    PanelDue extend the wire

    Scheduled Pinned Locked Moved
    PanelDue
    5
    31
    1.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • Phaedruxundefined
      Phaedrux Moderator
      last edited by

      https://duet3d.dozuki.com/Wiki/Connecting_an_LCD_control_panel#Section_Connecting_a_PanelDue

      With a high quality 4 wire connection you can probably reach ~1500mm. Maybe more if the cable is shielded twisted pair with low resistance.

      Z-Bot CoreXY Build | Thingiverse Profile

      FBGundefined 1 Reply Last reply Reply Quote 0
      • wilrikerundefined
        wilriker @FBG
        last edited by

        @FBG I use a cable about 2m long. Nothing fancy. 4x0.34mm², no shield, no pairs twisting (apart from the four wires slowly twisting in the outer sheath), run it at 115200 baud and except once I never saw any communication problems.

        Can you be a bit more precise on the errors you see? Also what's the resistance of your wires?

        Manuel
        Duet 3 6HC (v0.6) with RPi 4B on a custom Cartesian
        with probably always latest firmware/DWC (incl. betas or self-compiled)
        My Tool Collection

        1 Reply Last reply Reply Quote 0
        • FBGundefined
          FBG @Phaedrux
          last edited by

          @Phaedrux I use a wire shielded twisted pair but the problem happen...

          @wilriker If i choose 115200, the PanelDue not show me the files that there are inside the SDCard of Duet...
          My wire is 4x0.25-> https://www.igus.com/product/?artnr=CF240-02-04
          Maximum conductor resistance at 20 °C (following DIN EN 50289-1-2)-> 79 [Ω/km]

          Errors not always is the same. One of them is:
          Error: M409: control character in string

          Best Regards

          wilrikerundefined 1 Reply Last reply Reply Quote 0
          • wilrikerundefined
            wilriker @FBG
            last edited by

            @FBG of course you need to adjust your M575 command accordingly if you switch to another baud rate - otherwise there is no more communication possible at all.

            The control character error indeed looks like a communication issue. Can you try another cable? Maybe check your crimps. If possible measure the resistance yourself end to end (including crimp pins). You could also try to further lower the baud rate.

            Manuel
            Duet 3 6HC (v0.6) with RPi 4B on a custom Cartesian
            with probably always latest firmware/DWC (incl. betas or self-compiled)
            My Tool Collection

            FBGundefined 1 Reply Last reply Reply Quote 0
            • FBGundefined
              FBG @wilriker
              last edited by

              @wilriker yes yes, always i change the baud in the config.g

              Phaedruxundefined 1 Reply Last reply Reply Quote 0
              • Phaedruxundefined
                Phaedrux Moderator @FBG
                last edited by

                @FBG Just to be clear the baud rate in the config.g must match the baud rate set on the paneldue setup page.

                Z-Bot CoreXY Build | Thingiverse Profile

                FBGundefined 1 Reply Last reply Reply Quote 0
                • FBGundefined
                  FBG @Phaedrux
                  last edited by

                  @Phaedrux yes yes sure, and after reboot

                  1 Reply Last reply Reply Quote 0
                  • Phaedruxundefined
                    Phaedrux Moderator
                    last edited by

                    Can you show how you have your shielded cable connected and routed? Where is the shield grounded?

                    Z-Bot CoreXY Build | Thingiverse Profile

                    1 Reply Last reply Reply Quote 0
                    • FBGundefined
                      FBG
                      last edited by

                      @Phaedrux Attach a photo of the shield.
                      Tested again with 115200 and SD card not show, and the error messages show.

                      Is aleatory, now:
                      Error: Bad command: M[]09 F"d99f"
                      Error: M4: Command is not supported in machine mode FFF

                      alt text

                      Vetiundefined 1 Reply Last reply Reply Quote 0
                      • Vetiundefined
                        Veti @FBG
                        last edited by

                        @FBG

                        instead of increasing the speed go with a lower than 57k baud rate

                        FBGundefined 1 Reply Last reply Reply Quote 0
                        • FBGundefined
                          FBG @Veti
                          last edited by

                          @Veti Yes Veti, i tested all baudrates, with another baud rates the SD CARD work, but the error message, always happen

                          1 Reply Last reply Reply Quote 0
                          • Vetiundefined
                            Veti
                            last edited by Veti

                            you never wrote what the length of your wire is.

