    Stepper definition Z motors
    Using Duet Controllers
    1.5k
    • fcwiltundefined
      fcwilt
      From the DWC console execute M350 by itself.
      If that doesn't reveal the problem try commenting out the M350 in config.g and re-boot.
      Then from the DWC console execute M350 with one drive at a time to see if you can find what is causing the error.
      My printer is a Cartesian with these commands:
      - M584 X0 Y1:2 Z5 E3
      - M350 X16 Y16 Z16 E16 I1
      If I enter M350 X0 I get a driver 0 error.
      If I enter M350 Y0 I get a driver 1 error and a driver 2 error.
      if I enter M350 Z0 I get a driver 5 error.
      All those driver numbers in the errors match with the driver numbers in M584.
      Also check config-override.g for a M350 command.
      ahwitmerundefined 1 Reply Last reply Reply Quote 0
      • ahwitmerundefined
        ahwitmer @fcwilt
        @fcwilt
        Your advice works out. It had to do with the Z parameters. I was using Z:16:16:16:16
        After changing it to Z:16, the error message is not shown anymore!
        My Extruder steppers still do not shown amperage yet.
        Harald
        CoreXYUV
        • fcwiltundefined
          fcwilt
          @fcwilt said in Stepper definition Z motors:
          Your M906 has semi-colon where it should be a colon. That of course means everything after the semi-colon is considered a comment.
          M906 X3200 Y3200 Z2240:2240:2240:2240 U3200 V3200 E1360:1360:1360 ; 1360:1360:1360:1360 I30
          • Vetiundefined
            Veti @ahwitmer
            @ahwitmer said in Stepper definition Z motors:
            How do you mean Z does not allow for multiple values?
            Z0.0:0.1:0.2:0.5
            this is not allowed. z only take 1 values for all
            this applies to M92 M566 M203 M201 M906
            • ahwitmerundefined
              ahwitmer
              @Veti Indeed, followed up your advise and that works out fine. Thanks!
              @Veti @fcwilt
              And the story continues:
              My set-up
              Mainboard 4 z-steppers (Nema 23, 2.8 Ampere)
              Expboard 0: 3 extruders
              Expboard 1: X and Y stepper (nema 23, 4 Ampere)
              Exp board2: U and V stepper (Nema 23, 4 ampere)
              Mainboard: 12 V supply
              Expansion boards: 24 V supply
              Switch to 24 Volt was done in a later moment after I purchased several 12 Volt other elements. Have insufficient space to install another 24V power supply.
              Commissioning
              Okay now my Z-steppers provide the correct amperage when issuing M906.
              Commissioning the Z motors is done by first disabling the endstop requirement by
              M564 S0 H0
              Pushing the buttons on the machine movement tab should move the motors.
              Result
              Out of the 4, only two Z-steppers react on the commands to move.
              Both motors move irregularly.
              For one of the motors, once it starts stepping it will continue stepping, but it decides itself if it takes the required direction, sometimes it is up, some times it is down or it just stutters at the down command.
              The other motor hardly turns and also changes its mind regularly to up or down stuttering.
              In addition, the first motor is not activated after the step-cycle is finished, that is okay.
              The second motor however remains kept energized. I did not realize it until I found that the motor got quite hot and even the power cable became warm.
              I have a continuous readout of voltage (both 12 V and 24V) and that one is keeping stable during this excercize.
              Changing the mainboard from 12 V to 24 V will likely change the issue of the warm cable. Nevertheless keeping it energised is never the intention. I have to reset the board to get it de-energised.
              What would be the reason behind iregular stepping?
              Why is one motor kept energised?
              PS I did not yet switch cables to find out if the cables are crimped (in)correctly.
              Harald
              CoreXYUV
              • fcwiltundefined
                fcwilt
                If it were me I would comment out the existing stepper configuration commands (M92 M203 M201 M566 M906 M350) and create a test set for one Z stepper at a time.
                Then I would verify that each one works on it's on - thus checking the stepper, the wiring and the power).
