    I originally posted by mistake in 3.2-beta3.2 thread, but I think it is better here...

    I've been testing the new algorithm on my printer and have seen some strange results when tuning the bed heater. My bed is a 310x310x6mm aluminium plate with a magnetically attached steel sheet on top. The heater is a mains powered 250x250mm 500W Silicon pad (with the thermistor embedded in it). When tuning my target temperature is 60 degrees. Ambient temperature is around 21 degrees. This combination is probably not ideal as there is a lot of lag between the pad thermistor and the actual bed plate temperature.

    If I run the tuning from cold then it always seems to run for the full 30 cycles. However if I run it when it has cooled (from 60) to say 30 degrees (using the A parameter to specify the ambient temperature) then it will complete after 5 cycles. To try and understand what is going on I have added some additional debug to the tuning process. Here is the output from the first case:

    Auto tune starting phase 1, heater on
    Auto tune starting phase 2, heater settling
    Sample 1 dLow 1250.000000 tOn 11250.000000 heatingRate 0.585193
    Sample 1 dHigh 1750.000000 tOff 22750.000000 coolingRate 0.268330
    tOn 11250±0, tOff 22750±0, dHigh 1750±0, dLow 1250±0, R 0.585±0.000, C 0.268±0.000, V 0.0±0.0, cycles 1
    Sample 2 dLow 1250.000000 tOn 11500.000000 heatingRate 0.581589
    Sample 2 dHigh 2500.000000 tOff 25750.000000 coolingRate 0.234478
    tOn 11375±125, tOff 24250±1500, dHigh 2125±375, dLow 1250±0, R 0.583±0.002, C 0.251±0.017, V 0.0±0.0, cycles 2
    Auto tune starting phase 3, fan off
    Sample 1 dLow 1000.000000 tOn 10750.000000 heatingRate 0.608868
    Sample 1 dHigh 2500.000000 tOff 28250.000000 coolingRate 0.222683
    tOn 10750±0, tOff 28250±5, dHigh 2500±0, dLow 1000±0, R 0.609±0.000, C 0.223±0.000, V 0.0±0.0, cycles 1
    Sample 2 dLow 1250.000000 tOn 10250.000000 heatingRate 0.629652
    Sample 2 dHigh 2750.000000 tOff 30750.000000 coolingRate 0.197948
    tOn 10500±250, tOff 29500±1250, dHigh 2625±125, dLow 1125±125, R 0.619±0.010, C 0.210±0.012, V 0.0±0.0, cycles 2
    Sample 3 dLow 1000.000000 tOn 9750.000000 heatingRate 0.676344
    Sample 3 dHigh 2250.000000 tOff 34000.000000 coolingRate 0.179575
    tOn 10250±408, tOff 31000±2354, dHigh 2500±204, dLow 1083±118, R 0.638±0.028, C 0.200±0.018, V 0.0±0.0, cycles 3
    Sample 4 dLow 1250.000000 tOn 9750.000000 heatingRate 0.678182
    Sample 4 dHigh 2250.000000 tOff 37500.000000 coolingRate 0.164589
    tOn 10125±415, tOff 32625±3475, dHigh 2438±207, dLow 1125±125, R 0.648±0.030, C 0.191±0.022, V 0.0±0.0, cycles 4
    Sample 5 dLow 750.000000 tOn 9250.000000 heatingRate 0.724365
    Sample 5 dHigh 2500.000000 tOff 40000.000000 coolingRate 0.153312
    tOn 9950±510, tOff 34100±4285, dHigh 2450±187, dLow 1050±187, R 0.663±0.041, C 0.184±0.025, V 0.0±0.0, cycles 5
    Sample 6 dLow 1000.000000 tOn 9250.000000 heatingRate 0.710471
    Sample 6 dHigh 3000.000000 tOff 43500.000000 coolingRate 0.142683
    tOn 9833±534, tOff 35667±5251, dHigh 2542±267, dLow 1042±172, R 0.671±0.041, C 0.177±0.027, V 0.0±0.0, cycles 6
    Sample 7 dLow 1000.000000 tOn 9000.000000 heatingRate 0.728104
    Sample 7 dHigh 3000.000000 tOff 46500.000000 coolingRate 0.134402
