    Regular periodic loss of heater values in V3.2.10
    PanelDue
    305
    • OwenDundefined
      OwenD
      I am seeing regular loss of heater values for about 1 second on V3.2.10
      See video
      https://www.dropbox.com/s/1z4o3mstjd512wm/IMG_1560.MOV?dl=0
      • OwenDundefined
        OwenD
        I've traced this to the fact that I am running temperature checks in daemon.g however I can't figure out what is causing the Panel Due to blink.
        The blinking is only on active heaters, so must be related to the section of the macro that checks active heaters.
        Here is my daemon.g
        The {1}'s that appear are not in the code. The forum adds them for some reason.
        ; 0:/sys/daemon.g
        ; runs continually in background at approximately 1Hz if not delayed internally
        ;BEGIN HEATER CHECKS
        ; this section of daemon.g checks for heater faults
        ; RRF doesn't currently check for faults when idle but by default will shutdownduring printing if temperature excursion is > 15 degrees.
        ; Note: temp excursion value and time  may be manually set using M570
        ; checking if temp is rising requires a variable.  I have used a dummy tool offset (Tool2)  for this and to do elapsed time since last check
        ; G4 could be used but would also delay anything else in daemon.g
        ; this way allows other checks to run more frequently if needed however the G4 delays inside the loop will affect the frequency of daemon.g
        ; will be updated when variables are available in RRF.
        while iterations < #heat.heaters ; loop through all configured heaters
        	if state.upTime < 60
        		break; If uptime is < 60 seconds, break out so all fans etc have time to stabilise.
        	if ((tools[2].offsets[1]+10) > state.upTime) ; if checked in last 10 seconds escape loop and go to rest of daemon.g if present.  offset will be zero at startup via config.g
        		;echo "skipping loop " ^ " " ^ state.upTime  ^ " " ^ tools[2].offsets[1]+10
        		if tools[2].offsets[1] - state.upTime > 60 ; uptime must have rolled over so reset off set to zero
        			G10 P2 Y0
        			echo "upTime has rolled over.  Heater checking reset"
        		break
        	;echo "checking heater " ^ iterations ^ " " ^ state.upTime  ^ " " ^ tools[2].offsets[1]+10
        	if heat.heaters[iterations].state="tuning"
        		;echo "heater " ^ iterations ^ " is tuning - no check carried out"
        		continue ; don't check this heater as it is PID auto tuning
        	if (heat.heaters[iterations].current) > (heat.heaters[iterations].max) ; temp is over max so emergency shutdown required
        		;M41 P5 S1  ; activate output connected to externally powered latching relay here to sound alarm
        		echo "heater over max temp fault detected in daemon.g.  - shutting down"
        		M112; emergency shutdown
        		M81 S1 ; turn off power when fans have turned off
        	if (heat.heaters[iterations].current > 45) ; no real danger at below this temp as ambient may be close to this
        		;echo "heater " ^ iterations ^ " is above 45 degrees"
        		if (heat.heaters[iterations].state!="off") && (heat.heaters[iterations].current > heat.heaters[iterations].active + 15) ; temp is > 15 degrees above target.
