    M307: bad model parameters with Beta3.2 LPC

    Scheduled Pinned Locked Moved
    LPC
    3
    5
    646
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • MarMedundefined
      MarMed
      last edited by Phaedrux

      With beta3.2 I am getting the following error from setting the model parameters for my chamber heater

      M307 H2 B1 A29.9 C1151.3 D55
      Error: M307: bad model parameters
      

      on previous versions the parameters would set correctly.

      11/19/2020, 11:37:31 AM	M307 H2
      Heater 2 model: gain 29.9, time constant 1151.3, dead time 55.0, max PWM 1.00, calibration voltage 0.0, mode bang-bang
      11/19/2020, 11:37:28 AM	M307 H2 B1 A29.9 C1151.3 D55
      

      just to note, the parameters used is from previous RRF3.2 betas, but with the bad curve error, due to dead time being negative I used the recommendation here to measure and set the dead time manually.

      Additionally I receive a bad curve fit using the new tuning algorithm, is there a similar workaround using the new tuning?

      RRF3.2 Beta3.2 on LPC

      Thanks

      1 Reply Last reply Reply Quote 0
      • Vetiundefined
        Veti
        last edited by

        thin post needs to be moved to the lpc sub forum

        1 Reply Last reply Reply Quote 0
        • dc42undefined
          dc42 administrators
          last edited by dc42

          @MarMed, when you ran heater tuning under 3.2beta3.2, what parameters did it report when it gave the bad curve fit message?

          The gain of your heater looks very low and the dead time very high.

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          MarMedundefined 1 Reply Last reply Reply Quote 0
          • MarMedundefined
            MarMed @dc42
            last edited by

            @dc42
            This is on beta4.1

            Warning: Auto tune of heater 2 failed due to bad curve fit (R=0.030, C=0.001:0.000, D=2.3)
            

            I think the problem may be a combination of a very low power heater(250w), and the situation that the heated bed gets the chamber close to the target temperature already, around 50C and I then use the the chamber heater to reach a stable 60C.

            I've tried many combinations when tuning, with hotend and bed heater off, with hotend and bed heater on, and setting the ambient temperature. Each tuning takes 5h+ before it fails.

            Any idea why my old heater parameters is giving me an error now?

            M307 H2 B1 A29.9 C1151.3 D55
            Error: M307: bad model parameters
            

            is there manual parameters that might work with my setup in 3.2?

            Help is appreciated.

            1 Reply Last reply Reply Quote 0
            • dc42undefined
              dc42 administrators
              last edited by

              I have identified the problem and implemented a fix in 3.2RC1.

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              1 Reply Last reply Reply Quote 1