    • Craigundefined
      Craig
      last edited by Craig

      I went to the Gcode console and typed M307 H0 B1 and the heater went to fault and I got a message about using the wrong channel.

      1 Reply Last reply Reply Quote 0
      • Craigundefined
        Craig
        last edited by Craig

        If the M305 command for a real heater does not specify a sensor channel and the heater has not been configured yet, then it defaults to using the thermistor associated with that heater.

        What the heck does this mean?

        deckingmanundefined 1 Reply Last reply Reply Quote 0
        • Dinoundefined
          Dino
          last edited by

          Is your SSR hooked up the right way? When I first set mine up I had the polarity backwards and it wouldn't heat when I tried to tune it. I flipped the leads going into it and it's been fine ever since.

          1 Reply Last reply Reply Quote 0
          • mrehorstdmdundefined
            mrehorstdmd @Craig
            last edited by mrehorstdmd

            @craig said in M307 vs. M301:

            Pretty easy. Any reason you can think of that the RepRap Configutor I was directed to by Duet 3d doesn't work?

            The configurator will set the heaters up with M301 commands because it has not kept up with firmware changes. M307 is now the command to use for heater set-up.

            See: https://duet3d.dozuki.com/Wiki/Gcode#Section_M307_Set_or_report_heating_process_parameters

            Bang-bang mode on the bed heater often leads to Z banding in prints. PID regulates the temperature which prevents that type of Z banding in the prints, and is built into the firmware, so there's really no reason not to use it. All you have to do is turn it on and configure it.

            How many heaters does your printer use, and which connections are you using on the board for them? Which thermistor connections are you using?

            I just set up my machine with a Duet Ethernet board about a week ago.

            https://drmrehorst.blogspot.com/

            Craigundefined 1 Reply Last reply Reply Quote 0
            • deckingmanundefined
              deckingman @Craig
              last edited by

              @craig said in M307 vs. M301:

              If the M305 command for a real heater does not specify a sensor channel and the heater has not been configured yet, then it defaults to using the thermistor associated with that heater.

              What the heck does this mean?

              Well it kind of means what it says. The sensor channel is the "X" parameter and you can change it to use some channel other than it's default. On the same page, a bit further down it says "Xnnn Heater ADC channel, or thermocouple or PT100 adapter channel; defaults to the same value as the P parameter"

              Ian
              https://somei3deas.wordpress.com/
              https://www.youtube.com/@deckingman

              1 Reply Last reply Reply Quote 0
              • Craigundefined
                Craig @mrehorstdmd
                last edited by

                @mrehorstdmd My printer is a delta with 330 mm non-moving bed. It is heated by 120 volt 800w heater on an SSR. My experience is that using PID values will over switch the SSR and kill it. On my current printer I use the bang bang method with no problems.

                1 Reply Last reply Reply Quote 0
                • Jacotheronundefined
                  Jacotheron
                  last edited by

                  As @Craig said, one should never use PID/PWM with a relay - a mechanical relay will burn the contacts if you draw a large enough current through it and make a lot of noise until it stops working; for SSR you also don't wan't PWM signals, since most of them are 0-crossing relays (they switch off when the current cross over the 0 mark - in AC), which means it can at the fastest switch off at double the frequency of your mains (since it crosses the 0 mark 2 times in each wave), and PWM runs at KHz or MHz.

                  The banding issue mentioned above is specific for hot-ends, which ideally should be run with PID/PWM. For the heatbed, Bang Bang is good (that is how I run mine, even using the internal Mosfet for the heatbed, with sub 1C fluctuations).

                  Craigundefined 1 Reply Last reply Reply Quote 0
                  • Craigundefined
                    Craig @Jacotheron
                    last edited by

                    @jacotheron Thanks for the confirmation and info!

                    1 Reply Last reply Reply Quote 0
                    • mrehorstdmdundefined
                      mrehorstdmd
                      last edited by

                      According to the wiki, M307 has an F parameter that allows you to control the PWM frequency.

                      https://drmrehorst.blogspot.com/

                      1 Reply Last reply Reply Quote 0
                      • deckingmanundefined
                        deckingman
                        last edited by deckingman

                        Quote from the Wiki ...

                        "When using PID to control the bed heater, RepRapFirmware uses a low PWM frequency (10Hz) so as to be compatible with all standard types of SSR."

                        https://duet3d.dozuki.com/Wiki/Choosing_a_bed_heater

                        Been using an SSR in PID mode on my 240v 800 Watt bed heater for about 2 years - no probs.

                        Ian
                        https://somei3deas.wordpress.com/
                        https://www.youtube.com/@deckingman

                        1 Reply Last reply Reply Quote 0
                        • Danalundefined
                          Danal
                          last edited by Danal

                          Another confirmation: I'm using a 600MM Diameter 110/120V mains 1400 Watt heater on a delta, via an SSR. Low Voltage side of SSR is wired to Duet heater terminals (screw terminals). Heater is stuck directly to the bottom of 6mm thick 608mm diameter glass. No aluminum at all. Temps are VERY stable, and heating is quick.

                          My M307 is all defaults:

                          M307 H0
                          Heater 0 model: gain 90.0, time constant 700.0, dead time 10.0, max PWM 1.00, calibration voltage 0.0, mode bang-bang, inverted no, frequency default

                          0_1530201499812_IMG_1493.JPG

                          Delta / Kossel printer fanatic

                          1 Reply Last reply Reply Quote 1