        		;echo "heater " ^ iterations ^ " is on or in standby - checking if temp is rising"
        			G10 P2 X{heat.heaters[iterations].current} ; set dummy tool X offset to current temp of heater
        			G4 S3 ; wait 3 seconds
        			if (heat.heaters[iterations].current > tools[2].offsets[0] + 0.5) ; heat is rising by more than 0.5 degrees in 3 seconds
        				echo "heater runaway fault detected in daemon.g.  - shutting down"
        				if (state.status=="processing")
        					M25 ; pause print so you might be able to save it using M119
        				M0 ; unconditional stop.  If axes are homed and a print is being canceled will run cancel.g  otherwise will run stop.g
        			else
        				;echo "heater is on or standby but temp is falling on heater " ^ iterations ^ " - no action needed"
        		elif (heat.heaters[iterations].state="off") && ((heat.heaters[iterations].current) >= (fans[1].thermostatic.lowTemperature+0)) ; if heater is off and temp is greater than 50 there could be an issue
        			;echo "heater " ^ iterations ^ " is off but checking if temp is rising"
        				;echo "heater is off but temp is rising on heater " ^ iterations ^ "emergency shutdown"
        			else
        				;echo "heater is off & temp is falling or stable on heater " ^ iterations ^ " - no action needed"
        	else
        		;heater is below 45 degrees so only other fault may be an open circuit thermistor which should show -275 degrees
        		if heat.heaters[iterations].current < 0 ; we probably have a thermistor fault if heater is less than 0 degrees
        			M112 ; emergency shutdown
        	;Check if water pump is running correctly - we don't need to check this so often, so only check on first iteration
        	if (iterations=1) && ((heat.heaters[1].current) > (fans[1].thermostatic.lowTemperature+0))
        		if fans[1].rpm <= 500 ; Coolant pump RPM off or low
        			echo "Water pump fault - shutting down heaters - RPM : " ^ fans[1].rpm
        		elif (fans[1].rpm > 500) && (fans[1].rpm < 1400)
        			echo "WARNING: Water pump RPM low - RPM : " ^ fans[1].rpm
        		else
        			;echo "Coolant OK - RPM : "  ^ fans[1].rpm
        		if fans[5].rpm <=1000
        			echo "WARNING: Water pump FAN RPM low - RPM : " ^ fans[5].rpm
        	if iterations == #heat.heaters-1 ; all heaters have been checked
        		G10 P2 Y{state.upTime} ; set the new time to check again
        ; END HEATER CHECKS
        ; run other checks below this line
        • wilrikerundefined
          wilriker @OwenD
          @OwenD Sorry I didn't reply earlier. Just so I get this right: the issue does not appear without your daemon.g, correct?
          Manuel
          My Tool Collection
          OwenDundefined 2 Replies Last reply Reply Quote 0
          • OwenDundefined
            OwenD @wilriker
            @wilriker
            That is correct
            It also doesn't appear if the tool is off, only when active or on standby.
            My code ignores tools that are off unless the temp is rising so it must be the other sections causing it but I can't figure how or why.
            There is no effect on printing except that if you try to set a temp on the Paneldue and it blinks before you finish, the value is reset to zero.
            The time between blinks is approximately 10 seconds which is likely a multiple of the three second delays where I determine if the temp is rising or falling.
            Also updated to 3.2.11 and regressed back several versions with no change.
            • OwenDundefined
              OwenD
              Config.g
              ; generated by RepRapFirmware Configuration Tool v2.1.4 on Sat Jan 04 2020 09:46:45 GMT+1000 (Australian Eastern Standard Time)
              ; serial comms / Paneldue
              M575 P1 B57600 S1
              ; set up serial connection to paneldue
              G90                                                         ; send absolute coordinates...
              M83                                                         ; ...but relative extruder moves
              M550 P"3Dprinter"                                       	; set printer name
              M554 P192.168.1.1											; set gateway
              M553 P255.255.255.0											; set netmask
              M552 S1 P"XXXXXXX"                                             ; enable network
              M586 P0 S1                                                  ; enable HTTP
              M586 P1 S1                                                  ; enable FTP
              M586 P2 S0                                                  ; disable Telnet
