    how to setup a hotend for directly printing metal and ceramic.
    Hardware dev
    3.9k
      dc42 administrators @lynnmt
      @lynnmt thanks. Please try tuning again with a higher PWM (maybe 0.3 or 0.35) and Y20. At the current PWM the heater is barely capable of reaching 800C.
      lynnmtundefined 3 Replies Last reply Reply Quote 0
      • lynnmtundefined
        lynnmt @dc42
        as requested.
        seems to provide the same error with model parameters:
        "Auto tune of heater 1 failed due to bad curve fit (R=70.881 K=1.071:0.000 D=1.08)"
        what does this mean?
        dc42undefined 2 Replies Last reply Reply Quote 0
        • lynnmtundefined
          lynnmt @dc42
          I would also mention that it is not the heater it is the thermocouple whose temperature is below the setpoint at the output power due to all the insulation around the Thermocouple.
          the heater itself is glowing white hot.
          here is a picture of the setup. the thermocouple is inside a 0.05" OD aluminum oxide sheath inside the stainless steel ring, pasted on with zirconia paste as close as possible to the heater.
          • lynnmtundefined
            lynnmt @dc42
            if it helps here are some more hardware shots...
            lynnmtundefined 1 Reply Last reply Reply Quote 0
              @lynnmt that looks like a good tuning cycle. I'll look at why the resulting parameters are rejected and see if it makes sense to widen the limits. Thanks for the photos.
              • lynnmtundefined
                lynnmt @dc42
                @dc42 I am working on making the sensor response even faster.
                so I would expect the limits to need to be substantially wider even than those determined by the autotune.
                in practice, making up for sensor delay in a system like this is going to be a huge problem. ๐Ÿ˜•
                Thanks for taking a look!
                I will be in touch here and on the discord!
                  @lynnmt said in how to setup a hotend for directly printing metal and ceramic.:
                  This command works for me:
                  M307 H0 R70.881 K1.071:0.000 D1.08
                  So I think that in RRF 3.5.x the limits have already been extended sufficiently. Please try upgrading to the RRF 3.5.0 build. As you are using an attached SBC you will need to upgrade to 3.5.0-rc.3. After that you may optionally upgrade to the latest RRF 3.5 firmware binary from https://www.dropbox.com/scl/fo/ljnewqssbl9bdo9vex37f/h?rlkey=m11nef0mvuc9pc8wri7rabf1b&dl=0.
                  lynnmtundefined 2 Replies Last reply Reply Quote 0
                  • lynnmtundefined
                    lynnmt @lynnmt
                    @lynnmt Ah! I forgot to mention a important detail!
                    the glowplug heater is PTC!
                    • lynnmtundefined
                      lynnmt @dc42
                      excellent. Thanks for running the test.
                      I will try the upgraded firmware.
                      A further question,
                      is there some way to know what these heater limits are and to make them user adjustable without needing to compile firmware?
                      all the best,
                      Michael Lynn
                      • lynnmtundefined
                        lynnmt @lynnmt
                        @lynnmt
                        is this an unstable package release?
                        also,
                        will the instructions here be sufficient for making this firmware update or are there other sources to consider?
                        https://docs.duet3d.com/User_manual/Machine_configuration/DSF_RPi#software-installation
                        when I run the commands suggested for upgrading to unstable releases, here:
                        sudo rm -f /etc/apt/sources.list.d/duet3d.list
                        sudo bash -c "echo 'deb https://pkg.duet3d.com/ unstable armv7' > /etc/apt/sources.list.d/duet3d-unstable.list"
                        my command prompt on SBC returns
                        bash - "permision denied"
                        • lynnmtundefined
                          lynnmt @dc42
                          I have successfully upgraded to RRF 3.5.0-rc.3.
                          Autotuning of my heater still fails with the warning
                          running M303 H1 Y20 P0.27 S750 returns:
                          "Autotune failed due to bad curve fit (R=53.131 K=0.801:0.000 D=1.25)
                          If i then take the provided model parameters, and plug them into M307 as:
                          M307 H1 R53.131 K0.801 D1.25
                          this command returns
                          Error M307 : Bad model parameters.
                          The autotune makes a very nice curve, see picture here:
                          Not sure what to make of this.
