Duet3D Logo Duet3D
    • Tags
    • Documentation
    • Order
    • Register
    • Login

    Movement after M112 E-Stop!

    Scheduled Pinned Locked Moved
    CNC
    7
    61
    3.5k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • timschneiderundefined
      timschneider @hpiz
      last edited by timschneider

      @hpiz said in Movement after M112 E-Stop!:

      Also, M18 and M17 work exactly as expected for all or specific drivers.

      that was the next check I had in mind 🙂

      so I'm starting to run out of ideas.

      But one thing I've noticed while looking at the wiring/jumper picture is, that the GND Pin of the driver header is not connected. Can you show us a picture of the duet, one servo driver and the z-closed loop driver wiring? And maybe provide the datasheet for the drivers.

      Cause I needed the seperate GND connection between the Duet and each closed loop driver, for the alarm pin.

      And another thought, is your power supply strong enough to provide the over current in the stall event?

      I have not been able to observe this behaviour with my setup, so this is the reason why I try to understand this as good as possible and in the end hopefully solve the problem for you as well 🙂

      hpizundefined 1 Reply Last reply Reply Quote 0
      • hpizundefined
        hpiz @timschneider
        last edited by hpiz

        @timschneider Seeing as the control signals for drivers pull to ground and all my drivers use optoisolated inputs, I am using 5v as common and the only ground connected per cable is the shield ground which flies over with the endpoint signal wire over the the IO headers and is grounded there.

        My alarms for the servos are optoisolated for pull up, the z driver for the stepper is reverse poloarized optoisolated for pulldown, so I actually have the error pin for that one going to common (shared with alarm and brake) and 5v going into it's alarm output. I will eventually change to the proper setup and place a resistor between 5v and the alarm output, and ground on common to create an error low circuit. And then through configuration of integrated servos, change the output to be on when not in error so all drivers are error low.

        I'm using JMC 400W integrated servos on Y and X
        JMC Manual

        And the Z is a StepperOnline closed loop 400W stepper
        StepperOnline driver Manual

        Full Duet board picture

        Regarding power supplies, I actually don't know if there is enough overhead for stall current when it is moving at full speed and the 50kg of gantry and spindle are attached, but I think at the slow speed it is moving during these tests, and only moving the rotational inertia of the ballscrew plus the linear inertia of the little linear bearing, I would guesstimate there is little to no backfeed during these test.

        There is one power supply for the Duet and 24V accessories (endstops, relays, solenoids,etc...) and one for each driver. The Duet/Acc PSU is 480W and the driver ones are all 36V 600W, all PSU's are switch mode.

        Pic of PSU's just for fun

        Edit: forgot the other pics

        All driver wiring uses the following color code:
        Yellow - 5V
        Blue - Step/Pulse
        White - Dir
        Green - Enable
        Red - Error/Alarm
        Orange - Endstop input (except Z, unused for Z)
        Brown - Unused
        Black - Unused
        Shield - Ground on Duet side

        Back view of servo wiring

        "Top" view of servo wiring

        Just a pic showing the orange endstop signal wire going to the endstop wire

        Z Driver wiring

        timschneiderundefined 1 Reply Last reply Reply Quote 0
        • timschneiderundefined
          timschneider @hpiz
          last edited by

          @hpiz hm, so I don't see anything wrong ...
          Out of curiosity, can you try running your movement job file and pressing the emergency stop in the DWC? is it still moving?

          hpizundefined 2 Replies Last reply Reply Quote 0
          • hpizundefined
            hpiz @timschneider
            last edited by

            @timschneider When I get home from work today I'll grab that video evidence, but it does the same thing, albeit sometimes heavily delayed (~3-4 seconds), due to my WiFi I think, I've been having some intermittent disconnect issues with it lately.

            @dc42 would know best I think, but is it possible there is a need to either reflash my firmware, or possibly an issue with the board (I find the latter hard to believe).

            timschneiderundefined 1 Reply Last reply Reply Quote 0
            • timschneiderundefined
              timschneider @hpiz
              last edited by

              @hpiz maybe a dumb question, but do you have a while loop in your daemon.g without a G4?

