    Beginner Needs Help - Anycubic Kossel Plus + Duet WiFi -- HOW?
    141
    28.9k
    • mindbender9undefined
      mindbender9
      Ok, I'm getting confused about what values to put in the G31 line.
      G31 X0 Y32.82 Z0 P500
      • I measured the distance from the tip of the nozzle/hot-end to the circuit board of the dc42 IR probe, which came out to 32.82mm. I believe that the IR probe is off to the side of the nozzle along its Y-axis, because when I click on "Y-10", it moves in the direction of the mounted IR probe. Therefore, I'm entering "Y32.82".
      • For the X-value, I'm not sure if the probe is offset along the X-axis. From what I can see, the probe lines up directly in the path of the IR probe. So I'm going to make a guess and leave the X value of G31 as 0.
      • For the Z-value, there's a problem (of course). As I lower the nozzle to the bed, it stops at Z=0 and won't go any lower - but the nozzle's position is roughly 8-10mm above the bed - it won't drop any further. The IR Probe also is at zero at this same point, but will register "465" if I slide a single page of paper under it.
      Why is the Z-axis stopping at 8-10mm off of the bed?
      Here are the current config files:
      config.g
      ; generated by RepRapFirmware Configuration Tool on Sun May 13 2018 19:16:40
      G90					; Send absolute coordinates...
      M83					; ...but relative extruder moves
      M555 P1					; Set firmware compatibility to look like RepRapFirmare
      ;*** The homed height is deliberately set too high in the following - you will adjust it during calibration.
      M665 R134 L270 B85 H285		; Set delta radius, diagonal rod length, printable radius and homed height
      M666 X0 Y0 Z0			; Put your endstop adjustments here, or let auto calibration find them
      M550 Pduettest
      M552 S1					; Enable network
      M586 P0 S1				; Enable HTTP
      M586 P1 S0				; Disable FTP
      M586 P2 S0				; Disable Telnet
      M558 P1 X0 Y0 Z0 H30 F1000 T5000 ;I1 		; Set Z probe type to DC42 and the dive height + speeds
      ; M558 P0 X0 Y0 Z1 H5 F1000 T5000 ;I1 		; Set Z probe type to MANUAL and the dive height + speeds
      G31 X0 Y32.82 Z0 P500				; Set Z probe trigger value, offset and trigger height
      ;G31 X0 Y0 Z1.0 P500				; Set Z probe trigger value, offset and trigger height
      M557 R130 S20					; Define mesh grid
      M569 P0 S1					; Drive 0 goes forwards
      M569 P1 S1					; Drive 1 goes forwards
      M569 P2 S1					; Drive 2 goes forwards
      M569 P3 S1					; Drive 3 goes forwards
      M350 X16 Y16 Z16 E16 I1				; Configure microstepping with interpolation
      M92 X80 Y80 Z80 E96				; Set steps per mm
      M566 X1200 Y1200 Z1200 E1200			; Set maximum instantaneous speed changes (mm/min)
      M203 X18000 Y18000 Z18000 E1200			; Set maximum speeds (mm/min)
      M201 X1000 Y1000 Z1000 E1000			; Set accelerations (mm/s^2)
      M906 X1000 Y1000 Z1000 E800 I30			; Set motor currents (mA) and motor idle factor in per cent
      M84 S30						; Set idle timeout
      M208 Z0 S1					; Set minimum Z
      M574 X2 Y2 Z2 S1				; Set active high endstops
      M305 P0 T100000 B4267 C0 R4700			; Set thermistor + ADC parameters for heater 0
      M143 H0 S120					; Set temperature limit for heater 0 to 120C
      M305 P1 T100000 B4267 C0 R4700			; Set thermistor + ADC parameters for heater 1
      M143 H1 S275					; Set temperature limit for heater 1 to 275C
      M106 P0 S0.3 I0 F500 H-1 ; Set fan 0 value, PWM signal inversion and frequency. Thermostatic control is turned off
      M106 P1 S1 I0 F500 H1 T45 ; Set fan 1 value, PWM signal inversion and frequency. Thermostatic control is turned on