                Divide and Conquer.
                  Phaedrux Moderator @ahwitmer
                  Definitely check your wiring and ensure you have the motor phases correctly paired.
                  https://duet3d.dozuki.com/Wiki/Choosing_and_connecting_stepper_motors#Section_Identifying_the_stepper_motor_phases
                  • ahwitmerundefined
                    ahwitmer
                    @Phaedrux @fcwilt @Veti
                    The pairing of phases is verified again and shown to be connected correctly for all motors connected to the mainboard.
                    Still the steppers sometimes go up and sometimes go down.
                    Only wondering if there is a difference between
                    A1 A2 B1 B2 and A2 A1 B1 B2
                    CoreXYUV
                    • fcwiltundefined
                      fcwilt @ahwitmer
                      There appears to be a timing problem related to the expansion boards that deals with this issue.
                      https://forum.duet3d.com/topic/21326/just-another-bug-with-3hc
                      • ahwitmerundefined
                        ahwitmer @fcwilt
                        @fcwilt I'm going to take a look at it, thank you..... I'll be back 😉
                        CoreXYUV
                        • ahwitmerundefined
                          ahwitmer
                          @fcwilt @Phaedrux @Veti
                          Have been busy for some time with other pressing issues.
                          Last weekend I adopted the advise of fcwilt I modified the Config.g file using only one Z-motor (on mainboard driver 0). Then using an extra motor I tried to get it stepping.
                          It turned out that the cabling and crimping was the main origin of the problems.
                          One cable had to high AWG. That made the stepper squeek and respond differently on commands and got it quite warm.
                          I checked, recrimped all wires, now I have 4 working cables for the steppers.
                          Next I tested every driver connection to the mainboard.
                          Now I have three drivers working however the last one (driver 1 on mainboard) did not react to any stepping request. When requesting a large step, the system returns an error message.
                          Exchanging the cables did not have any effect. The cables are now working like a charm except on driver 1.
                          I have been careful with the motors not to rotate them when connected to the board.
                          This has all been done on 3.2. After my finding I decided to install 3.2.2 for the mainboard and the expansion boards. But helas no improvement. The other drivers still perform correctly. Driver 0.1 keeps on having issues....
                          Did I fry my driver in some way?
                          CoreXYUV
                            Anything is possible, but let's eliminate cabling first since that's the most likely issue. Is there anything visibly different about that driver header? Is the crimp making good contact?
                            • ahwitmerundefined
                              ahwitmer
                              @Phaedrux
                              I have 4 cables for the 4 motors,
                              I'm using driver 0.0 0.1 0.2 and 0.5
                              Modified my config.g so that I test driver by driver with any of the 4 cables
                              In total I test 16 times with a stepper. Every driver with any of the 4 cables.
                              Testing all cables on 0.0 0.2 and 0.5 and rotating/testing all 4 cables work perfectly in
                              Connecting any of the 4 cables to 0.1 results in the same error as shown above.
                              Because of this I conclude the cables are okay.
                              The connector on the motherboard looks very similar to the other connectors.
                              Nothing special there.
                              CoreXYUV
                                Thanks for the clarity on your testing. Before we conclude the driver is failed, can you share your current config.g? Just in case.
                                • ahwitmerundefined
                                  ahwitmer @Phaedrux
                                  @Phaedrux This is my Config file
                                  ;	generated by RepRapFirmware Configuration Tool v3.1.4 on Mon Oct 19 2020 10:28:42 GMT+0200 (Central European Summer Time)
                                  ; 	modified 25 jan 2021
                                  ;	General preferences
                                  G90        ;	 send absolute coordinates...
