    ToolBoard: 2 wires fan, heater fault and how to extrude ?

    Scheduled Pinned Locked Moved Unsolved
    Duet Hardware and wiring
    6
    112
    5.4k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • Pseud3mysundefined
      Pseud3mys @dc42
      last edited by

      @dc42 hi, With beta 4.1 boards don't reset, and with the semi auto config for H and L thermistor, 1 of the 2 return the correct temperature, and the heating work with this one. But, the second is still wrong (by 15°C, at ~17°C), what is the problem ? The two have exactly the same config except for H and L setting.

      1 Reply Last reply Reply Quote 0
      • Pseud3mysundefined
        Pseud3mys
        last edited by

        I check the 2 resistances values, both are at 4.34 Kohm (~11°C). but one thermistor return ~10°C degrees more than the real temperature (~21°C)..
        And it is enough to raise a fault with the heater, so it is disturbing.

        M308 S1 P"121.temp0" Y"thermistor" T500000 B3600 C1.196220e-7 H-12 L0
        M308 S2 P"122.temp0" Y"thermistor" T500000 B3600 C1.196220e-7 H-10 L-12
        

        All the value are equal exept for H and L but they don't change anything significantly (I tried to put the same value).
        So why one of the thermistor return a wrong value ?

        Pseud3mysundefined dc42undefined 2 Replies Last reply Reply Quote 0
        • Vetiundefined
          Veti
          last edited by

          measure the resistance of the thermistors at room temperature and see of they measure the same value.

          1 Reply Last reply Reply Quote 0
          • Pseud3mysundefined
            Pseud3mys @Pseud3mys
            last edited by Pseud3mys

            @Pseud3mys said in ToolBoard: 2 wires fan, heater fault and how to extrude ?:

            I check the 2 resistances values, both are at 4.34 Kohm (~11°C).

            Yes I already did it. It is the same value (4.34 kohm) at 11°C

            1 Reply Last reply Reply Quote 0
            • Vetiundefined
              Veti
              last edited by

              can you measure the resistance of R21 on the boards

              another thing to try is switch to the second thermistor port

              121.temp1

              Pseud3mysundefined 1 Reply Last reply Reply Quote 0
              • Pseud3mysundefined
                Pseud3mys @Veti
                last edited by

                Okay thank you I will try that this evening.

                1 Reply Last reply Reply Quote 0
                • Pseud3mysundefined
                  Pseud3mys
                  last edited by

                  okay so the R21 resistance is about 2K18 for both two board.
                  I saw on an other post that is the correct value.

                  1 Reply Last reply Reply Quote 0
                  • Vetiundefined
                    Veti
                    last edited by

                    then i dont know where the difference comes from.
                    you could get some pt1000 ones. maybe they provide better results.

                    Pseud3mysundefined 2 Replies Last reply Reply Quote 0
                    • Pseud3mysundefined
                      Pseud3mys @Veti
                      last edited by Pseud3mys

                      @Veti said in ToolBoard: 2 wires fan, heater fault and how to extrude ?:

                      then i dont know where the difference comes from.
                      you could get some pt1000 ones. maybe they provide better results.

                      but the thermistor isn't the problem, the two have the same resistance.

                      1 Reply Last reply Reply Quote 0
                      • Pseud3mysundefined
                        Pseud3mys @Veti
                        last edited by

                        @Veti I there a way to have the value that read the borad directly ?

                        1 Reply Last reply Reply Quote 0
                        • Vetiundefined
                          Veti
                          last edited by

                          i dont know where it could come from.

                          i would play a bit with the H and L values.

                          what do you get when you set the same on both?

                          Pseud3mysundefined 1 Reply Last reply Reply Quote 0
                          • Pseud3mysundefined
                            Pseud3mys @Veti
                            last edited by

                            @Veti I have a difference too, but I played a bit with the H and L value and now it is okay, the hotend doesn't return fault.

                            1 Reply Last reply Reply Quote 0
                            • dc42undefined
                              dc42 administrators @Pseud3mys
                              last edited by dc42

                              @Pseud3mys said in ToolBoard: 2 wires fan, heater fault and how to extrude ?:

                              I check the 2 resistances values, both are at 4.34 Kohm (~11°C). but one thermistor return ~10°C degrees more than the real temperature (~21°C)..
                              And it is enough to raise a fault with the heater, so it is disturbing.