                            @lynnmt do you have a temperature limit set for that heater? Use M143 H1 to check. If so then it may be set too low. If the heater has been assigned to a tool then it will have a default temperature limit. I found that I needed to increase the temperature limit to 1750C (M143 H1 S1750) for those parameters to be accepted.
                            Please post your config.g file.
                            • lynnmtundefined
                              lynnmt @dc42
                              config.g
                              ; Configuration file for Duet 3 MB 6HC (firmware version 3.3)
                              ; generated by RepRapFirmware Configuration Tool v3.4.1 on Fri Feb 23 2024 23:32:11 GMT-0600 (Central Standard Time)
                              G90                                          ; send absolute coordinates...
                              M83                                          ; ...but relative extruder moves
                              M550 P"Duet 3"                               ; set printer name
                              M918 P1 E4 F2000000                          ; configure direct-connect display
                              M569 P0.0 S0                                 ; physical drive 0.0 goes backwards
                              M569 P0.1 S1                                 ; physical drive 0.1 goes forwards
                              M569 P0.2 S1                                 ; physical drive 0.2 goes forwards
                              M569 P0.3 S0                                 ; physical drive 0.3 goes backwards
                              M584 X0.0 Y0.1 Z0.2 E0.3                     ; set drive mapping
                              M350 X16 Y16 Z16 E16 I1                      ; configure microstepping with interpolation
                              M92 X80.00 Y80.00 Z400.00 E93.00             ; set steps per mm
                              M566 X1200.00 Y1200.00 Z24.00 E300.00        ; set maximum instantaneous speed changes (mm/min)
                              M203 X9000.00 Y9000.00 Z180.00 E6000.00      ; set maximum speeds (mm/min)
                              M201 X500.00 Y500.00 Z100.00 E5000.00        ; set accelerations (mm/s^2)
                              M906 X800 Y800 Z800 E1000 I50                ; set motor currents (mA) and motor idle factor in per cent
                              M84 S30                                      ; Set idle timeout
                              M208 X0 Y0 Z0 S1                             ; set axis minima
                              M208 X235 Y235 Z250 S0                       ; set axis maxima
                              M574 X1 S1 P"io1.in"                         ; configure switch-type (e.g. microswitch) endstop for low end on X via pin io1.in
                              M574 Y1 S1 P"io2.in"                         ; configure switch-type (e.g. microswitch) endstop for low end on Y via pin io2.in
                              M574 Z1 S2                                   ; configure Z-probe endstop for low end on Z
                              M950 S0 C"io5.out"                           ; create servo pin 0 for BLTouch
                              M558 P9 C"io5.in" H5 F120 T6000              ; set Z probe type to bltouch and the dive height + speeds
                              G31 P500 X0 Y0 Z3                            ; set Z probe trigger value, offset and trigger height
                              M557 X60:215 Y30:195 S20                     ; define mesh grid
                              M308 S0 P"temp0" Y"thermistor" T100000 B4092 ; configure sensor 0 as thermistor on pin temp0
                              M950 H0 C"out0" T0                           ; create bed heater output on out0 and map it to sensor 0
                              M307 H0 B1 S1.00                             ; enable bang-bang mode for the bed heater and set PWM limit
                              M140 H0                                      ; map heated bed to heater 0
                              M143 H0 S150                                 ; set temperature limit for heater 0 to 150C
                              M308 S1 P"spi.cs0" Y"thermocouple-max31856"  ; configure sensor 1 as thermocouple via CS pin spi.cs1
                              M950 H1 C"out1" T1                           ; create nozzle heater output on out1 and map it to sensor 1
                              M307 H1 B0 S0.10                             ; disable bang-bang mode for heater  and set PWM limit
                              M143 H1 S900                                ; set temperature limit for heater 1 to 900C
                              M950 F0 C"out7" Q500                         ; create fan 0 on pin out7 and set its frequency
                              M106 P0 S0 H-1                               ; set fan 0 value. Thermostatic control is turned off
                              M563 P0 D0 H1 F0                             ; define tool 0
                              G10 P0 X0 Y0 Z0                              ; set tool 0 axis offsets
                              G10 P0 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                              M501                                         ; load saved parameters from non-volatile memory
                              T0                                           ; select first tool
                              I have set the temperature limit to 900 C.
                              why would there be a minimum limit for the model parameters to be accepted?
                              my heater cannot be allowed to operate above about 1300 C in air for an extended period, or its resistance will drift.