                            also check what wires that wires crosses or runs next to.

                            also which version is installed on the paneldue and which version of the duet firmware are you running?

                            FBGundefined 1 Reply Last reply Reply Quote 0
                            • FBGundefined
                              FBG @Veti
                              last edited by

                              @Veti PanelDue 7i version3.2.0, Duet2Ethernet with 3.1.1
                              Wire long around 3meters

                              Vetiundefined wilrikerundefined 2 Replies Last reply Reply Quote 0
                              • Vetiundefined
                                Veti @FBG
                                last edited by

                                @FBG said in PanelDue extend the wire:

                                Wire long around 3meters

                                from the documentation

                                There have been reports of cables up to 1500mm long being successfully used.

                                so you are double the longest possible length

                                1 Reply Last reply Reply Quote 0
                                • dc42undefined
                                  dc42 administrators
                                  last edited by

                                  A 3m cable should work as long as the conductors are not too thin.

                                  Duet WiFi hardware designer and firmware engineer
                                  Please do not ask me for Duet support via PM or email, use the forum
                                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                                  FBGundefined 1 Reply Last reply Reply Quote 0
                                  • FBGundefined
                                    FBG @dc42
                                    last edited by

                                    @dc42 I will test with 1mm wire, the actual is only 0.25mm

                                    dc42undefined 1 Reply Last reply Reply Quote 0
                                    • dc42undefined
                                      dc42 administrators @FBG
                                      last edited by

                                      @FBG, the maximum recommended resistance per conductor is 0.1 ohms. However, lower than that may allow higher baud rates.

                                      Duet WiFi hardware designer and firmware engineer
                                      Please do not ask me for Duet support via PM or email, use the forum
                                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                                      FBGundefined 1 Reply Last reply Reply Quote 0
                                      • FBGundefined
                                        FBG @dc42
                                        last edited by

                                        @dc42 My actual wire say: Max conductor resistance 79 ohms/km

                                        The new wire 1mm say: Max conductor resistance 19.5 ohms/km

                                        What do you think?

                                        dc42undefined 1 Reply Last reply Reply Quote 0
                                        • dc42undefined
                                          dc42 administrators @FBG
                                          last edited by

                                          @FBG said in PanelDue extend the wire:

                                          @dc42 My actual wire say: Max conductor resistance 79 ohms/km

                                          The new wire 1mm say: Max conductor resistance 19.5 ohms/km

                                          What do you think?

                                          0.079 ohms/m * 3 is about 0.24 ohms, well above the recommended 0.1 ohms maximum. The new wire will be about 0.06 ohms, so well within range.

                                          Duet WiFi hardware designer and firmware engineer
                                          Please do not ask me for Duet support via PM or email, use the forum
                                          http://www.escher3d.com, https://miscsolutions.wordpress.com

                                          1 Reply Last reply Reply Quote 0
                                          • wilrikerundefined
                                            wilriker @FBG
                                            last edited by

                                            @FBG said in PanelDue extend the wire:

                                            @Veti PanelDue 7i version3.2.0, Duet2Ethernet with 3.1.1

                                            Note that PanelDueFirmware 3.2 will have some minor issues with RepRapFirmware below 3.2. You are using RRF 3.1.1. The expected issues do NOT contain the "Bad command" errors you posted (these are actually more related to your wiring) but once you have sorted them you will still possibly encounter some issues like slower update rates.

                                            Manuel
                                            Duet 3 6HC (v0.6) with RPi 4B on a custom Cartesian
                                            with probably always latest firmware/DWC (incl. betas or self-compiled)
                                            My Tool Collection

                                            1 Reply Last reply Reply Quote 0