I have a problem with the X-axis endstop.
When I perform a homing operation, the axis moves but stops before reaching the X endstop. To actually reach the switch, I have to run the X homing procedure a dozen times.
The switch is connected as normally closed. The cable is quite long, about 5 meters.
The Y-axis also has a long cable, but it works fine.What could be the cause? How can I fix the problem?
-
When I perform a homing operation, the axis moves but stops before reaching the X endstop.
Would be good to know whether the move stops due to the endstop being triggered…
Context (please confirm):
You are running a 6HC + 1XD in a SBC setup?
Your config.g is still this here?; Configuration file for Duet 3 (firmware version 3.5.1) ; executed by the firmware on start-up ; ; SBC Config M291 P"Applying persistent configuration options" R"Please wait" S1 T60 ; show that persistent settings are being configured while exists(sbc) && plugins.DuetPiManagementPlugin.pid < 0 && iterations < 30 G4 S2 ; wait for DuetPiManagementPlugin to become available G4 S2 ; wait another moment M929 S2 ; start logging events to the SD Card M550 P"MD" ; set persistent hostname for printer ;M551 P"mdrapid" ; set password M586 P0 S1 C"*" ; configure HTTP & enable CORS M586 P1 S0 ; disable FTP M586 P2 S0 ; disable Telnet M292 ; hide message box again upon completion ; General Preferences G21 ; Work in millimetres G90 ; absolute coordinates M83 ; relative extruder moves ; Drives M569 P41.0 S1 R1 T2.5:2.5:5:5 ; physical drive 0.0 goes forwards with active high enable config pulses intervals (x) M569 P42.0 S1 R1 T2.5:2.5:5:5 ; physical drive 0.0 goes forwards with active high enable config pulses intervals (y) M569 P43.0 S1 R1 T2.5:2.5:5:5 ; physical drive 0.0 goes forwards with active high enable config pulses intervals (z) M584 X41.0 Y42.0 Z43.0 ; set drive mapping M92 X83.50 Y83.50 Z320.00 ; set steps per mm M566 X600.00 Y600.00 Z60.00 ; set maximum instantaneous speed changes (mm/min) M203 X3000.00 Y3000.00 Z1800.00 ; set maximum speeds (mm/min) M201 X500.00 Y500.00 Z20.00 ; set accelerations (mm/s^2) ; Axis Limits M208 X0 Y0 Z0 S1 ; set axis minima M208 X2000 Y4000 Z320 S0 ; set axis maxima ; Endstops M574 X1 S1 P"io2.in" ; configure switch-type (e.g. microswitch) endstop for low end on X via pin io2.in M574 Y1 S1 P"io3.in" ; configure switch-type (e.g. microswitch) endstop for low end on Y via pin io3.in ; Z-Probe M558 P5 C"io5.in" H10 F900 T3000 ; set Z probe type to switch and the dive height + speeds G31 P500 X0 Y0 Z8 ; set Z probe trigger value, offset and trigger height M557 X0:1250 Y0:2400 S200 ; define mesh grid ; PE320 Extruder M569 P40.0 S1 R1 T0:0:0:0 ; external drive CAN address 40 goes forward, active high enable M584 E40.0 ; set drive mapping - map extruder to CAN address 40 M350 E1 I0 ; configure extruder with NO microstepping M92 E301.6485 ; set steps per mm - extruder E-steps/mm (resolution of 1:48) or 166.7 steps/rev M566 E3000 ; set maximum instantaneous speed changes (mm/min) M203 E3000 ; set maximum speeds (mm/min) M201 E20000 ; set accelerations (mm/s^2) ; Temp sensor parameters M308 S0 P"2.spi.cs0" Y"rtd-max31865" A"Top" M308 S1 P"2.spi.cs1" Y"rtd-max31865" A"Middle" M308 S2 P"2.spi.cs2" Y"rtd-max31865" A"Bottom" M308 S3 P"2.spi.cs3" Y"rtd-max31865" A"Nozzle" ; Create heaters M950 H0 C"out0" T0 ; create Top heater output on out0 and map it to sensor 0 M950 H1 C"out1" T1 ; create Middle heater output on out1 and map it to sensor 1 M950 H2 C"out2" T2 ; create Bottom heater