      @ajlapp said in Leadshine BLM57180 Servos:

      M569 P0 S0 T8.5:8.5:50.0:67.0 D0 ; Drive 0 goes forwards
      M350 X16 I1 ; Configure microstepping with interpolation
      M92 X14000.00 ;P0 is the first internal driver on the Duet.

      • The first driver on the breakout board is P5, not P0. So use P5 in your M569 command. I assume you are using the breakout board.
      • M350 doesn't have any effect on external drivers.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      1 Reply Last reply Reply Quote 0
      • 691175002undefined
        691175002
        last edited by

        If the servo drive has optocouplers you probably need a 5-24 volt signal that can source or sink >2ma.

        1 Reply Last reply Reply Quote 0
        • ajlappundefined
          ajlapp
          last edited by

          I assume I still use M92 to set steps/mm....how does that look? Is P5 then referenced as E2?

          M92 E2:5000; Something like this?

          dc42undefined nhofundefined 2 Replies Last reply Reply Quote 0
          • nhofundefined
            nhof
            last edited by

            I have integrated a few different servo motors and here are a few odd things I have run into.

            1. signal timings as mentioned by David. Dir change especially can be tricky because it's not always listed on data sheets so try large-ish values. Looks like you need 0.85us min pulse width for step signals on the ACS806.
            2. signal voltage levels - check to make sure you are getting high enough voltage on the step/dir compared to the data sheet for the servo drive. Yours should accept anything over 4V.
            3. Make sure your signal GND is good. If this is not a good ground reference you will never get repeatable performance from the system.

            Depending on the servo software you might also be able to get a readout of the commanded position or input signal as you test. This will let you know where you are dropping steps or where the signal is getting funky.

            1 Reply Last reply Reply Quote 0
            • dc42undefined
              dc42 administrators @ajlapp
              last edited by

              @ajlapp said in Leadshine BLM57180 Servos:

              I assume I still use M92 to set steps/mm....how does that look? Is P5 then referenced as E2?

              M92 E2:5000; Something like this?

              No, still as X. The M584 command is the one that tells the firmware that you are using driver 5 for the X axis (which is what I assume you are doing - you haven't posted your config.g file so I can't check).

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              1 Reply Last reply Reply Quote 0
              • ajlappundefined
                ajlapp
                last edited by

                Config below. Ultimately I'm hoping to use two of these BLM57180 servos for the X axis. All of my testing had been completed with the servo connected to P0...the config below is me trying to switch to P5.

                ; Configuration file for Duet WiFi (firmware version 1.21)
                ; executed by the firmware on start-up
                ;
                ; generated by RepRapFirmware Configuration Tool v2 on Wed Jan 16 2019 13:17:53 GMT-0500 (Eastern Standard Time)

                ; General preferences
                G90 ; Send absolute coordinates...
                M83 ; ...but relative extruder moves

                ; Network
                M550 P"AAM_Large_Volume_Printer" ; Set machine name
                M551 P"password: ; Set password
                M552 P10.0.0.55 S1 ; Enable network and set IP address
                M553 P255.255.255.0 ; Set netmask
                M554 P192.168.1.254 ; Set gateway
                M586 P0 S1 ; Enable HTTP
                M586 P1 S0 ; Disable FTP
                M586 P2 S0 ; Disable Telnet

                M584 X0:5 Y1 Z2 E4;

                ; Drives
                M569 P1 S1 ; Drive 1 goes forwards
                M569 P2 S1 ; Drive 2 goes forwards
                M569 P3 S1 ; Drive 3 goes forwards

                M569 P5 S0 T8.5:8.5:50.0:67.0 D0 ; Drive 0 goes forwards M569 P0 S0 T8.5:8.5:50.0:67.0 D0
                M92 X400.00 ;

                M92 Y80.00 Z4000.00 E400.00 ; Set steps per mm
                M566 X6000.00 Y900.00 Z12.00 E120.00 ; Set maximum instantaneous speed changes (mm/min)
                M203 X30000.00 Y6000.00 Z180.00 E1200.00 ; Set maximum speeds (mm/min)
                M201 X500.00 Y500.00 Z20.00 E250.00 ; Set accelerations (mm/s^2)
                M906 X2000.00 Y800.00 Z800.00 E800.00 I30 ; Set motor currents (mA) and motor idle factor in per cent
                M84 S30 ; Set idle timeout

                ; Axis Limits
                M208 X0 Y0 Z0 S1 ; Set axis minima
                M208 X1000 Y1000 Z1000 S0 ; Set axis maxima