              I try to understand what is causing the delay, as dc42 said, if the M112 is processed, there should be no delay. So something is maybe delaying the processing of the M112, but again that is not explaining the first and the second stop. That was the reason why I asked for the power supply (short power down/undervoltage can cause many different sotware problems), but I think this is sufficient. The reason why I keep asking about the while loops without a "break" is, that the control of the gcode processing is not handed back to process other codes if it is running in a tight loop. Or if for what ever reason there is a blocking(queueable) G-Code infront of the M112, the processing of the M112 will be delayed e.g. turn a relay off with M42 (that was the reason why I asked you to put the M112 at the first and only position of the driver-error.g).

              On last idea is, to wire an e-stop and configure it as a estop in duet - just to rule the gcode processing out. if this also failes, it is something in the movement system or the drivers itself, but I don't think it is related to the drivers cause you are using two different kinds of drivers (servos and steppers)

              e.g. recycle your tool probe depressed over limit and uncomment T2 under triggers

              M581 T0 P0 S1 R0
              
              1 Reply Last reply Reply Quote 0
              • hpizundefined
                hpiz @timschneider
                last edited by

                @timschneider Here's a test without the additional modifications you suggested using the EStop button in DWC...

                https://drive.google.com/file/d/1hTqF0GCi4dEQjOZyk1uR_Ctzywv-66Zg/view?usp=drive_link

                I really think the delay I mentioned is just a network communication delay and not a delay within the Duet itself (it's not delayed every time), but I could be wrong. I would rate this test as having zero delay, as soon as I hit the button the first (very short) stop happened "instantly".

                @timschneider said in Movement after M112 E-Stop!:

                maybe a dumb question, but do you have a while loop in your daemon.g without a G4?

                I don't think any question about this behavior could be considered dumb, but no, I haven't even made a daemon.g, the only configuration I've done so far is the config.g, a few custom M command system macros, and the driver-error system macro everything else is stock.

                Screenshot of Duet System Files
                ^Any file with a modify date of 7/26/2023 is unmodified. Everything other than config.g is very very simple, but let me know if I need to share the contents of any of them.

                @timschneider said in Movement after M112 E-Stop!:

                I keep asking about the while loops without a "break" is, that the control of the gcode processing is not handed back to process other codes if it is running in a tight loop.

                I agree completely, it's what I would assume first as well, that would presumably have the same effect I'm having, but I only ever had the one loop in my movement test macro, no other loops were defined by me anywhere else.

                And finally, I changed the tool probe overpress trigger to T0 and got the same behavior...

                https://drive.google.com/file/d/1hVCYuPwHx6Yzlz80FHZKv9pIseA7QbPQ/view?usp=sharing

                timschneiderundefined 1 Reply Last reply Reply Quote 0
                • timschneiderundefined
                  timschneider @hpiz
                  last edited by

                  @hpiz thank you for all these test and based on these tests I think, we don't need to focus on the driver-error or external driver configuration. It appears to me, that there is a problem with the following configuration

                  • Duet 3 Main Board 6XD standalone mode
                  • Emergency Stop (DWC and external trigger confirmed)
                  • Active disabled/low external drivers

                  So may I ask you to do two more tests?

                  • check if the stepper motors are active or disabled after the final stop, are you able to move them freely or not? If they are blocked/active that could describe the first and second stop.
                  • put a M112 in the job file, somewhere in the middle. If the Y-axis is moving after the M112 in the job file, than there is a bug in the software, as the M112 is in the same input channel as the movement commands and there is no "normal" way, that movement will appear after the m112.
                  hpizundefined 1 Reply Last reply Reply Quote 0
                  • hpizundefined
                    hpiz @timschneider
                    last edited by

                    @timschneider So I'm starting to lose my mind, and have begun talking to myself on video (lol, really so I have to type less, but I am starting to get quite lost)

                    Disclaimer: While my Z stepper can and has moved after a first stop of M112, it is far far less consistent, more than 80% of the time it stops only once as it should (compared to like 2% for the servos). But while the hardware differences clearly are making a behavioral difference, I believe the underlying cause (that I am currently convinced of) is still a problem. I'll get there...

