    jrockland @Luke'sLaboratory
    last edited by 14 Jan 2021, 17:57

    @Luke-sLaboratory Ill have to read more about bang bang but if I check on my other machines it is deactivated everywhere

    undefined 1 Reply Last reply 14 Jan 2021, 17:59 Reply Quote 0
    • undefined
      dc42 administrators
      last edited by dc42 14 Jan 2021, 17:59

      Using an inverted heater output isn't safe. When you power up, you are relying on the Duet booting up and running that M950 command to turn the heater off. If any of that fails (for example, something prevents the Pi from running, e.g. the SD card goes bad), then the heater will remain on.

      What connection are you using that requires an inverted heater output?

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      undefined 1 Reply Last reply 14 Jan 2021, 18:00 Reply Quote 0
      • undefined
        Luke'sLaboratory @jrockland
        last edited by 14 Jan 2021, 17:59

        @jrockland info on the relays would still be useful, but yes, probably should look into disabling PWM control if it was previously operated bang-bang and it was successful.

        Luke
        http://lukeslab.online

        1 Reply Last reply Reply Quote 0
        • undefined
          jrockland @dc42
          last edited by 14 Jan 2021, 18:00

          @dc42 well that is the thing, it is inverted so it doesn't turn on as soon as I turn the board on. that is really weird. Ill have the board sent to my tech so he can look at it.

          if I remove the inversion the board feed power as soon as it turn on (checked with a meter)

          undefined undefined 2 Replies Last reply 14 Jan 2021, 18:05 Reply Quote 0
          • undefined
            Veti @jrockland
            last edited by 14 Jan 2021, 18:05

            @jrockland said in IMPORTANT ISSUE with bed temp controller:

            well that is the thing, it is inverted so it doesn't turn on as soon as I turn the board on.

            this suggests you got the wrong ssr.

            undefined 1 Reply Last reply 14 Jan 2021, 18:07 Reply Quote 0
            • undefined
              jrockland @Veti
              last edited by 14 Jan 2021, 18:07

              @Veti ssr's are out of the equation, they are disconnected. Im testing the board whit a multimeter

              1 Reply Last reply Reply Quote 0
              • undefined
                dc42 administrators @jrockland
                last edited by dc42 14 Jan 2021, 18:07

                @jrockland said in IMPORTANT ISSUE with bed temp controller:

                @dc42 well that is the thing, it is inverted so it doesn't turn on as soon as I turn the board on. that is really weird. Ill have the board sent to my tech so he can look at it.

                if I remove the inversion the board feed power as soon as it turn on (checked with a meter)

                We really need to know what sort of relay or SSR you are using, and how you have connected it to the Duet. If it's a relay board then it may be better to connect it to an IO_x_OUT pin instead; but a SSR is better because it allows you to use PWM and hence PID.

                Duet WiFi hardware designer and firmware engineer
                Please do not ask me for Duet support via PM or email, use the forum
                http://www.escher3d.com, https://miscsolutions.wordpress.com

                undefined undefined 2 Replies Last reply 14 Jan 2021, 18:10 Reply Quote 0
                • undefined
                  Luke'sLaboratory @dc42
                  last edited by 14 Jan 2021, 18:10

                  @dc42 He's talking about the actual board output, but I don't remember if i'm able to measure V_in across inactive outputs or not, since the ground is switched

                  Luke
                  http://lukeslab.online

                  1 Reply Last reply Reply Quote 0
                  • undefined
                    jrockland @dc42
                    last edited by 14 Jan 2021, 18:17

                    @dc42 on that specific machine we still use the old SRD-05VDC-SL-C, apparently we haven't blown them up yet. so no SSR'S on that one.

                    problem is probably in my gcode.

                    undefined 1 Reply Last reply 14 Jan 2021, 18:21 Reply Quote 0
                    • undefined
                      Luke'sLaboratory @jrockland
                      last edited by 14 Jan 2021, 18:21

                      @jrockland said in IMPORTANT ISSUE with bed temp controller:

                      SRD-05VDC-SL-C

                      Oh - so its a mechanical switch you were trying to drive with PWM. Well, that about "solves" it, other than inverting the heater signal. Datasheet shows ratings for 300 electrical switches/min, with only 30 mechanical switches/min allowed.