                ; Endstops
                M574 X1 Y1 S0 ; Set active high endstops

                ; Z-Probe
                M574 Z1 S2 ; Set endstops controlled by probe
                M558 P1 H5 F120 T6000 ; Set Z probe type to unmodulated and the dive height + speeds
                G31 P500 X0 Y0 Z2.5 ; Set Z probe trigger value, offset and trigger height
                M557 X15:0 Y15:195 S20 ; Define mesh grid

                ; Heaters
                M305 P0 T100000 B4138 R4700 ; Set thermistor + ADC parameters for heater 0
                M143 H0 S120 ; Set temperature limit for heater 0 to 120C
                M305 P1 T100000 B4138 R4700 ; Set thermistor + ADC parameters for heater 1
                M143 H1 S280 ; Set temperature limit for heater 1 to 280C

                ; Fans
                M106 P0 S0.3 I0 F500 H-1 ; Set fan 0 value, PWM signal inversion and frequency. Thermostatic control is turned off
                M106 P1 S1 I0 F500 H1 T45 ; Set fan 1 value, PWM signal inversion and frequency. Thermostatic control is turned on

                ; Tools
                M563 P0 D0 H1 ; Define tool 0
                G10 P0 X0 Y0 Z0 ; Set tool 0 axis offsets
                G10 P0 R0 S0 ; Set initial tool 0 active and standby temperatures to 0C

                ; Heaters
                M305 P0 X151 T"J"

                ; Automatic saving after power loss is not enabled

                ; Custom settings are not configured

                1 Reply Last reply Reply Quote 0
                • nhofundefined
                  nhof @ajlapp
                  last edited by nhof

                  @ajlapp You would just use M92 and the axis name. The drives would be mapped to an axis using M584 so it would end up looking something like this (this is assuming you have two separate drives hooked up to 5 and 6 which you want to drive together for the X ax):

                  M584 X5:6 ; map drive 5:6 to X axis
                  M350 X1 I0 ; set microstepping mode, full step with no interpolation
                  M92 X400 ; set steps/mm for X axis (drive 5 & 6)
                  M569 P5 S0 T8.5:8.5:50.0:67.0 ; set drive timings for drive 5 (first drive on breakout board)
                  M569 P6 S0 T8.5:8.5:50.0:67.0 ; set drive timings for drive 6 (second drive on breakout board)

                  How was the servo drive originally connected to the 0 output? And how are the new motors wired up? Do you have them daisy chained via an encoder cable or something or are they both just hooked up to the drive output?

                  1 Reply Last reply Reply Quote 0
                  • ajlappundefined
                    ajlapp
                    last edited by ajlapp

                    Solved

                    For one axis anyways...

                    I've always had the ACS806 wired directly into the stepper motor 4-pin connection....this was doing something so it seemed correct to me.

                    Anyway, I saw in the docs that the "expansion board" had dedicated pins for Step and Direction....so I wired directly to these pins on the 50-pin expansion port and it works perfectly.

                    So now my question is...can I wire to the 4-pin ports and can I ultimately use P0, P1 and P2? I have seven actuators and an extruder on this machine.

                    Thanks for all the help so far!

                    nhofundefined 1 Reply Last reply Reply Quote 0
                    • dc42undefined
                      dc42 administrators
                      last edited by dc42

                      I suggest you use one of the internal stepper drivers for the extruder. The maximum number of independently-controlled external stepper drivers supported without changing the firmware is 7, made up of 5 on the expansion connector and 2 on CONN_LCD.

                      Duet WiFi hardware designer and firmware engineer
                      Please do not ask me for Duet support via PM or email, use the forum
                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                      1 Reply Last reply Reply Quote 0
                      • nhofundefined
                        nhof @ajlapp
                        last edited by

                        If two of the actuators are always running together (twin x) you might try using just one step/dir output for both drivers. Assuming your setup is like this
                        2 X actuators
                        1 Y actuator
                        4 Z actuators (all independent)

                        If this is correct you could do something like the following
                        Drive 5: both X motors
                        Drive 6: Y motor
                        Drive 7, 8, 9, 10: Z motors
                        Drive 11: Extruder motor

                        1 Reply Last reply Reply Quote 0
                        • ajlappundefined
                          ajlapp
                          last edited by

                          I think both of those are workable solutions.

                          I should be operational sometime next week.

                          I’ll load some pics once the magic starts.

                          Thanks again.

                          1 Reply Last reply Reply Quote 0