              M569 P0 S1                                                  ; physical drive 0 (X) goes forwards
              M569 P1 S0                                                  ; physical drive 1 (Y) goes backwards
              M569 P2 S1                                                  ; physical drive 2 (Z) goes forwards
              M569 P3 S0                                                  ; physical drive 3 (E0) goes backwards
              M584 X0 Y1 Z2:4 E3											; two Z motors connected to driver outputs Z and E1
              M671 X-74:240 Y79:79 S5.5 									; leadscrews at left (connected to Z) and right (connected to E1) of X axis
              M350 X16 Y16 Z16 I1                           				; Configure microstepping with interpolation for XYZ
              M350 E16 I1													; Configure microstepping with interpolation for E0
              M92 X100.00 Y100.00 Z400.00                            		; set steps per mm XYZ
              ;M92 E83.151												; set steps for bowden
              M92 E854										; set E steps/mm for Titan Aero
              ; axis settings
              M98 P"0:/sys/set_max_speeds.g" ; set all the max speeds in macro as these are adjusted during home moves so we only want to adjust in one spot
              M906 X1100 Y1100 Z1100 E1400 I30                             ; set motor currents (mA) and motor idle factor in per cent
              M84 S30                                                     ; Set idle timeout
              M208 X0:215 Y0:198 Z0:180 									; X carriage moves from 0 to 200, Y bed goes from 0 to 198
              M574 X1 S1 P"xstop"                                         ; configure active-high endstop for low end on X via pin xstop
              M574 Y1 S1 P"ystop"                                         ; configure active-high endstop for low end on Y via pin ystop
              M574 Z1 S2                                                  ; configure Z-probe endstop for low end on Z
              M950 S0 C"exp.heater3"                                      ; create servo pin 0 for BLTouch
              M558 P9 C"^zprobe.in" H6 F120 T2400 A10 S0.03 R0.5 B0         ; set Z probe type to bltouch and the dive height + speeds
              G31 P500 X27 Y-2 Z0.48                                  	; set Z probe trigger value, offset and trigger height
              M557 X30:200 Y10:180 S30                                    ; define mesh grid
              M308 S0 P"bedtemp" Y"thermistor" A"Bed" B3950 C7.06e-8         		; configure sensor 0 as thermistor on pin bedtemp
              M950 H0 C"bedheat" T0 Q10                                       ; create bed heater output on bedheat and map it to sensor 0 and set PWM frequency to 10hz
              M140 H0 																		; Set bed themp to zero
              M143 H0 S130 A0 C0                                          ; set temperature limit for heater 0 to 130C - fault if too high
              M308 S1 P"e0temp" Y"thermistor" A"Nozzle-1" B4725 C7.06e-8          		; configure sensor 1 as thermistor on pin e0temp
              M950 H1 C"e0heat" T1                                        ; create nozzle heater output on e0heat and map it to sensor 1
              M143 H1 S285 A0 C0                                          ; set temperature limit for heater 1 to 280C - fault if too high
              ; Set PID autotune parameters
              M307 H0 R0.553 C379.7 D21.16 S0.80 B0 V0
              M307 H1 R2.354 C140.7:139.6 D7.38 S1.00 V24.3							;set PID values for heater 1 (hotend)
              ; Joystick
              M308 S3 P"exp.thermistor4" Y"linear-analog" A"JoyStick-X" F1 B100 C-100 ; set analog input on E3 Temp with min/max of -100 to 100
              M308 S4 P"exp.thermistor6" Y"linear-analog" A"JoyStick-Y" F1 B100 C-100 ; set analog input on E5 Temp with min/max of -100 to 100
              M581 T7 P7 ; set up trigger for GpIn 7
              M950 J7 C"!^exp.31" 										; Input 7 uses Expansion 31 pin activate pullup and inverted
              ; Servos and input/output
              M950 P5 C"exp.e5_stop" 										; Output 5 uses E5_STOP  pin
              M950 J6 C"exp.e6_stop" 										; Input 6 uses E6_STOP  pin
              ; Filament monitor
              M591 P1 C"e0stop" S1  D0 									; filament monitor for extruder 0 connected to E0 endstop
              M950 F0 C"fan0" Q50                                        ; create fan 0 on pin fan0 and set its frequency
              M106 P0 C"Part_Fan" S0 B2.0 H-1                             ; set fan 0 name and value. Thermostatic control is turned off