      M106 P2 S1 I0 F500 H1 T45 ; Set fan 2 value, PWM signal inversion and frequency. Thermostatic control is turned on
      M563 P0 D0 H1					; Define tool 0
      G10 P0 X0 Y0 Z0					; Set tool 0 axis offsets
      G10 P0 R0 S0					; Set initial tool 0 active and standby temperatures to 0C
      M501
      bed.g:
      M561 			; clear any bed transform
      ;G31 X0 Y0		; don't want any probe offset for this - ADDED 5/21/2018
      G28			; home the printer
      M401			; deploy the Z probe
      ; bed.g file for RepRapFirmware, generated by Escher3D calculator
      ; 10 points, 6 factors, probing radius: 105, probe offset (0, 0)
      ;M98 Pdeployprobe.g
      G30 P0 X0.00 Y105.00 Z-99999 H0
      G30 P1 X90.93 Y52.50 Z-99999 H0
      G30 P2 X90.93 Y-52.50 Z-99999 H0
      G30 P3 X0.00 Y-105.00 Z-99999 H0
      G30 P4 X-90.93 Y-52.50 Z-99999 H0
      G30 P5 X-90.93 Y52.50 Z-99999 H0
      G30 P6 X0.00 Y52.50 Z-99999 H0
      G30 P7 X45.47 Y-26.25 Z-99999 H0
      G30 P8 X-45.47 Y-26.25 Z-99999 H0
      G30 P9 X0 Y0 Z-99999 S6
      ;M98 Pretractprobe.g
      ; DEFAULT SETTINGS - Set by the RepRapFirmware Wizard
      ; Probe the bed at 3 peripheral and 0 halfway points, and perform 3-factor auto compensation
      ; Before running this, you should have set up your Z-probe trigger height to suit your build, in the G31 command in config.g.
      ;G30 P0 X0 Y84.9 H0 Z-99999
      ;G30 P1 X73.53 Y-42.45 H0 Z-99999
      ;G30 P2 X-73.53 Y-42.45 H0 Z-99999
      ;G30 P3 X0 Y0 Z-99999 S3 ;H0
      M402 ; retract the Z probe
      G1 X0 Y0 Z150 F15000 ; get the head out of the way of the bed
      homedelta.g:
      G91                        ; relative positioning
      G1 S1 X400 Y400 Z400 F1800 ; move all towers to the high end stopping at the endstops (first pass)
      G1 X-5 Y-5 Z-5 F1800 S2    ; go down a few mm
      G1 S1 X10 Y10 Z10 F360     ; move all towers up once more (second pass)
      G1 Z-5 F6000               ; move down a few mm so that the nozzle can be centred
      G90                        ; absolute positioning
      ;G1 X0 Y0 F6000            ; move X+Y to the centre
      Juiceundefined 1 Reply Last reply Reply Quote 0
        If you have mounted the IR sensor with the bottom edge of the board 1 to 3mm above the top of the nozzle as recommended, then it should not be triggering when the nozzle is 8-10mm above the bed. Please ask your supplier to replace the IR sensor.
        • Danalundefined
          Danal @dc42
          @dc42 said in Beginner Needs Help - Anycubic Kossel Plus + Duet WiFi -- HOW?:
          David:
          From his screenshots, I don't believe the probe is triggering.
          Mindbender9:
          You MAY need to up the M665 H parameter, and then allow auto calibration to give you a real value. H is currently 285, try 300.
          Finger on the power button!! Stop it if it drives into the bed.
          mindbender9undefined 1 Reply Last reply Reply Quote 0
            Good point, I didn't read his post properly. Yes, it looks like the H parameter may need to be increased.
              mindbender9 @Danal
              @danal
              I increased the M665 H parameter to 300, and then changed the bed.g G31 line to: G31 X0 Y32.82 to account for the IR probe distance from the nozzle. I then ran auto-calibrate.
              While the nozzle didn't bury itself, it did move outside the bed on the third survey while auto-calibrating. Here's a picture to show what I'm describing:
              Both the IR Probe and the nozzle are outside the circular bed/printable area. I stopped the auto-calibration at this point.
              Any idea how to correct this? I think we're getting close.
