    Duet 3HC Expansion looses Connection

    Scheduled Pinned Locked Moved Unsolved
    Duet Hardware and wiring
    10
    145
    6.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • developeralgo222undefined
      developeralgo222 @infiniteloop
      last edited by developeralgo222

      @infiniteloop said in Duet 3HC Expansion looses Connection:

      @developeralgo222

      Termination on each board in the CAN Bus chain works ?

      What @dc42 says. To test, throw-in some cheapo telephone lines (RJ11) and terminate CAN properly.

      i will try another cable , probably a phone cable or another ADSL 2+ high speed cable to replace the 10 ft cable from 6XD to 3HC1 and see if that makes a difference .

      infiniteloopundefined 1 Reply Last reply Reply Quote 0
      • infiniteloopundefined
        infiniteloop @developeralgo222
        last edited by

        @developeralgo222 said in Duet 3HC Expansion looses Connection:

        i will try another cable

        Great 😊

        developeralgo222undefined 1 Reply Last reply Reply Quote 0
        • developeralgo222undefined
          developeralgo222 @infiniteloop
          last edited by developeralgo222

          @infiniteloop said in Duet 3HC Expansion looses Connection:

          @developeralgo222 said in Duet 3HC Expansion looses Connection:

          i will try another cable

          Great 😊

          Made 2 different straight cables which are shielded and 1 std phone cable (Normally crossed, so i cut one end and crimped it to straight cable ).

          Cable 1 - Made from CAT 6 Cable (using only 2 pairs for CAN Bus --technically on 2 wires are used) and RJ11 at the ends
          Cable 2 - Made from CAT 8 Cable (using only 2 pairs for CAN Bus --technically on 2 wires are used) and RJ11 at the ends
          Cable 3 - Made from Std Phone Cable (using only 2 pairs for CAN Bus --technically on 2 wires are used) and RJ11 at the ends

          All of them behaved the same when testing each of the 4 x 3HC boards with nothing connected to them only power.

          6XD --> Board 1 (with CAN Jumpers) CAN_IN / CAN_OUT -- Sync

          6XD --> Board 2 (with CAN Jumpers) CAN_IN / CAN_OUT -- No Sync

          6XD --> Board 3 (with CAN Jumpers) CAN_IN / CAN_OUT -- No Sync

          6XD --> Board 4 (with CAN Jumpers) CAN_IN / CAN_OUT -- No Sync

          Not sure why CAN Bus would be this unreliable. For sure i checked the cables , tested them using a different cable tester ( Sperry ) this time to rule out anything. i don't think its the cables after this round of tests

          IMG_1056.jpg IMG_1058.jpg

          droftartsundefined infiniteloopundefined dc42undefined 3 Replies Last reply Reply Quote 0
          • droftartsundefined
            droftarts administrators @developeralgo222
            last edited by

            @developeralgo222 something to do with the mounting? You have them stacked, using what looks like electrically conductive standoffs. I don’t know if that connects the grounds of the boards at a point that causes problems, rather than at the PSUs. You could try powering all four boards (or all boards) from one PSU, see if that makes a difference.

            Ian

            Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

            developeralgo222undefined 1 Reply Last reply Reply Quote 0
            • developeralgo222undefined
              developeralgo222 @droftarts
              last edited by developeralgo222

              @droftarts said in Duet 3HC Expansion looses Connection:

              @developeralgo222 something to do with the mounting? You have them stacked, using what looks like electrically conductive standoffs. I don’t know if that connects the grounds of the boards at a point that causes problems, rather than at the PSUs. You could try powering all four boards (or all boards) from one PSU, see if that makes a difference.

              Ian

              Hmmm!!! i don't think so unless the boards themselves have Power rail circuit layer (copper) touching the mounting holes . That would be really really bad. When i did the Test setup they were separated (Not mounted) although still on Brass standoffs. Your thought might be something to investigate , i will check that and try Nylon standoffs

              1 Reply Last reply Reply Quote 0
              • infiniteloopundefined
                infiniteloop @developeralgo222
                last edited by

                @developeralgo222 said in Duet 3HC Expansion looses Connection:

                Not sure why CAN Bus would be this unreliable.