                    @timschneider said in Movement after M112 E-Stop!:

                    Active disabled/low external drivers

                    I'm starting to narrow onto this or something about the enable signal (although the pulse/step signal is still misbehaving imo), and it could be as simple a fix as a wiring change.... maybe, I'm still very confused though. And my gut tells me no wiring change can fix this.

                    I'm getting confused about the effect of the Enable jumper, I can have it on either position and the drivers are active with no other changes to Duet config or driver parameters.

                    Also within config.g what does enable high (R1) on a driver mean if the enable pin is actually a ground sink, does that mean enable high (R1) means the transistor is on for the Enable(-) pin meaning it's actually pulled to ground, because that appears to be what I'm seeing. Enable low (R0) keeps my enable wire high since I have it fed by 5V through the optoisolater at the servo. And when I switch to enable high (R1) the enable wire is low, indicating current is passing through the opto on the driver.

                    @timschneider said in Movement after M112 E-Stop!:

                    check if the stepper motors are active or disabled after the final stop, are you able to move them freely or not? If they are blocked/active that could describe the first and second stop.

                    M18 test + EStop drive enable check - Conclusion: Stepper and servo motors are disabled after final stop

                    @timschneider said in Movement after M112 E-Stop!:

                    put a M112 in the job file, somewhere in the middle.

                    M112 mid job - Conclusion: Same effect

                    Oh, I didn't stop there (warning: the oscilloscope will make an appearance)

                    M112 in job with M291 right after - Conclusion: M291 is not executed but G movements are

                    M112 at end of job expecting no strange movement - Conclusion: Still moved after a stop...

                    Investigating that last test a little deeper - Conclusion: Yup, it did still move, and past where it should have. Ok, obviously the buffering of move commands is superseded by the M112 which executes as soon as it's read.

                    What about the Z stepper, it does behave somewhat better - Conclusion: I'd say you can see a few steps after the first pause, but much better than my other drives.

                    Ok let's test the x axis - Conclusion: You can see a clear stop and restart, then final stop just like the Y. While I say in-vid it's about the servo's, I'm not sure they are to blame, there's more.

                    I kept going off video to try reversing the enable polarity in both the servo params and the duet, I found some quirks I mention in the next vid but it's really not in my focus right now. Anyways, none of that changed anything about the behavior.

                    At this point I felt I had no option but to pull out the scope. I'm analyzing the following video with the following assumptions...

                    • There is no signal being generated by the driver, the signals seen on scope are entirely from the Duet, I feel that's a pretty safe bet.

                    • The difference in behavior between my Servo's and my Z stepper is down to some kind of buffer/safe time between disabling the drive and re-enabling. I would have to either also assume most drivers have said wait time, or my board is acting differently.

                    Watching the control signals on scope in realtime

                    After this test, I really can't blame the servo's at all. They're doing exactly what they are being told to do by the Duet, think it might be time give up. Why would there be steps still coming out of the duet after a stop? Why would the enable signal go to disable->enable->disable? I really am having a hard time trying to think of any configuration or parameter I can change to just have the Duet not send steps after an M112 let alone deactivate, then reactivate a driver.😞

                    hpizundefined 1 Reply Last reply Reply Quote 0
                    • hpizundefined
                      hpiz @hpiz
                      last edited by

                      @hpiz I don't have the energy today, but I plan to show the same signals going to my z driver, but being ignored by the driver, which I assume will be the case. I mean why would one drive output behave differently from another?

                      timschneiderundefined 1 Reply Last reply Reply Quote 0
                      • timschneiderundefined
                        timschneider @hpiz
                        last edited by

                        @hpiz Thanks again for all these tests and measurements that go far beyond what I would have asked for.