    tOn 9714±574, tOff 37214±6165, dHigh 2607±295, dLow 1036±160, R 0.679±0.043, C 0.171±0.029, V 0.0±0.0, cycles 7
    Sample 8 dLow 750.000000 tOn 8750.000000 heatingRate 0.762012
    Sample 8 dHigh 2500.000000 tOff 49500.000000 coolingRate 0.128104
    tOn 9594±624, tOff 38750±7054, dHigh 2594±278, dLow 1000±177, R 0.690±0.048, C 0.165±0.031, V 0.0±0.0, cycles 8
    Sample 9 dLow 1000.000000 tOn 9000.000000 heatingRate 0.740379
    Sample 9 dHigh 3000.000000 tOff 52250.000000 coolingRate 0.125191
    tOn 9528±617, tOff 40250±7889, dHigh 2639±291, dLow 1000±167, R 0.695±0.048, C 0.161±0.032, V 0.0±0.0, cycles 9
    Sample 10 dLow 1000.000000 tOn 9000.000000 heatingRate 0.765968
    Sample 10 dHigh 3500.000000 tOff 57000.000000 coolingRate 0.110748
    tOn 9475±607, tOff 41925±9015, dHigh 2725±378, dLow 1000±158, R 0.702±0.051, C 0.156±0.034, V 0.0±0.0, cycles 10
    Sample 11 dLow 750.000000 tOn 9000.000000 heatingRate 0.739456
    Sample 11 dHigh 2500.000000 tOff 58000.000000 coolingRate 0.106328
    tOn 9432±594, tOff 43386±9759, dHigh 2705±366, dLow 977±167, R 0.706±0.049, C 0.151±0.035, V 0.0±0.0, cycles 11
    Sample 12 dLow 500.000000 tOn 8750.000000 heatingRate 0.766151
    Sample 12 dHigh 3000.000000 tOff 60750.000000 coolingRate 0.104071
    tOn 9375±599, tOff 44833±10504, dHigh 2729±360, dLow 938±207, R 0.711±0.050, C 0.147±0.036, V 0.0±0.0, cycles 12
    Sample 13 dLow 750.000000 tOn 8750.000000 heatingRate 0.743942
    Sample 13 dHigh 3250.000000 tOff 61500.000000 coolingRate 0.103689
    tOn 9327±600, tOff 46115±11026, dHigh 2769±373, dLow 923±205, R 0.713±0.049, C 0.144±0.037, V 0.0±0.0, cycles 13
    Sample 14 dLow 750.000000 tOn 8750.000000 heatingRate 0.793538
    Sample 14 dHigh 3500.000000 tOff 62500.000000 coolingRate 0.101916
    tOn 9286±597, tOff 47286±11432, dHigh 2821±406, dLow 911±203, R 0.719±0.051, C 0.141±0.037, V 0.0±0.0, cycles 14
    Sample 15 dLow 0.000000 tOn 8750.000000 heatingRate 0.053600
    Sample 15 dHigh 3500.000000 tOff 63250.000000 coolingRate 0.098418
    tOn 9250±592, tOff 48350±11740, dHigh 2867±427, dLow 850±300, R 0.675±0.173, C 0.138±0.037, V 0.0±0.0, cycles 15
    Sample 16 dLow 500.000000 tOn 8500.000000 heatingRate 0.790129
    Sample 16 dHigh 3250.000000 tOff 64000.000000 coolingRate 0.097789
    tOn 9203±601, tOff 49328±11982, dHigh 2891±424, dLow 828±303, R 0.682±0.170, C 0.136±0.037, V 0.0±0.0, cycles 16
    Sample 17 dLow 0.000000 tOn 8750.000000 heatingRate 0.056186
    Sample 17 dHigh 3250.000000 tOff 64250.000000 coolingRate 0.100125
    tOn 9176±593, tOff 50206±12143, dHigh 2912±420, dLow 779±352, R 0.645±0.221, C 0.134±0.037, V 0.0±0.0, cycles 17
    Sample 18 dLow 750.000000 tOn 8250.000000 heatingRate 0.805200
    Sample 18 dHigh 3000.000000 tOff 64250.000000 coolingRate 0.096790
    tOn 9125±614, tOff 50986±12231, dHigh 2917±408, dLow 778±342, R 0.654±0.218, C 0.132±0.037, V 0.0±0.0, cycles 18
    Sample 19 dLow 750.000000 tOn 8500.000000 heatingRate 0.771688
    Sample 19 dHigh 3000.000000 tOff 66000.000000 coolingRate 0.094537
    tOn 9092±614, tOff 51776±12368, dHigh 2921±398, dLow 776±333, R 0.660±0.214, C 0.130±0.037, V 0.0±0.0, cycles 19
    Sample 20 dLow 750.000000 tOn 8500.000000 heatingRate 0.797152
    Sample 20 dHigh 3750.000000 tOff 65500.000000 coolingRate 0.094485