                It's not about CAN - I've built several applications for constructing machinery from the ground up, connecting controllers via CAN, and these connections are rock-solid. This said, I am now convinced that we can rule out your CAN wiring as cause of the problem. Which leads me to believe we might face an effect which I described as "interesting" early on: some interference between GND and Earth.

                In your test setup, the boards were strictly isolated from Earth (which was just connected to the two PSUs). Earth is received from the electrical outlets and internally connected with the metal cases of the PSUs. In addition, the metal parts of you PnP machine should be "earthed" as well. The one million dollar question now is: have GND and Earth any potential contact? Or are they maybe decisively synced somewhere?

                The latter case is something I've done myself, but is not without pitfalls, so I'd like to ask @droftarts for a second opinion. At least, he's on the same trail …

                developeralgo222undefined 1 Reply Last reply Reply Quote 0
                • developeralgo222undefined
                  developeralgo222 @infiniteloop
                  last edited by

                  @infiniteloop said in Duet 3HC Expansion looses Connection:

                  @developeralgo222 said in Duet 3HC Expansion looses Connection:
                  The one million dollar question now is: have GND and Earth any potential contact? Or are they maybe decisively synced somewhere?

                  The latter case is something I've done myself, but is not without pitfalls, so I'd like to ask @droftarts for a second opinion. At least, he's on the same trail …

                  Today, I have isolated all the PSUs and all are ā€œEarthedā€ ( AC Ground ) . They don’t touch the aluminum metal table at all anywhere. I will also ā€œEarthā€ (AC ground ) the aluminum metal table today.

                  Is there anything I might be forgetting on this GND solution. I am trying to avoid creating GND loops

                  infiniteloopundefined 1 Reply Last reply Reply Quote 0
                  • infiniteloopundefined
                    infiniteloop @developeralgo222
                    last edited by

                    @developeralgo222

                    Is there anything I might be forgetting on this GND solution. I am trying to avoid creating GND loops

                    That’s complex. As a general rule, imagine a star topology, I.e. for each and every voltage, there should be a single point (or rail) from where to further route the power lines.

                    For your dual PSUs, you already have this central point: V+ (1 rail with 3 connectors on each PSU) is now interconnected as discussed above in this thread.

                    Now, if you connect GND (of the DC-output) to Earth, do it at a single point as well. Think of it as a common rail where all GND lines meet - kind of a ā€local Earthā€. Don’t take GND or V– from distant parts of the frame. Aside from the common rail, consider them as not being the same.

                    Voltage lines may be split or chained on their run, but may then never refer to another source of the same voltage again (that’s a loop). You often run into this trap with shielded lines: the shield carries GND (or, in some cases, V–), but if you supply GND from both ends, you might involuntarily establish a ground loop. The golden rule here is to always feed GND from the origin - leave it unconnected at the destination end.

                    The fact that most devices in your machine are controlled via V– complicates things. All switched V– lines from the DUETs may never have contact with the ā€local Earthā€, GND or any other V–.

                    Grounding the PnP machine is another topic: not all metal parts are always in touch with each other, there are potential isolators such as coatings, belts or lubricants in the way, some parts are clearly isolated by design (printed joints etc). Short cable bridges help in some cases, but for moving parts, you might need to route a dedicated GND line through your cable chain.

                    Considering USB ground loops, I recommend this article from the documentation: USB ground loops

                    developeralgo222undefined 1 Reply Last reply Reply Quote 0
                    • dc42undefined
                      dc42 administrators @developeralgo222
                      last edited by dc42

                      @developeralgo222 have you confirmed that the wires are not crossed between the ends of the 10ft cable? Your cable tester might not detect that. See https://docs.duet3d.com/en/User_manual/Machine_configuration/CAN_connection#example-of-a-good-cable and the photo after that.

                      Duet WiFi hardware designer and firmware engineer
                      Please do not ask me for Duet support via PM or email, use the forum
                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                      developeralgo222undefined 1 Reply Last reply Reply Quote 0
                      • developeralgo222undefined
                        developeralgo222 @dc42
                        last edited by developeralgo222

                        @dc42 said in Duet 3HC Expansion looses Connection:

                        @developeralgo222 have you confirmed that the wires are not crossed between the ends of the 10ft cable? Your cable tester might not detect that. See https://docs.duet3d.com/en/User_manual/Machine_configuration/CAN_connection#example-of-a-good-cable and the photo after that.