output on out2 and map it to sensor 2 M950 H3 C"out3" T3 ; create Nozzle heater output on out3 and map it to sensor 3 ; Set PID heater parameters M307 H0 R1.319 K0.319:0.000 D25.28 E1.35 S1.00 B0 M307 H1 R0.650 K0.120:0.000 D35.30 E1.35 S1.00 B0 M307 H2 R0.636 K0.188:0.000 D41.46 E1.35 S1.00 B0 M307 H3 R0.500 K0.137:0.000 D21.29 E1.35 S1.00 B0 ; Maximum extruder heater temperature M143 H0 S400 ; set temperature limit for heater 0 to 400C M143 H1 S400 ; set temperature limit for heater 0 to 400C M143 H2 S400 ; set temperature limit for heater 0 to 400C M143 H3 S400 ; set temperature limit for heater 0 to 400C ; Extruder heater fault detection M570 H0 P60 T30 ; An anomaly on heaters 0 must persist for 60 seconds, and must be greater or less than 30C from the setpoint, to raise a heater fault. M570 H1 P60 T30 ; An anomaly on heaters 1 must persist for 60 seconds, and must be greater or less than 30C from the setpoint, to raise a heater fault. M570 H2 P60 T30 ; An anomaly on heaters 2 must persist for 60 seconds, and must be greater or less than 30C from the setpoint, to raise a heater fault. M570 H3 P60 T30 ; An anomaly on heaters 3 must persist for 60 seconds, and must be greater or less than 30C from the setpoint, to raise a heater fault. ; Define Heaters as Tools M563 P0 H0 S"Top" M563 P1 H1 S"Middle" M563 P2 H2 S"Bottom" M563 P3 D0 H3 S"Nozzle" ; Heater Cooling Fans M950 F0 C"2.out0+io1.in" Q100 A"Heat Break Fan" ; Heat Break Fan -- 4-wire PWM 12V fan so invert it, 100Hz PWM, NO tacho M950 F1 C"!2.out3+out3.tach" Q100 A"Top Fan" ; Top Fan -- 4-wire PWM 12V fan so invert it, 100Hz PWM, tacho connected M950 F2 C"!2.out4+out4.tach" Q100 A"Middle Fan" ; Middle Fan -- 4-wire 12V PWM fan so invert it, 100Hz PWM, tacho connected M950 F3 C"!2.out5+out5.tach" Q100 A"Bottom Fan" ; Bottom Fan -- 4-wire 12V PWM fan so invert it, 100Hz PWM, tacho connected M106 P0 S1 T40 H0:1:2:3 ; Turn on Heat Break Fans when heaters 0-3 are above 40 deg M106 P1 S0.5 ; Run at 20% speed at 2200rpm (max 11000rpm) M106 P2 S0.5 ; Run at 20% speed at 2200rpm (max 11000rpm) M106 P3 S0.5 ; Run at 20% speed at 2200rpm (max 11000rpm) ; Bed Heaters ;M308 S4 P"1.temp0" Y"thermistor" A"Bed" T100000 B4725 C7.06e-8 ; configure bed thermistor at 1.temp0 ;M308 S5 P"1.temp1" Y"thermistor" A"Bed" T100000 B4725 C7.06e-8 ; configure bed thermistor at 1.temp1 ;M308 S6 P"1.temp2" Y"thermistor" A"Bed" T100000 B4725 C7.06e-8 ; configure bed thermistor at 1.temp2 ;M308 S7 P"temp0" Y"thermistor" A"Bed" T100000 B4725 C7.06e-8 ; configure bed thermistor at temp0 ;M950 H4 C"1.out0" T4 Q10 ; create bed heater output on 1.out0 and map it to temp sensor 4 ;M950 H5 C"1.out1" T5 Q10 ; create bed heater output on 1.out1 and map it to temp sensor 5 ;M950 H6 C"1.out2" T6 Q10 ; create bed heater output on 1.out2 and map it to temp sensor 6 ;M950 H7 C"1.out3" T7 Q10 ; create bed heater output on 1.out3 and map it to temp sensor 7 ;M307 H4 R0.421 K0.321:0.000 D5.73 E1.35 S1.00 B0 ; Bed PID tuning parameters ;M140 P0 H4 ; map heater 4 to heated bed 0 ;M140 P1 H5 ; map heater 5 to heated bed 1 ;M140 P2 H6 ; map heater 6 to heated bed 2 ;M140 P3 H7 ; map heater 7 to heated bed 3 ;M143 H4 S120 ; max temp -- 120 deg C ;M143 H5 S120 ; max temp -- 120 deg C ;M143 H6 S120 ; max temp -- 120 deg C ;M143 H7 S120 ; max temp -- 120 deg C ;M570 H4 P60 T15 ; An anomaly on heaters 4 must persist for 60 seconds, and must be greater or less than 15C from the setpoint, to raise a heater fault. ;M570 H5 P60 T15 ; An anomaly on heaters 4 must persist for 