                                  M83        ;	 ...but relative extruder moves
                                  M550 P"duet3"        ;	 set printer name
                                  M669 K1        ;	 select CoreXY mode
                                  G21												;	in milimeters
                                  	;	Communication
                                  ;M540 Mac Address										;	Mac address
                                  ;M552 P192.168.0.5										; 	IP address
                                  ;M554 P192.168.1.1										;	Gateway
                                  ;M553 P255.255.255.0										;	Netmask
                                  ;M552 S1
                                  ;	 Drives
                                  M569 P2.1 S1											; X	 physical drive 2.1 goes forwards
                                  M569 P2.0 S1											; Y	 physical drive 2.0 goes forwards
                                   M569 P0.1 S1        ; Z1	 physical drive 0.0 goes forwards
                                  ;M569 P0.1 S1        ; Z2	 physical drive 0.1 goes forwards
                                  ;M569 P0.2 S1        ; Z3	 physical drive 0.2 goes forwards
                                  ;M569 P0.5 S1        ; Z4	 physical drive 0.5 goes forwards
                                   M569 P3.1 S1        ; U	 physical drive 3.1 goes forwards
                                   M569 P3.0 S1        ; V	 physical drive 3.0 goes forwards
                                   M569 P0.3 S1        ; Kext1	 physical drive 0.3 goes forwards
                                   M569 P0.4 S1        ; Kext2	 physical drive 0.4 goes forwards
                                   M569 P2.2 S1        ; Kext3	 physical drive 2.2 goes forwards
                                   M569 P3.2 S1        ; Kext4	 physical drive 3.2 goes forwards
                                   M569 P1.0 S1        ; DEXT3	 physical drive 1.0 goes forwards
                                   M569 P1.1 S1        ; DEXT2	 physical drive 1.1 goes forwards
                                   M569 P1.2 S1        ; DEXT1	 physical drive 1.2 goes forwards
                                  ;M584 X2.1:3.1 Y2.0:3.0 Z0.0:0.1:0.2:0.5 U3.1 V3.0 E1.2:1.1:1.0:2.2:3.2:0.3:0.4 P5
                                   M584 X2.1:3.1 Y2.0:3.0 Z0.1 U3.1 V3.0 E1.2:1.1:1.0:2.2:3.2:0.3:0.4 P5
                                   M671 X0:0:255:255 Y-104.55:115.45:115.45:-104.55						; Coordinates of probing points
                                  M350 X16 Y16 Z16 U16 V16 E16:16:16:16:16:16:16 I1                                               		; configure microstepping with interpolation
                                  M92 X80.00 Y80.00 Z4000.00 U80.00 V80.00 E420.00:420.00:420.00:420.00:420.00:420.00:420.00            		; set steps per mm
                                  M566 X900.00 Y900.00 Z12.00 U900.00 V900.00 E120.00:120.00:120.00:120.00:120.00:120.00:120.00           	;	 set maximum instantaneous speed changes (mm/min)
                                  M203 X6000.00 Y6000.00 Z180.00 U6000.00 V6000.00 E1200.00:1200.00:1200.00:1200.00:1200.00:1200.00:1200.00 	;	 set maximum speeds (mm/min)
                                  M201 X500.00 Y500.00 Z20.00 U500.00 V500.00 E250.00:250.00:250.00:250.00:250.00:250.00:250.00           	;	 set accelerations (mm/s^2)
                                  M906 X3200 Y3200 Z2240 U3200 V3200 E1360:1360:1360;1360:1360:1360:1360 I30  					;	 set motor currents (mA) and motor idle factor in per cent
                                  M84 S30        ;	 Set idle timeout
                                  ;	 Axis Limits
                                  M208 X0 Y0 Z0 S1        ; set axis minima
                                  M208 X255 Y222 Z340 U255 V222 S0        ; set axis maxima
                                  ;	 Endstops
                                  ;M574 X1 S1 P"2.io1.in"        ; Expansion board 2, io1.in - active high endstop
                                      M574 X2 S1 P"2.io1.in"                               					; active low endstop
                                  ;M574 Y1 S1 P"2.io0.in"        ; Expansion board 2, io0.in - active high endstop
                                      M574 Y2 S1 P"2.io0.in"      								; active low endstop
                                  ;M574 U1 S1 P"3.io1.in"        ; Expansion board 3, io1.in - active high endstop
                                      M574 U2 S1 P"3.io1.in"									; active low endstop
                                  ;M574 V1 S1 P"3.io0.in"        ; Expansion board 3, io0.in- active high endstop
                                      M574 V2 S1 P"3.io0.in"      								; active low endstop