                        Yes i double checked that . i was suspecting that it might be the case but no. Cable tester that i use checks for all kinds of errors on cable from crossed , shorts , reversed, miswires, continuity, shield , etcs i have used various Fluke professional Cable testers for over 20 years and they have never failed, so i am confident when after all testing it says the cable is good, then its good.

                        They are Straight through cable (Left to right ) and on both ends

                        • Blue, Blue-white, Orange, Orange-white

                        Technically , in this case , Blue-White and Orange wires are used by CAN Bus connection in Duet Boards

                        IMG_1065.jpg

                        droftartsundefined 1 Reply Last reply Reply Quote 0
                        • droftartsundefined
                          droftarts administrators @developeralgo222
                          last edited by

                          @developeralgo222 i don’t know if this matters that much for a short cable, but wires of the same colour, ie blue and white-with-blue-stripe, make up the twisted pair. These should be wired to the centre two pins that Duet use for CAN. The other pair goes on the pins outside these. You’re using one wire from each twisted pair.

                          Ian

                          Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                          developeralgo222undefined 1 Reply Last reply Reply Quote 0
                          • developeralgo222undefined
                            developeralgo222 @droftarts
                            last edited by developeralgo222

                            @droftarts said in Duet 3HC Expansion looses Connection:

                            @developeralgo222 i don’t know if this matters that much for a short cable, but wires of the same colour, ie blue and white-with-blue-stripe, make up the twisted pair. These should be wired to the centre two pins that Duet use for CAN. The other pair goes on the pins outside these. You’re using one wire from each twisted pair.

                            Ian

                            Let me try it . i have tried almost everything Grounding, and everything in between that has been suggested but to no avail. Sometimes its usually the smallest thing that creates a nightmare.

                            developeralgo222undefined 1 Reply Last reply Reply Quote 0
                            • developeralgo222undefined
                              developeralgo222 @developeralgo222
                              last edited by

                              @developeralgo222 said in Duet 3HC Expansion looses Connection:

                              @droftarts said in Duet 3HC Expansion looses Connection:

                              @developeralgo222 i don’t know if this matters that much for a short cable, but wires of the same colour, ie blue and white-with-blue-stripe, make up the twisted pair. These should be wired to the centre two pins that Duet use for CAN. The other pair goes on the pins outside these. You’re using one wire from each twisted pair.

                              Ian

                              Let me try it . i have tried almost everything Grounding, and everything in between that has been suggested but to no avail. Sometimes its usually the smallest thing that creates a nightmare.

                              Didn't make a difference at all .

                              I have tried every kind of Cable connection as per the requirement but there is no reliable sync of CAN connection. I don't believe i am the only one who is building a PnP or a 3D printer that is encountering this issue. i have worked with various kinds of connections and boards but have never encountered such an issue with CAN Bus.

                              Can't Sync 3HC boards no matter the cable. Have used the documentation to double check everything. Remake the cables and test them. Not sure if it might actually be a Duet 3 3HC Hardware issue that is causing this ?

                              developeralgo222undefined 1 Reply Last reply Reply Quote 0
                              • developeralgo222undefined
                                developeralgo222 @developeralgo222
                                last edited by developeralgo222

                                @developeralgo222 said in Duet 3HC Expansion looses Connection:

                                Twisted pair cables terminated in RJ11 connectors are sold in some countries as "High Speed ADSL cables". One supplier of such cables is Kenable. Note, ADSL and telephone cables made with flat wire often cross the connections, making them unsuitable
                                

                                The price of kenable cables in US is so expensive while in UK they are extremely cheap. Can anyone point me to a link on Amazon or ebay for cable that works with Duet 3HC or 6XD CAN Bus without me cutting and remaking it, and is affordable

                                droftartsundefined 1 Reply Last reply Reply Quote 0
                                • droftartsundefined
                                  droftarts administrators @developeralgo222
                                  last edited by

                                  @developeralgo222 I'm sorry you're having so many problems with this. It really shouldn't be this difficult, and it has us foxed as well! Maybe the best option is to return to the last known working configuration, which was as a bench setup.

