    I have installed an emergency stop buttom and configured it with:
    M950 J0 C"^io8.in" ; Definition of emervengy stop pin
    M581 P0 R0 T0 ; Assigment of the emergency stop

    And it works perfect. When pressed I can see the emergency message on the console and prints stops.

    But I want to configure a little more the actions taken when pressing the emergency buttom. So I change the command to M581 P0 R0 T1 and create the fyle /sys/trigger1.g having this:

    M42 P5 S1 ; activates buzzer
    M112

    But it doesnt work. I dont see any message in the console now when pressing the buttom.
    Im suspecting the system cant find the file? because another one of my problems is that the macros I put on the MACROS folder, are just not found unless I specifically called them with /macros/macro_name.g

    Thanks in advance

    1 Reply Last reply Reply Quote 0
    • undefined
      Zhang Jianyu
      last edited by 12 Nov 2020, 17:40

      Trigger 1 is already reserved for a print pause trigger, so you could try renaming your file to trigger2.g and reconfiguring the trigger to use T2.

      If you are calling other macro files with M98 command, I think it will only look in the /sys/ folder. To get around this, you could move all your macros to /sys/, or use the full path like so in your script: M98 P"0:/macros/mymacro.g"

      undefined 1 Reply Last reply 12 Nov 2020, 18:02 Reply Quote 1
      • undefined
        Tinchus @Zhang Jianyu
        last edited by 12 Nov 2020, 18:02

        @Zhang-Jianyu
        Ahhhhh that solved the problem, partially.
        Now the trigger2.g file is being executed, but not totally. Tis is what I have inside
        M42 P5 S1
        M112

        The M112 is executed, but the M42 not. The same command run manually starts the buzzer

        1 Reply Last reply Reply Quote 0
        • undefined
          Zhang Jianyu
          last edited by 12 Nov 2020, 18:41

          Is it possible the emergency stop command is resetting the buzzer output signal as well?

          To test this, you could try to insert a delay before the emergency stop to see if the buzzer works (for a short time) and then stops, something like:

          M42 P5 S1 ; activate buzzer
          G4 S5 ; wait 5 seconds
          M400 ; wait for buffered commands to execute (maybe does nothing?)
          M112 ; e-stop
          undefined 1 Reply Last reply 14 Nov 2020, 03:44 Reply Quote 1
          • undefined
            Tinchus @Zhang Jianyu
            last edited by 14 Nov 2020, 03:44

            @Zhang-Jianyu Thanks for the tips.
            I have tried your idea. Using it exactly as your wrote, it "works", the problem I see is that this is not exactly and emergency stop. The buzzer works, but the printing doesnt stop till the buffer is empty, and in my example gcode, that took like 5 extra seconds. That makes a total of 10 second to stop the printing... no t exactly an emergency stop jajajaja
            Then I tried:
            removing the M400: still not perfect, the machines stops after 5 seconds (little more may be), but buzzer is not triggered
            removing the G4 delay: the same, it stop after seconds, and buzzer is not triggered.

            1 Reply Last reply Reply Quote 1
            • undefined
              Phaedrux Moderator
              last edited by 14 Nov 2020, 06:21

              Why the buzzer? Presumably you're the one that pushed the estop button, what do you need the notification for?

              https://duet3d.dozuki.com/Wiki/Gcode#Section_M112_Emergency_Stop

              Since the board needs to be reset after, you could add the buzzer to the end of config.g to hear it when the machine boots back up?

              Z-Bot CoreXY Build | Thingiverse Profile

              undefined 1 Reply Last reply 14 Nov 2020, 19:33 Reply Quote 1
              • undefined
                Tinchus @Phaedrux
                last edited by 14 Nov 2020, 19:33

                @Phaedrux you are right, buzzr is just a "detail". I want the buzzer also for notification when print ends, stops, pause, etc.

                IF I add the buzzer to the end of the config file, how do I make it stop automatically, is there any way to create a counter, like "beeo for 5 seconds"

                undefined 1 Reply Last reply 14 Nov 2020, 19:43 Reply Quote 0
                • undefined
                  jay_s_uk @Tinchus
                  last edited by 14 Nov 2020, 19:43

                  @Tinchus you can add a delay for example

                  G4 S5
                  

                  That's a 5 second delay. And then send the code to turn it off.