              • Juiceundefined
                Juice @mindbender9
                @mindbender9 said in Beginner Needs Help - Anycubic Kossel Plus + Duet WiFi -- HOW?:
                Are you sure that the offset for the probe is in the +Y direction only? Looking at your pictures compared to how my effector is installed (as by the anycubic manual) the probe may need offsetting on both axis. Can you post a picture of your effector from the front (between x and y motors) of the machine so we can see it relative to the bed?
                I also noticed that the config-override.g file you posted has no updated parameters in it. When you do get the probe measuring all areas of the bed properly and you do an M500 to save the settings, double check that the override file has been updated.
                Oh, and since you've been having lots of crashes when attempting to print, before you start printing anything next time, manually lower the nozzle to different points on the bed to make sure that "zero" isn't above or below the bed.
                  mindbender9 @Juice
                  @juice
                  Hopefully, you'll be able to recognize something from these pictures.
                  View from front between X and Y motors:
                  View from right side between Y and Z motors:
                  View from left side between X and Z motors:
                  • Danalundefined
                    Danal
                    M557 R130 S20 seems wrong for a printer with a 230 diameter bed. Radius of 130 would be diameter of 260. This will move the nozzle off the bed.
                    Try a radius of 105, for diameter of 210, to keep things well away from the edges. If that works, you may be able to raise it slightly, watching for the edges. To start with, something like M557 R105 S20
                      mindbender9 @Danal
                      @danal said in Beginner Needs Help - Anycubic Kossel Plus + Duet WiFi -- HOW?:
                      Hi @Danal,
                      I changed the M557's R value to R105, R90 and R80 but the third stop of the autocalibrate still ran into issues (regardless of the R-value the was set).
                      With R105, it looks like the IR probe is just hovering outside of the edge of the bed, while the nozzle is inside the bed area. When I started lowering the R-value, the IR probe position didn't change. Here's a picture:
                      So it looks like the IR probe doesn't see the bed and keeps dropping, while the nozzle is inside the area of the bed, and this ends with nozzle contact as a result. And lowering the R-value doesn't not change this position.
                      I think we're close, but the nozzle's refusal to reflect any of the R-values is odd.
                        dc42 administrators @mindbender9
                        The Z probe offset is measured from the nozzle to the probe. So Y32.82 means the probe is 32.83mm in the +Y direction relative it the nozzle. Looking from the front of the printer towards the Z axis at the back, this means the sensor is behind the nozzle.
                        If the sensor is actually 32.82mm in front of the nozzle, you should use Y-32.82 in the G31 command.
                          mindbender9 @dc42
                          Edit: Hi @dc42 - Changing the Y-value did not change anything with the nozzle. The hot-end/IR probe went to the same position as it did on previous attempts. No change.
                          • Danalundefined
                            Danal
                            If physical results have stopped changing even when you change the numbers in two different commands, then something is not saving, or not reseting, or something...
                            While you should NOT have to do this, just for debugging, try a power cycle between each change.
                              mindbender9
                              Terrible results when I try to print.
                              • Good News: I've taken care of the Z-probe setup. I changed the bed.g file settings to only use three calibration points and it worked. So I went back to the 10-point settings and changed any that went off the bed. When I click Auto-Delta Calibration, all 10 calibration points now complete successfully - the nozzle comes within 0.2mm of the bed, the Z-probe LED flashes and the nozzle retracts then goes to the next point. I have placed the M500 code at the end of bed.g and M501 at the end of config.g.
                              • Bad News: Whenever I upload a gcode file of a 0.2mm test circle (after performing a calibration prior), the nozzle buries itself hard into the bed. Every time. And while I am not fast enough to power off the nozzle (it's dropping that fast), I think I'm at my last ropes here. I'm attaching whatever config files I have at this point.
                              • More Bad News: The Duet Wifi web interface keeps disconnecting when I open the webpage in either Google Chrome or Microsoft Edge. It takes 30 seconds or more to allow me to reconnect, or I have to manually restart the board.
                              • Question: Why does the nozzle bury itself into the bed when I just auto-calibrated the printer a few seconds before? Why is there a height difference that puts the Z-position below the bed after the auto-calibration?