                                  M574 Z1 S2        ; configure Z-probe endstop for low end on Z
                                  	;	 Z-Probe
                                  M950 S0 C"io7.out"        ;	 create servo pin 0 for BLTouch
                                  M558 P9 C"^io7.in" H5 F120 T6000                                                        	;	 set Z probe type to bltouch and the dive height + speeds
                                  G31 P500 X0 Y-104.55 Z0	;	 set Z probe trigger value, offset and trigger height
                                  M557 X0:255 Y0:222 S20	;	 define mesh grid
                                  ; M671 verplaatst naar bed
                                  	;	 Heaters
                                  M308 S0 P"temp0" Y"thermistor" T100000 B4138                                            	;	 configure sensor 0 as thermistor on pin temp0
                                  M950 H0 C"out0" T0        ;	 create bed heater output on out0 and map it to sensor 0
                                  M307 H0 B1 S1.00        ;	 enable bang-bang mode for the bed heater and set PWM limit
                                  M140 H0        ;	 map heated bed to heater 0
                                  M143 H0 S120        ;	 set temperature limit for heater 0 to 120C
                                  M308 S1 P"temp1" Y"thermistor" T100000 B4138                                            	;	 configure sensor 1 as thermistor on pin temp1
                                  M950 H1 C"out1" T1        ;	 create nozzle heater output on out1 and map it to sensor 1
                                  M307 H1 B0 S1.00        ;	 disable bang-bang mode for heater  and set PWM limit
                                  M308 S2 P"temp2" Y"thermistor" T100000 B4138                                            	;	 configure sensor 2 as thermistor on pin temp2
                                  M950 H2 C"out2" T2        ;	 create nozzle heater output on out2 and map it to sensor 2
                                  M307 H2 B0 S1.00        ;	 disable bang-bang mode for heater  and set PWM limit
                                  M308 S3 P"2.temp0" Y"thermistor" T100000 B4138                                          	;	 configure sensor 3 as thermistor on pin 2.temp0
                                  M950 H3 C"2.out0" T3        ;	 create nozzle heater output on 2.out0 and map it to sensor 3
                                  M307 H3 B0 S1.00        ;	 disable bang-bang mode for heater  and set PWM limit
                                  M308 S4 P"3.temp0" Y"thermistor" T100000 B4138                                          	;	 configure sensor 4 as thermistor on pin 3.temp0
                                  M950 H4 C"3.out0" T4        ;	 create nozzle heater output on 3.out0 and map it to sensor 4
                                  M307 H4 B0 S1.00        ;	 disable bang-bang mode for heater  and set PWM limit
                                  M308 S5 P"1.temp0" Y"thermistor" T100000 B4138                                          	;	 configure sensor 5 as thermistor on pin 1.temp0
                                  M950 H5 C"1.out0" T5        ;	 create nozzle heater output on 1.out0 and map it to sensor 5
                                  M307 H5 B0 S1.00        ;	 disable bang-bang mode for heater  and set PWM limit
                                  ;	 Fans
                                  M950 F0 C"out4" Q500        ;	 create fan 0 on pin out4 and set its frequency
                                  M106 P0 S0 H-1        ;	 set fan 0 value. Thermostatic control is turned off
                                  M950 F1 C"out5" Q500        ;	 create fan 1 on pin out5 and set its frequency
                                  M106 P1 S1 H-1        ;	 set fan 1 value. Thermostatic control is turned off
                                  M950 F2 C"out6" Q500        ;	 create fan 2 on pin out6 and set its frequency
                                  M106 P2 S1 H-1        ;	 set fan 2 value. Thermostatic control is turned off
                                  ;	 Tools
                                  M563 P0 S"Kraken 1" D0 H1 F0        ;	 define tool 0 Kraken 1
                                  G10 P0 X72.94 Y-10.265 Z0:0:0:0 U72.94 V-10.265							;	 set tool 0 axis offsets
                                  G10 P0 R0 S0        ;	 set initial tool 0 active and standby temperatures to 0C
                                  M563 P1 S"Kraken 2" D1 H2 F0        ;	 define tool 1 Kraken 2
                                  G10 P X93.47 Y-10.265 Z0:0:0:0  U93.47 V-10.265							;	 set tool 1 axis offsets