                        I guess I can't help you any further and @dc42 needs to take over, as it appears to me, that there is a problem with the following configuration:

                        • Duet 3 Main Board 6XD standalone mode
                        • CNC Mode
                        • Firmware 3.4.6
                        • Emergency Stop (DWC, gcode (M112 even within the jobfile itself) and external trigger (trigger0) confirmed)
                        • Maybe: two motors on one axis

                        Observed behaviour:

                        • movement commands are queued and the Movement System starts to move the drives
                        • M112 is processed
                        • all drives are disabled
                        • at least one movemend command is still being processed in the queue and this will reactivate the drives again
                        • all drives are disabled again (is it done by the M112 or maybe a stop.g/cancle.g?)

                        maybe I can reproduce it with a simple bench setup.

                        timschneiderundefined 1 Reply Last reply Reply Quote 0
                        • timschneiderundefined
                          timschneider @timschneider
                          last edited by timschneider

                          @dc42 I was able to reproduce this behaviour with an brand new of the shelf 6XD WD32096 v1.01 firmware 3.4.6 reflashed to be sure. In standalone mode.

                          Enable Jumper in active Enable.

                          Following config.g

                          ; Enable network
                          M552 P0.0.0.0 S1
                              
                          ;CNC Mode
                          M453                            ; Select CNC device mode
                          M669 K0 S2 T1
                          
                          M569 R0 P0.4 S0 T3:3:6:0       ; physical drive 0.4 goes backwards
                          M569 R0 P0.5 S0 T3:3:6:0       ; driver 5 requires an active high enable, 2.5us minimum step pulse, 2.5us minimum step interval, 5us DIR setup time and no hold time
                          M569 R0 P0.3 S0 T3:3:6:0       ; driver 5 requires an active high enable, 2.5us minimum step pulse, 2.5us minimum step interval, 5us DIR setup time and no hold time
                          
                          M569 P0.0 S0 R0 T5:5:9:0       ; physical drive 0.0 goes backwards
                          M569 P0.1 S1                    ; physical drive 0.1 goes forwards
                          M569 P0.2 S1                    ; physical drive 0.2 goes forwards
                          
                          M584 X0.3 Y0.4:0.5 Z0.0             ; set drive mapping
                          
                          M92 X160.00 Y320.00 Z640.00     ; set steps per mm
                          M566 X1800.00 Y180.00 Z120.00     ; set maximum instantaneous speed changes (mm/min)
                          M203 X15000.00 Y12000.00 Z5000.00 I5  ; set maximum speeds (mm/min)
                          M201 X400.00 Y200.00 Z200.00        ; set accelerations (mm/s^2)
                          
                          ;M564 H0                         ; Allow stepper movement before homing
                          ; Axis Limits
                          M208 X0 Y0 Z0 S1                ; set axis minima
                          M208 X600 Y1200 Z170 S0         ; set axis maxima
                          
                          ;Machine Initialization
                          M18                          ; disable all steppers
                          M17                          ; enable z stepper so it doesn't fall
                          

                          test_movement.gcode

                          G90
                          G21
                           
                           
                          G1 Y500 F4000
                          G1 Y600 F4000
                           
                          G1 Y500 F4000
                          G1 Y600 F4000
                           
                          G1 Y500 F4000
                          G1 Y600 F4000
                           
                          G1 Y500 F4000
                          G1 Y600 F4000
                           
                          G1 Y500 F4000
                          G1 Y600 F4000
                          

                          M122
                          Screenshot 2023-11-03 at 12-03-32 My Duet.png

                          EmergencyStop pressed mid job via DWC

                          Channel 1 (yellow) is STEP-
                          Channel 2 (pink) is ENABLE-
                          SDS00004.png

                          there is a ENABLE low, when the Emergency Stop is pressed, then high again, then low, high, low again (low is off in this setup). I've tried it also the other was around with R1 - it just inverts the curve.

