    Movement after M112 E-Stop!
    CNC
    3.6k
    • hpizundefined
      hpiz @dc42
      @dc42 From my experience, it would seem it is just continuing with the moves it was already performing. For example, I don't really see any behavior difference between the following two GCode jobs...
      G90
      G21
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      M112
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      vs
      G90
      G21
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      G1 Y500 Z100 F4000
      G1 Y600 Z0 F4000
      M112
      The M112 seems to be executed as it's read into the buffer, around the second movement loop, it then tries to complete the third loop after a brief stop (0.25 secs), nothing after M112 seems to ever try to execute, so that's good. Not sure if this matters, but the continued moves seem to move beyond where they should, which in my mind could only happen if more steps are sent than should. I'm gonna test my Duet 2 ethernet today (will post back maybe 2 hours from now) and see if it's got the same step continuation.
      As far as the code goes, I wish I could help more but I mostly make websites in C#. Though, I will keep trying.
      • hpizundefined
        hpiz @dc42
        @dc42 My Duet 2 does not produce pulses after M112 running 3.4.6
        Note: The scope is in trigger mode
        Duet2: M112 in job
        Duet2: Using DWC Endstop
          dc42 administrators @hpiz
          Thanks all, I'll be away at FormNext for a week but I'll look into this as a matter of urgency when I return.
          timschneiderundefined 1 Reply Last reply Reply Quote 0
          • timschneiderundefined
            timschneider @dc42
            @dc42 we have to thank you for your very fast response and in the middle of the preperation for the Formnext!
            @dc42 said in Movement after M112 E-Stop!:
            All, when you see this behaviour is it just the remainder of the current move that continues to execute after a pause?
            To check that, I did another test. Setup as above with SBC. Jobfile the following:
            G90
            G21
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            G1 Y0 F60
            G1 Y1 F60
            So every move is around 1 sec (F60 is within the jerk so i guess there is not much acceleration). Based on that, the delay should be less than 1-1.5s, but in fact, it is again around 3.5s (3.46s) as in all the samples above, regardless of the movement length and speed.
            So from my understanding, it is not only the remainder of the current move.
              timschneider @timschneider
              @timschneider
              I think the problem is in the IterateDrivers Function in the Platform.cpp
              the following code snippets are based on the 3.4-dev branch
              The else if branch will disable all extruders, but the problem is, that it will start working from GetTotalAxes() to MaxAxesPlusExtruders. But there are only MaxExtruders allowed.
              That means in numbers for the MB6XD
              MaxAxesPlusExtruders = 25
              GetTotalAxes() = 3 in this case XYZ
              MaxExtruders  = 16
              So from 3 - 24 it will work with the else if branch
              size_t LogicalDriveToExtruder(size_t drive) noexcept { return MaxAxesPlusExtruders - 1 - drive; }
              25 - 1 - 3 = 21
              25 - 1 - 4 = 20
              25 - 1 - 24 = 0
              DriverId extruderDrivers[MaxExtruders] -> array of 16 elements
              so the following code will read some random data for the elements from 3 - 8
              const DriverId id = extruderDrivers[LogicalDriveToExtruder(axisOrExtruder)];
              and this code will sometimes end up in the remoteFunc e.g. in our case send can message and wait for a reply
              if (id.IsLocal())
              	localFunc(id.localDriver);
              else
              	remoteFunc(id);
              but there will be no reply and this will delay the e-stop (stop step generation and clear the movement system) around 3 - 3.5 sec
              I've changed the IterateDrivers the following:
              // Function to identify and iterate through all drivers attached to an axis or extruder
              void Platform::IterateDrivers(size_t axisOrExtruder, function_ref<void(uint8_t)> localFunc, function_ref<void(DriverId)> remoteFunc) noexcept
              	if (axisOrExtruder < reprap.GetGCodes().GetTotalAxes())
              		for (size_t i = 0; i < axisDrivers[axisOrExtruder].numDrivers; ++i)
              			const DriverId id = axisDrivers[axisOrExtruder].driverNumbers[i];
              			if (id.IsLocal())
              			else
              				remoteFunc(id);
              	else if (axisOrExtruder >= (MaxAxesPlusExtruders - MaxExtruders) && axisOrExtruder < MaxAxesPlusExtruders)
              		if (id.IsLocal())
              		else
              			remoteFunc(id);