60 seconds, and must be greater or less than 15C from the setpoint, to raise a heater fault. ;M570 H6 P60 T15 ; An anomaly on heaters 4 must persist for 60 seconds, and must be greater or less than 15C from the setpoint, to raise a heater fault. ;M570 H7 P60 T15 ; An anomaly on heaters 4 must persist for 60 seconds, and must be greater or less than 15C from the setpoint, to raise a heater fault. ; Define Bed Heaters as Tools ;M563 P4 H4 S"Bed 0" ;M563 P5 H5 S"Bed 1" ;M563 P6 H6 S"Bed 2" ;M563 P7 H7 S"Bed 3" ; Define Inputs M950 J0 C"io0.in" ; Relay 12 - Estop M950 J1 C"io1.in" ; Relay 13 - Reset ;M950 J2 C"io2.in" ; Relay 14 - X-Endstop ;M950 J3 C"io3.in" ; Relay 15 - Y-Endstop ;M950 J4 C"io4.in" ; Relay 16 - Z-Endstop ;M950 J5 C"io5.in" ; Relay 17 - Z-Probe M950 J6 C"io6.in" ; Relay 18 - FREE M950 J7 C"io7.in" ; Relay 19 - FREE M950 J8 C"io8.in" ; Relay 20 - FREE M950 J9 C"1.io0.in" ; Relay 21 - FREE M950 J10 C"1.io1.in" ; Relay 22 - FREE M950 J11 C"2.io0.in" ; Smart Wiring Loom - Material sensor LEFT M950 J12 C"2.io2.in" ; Smart Wiring Loom - Material sensor RIGHT M950 J13 C"40.io0.in" ; 1XD board - Servo Drive Fault ; Configure Input Triggers M581 P1 T2 S1 R0 ; Relay 13 - trigger 2 (Reset) activates on falling edge when Estop button is pressed M581 P13 T3 S1 R0 ; Trigger 3 (Servo Drive Fault) activates on falling edge when servo fault detected ; Define Ouputs M950 P0 C"out4" ; Relay 1 - Pellet Material Feed Solenoid M950 P1 C"out5" ; Relay 2 - Part Cooling Solenoid M950 P2 C"out6" ; Relay 3 - FREE M950 P3 C"out7" ; Relay 4 - FREE M950 P4 C"out8" ; Relay 5 - FREE M950 P5 C"out9" ; Relay 6 - FREE M950 P6 C"1.out1" ; Relay 7 - FREE M950 P7 C"1.out2" ; Relay 8 - FREE M950 P8 C"1.out3" ; Relay 9 - FREE M950 P9 C"1.out4" ; Relay 10 - FREE M950 P10 C"1.out5" ; Relay 11 - FREE M950 P11 C"40.io0.out" ; 1XD board - Clear Servo Drive Faults ; Set Outputs M42 P0 S0 ; Output OFF M42 P1 S0 ; Output OFF M42 P2 S0 ; Output OFF M42 P3 S0 ; Output OFF M42 P4 S0 ; Output OFF M42 P5 S0 ; Output OFF M42 P6 S0 ; Output OFF M42 P7 S0 ; Output OFF M42 P8 S0 ; Output OFF M42 P9 S0 ; Output OFF M42 P10 S0 ; Output OFF M42 P11 S0 ; Output OFF ; Select Tool T3 ; select nozzle heater with PE320 extruder M568 P3 A0 ; set nozzle heater to off ; Custom settings
-
- Please provide your config.g and homex.g files.
- Which firmware version are you using?
- Which input is the X endstop switch connected to?
- Do the X endstop wires run parallel to any stepper motor wires over a significant distance?
-
@infiniteloop said in Homing X triggers before reaching endstop:
Would be good to know whether the move stops due to the endstop being triggered…
Context (please confirm):
You are running a 6HC + 1XD in a SBC setup?
Your config.g is still this here?Yes provided hardware setup (6HC + 1XD in SBC configuration) and the config.g you referenced are both correct.
We verified the switch using a multimeter and it works correctly.
Also, when we press the switch, the X endstop indicator in DWC lights up green as expected.What’s interesting is that when the X axis starts close to the switch, the homing procedure works normally.
However, if the axis is farther away, we need to run the homing sequence several times before it actually reaches the switch.
It looks like the system thinks the endstop has been triggered before it actually touches the switch. -
Well one possible answer is that the X homing command simply isn't moving as far as you think it is going to move.
We need to see the actual homing code for X.
