Hi,
I have the same problem, when I try to reset my password and login again I have this message : "Warning: Your account has exceeded allowed number of login attempts. Please try again in 1 hour".
Hi,
I have the same problem, when I try to reset my password and login again I have this message : "Warning: Your account has exceeded allowed number of login attempts. Please try again in 1 hour".
Hi everyone, thank you for your comments, I found the problem, I just replaced the GND cable of the Due2x.
No the steer drivers on the DueX2 are cold, the DueX2 is mounted on pla printed box without any metal screws , I make some tests, after removing all on Duetwifi ( steper motor, heater, switch, fan, sd card ),the message is displayed just with the main power ( 24v) turned on.
Thank, but I have make the modifications , now the config is :
config.g
; Z probe
M307 H5 A-1 C-1 D-1
M558 P5 X0 Y0 Z1 H5 F120 T6000
retractprobe.g
M280 P5 S90
deployprobe.g
M280 P5 S10
For the BLTouch the trace was cut (it's a BLTouch smart), but I have the same message "Error: Short-to-ground on drivers 5 6. Error: Over temperature shutdown on drivers 5 6"
a duetx2, the blotch work perfectly, my config is :
M307 H5 A-1 C-1 D-1
M558 P7 X0 Y0 Z1 H5 F120 T6000
G31 X0 Y0 Z0 P25
but I have this message every 5 seconds ""Error: Short-to-ground on drivers 5 6. Error: Over temperature shutdown on drivers 5 6"
When I connect my new Duetx2, I have this continuous message "Error: Short-to-ground on drivers 5 6. Error: Over temperature shutdown on drivers 5 6", There's no stepper motor connected to the duetx2, just the bltouch.
When I connect the new duetx2I have this message "Error: Short-to-ground on drivers 5 6, Error: Over temperature shutdown on drivers 5 6" . I don't use the stepper motor 5 and 6. just the servo output for the bltouch (It works well).