Solved DWC Temperature Chart goes upto 2000?
@doctrucker can you set a maximum in your config for each heater? I know you have the fault handling, but try something along the lines of
M143 H0 S120 M143 H1 S275
obviously adjust them to the maximum for your bed and tool.
Place the bed one after the M140 H0 and the other one after the M307 H1 -
@doctrucker as @jay_s_uk says use M143, but set it for both heaters.
You mean like I already have in the config file clip above?
@doctrucker said in DWC Temperature Chart goes upto 2000?:
[...clipped...] M143 H0 S120 A0 C0 ; Raise a heater fault if heatbed exceeds 120C. M143 H1 S255 A0 C0 ; Raise a heater fault if hotend exceeds 255C. [...clipped...]
@doctrucker it might be cause you're not setting a P value for each one so the S value is being overwritten by the lines below?
I've not used the monitoring function but thats the way the wiki reads
https://duet3d.dozuki.com/Wiki/Gcode#Section_M143_in_RRF_3_01RC2_and_latermaybe something like
M143 H0 S120 P0 A0 C0 M143 H0 S10 P1 A0 C1
edit: I meant P1 on the second line. updated to reflect
@jay_s_uk Running the M143 H[0/1] commands on the terminal sheds a little more light. Looks like the high and low need to be asigned to unique P numbers? Will try and see if the following improves...
14/04/2021, 09:33:17 M143 H1 Heater 1 monitor 0 uses sensor 1 to generate a heater fault if the reading falls below 5.0°C Heater 1 monitor 1 is disabled Heater 1 monitor 2 is disabled 14/04/2021, 09:33:03 M143 H0 Heater 0 monitor 0 uses sensor 0 to generate a heater fault if the reading falls below 10.0°C Heater 0 monitor 1 is disabled Heater 0 monitor 2 is disabled
@jay_s_uk yup, "P" was the problem. Bit dodgy that as I had specifically set the upper and lower limits and had no idea they weren't being respected. Will read the release notes again to make sure that is clearly stated.
So the old code that did not work:
M143 H0 S120 A0 C0 ; Raise a heater fault if heatbed exceeds 120C. M143 H1 S255 A0 C0 ; Raise a heater fault if hotend exceeds 255C. M143 H0 S10 A0 C1 ; Raise a heater fault if heatbed falls below 10C. M143 H1 S5 A0 C1 ; Raise a heater fault if hotend falls below 5C.
This needed to be:
M143 H0 S120 A0 C0 P0 ; Raise a heater fault if heatbed exceeds 120C. M143 H1 S255 A0 C0 P0 ; Raise a heater fault if hotend exceeds 255C. M143 H0 S10 A0 C1 P1 ; Raise a heater fault if heatbed falls below 10C. M143 H1 S5 A0 C1 P1 ; Raise a heater fault if hotend falls below 5C.
Setting the lower limits after the upper caused the upper limits to be overwritten.
Gives the following console feedback:
14/04/2021, 09:36:38 M143 H1 Heater 1 monitor 0 uses sensor 1 to generate a heater fault if the reading exceeds 255.0°C Heater 1 monitor 1 uses sensor 1 to generate a heater fault if the reading falls below 5.0°C Heater 1 monitor 2 is disabled 14/04/2021, 09:36:29 M143 H0 Heater 0 monitor 0 uses sensor 0 to generate a heater fault if the reading exceeds 120.0°C Heater 0 monitor 1 uses sensor 0 to generate a heater fault if the reading falls below 10.0°C Heater 0 monitor 2 is disabled
@doctrucker looks like it was changed in RRF 1.20?
@jay_s_uk I've skipped from RRF1 to RRF3. It was working when I did a full heater interlock test on RRF1 which I shared many months ago. Need to repeat that!
The meaning of the M143 P parameter was changed in RRF3. See https://duet3d.dozuki.com/Wiki/Gcode?revisionid=HEAD#Section_M143_Maximum_heater_temperature.
@dc42 perhaps flag a warning if no P parameter is used so it is harder to accidentally overwrite alarm conditions like I did?