                              M308 S1 P"121.temp0" Y"thermistor" T500000 B3600 C1.196220e-7 H-12 L0
                              M308 S2 P"122.temp0" Y"thermistor" T500000 B3600 C1.196220e-7 H-10 L-12
                              

                              All the value are equal exept for H and L but they don't change anything significantly (I tried to put the same value).
                              So why one of the thermistor return a wrong value ?

                              You don't need to set the H and L values in config.g because after you run the semi-automatic calibration procedure, the required H and L values are store in non-volatile memory.

                              You could try removing the H and L values and run the semi-automatic calibration again on the board that is showing the error. But if that doesn't work, use your manually-adjusted H value.

                              Duet WiFi hardware designer and firmware engineer
                              Please do not ask me for Duet support via PM or email, use the forum
                              http://www.escher3d.com, https://miscsolutions.wordpress.com

                              Pseud3mysundefined 1 Reply Last reply Reply Quote 0
                              • Pseud3mysundefined
                                Pseud3mys @dc42
                                last edited by

                                @dc42 I change the H value manually and now it work. Thank you for your help !

                                1 Reply Last reply Reply Quote 0
                                • flajziundefined
                                  flajzi @dc42
                                  last edited by

                                  @dc42 I have same problem. After few hours of printing the extruder heater goes offline, temperature goes to 2000 °C (I'm using PT1000)
                                  Snímek obrazovky 2020-12-12 v 11.01.12.png
                                  Updated to latest 3.2-beta4.1 and problem remains. It keeps printing so I guess it's still keeping 220 °C, but to CAN bus it reports offline status.
                                  M122 on Toolboard says:

                                  Diagnostics for board 1:
                                  Duet TOOL1LC firmware version 3.2-beta4.1 (2020-12-03)
                                  Bootloader ID: not available
                                  Never used RAM 4120, free system stack 36 words
                                  HEAT 46 CanAsync 89 CanRecv 83 TMC 54 MAIN 216 AIN 64
                                  Last reset 11:35:12 ago, cause: software
                                  Last software reset at 2020-11-22 15:02, reason: HardFault, available RAM 4168, slot 0
                                  Software reset code 0x0060 ICSR 0x00000003 SP 0x200011c8 Task 
                                  Stack: 20001018 20001304 0000000f 00000001 20000928 000172cd 00018250 01000000 00077dfa 00077ef4 20001218 200032d0 00000020 00017a61 20004660 00000000 20001300 00008895 00077dfa 20004670 00077ef4 42651000 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5
                                  Driver 0: position 11794334, 409.0 steps/mm, standstill, SG min/max 0/112, read errors 0, write errors 1, ifcnt 35, reads 15910, writes 16, timeouts 0, DMA errors 0
                                  Moves scheduled 562468, completed 562468, in progress 0, hiccups 0
                                  No step interrupt scheduled
                                  VIN: 24.2V
                                  MCU temperature: min 39.2C, current 41.7C, max 51.2C
                                  Ticks since heat task active 43, ADC conversions started 41546663, completed 41546662, timed out 0
                                  Last sensors broadcast 0x00000002 found 1 47 ticks ago, loop time 0
                                  CAN messages queued 501025, send timeouts 0, received 938189, lost 0, free buffers 36
                                  

                                  Any thoughts? Can I contribute with more debug infos to solve this?

                                  1 Reply Last reply Reply Quote 0
                                  • dc42undefined
                                    dc42 administrators
                                    last edited by

                                    @flajzi, it looks as though the heat task stack may still be too small. Please try the tool board firmware at https://www.dropbox.com/sh/jv86vnaqjs1j4qd/AAA00AGN-pHCX4ok4L81ukv-a?dl=0. Post a fresh M122 B1 report when either the problem occurs again or the print finishes.

                                    Duet WiFi hardware designer and firmware engineer
                                    Please do not ask me for Duet support via PM or email, use the forum
                                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                                    flajziundefined 2 Replies Last reply Reply Quote 0
                                    • flajziundefined
                                      flajzi @dc42
                                      last edited by

                                      @dc42 Hi again. Problem with 2000 °C is back.
                                      It's keeping same temperature, but it reports nonsense. This is M122 output:

