Detecting Z-Probe Pickup on move command
Gcode meta commands
2.5k
    T3P3Tony administrators @sinned6915
    @sinned6915 the break is only called if the if statement evaluates to true. If you only got to 41 iterations 41 then the while loop evaluated to false and ended before the if statement evaluated to true.
    Using M564 makes sense if you have your bed unable to move below 0.
    The 500 report for value, if only for a brief moment could just be the probe moving between the two levels.
    Either probe type 5 or 8 should work in this case. 5 might be slightly slower to respond but i don't think that is the root cause of the issue. Also no it does not matter that you are on Duet 2.
    Try much smaller movements. Don't forget that the move you send will complete, maybe 0.5mm is too much.
      fcwilt @sinned6915
      @sinned6915 said in Detecting Z-Probe Pickup on move command:
      @fcwilt I think you might be right abtou G1 vs. G30 . I think that to meake it work though, I need to redefine the probe to be active LOW so that it beleives its 'triggered' when the circuit comepletes.
      So you are determined to make it work using the switch as a probe and doing a while loop?
        @sinned6915, if you want to use a G1 command in a while loop with a test to stop movement, you will need to use M400 after the G1 command. Otherwise the G1 commands will be put in the move queue and will not happen instantly. That is why movement continues after the switch is triggered.
        Alternatives are to configure the switch as an endstop switch and then use a G1 H1 move; or configure the switch as a Z probe and use a G30 move.
        undefined 1 Reply Last reply 10 Feb 2021, 22:43 Reply Quote 1
          fcwilt @dc42
          @dc42 said in Detecting Z-Probe Pickup on move command:
          Bless you, good sir. Bless you.
          undefined 1 Reply Last reply 10 Feb 2021, 23:56 Reply Quote 0
            sinned6915 @fcwilt
            @dc42- the many movements filling the que and then clearing it out makes sense.
            i think i discovered that by accident earlier too. with really small small steps, like Z=-0.01 it will move and 'softly' pickup the probe and stop.
            when I change to a valuue of Z-0.1 i would still overrun it. Then i threw in an M400 and the behavior really changed.
            @fcwilt I have been struggling the z-endstop logic all afternoon. as i have tried to show you, I already HAVE the switch set as both endstop and as probe, and I tried using the G1 and G31 commands before I got to this point. I have not doubted you, I just have not ben able to make it work. don't take it peronsally.
            and
            M558 K0 P5 C"^zprobe.in" H8 R0.5 F200 T9000 A1 S0.03
            it seems that to make it work, I HAVE to change the probe logic, and that is where I am getting tripped up. it also has to get changed back to probe the bed.
            https://duet3d.dozuki.com/Wiki/Gcode#Section_M558_in_RepRapFirmware_Num_3
            is where the RRF3 specific stuff was hidden at.
            neither method is foolproof. as an engineer my brain is thinking not 'if this bad thing happens' but more 'WHEN this bad thing happens', which will cause the least amount of carnage.
            undefined 2 Replies Last reply 11 Feb 2021, 00:04 Reply Quote 0
              fcwilt @sinned6915
              @fcwilt I have been struggling the z-endstop logic all afternoon. as i have tried to show you, I alrady HAVE the switch set as both endstop and as probe, and I tried using the G1 and G31 commands before I got to this point. I am have not doubted you, I just have not ben able to make it work. don't take it peronsally.
              I cannot find the configuration commands that set the switch to be an Z endstop.
              Can you guide me to them?
              undefined 1 Reply Last reply 11 Feb 2021, 00:28 Reply Quote 0
                fcwilt @sinned6915
                You should not have to do that.
                Once the probe displays 1000 in the DWC when it is activated and 0 when it is not you have the correct settings for all uses as a probe.
                Unless you have two probes - then you can configure each one separately to obtain the correct values.
                  sinned6915 @fcwilt
                  @fcwilt said in Detecting Z-Probe Pickup on move command:
                  I am reading the command reference for M574. There is a difference in the application in RRF2 an 3.
                  https://duet3d.dozuki.com/Wiki/Gcode#Section_M574_RepRapFirmware_Num_3
                  and the Snnn options -
                  1 = switch-type (eg microswitch) endstop input,
                  2 = Z probe (when used to home an axis other than Z),
                  3 = single motor load detection,
                  4 = multiple motor load detection (see Notes).
                  M574 says if you use the swtich as active low, invert it by prefixing the pin name with !.
                  eg: P"!xstop"
                  RRF3 introduced the C parameter to define the input pin, and the M558 notes for RRF3 says to invert the input, prefix the C with !.
                  eg: !C
                  EDIT: The other issue is that the logic and threshold numbers change. Changing the probe type inverts the probe value. I was under the impression that 1000 was high and 0 was low, but it seems to be more realted to the state of the probe.
                    fcwilt
                    You posted this earlier on...
                    From the documentation you pasted...