                          The Setup:
                          2023-11-03-12-03-03-888.jpg
                          2023-11-03-12-03-08-248.jpg

                          gloomyandyundefined 1 Reply Last reply Reply Quote 1
                          • gloomyandyundefined
                            gloomyandy @timschneider
                            last edited by

                            @timschneider If you still have the test system available, is there any chance you could run the test again but use M112 entered in the console rather than using the emergency stop button. The reason I ask is because the emergency stop button in DWC runs M112 followed by M999 so some of what you are seeing may be down to the software reset (M999) operation.

                            timschneiderundefined 1 Reply Last reply Reply Quote 0
                            • timschneiderundefined
                              timschneider @gloomyandy
                              last edited by

                              @gloomyandy sure. I did even more tests.
                              run M112 from console will change the behaviour a bit, the last disable / enable toggle will disappear. It appears to me, that a reset will also toggle the driver enable once.

                              I've changed the test setup to be able to test the sbc setup.
                              Unfortunately, it will also fail, so there is also movement after the M112.

                              the following screens are all taken with SBC setup 3.4.6
                              2023-11-03-13-30-13-724.jpg
                              Screenshot 2023-11-03 at 13-43-18 rockpi-4cplus.png
                              and the following config.g

                              M669 K0 X1:0:0 Y0:1:0 Z0:0:1 S1 T1                      ; Cartesian kinematics
                              
                              ; Drives
                              M569 P0 R0 T1:1:2:0
                              M569 P1 R0 T1:1:2:0
                              M569 P2 R0 T1:1:2:0
                              M569 P3 R0 T1:1:2:0
                              M569 P4 R0 T1:1:2:0
                              M569 P5 R0 T1:1:2:0
                              
                              M569 P0 S1
                              M569 P1 S1
                              M569 P2 S1
                              M569 P3 S1
                              M569 P4 S1
                              M569 P5 S1
                              
                              G90                                                     ; send absolute coordinates...
                              M584 X0 Y4:5 Z3                                         ; set drive mapping
                              
                              M92 X400 Y400 Z800                                      ; set steps per mm 4000 steps/rev / 10 mm pitch - 5mm on z
                              
                              M566 X120.0 Y120.0 Z120.00 P1                           ; set maximum instantaneous speed changes (mm/min) and apply jerk on every move
                              M203 X10000.00 Y10000.00 Z7000.00                       ; set maximum speeds (mm/min)
                              M201 X400.00 Y500.00 Z1000.00                           ; set accelerations (mm/s^2)
                              M204 P250 T1250                                         ; Set printing and travel accelerations
                              M84 S30                                                 ; Set idle timeout
                              
                              ; Axis Limits
                              M208 X0 Y0 Z0 S1                                        ; set axis minima
                              M208 X1330 Y1036 Z278 S0                               ; set axis maxima
                              
                              ; Mode Selector
                              M453                                                    ; Select CNC Mode
                              

                              without M669 S1 T1
                              SDS00027.png

                              with M669 S1 T1
                              SDS00028.png

                              with M112 in console
                              SDS00030.png

                              with Emergency Stop in DWC
                              SDS00031.png

                              hpizundefined timschneiderundefined 2 Replies Last reply Reply Quote 1
                              • hpizundefined
                                hpiz @timschneider
                                last edited by

                                @timschneider What a relief to hear this is reproducible, I was starting to get really depressed. And you beat me to yanking my 6xd out of the cabinet and wiring resistors on an unconnected drive output on the 6xd. That was literally gonna be my next course of troubleshooting.

                                I took a vacation day today, so I'm about to test the Z (although your test all but confirm this is board/firmware behavior). Will post vid shortly.

                                1 Reply Last reply Reply Quote 0
                                • timschneiderundefined
                                  timschneider @timschneider
                                  last edited by

                                  I did some more test, as I was not able to see this behaviour in my last cnc build. So I was recording the STEP and Enable Signal for the other driver 0,1,2,3 and 5 as well, all with M112 mapped to the Y-axis.