                                  G10 P1 R0 S0        ;	 set initial tool 1 active and standby temperatures to 0C
                                  M563 P2 S"Kraken 3"D2 H3 F1        ;	 define tool 2 Kraken 3
                                  G10 P X93.47 Y10.265 Z0:0:0:0 U93.47 V10.265							;	 set tool 2 axis offsets
                                  G10 P2 R0 S0        ;	 set initial tool 2 active and standby temperatures to 0C
                                  M563 P3 S"Kraken 4" D3 H4 F1        ;	 define tool 3 Kraken 4
                                  G10 P X72.94 Y10.265 Z0:0:0:0 U72.94 V10.265							;	 set tool 3 axis offsets
                                  G10 P3 R0 S0        ;	 set initial tool 3 active and standby temperatures to 0C
                                  M563 P4 S"Diamond" D6:4:5 H5 F0:2                                                               ;	 define tool 4 Diamond
                                  G10 P4 X0 Y0 Z0:0:0:0 U0 V0									;	 set tool 4 axis offsets
                                  G10 P4 R0 S0        ;	 set initial tool 4 active and standby temperatures to 0C
                                  M567 P4 E0.33:0.33:0.34        ;	 set mixing ratios for tool 4
                                  ;	 Custom settings are not defined
                                  ;	 Miscellaneous
                                  T4        ;	 select first tool
                                  M501	;	load saved parameters from non-volatile memory
                                  M911 S10 R11 P"M913 X0 U0 Y0 V0 G91 M83 G1 Z3 E-5 F1000"	;	set voltage thresholds and actions to run on power loss
                                  CoreXYUV
                                    I know we've had issues previously, but had this driver worked before at all?
                                    I can't see anything obvious in the config.
                                    Please contact your vendor and initiate a warranty exchange. Include a link to this thread as authorization.
                                    • Vetiundefined
                                      Veti @ahwitmer
                                      there is a ; instead of a : in the E definition
                                      and all your thermistors are not corrrect B4138 is the default. look up the correct value in the thermistor documentation.
                                      Phaedruxundefined ahwitmerundefined 2 Replies Last reply Reply Quote 0
                                        Phaedrux Moderator @Veti
                                        @Veti Eagle eye! That's a good catch, but I'm not sure it will have an impact on driver 5.
                                        • ahwitmerundefined
                                          ahwitmer @Veti
                                          @phaedrux @Veti Indeed eagle eyes, great modified it.
                                          I'm aware that I am using the default values for the thermistor. I'm taking it step by step.
                                          Configuration via RRF config tool, then step by step modifying the parameters of the elements.
                                          After changing the ; for a : and modifying the thermistor data, the problem with driver 1 stil remains. 😰
                                          I will contact Duet3D
                                          Thanks for the support.
                                          Harad
                                          CoreXYUV
                                          • ahwitmerundefined
                                            ahwitmer
                                            @Phaedrux @Veti
                                            Phaedrux, your suggestion was to ask for a warranty exchange.
                                            I did ask for the exchange, the company seemed to be not too willing to help out. Luckally they checked with the people of Duet3d and I could exchange my controller board.
                                            Although the card seemed to be used already, the problems were over. My four Z-motors are finally working correctly without any flaws.
                                            It was somehow surprising to see that the temperatures measured by the NTC's were significantly different, although I used the same parameters as before. But that is a next step.
                                            Thank you very much for your help solving my problems! Again many thanks!
                                            This topic can be closed, problem solved!
                                            CoreXYUV