    Hot end: Auto tune of heater 1 failed
    1.4k
      deckingman @gruen
      @gruen The A parameter is the gain and I believe that it is also a fair indication of the temperature that the heater could reach if running at full power. Aluminium melts at about 660 Deg C so your heater is dangerously over powered. Is it a 12V one running on 24V?
      • gruenundefined
        gruen
        I use the 24V from here:
        https://e3d-online.com/high-temperature-heater-cartridges
        with https://e3d-online.com/v6-plated-copper-heater-block a titan heat break and
        https://e3d-online.com/plated-copper-nozzles-v6.
          deckingman @gruen
          @gruen That combination of a copper heat block which is much better at conducting heat than aluminium, plus a high temperature 65 Watt heater probably explains why you could potentially reach around 1,665 deg C and melt mild steel, let alone copper or aluminium. You need about a quarter of that heating power. 20 Watt would probably work but AFAIK the smallest E3D do is 30 watt. Try one of those.
          • gruenundefined
            gruen
            I need 400°C for print with PEI. I don't think this work with 20 Watt. 😕
              The reason for the error is that the predicted maximum temperature is above 1500C. The solution is to use a less powerful heater, because the one you are using is way too powerful. 40W would be sufficient, probably even 30W.
              As a temporary workaround, you could use M143 to set the maximum permitted temperature to 1200C, which will cause the firmware to allow up to 1700C predicted maximum temperature. Then you can use M307 to set those A, C and D values. Then use another M143 command to set a more reasonable temperature limit.
              But I repeat, you should use a less powerful cartridge so that in the event of heater control failing, the risk of fire is reduced.
                deckingman @gruen
                @gruen said in Hot end: Auto tune of heater 1 failed:
                65 watts is giving you the potential to reach 1665 deg C. So on that basis and assuming a linear relationship between heater power and hot end temperature, then 20Watts would you the potential to reach (1665/65*20 ) = 512 deg C. But as I said, you'll probably find that a 20 watt cartridge is hard to find so try a 30 Watt which would give you a maximum temperature in the order of 768 deg C using the above assumptions.
                • gruenundefined
                  gruen
                  With M143 workaround works the auto tune.
                  After successfull auto tune does M500 only write:
                  ; config-override.g file generated in response to M500
                  ; Heater model parameters
                  M307 H0 A C D S V B0
                  M307 H1 A C D S V B0
                  M307 H2 A C D S V B0
                  M307 H3 A C D S V B0
                  ; Workplace coordinates
                    dc42 administrators @gruen
                    M500 doesn't yet work when using Duet 3 with attached RPi. Put the M307 command with the values from tuning directly in config.g instead.
                    • gruenundefined
                      gruen
                      I use the workaround and set with M143 the maximum permitted temperature to 1200°C. After another M143 H2 400 stays the Temperature Chart at 1200°C.
                      Can I reset the upper limit?
                        If you refresh DWC, does the upper limit do back down? I have a feeling that DWC rescales its temperature chart when the limit increases, but not when it decreases.
                        • gruenundefined
                          gruen
                          Oh, my error. M143 H2 S400 works. Thanks.