              																; Adjust MCU temp reading to match ambient
              ;water pump
              M950 F1 C"!fan1+^exp.pb6" Q25000                             ; create fan 1 (water pump) on inverted pin fan1 and set its frequency.  Set RPM to E3 stop with pullup enabled
              M106 P1 C"Water Pump" H1 L0.5 X1 B1.2  T50:60                       ; set fan 1 name and value. Thermostatic control is turned on.  Monitoring hoted sensor
              ; water temp monitor & fan
              M950 F5 C"!fan2+^exp.e3_stop" Q25000                                        ; create fan 2 on pin fan2 and set its frequency
              M308 S5 P"e1temp" Y"thermistor" A"Water temp" T10000 B3950  					; Configure Water temp sensor
              M106 P5 C"Radiator Fan" H5 L0 X1 B1.2  T30:34    	; set fan 4 value, turn on at 30% if the water temperature reaches 30C, and increase to full speed gradually as the temperature rises to 40C
              ; MCU temp sensor
              M308 S2 P"mcu-temp" Y"mcu-temp" A"Duet Board" 					; Configure MCU sensor
              ; Calibrate MCU temp
              M912 P0 S-4
              ; create dummy fan so we can use variables
              M950 F3 C"duex.fan3" Q0                                       ; create fan 3 on pin and set its frequency
              M106 P3 C"No_Filament" S0 X255 H-1
              M563 P0 S"Extruder1" D0 H1 F0                               ; define tool 0
              G10 P0 X0 Y0 Z0                                             ; set tool 0 axis offsets
              G10 P0 R0 S0  ; set initial tool 0 active and standby temperatures to 0C
              ; create dummy tool so we can store some variables
              M563 P2 S"DummyTool"                              ; define dummy tool 2
              G10 P2 X0 Y0 Z0                                   ; set tool 2 axis offsets
              G10 P2 R0 S0  ; set initial tool 2 active and standby temperatures to 0C
              ;Select tool zero
              T0 P0
              ; extrusion
              if move.extruders[state.currentTool].filament=""
              	echo "No filament loaded.  Cold extrude & retract set to defaults"
              	M302 S190 R110 ; Allow extrusion starting from 190°C and retractions already from 110°C (defaults)
              else
              	echo "Filament loaded.  Set values per config for filament"
              	M703 ; if a filament is loaded, set all the heats and speeds for it by loading config.g
              	M106 P3 C{move.extruders[state.currentTool].filament} S0 H-1
              ; Custom settings
              M376 H4   ; set bed compensation taper (H4 means taper over 4mm)
              ; Power failure recovery
              M911 S22.5 R23.0 P"M42 P5 S0 M106 P0 S0 M913 X0 Y0 G91 M83 G1 Z3 E-2 F1000" ; If power drops below 22v then turn off fans, Set X & Y current to zero, raise head, retract.
              ; Set some variables for later re-usen( not yet possible)
              ; var Bed_Center_Probe_Point_X =move.compensation.probeGrid.xMax-move.compensation.probeGrid.xMin)/2) + move.compensation.probeGrid.xMin - sensors.probes[0].offsets[0]
              ; var Bed_Center_Probe_Point_Y = (move.compensation.probeGrid.yMax-move.compensation.probeGrid.yMin)/2) + move.compensation.probeGrid.yMin - sensors.probes[0].offsets[1]
              ; turn on LED strip driven by P5 output
              M42 P5 S1
              ;play startup tune
              G4 S8					; Allow time for PanelDue to start & wifi connection etc
              M98 P"0:/macros/songs/itchyscratchy.g"								; Play tune
              M501 ; load config-overide.g
              Config.overide.g
              ; config-override.g file generated in response to M500 at 2021-02-20 20:22
              ; Heater model parameters
              M307 H0 R0.553 C379.700:379.700 D21.16 S0.80 V0.0 B0
              M307 H1 R2.417 C224.955:141.453 D6.01 S1.00 V24.3 B0
              ; Workplace coordinates
              G10 L2 P1 X0.00 Y0.00 Z0.00
              G10 L2 P2 X0.00 Y0.00 Z0.00
              G10 L2 P3 X0.00 Y0.00 Z0.00
              G10 L2 P4 X0.00 Y0.00 Z0.00
              G10 L2 P5 X0.00 Y0.00 Z0.00
              G10 L2 P6 X0.00 Y0.00 Z0.00
              G10 L2 P7 X0.00 Y0.00 Z0.00
              G10 L2 P8 X0.00 Y0.00 Z0.00
              G10 L2 P9 X0.00 Y0.00 Z0.00
              M486 S-1
              M122
              M122
              RepRapFirmware for Duet 2 WiFi/Ethernet version 3.2.2 running on Duet WiFi 1.02 or later
              Board ID: 08DGM-917NK-F2MS4-7J1DA-3S86T-TZTWD