                              I set a lower limit, because the thermocouple has a large offset temperature and I dont know it exactly. so I set a conservative limit, as I wanted to avoid destroying my heater.
                              soare0undefined 1 Reply Last reply Reply Quote 0
                              • soare0undefined
                                soare0 @lynnmt
                                @lynnmt I think it is only for the model to work. Normally, it should be a real โ€limitโ€ here, and for the heaters wich I not did autotune (or failed, probably because of the same problem as yours now, and for wich I set the model parameters manually), I get some warnings like: โ€your temperature may reach XXX degreesโ€, but this did not happened... yet.
                                M143 H4 S100                                        ; set temperature limit for heater 1 to 100C
                                And the model:
                                M307 H4 R0.217 K0.124:0.000 D19.84 E1.35 S1.00 B1
                                So the software warns me at start-up that based on my M307, and ... do not know what else, the heater will reach 176C. I could not care less, as it works, just an annoying message more.
                                • lynnmtundefined
                                  lynnmt
                                  So after taking @dc42 suggestion and raising the temperature limit to 1750C,
                                  the Autotune (at 700 C target temperature and 0.27 pwm limit with Y20) worked and returned parameters:
                                  Heater 1: heating rate 44.460, cooling rate 0.824, dead time 1.70, max PWM 0.27, mode PID, calibrated at 23.6V
                                  Predicted max temperature rise 1918ยฐC
                                  PID parameters: heating P2.4 I0.233 D2.8, steady P2.4 I0.499 D2.8
                                  This seems to be reliable enough given my janky current setup to transfer to the working printhead.
                                  We also characterized the offset temperature from the glowplug tip to the thermocouple y measuring the tip temperature with an identical type K thermocouple.
                                  here is the result
                                  thanks for the guidance. I think this is enough for a start. ๐Ÿ™‚
                                  OwenDundefined 1 Reply Last reply Reply Quote 0
                                  • OwenDundefined
                                    OwenD @lynnmt
                                    @lynnmt
                                    Unrelated to the tuning, but I wonder if adopting a setup similar to hot wire tig welding would be beneficial in this application ?
                                    Essentially the wire has a current applied by an external DC power source (sometimes AC), with the bed being the ground.
                                    When a connection occurs during feeding, the wire is "pre heated" allowing for faster melting & higher deposition rates.
                                    The current used isn't enough that the wire can create an arc on its own.
                                    • lynnmtundefined
                                      lynnmt @OwenD
                                      @OwenD
                                      others have already done this.
                                      https://hackaday.io/project/169412-wire-3d-printer
                                      https://www.digitalalloys.com/
                                      it requires large currents and does not work with glasses or ceramics.
                                      neat process, but will not work for my application unfortunately.
                                      • OwenDundefined
                                        OwenD @lynnmt
                                        @lynnmt
                                        Those examples are using the current to melt the wire (akin to MIG welding), so they are nothing like TIG hot wire.
                                        In hot wire TIG, the current through the wire is much lower and used only to aid melting the wire by getting it hot.
                                        The main heat source is external. In TIG it's a high current arc carried via a tungsten electrode, but a heating cartridge would equally work.
                                        Naturally it wouldn't work with non conductive materials.
                                        Anyway, just a thought.
                                        • lynnmtundefined
                                          lynnmt
                                          So one of our project members, Shields experiments provided us a thermocouple isolator interposer for the duet thermocouple board.
                                          this allows us to use a thermocouple directly on the tip of the heater with no insulation and no stainless steel ring.
                                          Unfortunately, this also means that our model parameters are once again out of range...
                                          can you point me to the place in the firmware where I can adjust the model parameter range?
                                          I have no fear of finding and modifying it to make this work. ๐Ÿ™‚
                                            @lynnmt the validation of model parameters is in function FopDt::SetParameters in file FOPDT.cpp.
                                            However, I decided to remove the check on maximum temperature increase when validating parameters, which should resolve the problem for you. You will still see a warning if the estimated maximum temperature is high. I have also provided a more detailed error message when validation of model parameters fails. You can find the latest 3.5.0-rc.3+4 firmware binaries with these changes included at https://www.dropbox.com/scl/fo/yzchzlyxmxlzywjawqflu/h?rlkey=tl7dfs75yozhfgpze0jnkn32n&dl=0.
                                            lynnmtundefined 1 Reply Last reply Reply Quote 1