                                  For cables in the USA on Amazon, these look like the correct ones: https://www.amazon.com/Kenable-Speed-Broadband-Modem-Cable/dp/B011SS7LYU

                                  Ian

                                  Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                                  developeralgo222undefined 1 Reply Last reply Reply Quote 0
                                  • developeralgo222undefined
                                    developeralgo222 @droftarts
                                    last edited by developeralgo222

                                    @droftarts said in Duet 3HC Expansion looses Connection:

                                    @developeralgo222 I'm sorry you're having so many problems with this. It really shouldn't be this difficult, and it has us foxed as well! Maybe the best option is to return to the last known working configuration, which was as a bench setup.

                                    For cables in the USA on Amazon, these look like the correct ones: https://www.amazon.com/Kenable-Speed-Broadband-Modem-Cable/dp/B011SS7LYU

                                    Ian

                                    I agree this should not be this difficult. I have checked and double checked a lot of things but i can't get the CAN Sync to work. I decided to close my eyes, curse as much as i can and then ordered those cables let's hope that those help. Will get them in a week.

                                    developeralgo222undefined 1 Reply Last reply Reply Quote 0
                                    • developeralgo222undefined
                                      developeralgo222 @developeralgo222
                                      last edited by developeralgo222

                                      @developeralgo222 said in Duet 3HC Expansion looses Connection:

                                      @droftarts said in Duet 3HC Expansion looses Connection:

                                      @developeralgo222 I'm sorry you're having so many problems with this. It really shouldn't be this difficult, and it has us foxed as well! Maybe the best option is to return to the last known working configuration, which was as a bench setup.

                                      For cables in the USA on Amazon, these look like the correct ones: https://www.amazon.com/Kenable-Speed-Broadband-Modem-Cable/dp/B011SS7LYU

                                      Ian

                                      I agree this should not be this difficult. I have checked and double checked a lot of things but i can't get the CAN Sync to work. I decided to close my eyes, curse as much as i can and then ordered those cables let's hope that those help. Will get them in a week.

                                      @dc42, @droftarts , What is the expected terminating resistors values at the end of the CAN Bus for Duet boards? Ideally , Each resistor should ideally be 120 ohm, for a 60 ohm difference between CANH and CANL. When i measure the resistance with Multimeter on the terminated 3HC Board i get a difference of 70.4 Ohms and for Unterminated CAN_H & CAN_L i get 126.6 Ohms ? are this the expected values ?

                                      Was doing some research and to continue troubleshooting, came across some explanation
                                      General CAN Bus wiring and troubleshooting concepts document

                                      Other CAN Bus terminating resistor values can be used and calculated based on specific baudrates and bus lengths - but, as you increase the baudrate, the pickier it gets about correct termination, whereas on lower baudrates you can get away with missing terminating resistors, by chance
                                      

                                      Looking at the Duet Board / Schematic - i see Shield_GND terminal on the main board 6XD which i assume is for Ethernet Grounding.

                                      Where is the CAN Grounding on Duet Boards ? since The CAN_GND of the CAN network should be connected to the functional earth potential (FE) at only one point i.e either on Main Board ( 6XD ) or on the Last 3HC on the Chain . Looking at the Kicad PCB design for 6XD , i see CAN_SHD_GND is that the same as CAN_GND in Duet 6XD design ?

                                      1 Reply Last reply Reply Quote 0
                                      • developeralgo222undefined
                                        developeralgo222 @infiniteloop
                                        last edited by

                                        @infiniteloop said in Duet 3HC Expansion looses Connection:

                                        @developeralgo222

                                        Is there anything I might be forgetting on this GND solution. I am trying to avoid creating GND loops

                                        That’s complex. As a general rule, imagine a star topology, I.e. for each and every voltage, there should be a single point (or rail) from where to further route the power lines.

                                        For your dual PSUs, you already have this central point: V+ (1 rail with 3 connectors on each PSU) is now interconnected as discussed above in this thread.

                                        Now, if you connect GND (of the DC-output) to Earth, do it at a single point as well. Think of it as a common rail where all GND lines meet - kind of a ā€local Earthā€. Don’t take GND or V– from distant parts of the frame. Aside from the common rail, consider them as not being the same.

                                        Voltage lines may be split or chained on their run, but may then never refer to another source of the same voltage again (that’s a loop). You often run into this trap with shielded lines: the shield carries GND (or, in some cases, V–), but if you supply GND from both ends, you might involuntarily establish a ground loop. The golden rule here is to always feed GND from the origin - leave it unconnected at the destination end.

