duet support via PM or email, use the forum
                              http://www.escher3d.com, https://miscsolutions.wordpress.com

                              1 Reply Last reply Reply Quote 0
                              • matej1006undefined
                                matej1006
                                last edited by matej1006

                                @dc42 Yes i have noctua 4 wire pwm i have blue wire to fan7 on duex and tacho with 1n4148 connected to pb6 on duex
                                and previus version also didn't work same problem random number between 25000 and 30000
                                and now after i send home posittion then show's that strange nubmer for PWM before that is around 1700 RPM

                                1 Reply Last reply Reply Quote 0
                                • zerspaner_gerdundefined
                                  zerspaner_gerd
                                  last edited by

                                  For me, two sensor inputs are created?

                                  inputs.jpg

                                  Where does the numbering start?
                                  An example on Gcode Wiki shows J1, so I thought it started at one.

                                  Shouldn't "M581 T3 S0" make a change?
                                  There is only one message
                                  746d9d07-8709-4c35-b6cd-13a44979ffd3-image.png

                                  Board: Duet WiFi 1.03 | Firmware Version: 3.1.1 | WiFi Server Version: 1.23 | Web Interface Version: 3.1.1

                                  dc42undefined 1 Reply Last reply Reply Quote 0
                                  • zerspaner_gerdundefined
                                    zerspaner_gerd
                                    last edited by zerspaner_gerd

                                    Would have another question
                                    Should you invert the pin on M950 or with M581 S1?

                                    What happens to the following constellation:

                                    M950 J1 C"!e0stop"				
                                    M581 P1 T0 S1 C0
                                    

                                    Board: Duet WiFi 1.03 | Firmware Version: 3.1.1 | WiFi Server Version: 1.23 | Web Interface Version: 3.1.1

                                    dc42undefined 1 Reply Last reply Reply Quote 0
                                    • sdaviundefined
                                      sdavi
                                      last edited by

                                      @dc42 I came across a minor issue in 3.01RC2 (tested on DuetWifi). The gcode line numbers do not reset each time M32 is run, so a gcode file that contains conditional gcode errors will display the incorrect line number if it's not the first one run since reset.

                                      dc42undefined 1 Reply Last reply Reply Quote 0
                                      • dc42undefined
                                        dc42 administrators @sdavi
                                        last edited by

                                        @sdavi said in New firmware 3.01-RC2 available:

                                        @dc42 I came across a minor issue in 3.01RC2 (tested on DuetWifi). The gcode line numbers do not reset each time M32 is run, so a gcode file that contains conditional gcode errors will display the incorrect line number if it's not the first one run since reset.

                                        Thanks for reporting that, I'll fix it in RC3.

                                        Duet WiFi hardware designer and firmware engineer
                                        Please do not ask me for Duet support via PM or email, use the forum
                                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                                        1 Reply Last reply Reply Quote 0
                                        • dc42undefined
                                          dc42 administrators @zerspaner_gerd
                                          last edited by

                                          @zerspaner_gerd said in New firmware 3.01-RC2 available:

                                          For me, two sensor inputs are created?
                                          Where does the numbering start?

                                          The numbering starts at 0. The OM will report "sensors.inputs" up to the highest one you have configured. So when you create sensor 1, it reports inputs 0 and 1, and it reports that sensor 0 is not configured.

                                          Duet WiFi hardware designer and firmware engineer
                                          Please do not ask me for Duet support via PM or email, use the forum
                                          http://www.escher3d.com, https://miscsolutions.wordpress.com

                                          1 Reply Last reply Reply Quote 0
                                          • dc42undefined
                                            dc42 administrators @zerspaner_gerd
                                            last edited by

                                            @zerspaner_gerd said in New firmware 3.01-RC2 available:

                                            Would have another question
                                            Should you invert the pin on M950 or with M581 S1?

                                            You can do either. I left the S0/S1 parameter options so that you can trigger on both the rising and falling edges of an input.

                                            What happens to the following constellation:

                                            M950 J1 C"!e0stop"				
                                            M581 P1 T0 S1 C0
                                            

                                            S1 triggers on an inactive-to-active transition, which for an inverted pin is a high-to-low transition.

                                            Duet WiFi hardware designer and firmware engineer