    chamber heater alarms out expecting 1.8C/sec
    Using Duet Controllers
    1.0k
    • rexxundefined
      rexx
      my chamber will need about 10 min to get to temp evenly and soke the heat in and i was wondering wich was the easyiest way to this up
      also if i need to open the door during the active chamber it would need not to alarm out a fault i am just opening the door so i will loose a bit of heat calling for a no heat alarm
      oozeBotundefined 1 Reply Last reply Reply Quote 0
      • oozeBotundefined
        oozeBot @rexx
        @rexx I'm assuming you are running 3.4 or maybe 3.3 when the heater faults were updated? If so, you'll need to really "dumb down" the parameters. Here is what we settled on for our chamber heaters that works well all the way to 80c (highest we've tested).
        M307 H2 B1 C7200 D50 R0.01
        • rexxundefined
          rexx
          @oozebot said in chamber heater alarms out expecting 1.8C/sec:
          this is great thank you! i am looking for 80C too! i am 3.4 and will give it a try does this pass all the heating alarms even if you open the door for secrvice? as we know needs access to the door while under heating the chamber loads?
          • oozeBotundefined
            oozeBot @rexx
            @rexx yes, that will dumb it down enough where it will keep on heating with the doors open.. however, that obviously can cause other issues.
            • rexxundefined
              rexx
              also are you using bang bang or pid?i think i need bang bang for ssr controls
              • oozeBotundefined
                oozeBot @rexx
                @rexx Yes - bang bang. The "B1" in the M307 command I posted is what sets it.
                rexxundefined 1 Reply Last reply Reply Quote 1
                • rexxundefined
                  rexx @oozeBot
                  @oozebot
                  so C d or R sets the heating time out expected themistor or thermocouple feed back
                  is R0.01 under the .1 so .01 does that mean it ignores the .1-1 set points as it lower than the default swing?
                  big up from the newer guy if it has not been obvious... i thank you for your guidance
                  • rexxundefined
                    rexx
                    ;M307 H0 B1 C7200 D50 R0.01 does this look possible to you my chamber is 0
                    i am using 3-32VDC control side ssr to 120vac switching side and a thermocouple J tru daughter board
                    J is showing heats correctly on the chamber in DWC
                    • oozeBotundefined
                      oozeBot @rexx
                      @rexx check out the thread I linked below. I don't see any issue with your M307 as long as your chamber is heater 0.
                      With our current M307, here is what RRF is reporting:
                      Heater 2: heating rate 0.010, cooling rate 0.014, dead time 50.00, max PWM 1.00, mode bang-bang
                      https://forum.duet3d.com/topic/26733/3-4b7-7-chamber-heater-faults
                      • rexxundefined
                        rexx @oozeBot
                        @oozebot 👍 👍
                        lucky i can run the chamber with the doors open as the chamber was designed to run FLA full load amps continuiously if needed its only alarms that are an issue as long as the chamber fans are on i am good to draw endlessly if needed but wont be needed if you get me
                        • rexxundefined
                          rexx
                          ok so i tried it and it heated a tad bit longer before
                          Heater 0 fault: temperature rising too slowly: expected 0.76°C/sec measured -0.01°C/sec
                          elapsed time was like 4-5 sec on
                          oozeBotundefined 2 Replies Last reply Reply Quote 0
                          • oozeBotundefined
                            oozeBot @rexx
                            @rexx What that is saying is that the measured temp actually decreased between polling. Perhaps that is due to your doors being open? I guess I was thinking momentarily opening the doors, not leaving them open.
                            So your current M307 is?
                            rexxundefined 2 Replies Last reply Reply Quote 1
                            • rexxundefined
                              rexx @oozeBot
                              @oozebot
                              yes but the 5 sec is not enough time to get to the thermistor
                              my pannels are off for testing once i get heats on long enough i will close them but i can still touch the heater itself warm but not hot so the termocouple wont see it either if my hand cant tell either will the termistor 8" away
                              • rexxundefined
                                rexx @oozeBot
                                @oozebot
                                i feel a hair dryer on a relay to the thermocouple could keep the heater alarms happy "lol not doing jk"
                                • oozeBotundefined
                                  oozeBot @rexx
                                  @rexx Something that may have helped us out is that the probe for the chamber heater is mounted on our toolheads. We park it dead center of the build plate, a few mm up on Z, when preheating our machines.
                                  rexxundefined 1 Reply Last reply Reply Quote 0
                                  • rexxundefined
                                    rexx @oozeBot
                                    @oozebot
                                    Probe is in the chamber itself on the circulating side of the air return (OEM STRATASYS 768 chamber) so the probe will only get heat after the entire chamber starts to rise its not a small printer at all
                                    • oozeBotundefined
                                      oozeBot @rexx
                                      @rexx I'm afraid you are running up against the same issue we were able to overcome where the probe simply can't dip negative without causing a heater fault. Adding @dc42 for awareness.
                                      rexxundefined 2 Replies Last reply Reply Quote 0
                                      • oozeBotundefined
                                        oozeBot @rexx
                                        @rexx said in chamber heater alarms out expecting 1.8C/sec:
                                        I'm curious about this though. I would not have anticipated the "expected 0.76c/sec" with that M307. We were seeing errors like:
                                        Error: Heater 0 fault: temperature rising too slowly: expected -0.00°C/sec measured -0.01°C/sec
                                        do you have M141 set?
                                        https://duet3d.dozuki.com/Wiki/M141
                                        • rexxundefined
                                          rexx @oozeBot
                                          @oozebot of course it would be to easy to set and forget a simple heater why not use a time out call for heat only 2 min it should see a increase in temp 5 min should continue to see increases and 15 min the target must have been reached once to stay on
                                          add a temprature deviaton of 15% for opening the door
                                          its rocket science apparently but i thank you for your time today and efforts and shares in relation
                                          as for the probe on your head i cannot do this as i have a peltier cooling plate on the heat break to disable heat creeps but was not on during this testing
                                          • rexxundefined
                                            rexx @oozeBot
                                            @oozebot
                                            M141 H0 this is all 141 under chamber config.g