                                        The fact that most devices in your machine are controlled via V– complicates things. All switched V– lines from the DUETs may never have contact with the ā€local Earthā€, GND or any other V–.

                                        Grounding the PnP machine is another topic: not all metal parts are always in touch with each other, there are potential isolators such as coatings, belts or lubricants in the way, some parts are clearly isolated by design (printed joints etc). Short cable bridges help in some cases, but for moving parts, you might need to route a dedicated GND line through your cable chain.

                                        Considering USB ground loops, I recommend this article from the documentation: USB ground loops

                                        @infiniteloop , @dc42 , @droftarts

                                        Can you give detail on this ? Currently i have the 2 PSUs connected like this

                                        PSUs_Negative_Output_Connection_With_DC_to_AC_GND_1.png

                                        Do i need to connect anything differently here ?

                                        infiniteloopundefined 1 Reply Last reply Reply Quote 0
                                        • infiniteloopundefined
                                          infiniteloop @developeralgo222
                                          last edited by

                                          @developeralgo222 said in Duet 3HC Expansion looses Connection:

                                          Can you give detail on this ? Currently i have the 2 PSUs connected like this

                                          I’d rather like to take the Monty Python turn: And now for something completely different … 😵

                                          Well, let’s see where we are:

                                          1. your wiring of the PSUs looks OK.
                                          2. the test setup for CAN with isolated boards works - am I right with this?
                                          3. if mounted on the PnP machine, only the CAN connection 6XD <-> 3HC ā€ž1ā€œ works, all other connections fail - am I right with this?

                                          If this is the current state of affairs, I’d like you to run another test: As of the photo below, the boards are stacked with electrically conductive standoffs who are, in turn, attached to the frame of the PnP machine. Now, can you detach the whole stack from the machine - but keep the standoffs between the boards in place? I’d like to know whether CAN becomes dysfunctional due to the GND it gets from the PnP machine or due to the electrical interconnection of the boards via the standoffs alone.

                                          1705432630700-img_1050.jpg

                                          Please be assured that me, like @droftarts, am sorry for the problems you face. More so, I’m sincerely foxed by my inability to spot the root cause of the mystic CAN bus failure.

                                          droftartsundefined developeralgo222undefined 2 Replies Last reply Reply Quote 0
                                          • droftartsundefined
                                            droftarts administrators @infiniteloop
                                            last edited by

                                            @infiniteloop The stack of boards in that image are standing on what looks like a plastic toolbox, not connected to the machine.

                                            As far as I can tell, there is no copper in close proximity to the mounting holes, at least on the 3HC v1.0 I have in my hands. There's no exposed copper around the holes, no via through-plating, and it looks like the copper ground plane doesn't extend to the holes. So I'm pretty sure they are electrically isolated from each other.

                                            @developeralgo222 Plugging the two power supplies in to the same power bar should be fine. While we don't advise the same thing to get around USB ground loops, putting the two earths as close to each other as possible should largely mitigate a ground loop, if the PSUs are similar. I don't know if there's something about the phasing between them causing a problem; I'm no electrical engineer!

                                            However... to mitigate that, have you tried powering all boards from one PSU, at least for testing? One PSU should have plenty of current to power all the boards, so long as no demanding load is put on it. Boards usually draw around 200-300mA with no peripherals connected.

                                            For the CAN question, I don't think termination resistors values need changing, because we (a) run at 1Mbit (ie not that fast) and (b) your CAN bus is short (less than five meters). The 70.4 Ohm reading on the terminated 3HC might be interesting; can you check the resistance in the same way on all the boards, and see if there has been damage to the R37 and R38? These are two tiny 59R resistors (I think they work in series to be around 120R) between the CAN RJ11 ports and the CAN termination jumpers. Highlighted red (from the ibom here) :
                                            1f57e26d-d674-4aeb-8589-07236506c1ab-image.png
                                            This is the circuit diagram:
                                            d3339a84-3d7d-47b0-a097-daa8ad057900-image.png
                                            Though it may just be a measurement error.

                                            Ian

                                            Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                                            developeralgo222undefined 1 Reply Last reply Reply Quote 0