              Used output buffers: 3 of 24 (20 max)
              Static ram: 23460
              Dynamic ram: 74708 of which 80 recycled
              Never used RAM 13832, free system stack 97 words
              Tasks: NETWORK(ready,135) HEAT(blocked,308) MAIN(running,377) IDLE(ready,20)
              Owned mutexes: WiFi(NETWORK)
              Last reset 07:45:00 ago, cause: software
              Last software reset at 2021-02-20 22:48, reason: User, GCodes spinning, available RAM 14284, slot 2
              Error status: 0x10
              Aux0 errors 0,0,0
              MCU temperature: min 26.4, current 27.1, max 31.6
              Supply voltage: min 24.1, current 24.3, max 24.5, under voltage events: 0, over voltage events: 0, power good: yes
              Driver 0: position 1500, standstill, SG min/max 0/1023
              Driver 1: position 18300, standstill, SG min/max 0/459
              Driver 2: position 21160, standstill, SG min/max 0/116
              Driver 3: position 0, standstill, SG min/max 0/1023
              Driver 4: position 0, standstill, SG min/max 0/139
              Driver 5: position 0
              Driver 6: position 0
              Driver 7: position 0
              Driver 8: position 0
              Driver 9: position 0
              Driver 10: position 0
              Driver 11: position 0
              Date/time: 2021-02-21 06:33:38
              Slowest loop: 397.12ms; fastest: 0.17ms
              === Storage ===
              Free file entries: 10
              SD card longest read time 1.7ms, write time 391.0ms, max retries 0
              DMs created 83, maxWait 713668ms, bed compensation in use: none, comp offset 0.000
              === MainDDARing ===
              Scheduled moves 98341, completed moves 98341, hiccups 0, stepErrors 0, LaErrors 0, Underruns [0, 0, 143], CDDA state -1
              === AuxDDARing ===
              Segments left: 0
              Movement lock held by null
              HTTP is idle in state(s) 0
              Telnet is idle in state(s) 0
              File is idle in state(s) 0
              USB is idle in state(s) 0
              Aux is idle in state(s) 0
              Trigger is idle in state(s) 0
              Queue is idle in state(s) 0
              LCD is idle in state(s) 0
              Daemon is idle in state(s) 0
              Code queue is empty.
              === Network ===
              Slowest loop: 393.30ms; fastest: 0.00ms
              HTTP sessions: 1 of 8
              - WiFi -
              Network state is active
              WiFi firmware version 1.25
              WiFi MAC address bc:dd:c2:89:a0:bb
              WiFi Vcc 3.38, reset reason Power up
              WiFi flash size 4194304, free heap 24528
              WiFi IP address 192.168.1.163
              WiFi signal strength -58dBm, mode 802.11n, reconnections 0, sleep mode modem
              Clock register 00002002
              Socket states: 4 0 0 0 0 0 0 0
              === Filament sensors ===
              Extruder 0 sensor: ok
              • OwenDundefined
                OwenD @wilriker
                @wilriker
                I'd hazard a guess it's got something to do with my using a dummy tool offset to store the variables for the elapsed time & last recorded temp.
                These are done at similar intervals (or at least a multiple of)
                Not sure why that would cause a refresh of the Paneldue temps though.
                If that turns out to be the case, I wouldn't lose too much sleep over it as it'll rectify itself when we get variables.
                • wilrikerundefined
                  wilriker @OwenD
                  @OwenD Usually PanelDueFirmware reacts only passively on status updates sent by/requested from RRF. It does not make any assumptions (with the exception for the caption of the Reprint/Resimulate button). So this means it does see that this tool's state, the heater state as well as the active/current temps are being set to be all default temporarily while current temp stays as is.
                  As for why your daemon.g resets all of these values, I don't know yet.
                  Manuel
                  My Tool Collection
                  • mfs12undefined
                    mfs12
                    Hey @OwenD,
                    since 3.2.10 quite some changes were made to paneldue's firmware. please re-test the issue reported and open a new thread if your problem persists.
                    https://forum.duet3d.com/topic/24889/paneldue-3-4-0-pre1-released/6
                    Visit me on github at https://github.com/mfs12/