              But this will only address the delay - I think this is a good time to add a secondary layer to prevent the EnableSignale from getting high again. (Because of the delay, prepare moves where re-enableing the drivers again)
              platform.cpp
               src/Platform/Platform.cpp | 7 ++++---
               1 file changed, 4 insertions(+), 3 deletions(-)
              diff --git a/src/Platform/Platform.cpp b/src/Platform/Platform.cpp
              index c8f7793c..fdd6f2d3 100644
              --- a/src/Platform/Platform.cpp
              +++ b/src/Platform/Platform.cpp
              @@ -424,7 +424,7 @@ Platform::Platform() noexcept :
               #if HAS_MASS_STORAGE
               	logger(nullptr),
               #endif
              -	board(DEFAULT_BOARD_TYPE), active(false), errorCodeBits(0),
              +	board(DEFAULT_BOARD_TYPE), active(false), preventDriverEnable(true), errorCodeBits(0),
               	nextDriveToPoll(0),
               	lastFanCheckTime(0),
               #if SUPPORT_PANELDUE_FLASH
              @@ -861,6 +861,7 @@ void Platform::Init() noexcept
               	DuetExpansion::DueXnTaskInit();								// must initialise interrupt priorities before calling this
               #endif
               	active = true;
              +	preventDriverEnable = false;
               // Reset the min and max recorded voltages to the current values
              @@ -2439,7 +2440,7 @@ void Platform::IterateDrivers(size_t axisOrExtruder, function_ref<void(uint8_t)>
              -	else if (axisOrExtruder < MaxAxesPlusExtruders)
              +	else if (axisOrExtruder >= (MaxAxesPlusExtruders - MaxExtruders) && axisOrExtruder < MaxAxesPlusExtruders)
               		if (id.IsLocal())
              @@ -2572,7 +2573,7 @@ void Platform::DisableOneLocalDriver(size_t driver) noexcept
               // Enable the local drivers for a drive. Must not be called from an ISR, or with interrupts disabled.
               void Platform::EnableDrivers(size_t axisOrExtruder, bool unconditional) noexcept
              -	if (unconditional || driverState[axisOrExtruder] != DriverStatus::enabled)
              +	if (unconditional || (driverState[axisOrExtruder] != DriverStatus::enabled && !preventDriverEnable))
               		driverState[axisOrExtruder] = DriverStatus::enabled;
               		const float requiredCurrent = motorCurrents[axisOrExtruder] * motorCurrentFraction[axisOrExtruder];
              platform.h
               src/Platform/Platform.h | 5 ++++-
               1 file changed, 4 insertions(+), 1 deletion(-)
              diff --git a/src/Platform/Platform.h b/src/Platform/Platform.h
              index c3f006b4..4f2b2196 100644
              --- a/src/Platform/Platform.h
              +++ b/src/Platform/Platform.h
              @@ -528,7 +528,7 @@ public:
               	uint32_t GetSteppingEnabledDrivers() const noexcept { return steppingEnabledDriversBitmap; }
               	void DisableSteppingDriver(uint8_t driver) noexcept { steppingEnabledDriversBitmap &= ~StepPins::CalcDriverBitmap(driver); }
              -	void EnableAllSteppingDrivers() noexcept { steppingEnabledDriversBitmap = 0xFFFFFFFFu; }
              +	void EnableAllSteppingDrivers() noexcept { if (!preventDriverEnable) { steppingEnabledDriversBitmap = 0xFFFFFFFFu; } }
               #ifdef DUET3_MB6XD
               	bool HasDriverError(size_t driver) const noexcept;
              @@ -643,6 +643,8 @@ public:
               	const GpInputPort& GetGpInPort(size_t gpinPortNumber) const noexcept
               		pre(gpinPortNumber < MaxGpInPorts) 	{ return gpinPorts[gpinPortNumber]; }
              +	void SetPreventDriverEnable() noexcept { preventDriverEnable = true; }
               #if MCU_HAS_UNIQUE_ID
               	const UniqueId& GetUniqueId() const noexcept { return uniqueId; }
               	uint32_t Random() noexcept;
              @@ -742,6 +744,7 @@ private:
               #endif
               	bool active;
              +	bool preventDriverEnable;
               	uint32_t errorCodeBits;
               	void InitialiseInterrupts() noexcept;
              RepRap.cpp
               src/Platform/RepRap.cpp | 1 +
               1 file changed, 1 insertion(+)
              diff --git a/src/Platform/RepRap.cpp b/src/Platform/RepRap.cpp
              index 5d5a28aa..168619c4 100644
              --- a/src/Platform/RepRap.cpp
              +++ b/src/Platform/RepRap.cpp
              @@ -1004,6 +1004,7 @@ void RepRap::EmergencyStop() noexcept
               	else
               #endif
              +		platform->SetPreventDriverEnable(); // prevent any conditional call to EnableDrivers
               		platform->DisableAllDrivers();				// disable all local and remote drivers - need to do this to ensure that any motor brakes are re-engaged
               		switch (gCodes->GetMachineType())
              With these changes, there will be no delay at all after the estop is pressed in DWC and processed by RRF.