                      FWIW - this is why we always ask for the config.g when diagnosing issues.

                      Luke
                      http://lukeslab.online

                      undefined 1 Reply Last reply 14 Jan 2021, 18:23 Reply Quote 0
                      • undefined
                        Veti
                        last edited by 14 Jan 2021, 18:23

                        as i said not having a quality ssr gives you a good chance of burning down your house

                        get some quality components like
                        Omron G3NA-210B-DC5 (10A) or Crydom D2425 (25A) or Crydom 84134000 (10A) SSR

                        undefined 1 Reply Last reply 14 Jan 2021, 18:26 Reply Quote 0
                        • undefined
                          jrockland @Luke'sLaboratory
                          last edited by 14 Jan 2021, 18:23

                          @Luke-sLaboratory driving relays with io's isn't the right way ? pretty sure it is what there telling us to do in the wiring diagram.. I might be wrong..

                          undefined undefined undefined 3 Replies Last reply 14 Jan 2021, 18:24 Reply Quote 0
                          • undefined
                            Veti @jrockland
                            last edited by 14 Jan 2021, 18:24

                            @jrockland said in IMPORTANT ISSUE with bed temp controller:

                            pretty sure it is what there telling us to do in the wiring diagram.. I might be wrong..

                            what wiring diagram?

                            1 Reply Last reply Reply Quote 0
                            • undefined
                              Luke'sLaboratory @jrockland
                              last edited by 14 Jan 2021, 18:26

                              @jrockland IOs are fine, but you're trying to use a PWM signal (based on PID values) instead of a simple off/on. the mechanical relay can't keep up, and it may cause some other issues like latching on and causing the issue described. You'll need to re-enable Bang-bang, which will output either full voltage or none.

                              Luke
                              http://lukeslab.online

                              undefined 2 Replies Last reply 14 Jan 2021, 18:27 Reply Quote 0
                              • undefined
                                jrockland @Veti
                                last edited by 14 Jan 2021, 18:26

                                @Veti O don't worry for me, theses machines are intended to crash so they have fire extinguishing system in place. and I don't run them in my house.

                                ever seen an axis with over 60lbs of torque crash ? parts goes flying XD

                                1 Reply Last reply Reply Quote 0
                                • undefined
                                  jrockland @Luke'sLaboratory
                                  last edited by 14 Jan 2021, 18:27

                                  @Luke-sLaboratory That would explain why it was working before the update, bang bang was probably activated before...

                                  I will try to find how to write it properly using bang bang.

                                  1 Reply Last reply Reply Quote 0
                                  • undefined
                                    fcwilt @jrockland
                                    last edited by fcwilt 14 Jan 2021, 18:28

                                    This post is deleted!
                                    1 Reply Last reply Reply Quote 0
                                    • undefined
                                      jrockland @Luke'sLaboratory
                                      last edited by 14 Jan 2021, 18:28

                                      @Luke-sLaboratory hmm wait if I look at my config file bang bang IS activated..

                                      undefined 1 Reply Last reply 14 Jan 2021, 18:29 Reply Quote 0
                                      • undefined
                                        jrockland
                                        last edited by 14 Jan 2021, 18:29

                                        @fcwilt you where right (before deleting your comment) but my config was set as using bang bang..

                                        undefined 1 Reply Last reply 14 Jan 2021, 18:30 Reply Quote 0
                                        • undefined
                                          fcwilt @jrockland
                                          last edited by 14 Jan 2021, 18:29

                                          @jrockland said in IMPORTANT ISSUE with bed temp controller:

                                          @Luke-sLaboratory hmm wait if I look at my config file bang bang IS activated..

                                          Even with the slow rate of "bang bank" a mechanical relay is not a good choice.

                                          Frederick