chamber heater alarms out expecting 1.8C/sec
my chamber will need about 10 min to get to temp evenly and soke the heat in and i was wondering wich was the easyiest way to this up
also if i need to open the door during the active chamber it would need not to alarm out a fault i am just opening the door so i will loose a bit of heat calling for a no heat alarm -
@rexx I'm assuming you are running 3.4 or maybe 3.3 when the heater faults were updated? If so, you'll need to really "dumb down" the parameters. Here is what we settled on for our chamber heaters that works well all the way to 80c (highest we've tested).
M307 H2 B1 C7200 D50 R0.01
@oozebot said in chamber heater alarms out expecting 1.8C/sec:
this is great thank you! i am looking for 80C too! i am 3.4 and will give it a try does this pass all the heating alarms even if you open the door for secrvice? as we know needs access to the door while under heating the chamber loads?
@rexx yes, that will dumb it down enough where it will keep on heating with the doors open.. however, that obviously can cause other issues.
also are you using bang bang or pid?i think i need bang bang for ssr controls
@rexx Yes - bang bang. The "B1" in the M307 command I posted is what sets it.
@oozebot
so C d or R sets the heating time out expected themistor or thermocouple feed back
is R0.01 under the .1 so .01 does that mean it ignores the .1-1 set points as it lower than the default swing?big up from the newer guy if it has not been obvious... i thank you for your guidance
;M307 H0 B1 C7200 D50 R0.01 does this look possible to you my chamber is 0
i am using 3-32VDC control side ssr to 120vac switching side and a thermocouple J tru daughter board
J is showing heats correctly on the chamber in DWC -
@rexx check out the thread I linked below. I don't see any issue with your M307 as long as your chamber is heater 0.
With our current M307, here is what RRF is reporting:
Heater 2: heating rate 0.010, cooling rate 0.014, dead time 50.00, max PWM 1.00, mode bang-bang https://forum.duet3d.com/topic/26733/3-4b7-7-chamber-heater-faults
lucky i can run the chamber with the doors open as the chamber was designed to run FLA full load amps continuiously if needed its only alarms that are an issue as long as the chamber fans are on i am good to draw endlessly if needed but wont be needed if you get me
ok so i tried it and it heated a tad bit longer before
Heater 0 fault: temperature rising too slowly: expected 0.76°C/sec measured -0.01°C/sec
elapsed time was like 4-5 sec on -
@rexx What that is saying is that the measured temp actually decreased between polling. Perhaps that is due to your doors being open? I guess I was thinking momentarily opening the doors, not leaving them open.
So your current M307 is?
@oozebot
yes but the 5 sec is not enough time to get to the thermistor
my pannels are off for testing once i get heats on long enough i will close them but i can still touch the heater itself warm but not hot so the termocouple wont see it either if my hand cant tell either will the termistor 8" away -
@oozebot
i feel a hair dryer on a relay to the thermocouple could keep the heater alarms happy "lol not doing jk" -
@rexx Something that may have helped us out is that the probe for the chamber heater is mounted on our toolheads. We park it dead center of the build plate, a few mm up on Z, when preheating our machines.
@oozebot
Probe is in the chamber itself on the circulating side of the air return (OEM STRATASYS 768 chamber) so the probe will only get heat after the entire chamber starts to rise its not a small printer at all -
@rexx said in chamber heater alarms out expecting 1.8C/sec:
I'm curious about this though. I would not have anticipated the "expected 0.76c/sec" with that M307. We were seeing errors like:
Error: Heater 0 fault: temperature rising too slowly: expected -0.00°C/sec measured -0.01°C/sec
do you have M141 set?
@oozebot of course it would be to easy to set and forget a simple heater why not use a time out call for heat only 2 min it should see a increase in temp 5 min should continue to see increases and 15 min the target must have been reached once to stay on
add a temprature deviaton of 15% for opening the doorits rocket science apparently but i thank you for your time today and efforts and shares in relation
as for the probe on your head i cannot do this as i have a peltier cooling plate on the heat break to disable heat creeps but was not on during this testing
@oozebot
M141 H0 this is all 141 under chamber config.g