                                      Diagnostics for board 1:
                                      Duet TOOL1LC firmware version 3.2-beta4.1+1 (2020-12-12)
                                      Bootloader ID: not available
                                      Never used RAM 3960, free system stack 36 words
                                      HEAT 86 CanAsync 89 CanRecv 83 TMC 54 MAIN 209 AIN 64
                                      Last reset 04:39:13 ago, cause: software
                                      Last software reset at 2020-11-22 15:02, reason: HardFault, available RAM 4168, slot 0
                                      Software reset code 0x0060 ICSR 0x00000003 SP 0x200011c8 Task 
                                      Stack: 20001018 20001304 0000000f 00000001 20000928 000172cd 00018250 01000000 00077dfa 00077ef4 20001218 200032d0 00000020 00017a61 20004660 00000000 20001300 00008895 00077dfa 20004670 00077ef4 42651000 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5
                                      Driver 0: position 7738615, 409.0 steps/mm, standstill, SG min/max 0/112, read errors 0, write errors 1, ifcnt 42, reads 53596, writes 14, timeouts 0, DMA errors 0
                                      Moves scheduled 219075, completed 219075, in progress 0, hiccups 0
                                      No step interrupt scheduled
                                      VIN: 24.2V
                                      MCU temperature: min 38.4C, current 54.5C, max 57.9C
                                      Ticks since heat task active 151, ADC conversions started 16686702, completed 16686701, timed out 0
                                      Last sensors broadcast 0x00000002 found 1 155 ticks ago, loop time 0
                                      CAN messages queued 201492, send timeouts 0, received 370230, lost 0, free buffers 36
                                      
                                      1 Reply Last reply Reply Quote 0
                                      • flajziundefined
                                        flajzi @dc42
                                        last edited by flajzi

                                        @dc42 And hello again... Problem with 2000 °C persists also in RC1 release...

                                        37612105-0544-4760-af48-466ab46677a7-image.png
                                        I don't know if that could be an issue, but I'm using PT1000 sensor instead of thermistor...

                                        Diagnostics for board 1:
                                        Duet TOOL1LC firmware version 3.2-RC1 (2020-12-19)
                                        Bootloader ID: not available
                                        Never used RAM 3960, free system stack 38 words
                                        HEAT 86 CanAsync 89 CanRecv 83 TMC 54 MAIN 219 AIN 64
                                        Last reset 03:17:23 ago, cause: power up
                                        Last software reset at 2020-11-22 15:02, reason: HardFault, available RAM 4168, slot 0
                                        Software reset code 0x0060 ICSR 0x00000003 SP 0x200011c8 Task  Freestk 4294967295 ok
                                        Stack: 20001018 20001304 0000000f 00000001 20000928 000172cd 00018250 01000000 00077dfa 00077ef4 20001218 200032d0 00000020 00017a61 20004660 00000000 20001300 00008895 00077dfa 20004670 00077ef4 42651000 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5 a5a5a5a5
                                        Driver 0: position 7455393, 409.0 steps/mm, standstill, SG min/max 0/112, read errors 0, write errors 0, ifcnt 16, reads 23696, writes 16, timeouts 0, DMA errors 0
                                        Moves scheduled 218054, completed 218054, in progress 0, hiccups 0
                                        No step interrupt scheduled
                                        VIN: 24.2V
                                        MCU temperature: min 36.8C, current 51.7C, max 62.4C
                                        Ticks since heat task active 198, ADC conversions started 11796908, completed 11796907, timed out 0
                                        Last sensors broadcast 0x00000002 found 1 202 ticks ago, loop time 0
                                        CAN messages queued 142406, send timeouts 0, received 324917, lost 0, free buffers 36
                                        

                                        My setup is this:

                                        M308 S1 P"1.temp0" Y"pt1000" A"Nozzle"; configure sensor 1 as PT1000 on pin 1.temp0
                                        M950 H1 C"1.out0" T1                           ; create nozzle heater output on 1.out0 and map it to sensor 1
                                        M143 H1 S285                                   ; set temperature limit for heater 1
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • dc42undefined
                                          dc42 administrators
                                          last edited by

                                          Please post your complete config.g file.

                                          Does the 2000C error occur immediately after starting the system, or is the displayed temperature normal at first and changes to 2000C and heater offline later? If it occurs immediately, try putting a G4 P500 command right at the start of config.g.

                                          Duet WiFi hardware designer and firmware engineer
                                          Please do not ask me for Duet support via PM or email, use the forum
                                          http://www.escher3d.com, https://miscsolutions.wordpress.com

                                          flajziundefined 2 Replies Last reply Reply Quote 0
                                          • Meltexundefined
                                            Meltex
                                            last edited by Meltex

                                            I have had the same issue. But I found out that screw in terminal block was broken, so i just soldered thermistor wire directly to PCB and problem dissapeared. So check wires and terminals.

                                            flajziundefined 1 Reply Last reply Reply Quote 0