Also, have you verified that the X axis steps-per-mm setting is correct?
Frederick
-
@fcwilt The homing code for the X axis appears to be correct.
The working area of the machine is X1200Y2300 mm, and in the homing file, the G1 command for X is set to -1205 and Y -2305, which seems appropriate given the dimensions.Here is the relevant portion of the homing code for X:
G91 ; relative positioning G1 H2 Z10 F3000 ; lift Z relative to current position G1 H1 X-1205 F3000 ; move quickly to X axis endstop and stop there (first pass) G1 H2 X5 F3000 ; go back a few mm G1 H1 X-1205 F1500 ; move slowly to X axis endstop once more (second pass) G1 H2 Z-10 F3000 ; lower Z again G90 ; absolute positioning
Is it possible that the cable length (approx. 5 meters) is introducing additional resistance, making the controller interpret the switch as open?
Or could it be due to electrical noise from nearby signal or motor cables? -
@sebastianwac said in Homing X triggers before reaching endstop:
G91 ; relative positioning G1 H2 Z10 F3000 ; lift Z relative to current position G1 H1 X-1205 F3000 ; move quickly to X axis endstop and stop there (first pass) G1 H2 X5 F3000 ; go back a few mm G1 H1 X-1205 F1500 ; move slowly to X axis endstop once more (second pass) G1 H2 Z-10 F3000 ; lower Z again G90 ; absolute positioning
One small observation. The G1 H2 X5 F3000 command - you don't need H2 since the preceding G1 H1 X-1205 F3000 will have marked the X axis as homed and at the point plain G1 moves will work as expected.
Is it possible that the cable length (approx. 5 meters) is introducing additional resistance, making the controller interpret the switch as open?
Or could it be due to electrical noise from nearby signal or motor cables?5 meters is a lot. It could be picking up noise.
Is the wire twisted or shielded? Is the end-stop device a simple switch, like a micro-switch? Is it normally closed? Normally closed is the best as the signal wire is connected to ground, making it resistant to noise.
Frederick
-
Or could it be due to electrical noise from nearby signal or motor cables?
IMHO, that’s the most plausible scenario. To test, take another cable of similar length and route it as far away from any steppers and wiring harnesses as possible.
-
@sebastianwac said in Homing X triggers before reaching endstop:
Is it possible that the cable length (approx. 5 meters) is introducing additional resistance, making the controller interpret the switch as open?
Or could it be due to electrical noise from nearby signal or motor cables?Did you see my reply of 9 May?
-
Yes, the endstop wire is shielded, and the switch is a simple normally closed micro-switch, as recommended.
I’ve also noticed something very specific:
Right after powering on or resetting the controller, homing works perfectly — regardless of the axis position.
However, after performing an extrusion (extrude command), homing no longer works properly — the axes stop too early, as if the endstop had already been triggered.Could this behavior be caused by interference from the extruder motor?
The endstop wires are routed separately from the extruder motor cables, so they don't share the same path.Would it be possible to reset the extruder driver via G-code after each extrusion or print to prevent this issue?
-
@sebastianwac said in Homing X triggers before reaching endstop:
Would it be possible to reset the extruder driver via G-code after each extrusion or print to prevent this issue?
You could test with this. https://docs.duet3d.com/User_manual/Reference/Gcodes#m18-disable-motors
-
The endstop wires are routed separately from the extruder motor cables, so they don't share the same path.
Just for clarity - how exactly have you wired the X endstop? From my understanding, there are two lines:
- line 1 from Pin "io2.in" to endstop
- the other line from GND (where exactly do you take it from?) to endstop
Am I right with this assumption? Or do you supply 5V instead of GND? If so, where do you pick it up? Are any pull-up or pull-down resistors involved?
-
@infiniteloop
Endstop is wired to IN and GND pins of IO_2 connector.@Phaedrux
Thanks. I used M84 E0 at start of homing codes and it did the job. Now it is working correctly every time. -
@sebastianwac said in Homing X triggers before reaching endstop:
I used M84 E0 at start of homing codes and it did the job. Now it is working correctly every time.
That confirms that the issue was caused by interference between the extruder motor cable and the endstop cable. You said they are routed separately, but do they run parallel and close together for an appreciable distance?
Using shielded cable for endstop wires offers protection against capacitively coupled interference, but not against inductively coupled interference. You can defend against inductively coupled interference by using twisted pair cable. Preferably, the signal and ground wires of the endstop switch should be connected to the Duet using a single twisted pair; and the stepper motor should be connected to the Duet using two twisted pairs, each motor phase using one pair.