              timschneiderundefined dc42undefined 2 Replies Last reply Reply Quote 2
                @hpiz so I've recompiled a clean version of the 3.4-dev branch with only the IterateDrivers fix pull request on github.
                This is not a production version and only for testing purpose, it is based on the current 3.4-dev branch and only for MB6XD. Use on your own risk.
                Duet3Firmware_MB6XD.bin
                Maybe you can try, and we can see if this will fix the problem for you too.
                timschneiderundefined hpizundefined 2 Replies Last reply Reply Quote 0
                  @dc42 the missing MB6HC test.
                  MB6HC in standalone mode
                  following config
                  ; Enable network
                  M552 P0.0.0.0 S1
                  ;CNC Mode
                  M453                            ; Select CNC device mode
                  M669 K0 S2 T1
                  M584 X5 Y0.0:0.1:0.2:0.3 Z4             ; set drive mapping
                  M92 X160.00 Y320.00 Z640.00     ; set steps per mm
                  M566 X1800.00 Y180.00 Z120.00     ; set maximum instantaneous speed changes (mm/min)
                  M203 X15000.00 Y12000.00 Z5000.00 I5  ; set maximum speeds (mm/min)
                  M201 X400.00 Y200.00 Z200.00        ; set accelerations (mm/s^2)
                  ;M564 H0                         ; Allow stepper movement before homing
                  M208 X0 Y0 Z0 S1                ; set axis minima
                  M208 X600 Y1200 Z170 S0         ; set axis maxima
                  ;Machine Initialization
                  ;M18                          ; disable all steppers
                  ;M17                          ; enable z stepper so it doesn't fall
                  no delay.
                  with the following config (added stepper driver timings)
                  ; Enable network
                  M552 P0.0.0.0 S1
                  ;CNC Mode
                  M669 K0 S2 T1
                  M569 R0 P0 S0 T3:3:6:0
                  M569 R0 P1 S0 T3:3:6:0
                  M569 R0 P2 S0 T3:3:6:0
                  M569 R0 P3 S0 T3:3:6:0
                  M569 R0 P4 S0 T3:3:6:0
                  M569 R0 P5 S0 T3:3:6:0
                  the delay is there again. I think it will fill the following struct (slowDriversBitmap and slowDriverStepTimingClocks), and will cause IterateDrivers to send can messages.
                  	DriverId extruderDrivers[MaxExtruders];					// the driver number assigned to each extruder
                  #ifdef DUET3_MB6XD
                  ... disabled for MB6HC
                  #else
                  	uint32_t slowDriversBitmap;								// bitmap of driver port bits that need extended step pulse timing
                  	uint32_t slowDriverStepTimingClocks[4];					// minimum step high, step low, dir setup and dir hold timing for slow drivers
                  M112 in job file, because there is no enable signal turned on and off for the interal / smart drivers.
                  jobfile
                  G90
                  G21
                  G1 Y0 F60
                  G1 Y3 F60
                  G1 Y0 F60
                  G1 Y3 F60
                  M112
                  G1 Y0 F60
                  G1 Y1 F60
                  G1 Y0 F60
                  G1 Y1 F60
                  G1 Y0 F60
                  G1 Y1 F60
                  G1 Y0 F60
                  G1 Y1 F60
                  G1 Y0 F60
                  G1 Y1 F60
                  G1 Y0 F60
                  G1 Y1 F60
                  without driver timings:
                  with driver timings (same job file):
                  • hpizundefined
                    hpiz @timschneider
                    @timschneider said in Movement after M112 E-Stop!:
                    You sir, are a wizard. I spent probably 2 hours looking at the code and IterateDrives was not something I even looked at, I kept going back to the DisableAllDrivers in the platform, which I guess was in the ballpark for the enable signal, but I was mostly looking for step loop hangs.