                    Notice the other than Z
                    Again from the documentation you pasted...
                    To use that switch as an Z endstop you need an M574 like this.
                    M574 Z1 S1 C"name_of_pin_switch_is_connected_to"
                    You also may need the ^ and/or ! character to get the endstop state to match the switch state.
                    Is this switch used for some other purpose - you mention probing the bed? I was thinking this switch was mounted to the frame but it seems it may be mounted to the gantry?
                    I don't think the same input can be an endstop input and a z probe input at the same time. But I need to verify that. In any case re-configuring it depending on what you need to do that that moment is perfectly fine and not uncommon.
                    undefined 2 Replies Last reply 11 Feb 2021, 02:20 Reply Quote 0
                      sinned6915 @fcwilt
                      @fcwilt i agree with your breakdown of the options and paramters.
                      Here's the thing though, I gave up trying to migrate my RRF2 setup by hand becasue of all the version changes and choose to use the RRF3 configurator and just start over. I reloaded the .json file and configs that ended up with to make the screenshot.
                      These were my results and it seemed reasonable, and I have been using it since. I trusted that the configurator was vetted and correct.
                      The additonal drives that I had to define for Z were later reworked and remapped.
                      Could there be a mistake in the configurator or in the docs?
                      undefined 1 Reply Last reply 11 Feb 2021, 04:04 Reply Quote 0
                        sinned6915 @fcwilt
                        I am physically (mechanically and electrically) deploying and retracting the switch that is used for probing and z-endstop.
                        The top half is mounted to the carraige. It has 2 magnets- one is wired to zprobe.in, the other to ground. The LED is wired to Vcc and when the circuit is complete (ie probe picked up)
                        The bottom half also has 2 magnets. One magnet is to wired to the Common terminal, the other to the Normally Closed terminal. It acts like a momentary swtich.
                        Here are the details if you want to dive in -
                        https://github.com/nionio6915/Euclid_Probe
                        undefined 1 Reply Last reply 11 Feb 2021, 02:56 Reply Quote 0
                          fcwilt @sinned6915
                          @sinned6915
                          Thank you. That helps tremendously.
                          So when the top half picks up the bottom have you have a assembly of the two parts with a "push button" on the underside which you can use as a Z probe? Is that correct?
                          Is they system used to pick up any other kind of bottom half?
                          Or is it just to have a Z probe that can be installed and removed automatically as needed?
                            fcwilt @sinned6915
                            There have been mistakes in both in the past.
                            I don't use the configurator - I rather learn the commands - it makes solving problems easier.
                              sinned6915
                              I get the behavior that I want with a pickup of the probe and exiting the dock, but the macro seems to loop now and I dont understand why.
                              After homing X & Y, trying to home Z seems to deploy the probe correctly using a G1 H1 command. Then the carraige moves to the center of the bed as instreucted in the homez.g files, but at the point where the G30 command is used, the machine appeard to start the deploypobe over. I am confused why it is doing this?
                              Should I be using a G1 H1 command here instead?
                              ; deployprobe.g
                              M118 S"deployprobe.g start"
                              echo sensors.probes[0].value[0]
                              G91
                              M564 H0 S0 ; allow movement while not homed
                              G1 Z15 F6000 ; move Z 10 for clearance above dock.
                              ; need to figure out some safety check on this
                              G90
                              if sensors.probes[0].value[0]!=1000 ; if sensor is value other than 1000 do this
                              abort "deployprobe: value0 Probe already picked up. Manually return probe to the dock"
                              ; if we're here we know it's becasue the above is true which I assume is because you have an N0 switch as a probe.
                              ; change probe temporarily to mimic NO to go to NC on pickup
                              M558 K0 P8 C"^!zprobe.in" H10 R0.5 F200 T9000 A1 S0.03
                              M118 S"Flipped probe from NC to NO"
                              M400
                              G1 X0 Y0 F6000 ; move above probe dock location
                              M400 ; wait for moves to finish
                              G1 H1 Z-280 F300 ; controlled linear move up the height of build envelope
                              ; H1 terminate the move when the endstop switch is triggered
                              ; and set the axis position to the axis limit defined by M208
                              G91 ; relative coords
                              G1 Z-1 F600 ; move bed up 1 to clear probe from dock since mags pull it up
                              M400 ; wait for move to finish
                              G1 X50 F3000 ; move right so probe moves out of the dock
                              G1 Z5 F3000 ; move bed to clear probe from glass build surface
                              G1 X100 F6000 ;
                              G90 ; absolute coords
                              M558 K0 P8 C"^zprobe.in" H10 R0.5 F200 T9000 A1 S0.03 ; NC synatax
                              M118 S"Flipped probe from NO to NC"
                              G4 S5 ; wait 1 second
                              ; M564 S1 ; limit axis to print area
                              ; while sensors.probes[0].value[0]=1000 ; loop to check when NC probe value changes from 1000 to 0
                              ; while sensors.probes[0].value[0]=0 ; loop to check when N0 probe value changes from 0 to 1000
                              ; if sensors.probes[0].value[0]=0 ; if sensor is value is 0 do this
                              ; move bed with probe dock up 0.5mm at a time until the switch activate.