                              config.g:
                              ; Configuration file for Duet WiFi (firmware version 1.20 or newer)
                              M665 R134 L270 B85 H300		; Set delta radius, diagonal rod length, printable radius and homed height
                              M550 Pduettest
                              G31 X0 Y-32.82 Z0 P500				; Set Z probe trigger value, offset and trigger height
                              M557 R80 S20					; Define mesh grid
                              M501
                              bed.g:
                              ; bed.g
                              ; called to perform automatic delta calibration via G32
                              G31 X0 Y0 Z20		; POSSIBLE PROBLEM WITH Z=32.82
                              ;G31 X0 Y0 Z32.82		; don't want any probe offset for this - ADDED 5/21/2018
                              M98 Pdeployprobe.g
                              G30 P2 X55.00 Y-65.00 Z-99999 H0
                              G30 P3 X0.00 Y-80.00 Z-99999 H0
                              G30 P4 X-72.00 Y-50.00 Z-99999 H0
                              G30 P5 X-87.00 Y52.50 Z-99999 H0
                              M98 Pretractprobe.g
                              M500 ; Save results
                              homedelta.g:
                              ; homedelta.g
                              ; called to home all towers on a delta printer
                                It buries the nozzle in the bed because you are telling it that the IR sensor triggers when it is 20mm above the bed (Z20 in G31). The actual trigger height will be much lower than that. Measure the IR sensor trigger height and use that value in the G31 Z parameter instead.
                                  mindbender9 @dc42
                                  • When you say to measure the trigger height for the IR sensor, what height would that be? Is that the Z-position from the bed to the bottom of the sensor? But at what height? I'm don't understand.
                                  Edit: I'll go over the "Measuring the trigger height" section of your instructions when I get home. Thanks!
                                  One other question:
                                  • The G31 line from the bed.g file says:
                                  G31 X0 Y0 Z20
                                  While the config.g line has:
                                  Question: Should the two G31 lines match in both files?
                                  Thanks for your help!
                                    mindbender9
                                    So I performed a number of Trigger Height measurements tonight and only two of the ten tests were even close. I don't understand why there's such a variance between the numbers.
                                    Z-Height #1: 2.377
                                    Z-Height #2: 3.953
                                    Z-Height #3: 2.641
                                    Z-Height #4: 3.09
                                    Z-Height #5: 3.391
                                    Z-Height #6: 4.415
                                    Z-Height #7: 2.103
                                    Z-Height #8: 3.628
                                    Z-Height #9: 3.653
                                    Z-Height #10: 3.516
                                    Now, two of the Auto Calibration points land outside of the bed. And I'm unable to change these outside positions no matter what G1 Xx Yy Z99999 H0 values I save to the bed.g file. It's like the board isn't reading the bed.g file. What happened?
                                    What do I do now?
                                      1. Is the variance is between probing at different points? If so then on a delta printer this is generally caused by the tilt of the effector varying with XY position. The tilt causes the relative heights of the nozzle and the prove to vary with XY position.
                                      Inconsistency in the trigger height for the IR sensor can also be due to using a transparent bed surface (e.g. glass or PEI) that is not backed by a black surface, or that has scuff marks on the top.
                                      1. If your initial delta parameters are a long way out, that could cause probe points to be outside the bed limits. Try a smaller probing radius. You can always move some of the probe points further out when you have it working.
                                        mindbender9 @dc42
                                        All points were for the same position. Dead center, at the middle of the bed.
                                        Using a replacement black bed top from the manufacturer.
                                        Will do. I’ll reduce the quantity of probe points using the wizard and see what happens.
                                        Question for @dc42 - What should be entered for G31 in the bed.g file? Should the XYZ values match the config.g G31 line or should they be zeroed out?
                                          @mindbender9, please clarify what type of Z-probe you are using. I was assuming it was my own IR sensor, but skimming through this rather long thread, I found user @3mm mentioning the IR sensor but no confirmation that you are using one too.
                                            mindbender9 @dc42
                                            Hi @dc42 - The IR sensor that I'm using is the "Mini differential IR height sensor" - I believe this might be one that you designed.
                                            It is currently mounted on my hot-end with an offset of 32.82mm (distance from the nozzle).