                    I loaded up your firmware and after 6 tests (M112 in job, driver error, and DWC EStop) I was unable to get any motion after M112. Bravo, I think I'm gonna keep your firmware until dc42 takes the pull request and releases. I still have a lot of work to do on my machine, although I've taken like a two week break.
                      dc42 administrators @timschneider
                      @timschneider thanks for your detailed analysis!
                      I think the correct fix to IterateDrivers is to change the else if condition to this:
                      else if (axisOrExtruder < MaxAxesPlusExtruders && LogicalDriveToExtruder(axisOrExtruder) < reprap.GetGCodes().GetNumExtruders())
                      This will ensure that no action is taken if IterateDrivers is called with a logical drive number that is too high to be an axis but too low to be an extruder.
                      I agree that an additional layer of protection is needed to guard against CAN delays so I will review your solution, although I think there may already be an 'active' flag that we could use for this purpose.
                      EDIT: I've reviewed your code that add the preventDriverEnable flag and I don't think it will have the desired effect; because function EnableAllSteppingDrivers doesn't actually enable drivers, it just clears the "don't step" flag that gets set during homing of an axis that has multiple motors with separate endstops. So instead I've changed Move::MoveLoop to self-terminate the Move task when emergency stop has been commanded, thereby preventing further calls to DDA::Prepare.
                      These changes are now committed to the 3.5-dev branch of RRF. Please test them on your machine.
                      timschneiderundefined 1 Reply Last reply Reply Quote 1
                        timschneider @dc42
                        I agree that this "else if" check is much better, more future proof and less error prone, just note the performance degradation due to calling LogicalDriveToExtruder twice. I am not aware if this can be solved at compile time.
                        I wouldn't have dared to even consider the change, but in the end it should be safe - and that looks safe to me.
                        I'll compile and check each part alone and post results.
                        Tim
                          @timschneider thanks. The LoigicalDriveToExtruder function is inlined, so I expect the compiler to optimise the two calculations into one.
                          Edit: yes the second call is optimised away. Here's the start of the else-if:
                          4652              	.L545:
                          4653 0082 1F29     		cmp	r1, #31
                          4654 0084 FAD8     		bhi	.L544
                          4655 0086 C1F11F01 		rsb	r1, r1, #31
                          4656 008a D3F8F832 		ldr	r3, [r3, #760]
                          4657 008e 8B42     		cmp	r3, r1
                          4658 0090 F4D9     		bls	.L544
                          4659 0092 00EB4100 		add	r0, r0, r1, lsl #1
                          4660 0096 B0F8843A 		ldrh	r3, [r0, #2692]
                          4661 009a C3F30724 		ubfx	r4, r3, #8, #8
                          4662 009e ADF81030 		strh	r3, [sp, #16]	@ movhi
                          4663 00a2 FFF7FEFF 		bl	_ZN12CanInterface13GetCanAddressEv
                          4664 00a6 8442     		cmp	r4, r0
                          4665 00a8 0AD0     		beq	.L555
                            timschneider @dc42
                            I think it is a success!
                            without the IterateDrivers fix there is a small delay 1.34s in the step generation shut down, but the drivers are not re-enabled.
                            with both patches 'no' delay at all.
                            dc42undefined 1 Reply Last reply Reply Quote 3
                              @timschneider, many thanks for your thorough testing and for diagnosing the cause of the problem. I'll mark https://github.com/Duet3D/RepRapFirmware/issues/927 as fixed in 3.5. If/when we release 3.4.7 the fix will be in that version too. I've already back-ported the fix to the 3.4-dev source code.
                              dc42 created this issue in Duet3D/RepRapFirmware
                              closed M112 doesnt stop all movement #927