                                  M584 X4 Y0:1:3:5 Z2
                                  and
                                  M584 X4 Y0:1:2:5 Z3

                                  btw. the resistors are all 15k

                                  driver0
                                  SDS00039.png

                                  driver1
                                  SDS00035.png

                                  driver2
                                  SDS00036.png

                                  driver3
                                  SDS00037.png

                                  driver5
                                  SDS00038.png

                                  timschneiderundefined hpizundefined 2 Replies Last reply Reply Quote 0
                                  • timschneiderundefined
                                    timschneider @timschneider
                                    last edited by

                                    it looks like the motion system takes some time to shut down - so is it possible that the following will reactivate the drive again after an EmergencyStop?

                                    In the function void DDA::Prepare(SimulationMode simMode) noexcept

                                    9f96e938-c5d8-4030-8b83-472de581d0de-grafik.png

                                    1 Reply Last reply Reply Quote 0
                                    • hpizundefined
                                      hpiz @timschneider
                                      last edited by

                                      @timschneider Obviously my scope is way worse than Tim's so I would reference Tim's scope grabs over my shoddy videos, but I'm trying to do what I can...

                                      Z stepper test with M112 in job

                                      Z stepper test with no M112 in job, using DWC EStop

                                      And lastly...
                                      Z stepper test using external estop trigger with T0

                                      That last one, in my mind, all but confirms there is a wait delay in that driver after enable is reactivated, and depending on how long the Duet keeps it enabled, eventually it too does move, but reacts to disabling immediately.

                                      timschneiderundefined 1 Reply Last reply Reply Quote 0
                                      • timschneiderundefined
                                        timschneider @hpiz
                                        last edited by

                                        @hpiz I was using the 6XD quite a while without noticeing, so I think it is a good teamwork!

                                        and I guess I maybe found the place where the delay kicks in

                                        e0c3232f-73bb-4629-bb4b-299e4397a611-grafik.png

                                        when the seperate move thread was added, the active switch fall overboard and it appears to me, that TerminateAndUnlink needs some time to terminate and unlink, and in the meantime, new moves are prepared, and the prepare move is enableing the drive again.

                                        droftartsundefined 1 Reply Last reply Reply Quote 0
                                        • droftartsundefined
                                          droftarts administrators @timschneider
                                          last edited by

                                          @timschneider @hpiz Thanks for all your investigative work, I've flagged this to @dc42.

                                          Ian

                                          Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                                          dc42undefined 1 Reply Last reply Reply Quote 0
                                          • dc42undefined
                                            dc42 administrators @droftarts
                                            last edited by dc42

                                            Hi all, so does this issue occur only when using external drivers, for example with a 6XD? Does it occur only in SBC mode?

                                            @timschneider which source code branch are you looking at? The current 3.5-dev and 3.4-dev source code has this for Move::Exit:

                                            void Move::Exit() noexcept
                                            {
                                            	StepTimer::DisableTimerInterrupt();
                                            	rings[0].Exit();
                                            #if SUPPORT_ASYNC_MOVES
                                            	rings[1].Exit();
                                            #endif
                                            #if SUPPORT_LASER || SUPPORT_IOBITS
                                            	delete laserTask;
                                            	laserTask = nullptr;
                                            #endif
                                            	moveTask.TerminateAndUnlink();
                                            }
                                            

                                            That should be sufficient to stop all movement.

                                            @hpiz which firmware version are you using?

                                            PS - when Emergency Stop is pressed in DWC, it sends M112 and then after a little while it sends M999 to reset the Duet. At the reset the driver Enable signal may go to Enabled again, depending on its polarity. But by then the movement queue is empty because RRF has re-initialised.

                                            Duet WiFi hardware designer and firmware engineer
                                            Please do not ask me for Duet support via PM or email, use the forum
                                            http://www.escher3d.com, https://miscsolutions.wordpress.com

                                            timschneiderundefined hpizundefined 2 Replies Last reply Reply Quote 0