                              ; This will get ugly if the switch fails as you have limits off!
                              ; echo sensors.probes[0].value[0]
                              ; echo iterations
                              ; if iterations=1000
                              ; break
                              if sensors.probes[0].value[0]!=0
                              abort "deployprobe: endvalue not 0 Probe not picked up! Print cancelled."
                              Here is the console output-
                              Here are the contents of homez.g-
                              ; homez.g
                              M118 S"homez.g started"
                              if !move.axes[0].homed || !move.axes[1].homed ; If the printer hasn't been homed, home it
                              M98 P"0:/sys/homexy.g"
                              M290 S0 R0 ; clear baby steps per Wes C
                              G91 ; relative positioning
                              ; G1 H2 Z6 F6000 ; lift Z relative to current position
                              G90 ; absolute positioning
                              M401 P0 ; This runs macro file deployprobe
                              G1 X145 Y162.5 F9000 ; go to first probe point
                              M400
                              M400
                              G4 P500
                              M118 S"Call 4 point macro"
                              M98 P"0:/sys/bed4point.g" ; tram bed
                              G1 X145 Y165 F9000 ; go back to the first probe point and reprobe 0 in case it moved
                              G30
                              M402 P0 ; retract probe
                              G1 Z10 F600 ; lift Z relative to current position
                              M564 S1 H0
                              ; G1 X150 Y0 F9000 ; move carraige to center front
                                fcwilt
                                G1 H1 commands are used with endstops. G1 H1 commands have nothing to do with deploying Z probes.
                                G30 commands are used with a Z probe.
                                There is no reason I can think of to be using while loops to accomplish your goal.
                                If you configure the switch device as an Z endstop then a G1 H1 move in the correct direction will stop when the switch is activated.
                                If you configure the switch device as a Z probe then a G30 command (if it moves toward the switch) will stop when the switch is activated.
                                The above assumes the switch device is activated with sitting in the dock.
                                Rather then spend time working with loops why don't you try to get one of the above approaches to work.
                                You can code some simple macros to test each approach.
                                undefined 1 Reply Last reply 12 Feb 2021, 05:42 Reply Quote 1
                                  sinned6915 @fcwilt
                                  @fcwilt I am a little confused by your response. I am not using while loops anymore. The test bits of code from earlier are all commented out. I just have not deleted them yet.
                                  I have a G1 H1 Z-280 F300 to pick the switch up from the dock.
                                  Once the switch is picked up from the dock and positioned at the center of the bed, when I issue the G30 command to what I think should be singe point probe to define Z=0.
                                  Instead it seems to start the deployprobe.g macro again. That is what makes no sense to me
                                  Are you saying I should use G1 instead? If that is the case, then how do we take into account the probe offset?
                                  undefined 2 Replies Last reply 12 Feb 2021, 06:22 Reply Quote 0
                                    fcwilt @sinned6915
                                    Sorry - my bad - I was looking at the commands and didn't notice the bits you had commented out.
                                    This works? Is that switch at that point configured as a Z endstop?
                                    I'm not sure what you mean by "again" - when was it called before this?
                                    The G30 command uses the Z probe. So it calls deployprobe.g before it tries to use it.
                                    And retractprobe.g will be called when the G30 is finished with it.
                                    Is that not happening?
                                      OwenD
                                      You shouldn't have the moves to pick up the probe in deployprobe.g
                                      I believe the intent of deployprobe.g is to extend the probe such as when a bltouch or servo probe is used.
                                      As stated above, it is called internally at the start of G30.
                                      If you're manually calling deployprobe.g using M98 and later using G30, then it would do it twice.
                                      Move all that code to say "pickup-probe.g" and likewise put the code to dock the probe into say "dock-probe.g"
                                      undefined 1 Reply Last reply 12 Feb 2021, 16:03 Reply Quote 1
                                        fcwilt @sinned6915
                                        @sinned6915
                                        I got to thinking about your homeZ.g file.
                                        You call M401 which invokes deployprobe.g.
                                        Later you call G30 - which normally would call M401 but it seems to notice that M401 has already been called and does not call M401 again. It also does not call M402 as it normally would
                                        Later still you call M402 which invokes retractprobe.g.
                                        Are you invoking deployprobe.g directly using M98 somewhere? G30 does not notice that and invokes M401 calling deployprobe.g as it normally would.
                                          You might want to configure two separate Z probes, one for the real probe and one for the pickup mechanism. RRF3.2 supports this. They can have each have their own deploy and retract files.
                                          undefined 1 Reply Last reply 12 Feb 2021, 16:31 Reply Quote 2
                                          39 out of 57