    tOn 9062±612, tOff 52462±12421, dHigh 2962±428, dLow 775±325, R 0.667±0.211, C 0.128±0.037, V 0.0±0.0, cycles 20
    Sample 21 dLow 1000.000000 tOn 8500.000000 heatingRate 0.781730
    Sample 21 dHigh 3000.000000 tOff 66250.000000 coolingRate 0.097950
    tOn 9036±609, tOff 53119±12472, dHigh 2964±418, dLow 786±321, R 0.673±0.207, C 0.126±0.037, V 0.0±0.0, cycles 21
    Sample 22 dLow 0.000000 tOn 8500.000000 heatingRate 0.056254
    Sample 22 dHigh 3500.000000 tOff 67500.000000 coolingRate 0.093961
    tOn 9011±605, tOff 53773±12548, dHigh 2989±423, dLow 750±354, R 0.645±0.239, C 0.125±0.036, V 0.0±0.0, cycles 22
    Sample 23 dLow 750.000000 tOn 8500.000000 heatingRate 0.789738
    Sample 23 dHigh 3250.000000 tOff 66500.000000 coolingRate 0.094778
    tOn 8989±601, tOff 54326±12544, dHigh 3000±417, dLow 750±346, R 0.651±0.236, C 0.124±0.036, V 0.0±0.0, cycles 23
    Sample 24 dLow 750.000000 tOn 8500.000000 heatingRate 0.794132
    Sample 24 dHigh 3750.000000 tOff 66250.000000 coolingRate 0.097583
    tOn 8969±596, tOff 54823±12508, dHigh 3031±435, dLow 750±339, R 0.657±0.233, C 0.123±0.036, V 0.0±0.0, cycles 24
    Sample 25 dLow 0.000000 tOn 8500.000000 heatingRate 0.055224
    Sample 25 dHigh 3500.000000 tOff 66750.000000 coolingRate 0.095105
    tOn 8950±592, tOff 55300±12477, dHigh 3050±436, dLow 720±363, R 0.633±0.257, C 0.121±0.035, V 0.0±0.0, cycles 25
    Sample 26 dLow 1000.000000 tOn 8500.000000 heatingRate 0.797152
    Sample 26 dHigh 3000.000000 tOff 66500.000000 coolingRate 0.095806
    tOn 8933±587, tOff 55731±12422, dHigh 3048±428, dLow 731±360, R 0.639±0.254, C 0.120±0.035, V 0.0±0.0, cycles 26
    Sample 27 dLow 1250.000000 tOn 8500.000000 heatingRate 0.793937
    Sample 27 dHigh 3750.000000 tOff 66500.000000 coolingRate 0.093961
    tOn 8917±581, tOff 56130±12359, dHigh 3074±440, dLow 750±366, R 0.645±0.251, C 0.120±0.035, V 0.0±0.0, cycles 27
    Sample 28 dLow 1000.000000 tOn 8250.000000 heatingRate 0.805200
    Sample 28 dHigh 3000.000000 tOff 65750.000000 coolingRate 0.093893
    tOn 8893±584, tOff 56473±12267, dHigh 3071±432, dLow 759±363, R 0.651±0.248, C 0.119±0.034, V 0.0±0.0, cycles 28
    Sample 29 dLow 750.000000 tOn 8500.000000 heatingRate 0.783488
    Sample 29 dHigh 2750.000000 tOff 67000.000000 coolingRate 0.095667
    tOn 8879±578, tOff 56836±12205, dHigh 3060±429, dLow 759±356, R 0.655±0.245, C 0.118±0.034, V 0.0±0.0, cycles 29
    Sample 30 dLow 1000.000000 tOn 8500.000000 heatingRate 0.808610
    Sample 30 dHigh 2750.000000 tOff 66750.000000 coolingRate 0.092288
    tOn 8867±573, tOff 57167±12131, dHigh 3050±425, dLow 767±353, R 0.660±0.242, C 0.117±0.034, V 0.0±0.0, cycles 30
    Warning: heater behaviour was not consistent during tuning
    tOn 8867±573, tOff 57167±12131, dHigh 3050±425, dLow 767±353, R 0.660±0.242, C 0.117±0.034, V 0.0±0.0, cycles 30
    Auto tuning heater 0 completed after 30 cycles in 2137 seconds. This heater needs the following M307 command:
    M307 H0 R0.788 C289.8 D2.74 S1.00 V0.0
    Edit the M307 H0 command in config.g to match this.
    Heater 0 switched off

    and this is the output from the "pre-heated" case:

    Auto tuning heater 0 using target temperature 60.0°C and PWM 1.00 - do not leave printer unattended
    ok
    Auto tune starting phase 2, heater settling
    Sample 1 dLow 750.000000 tOn 9250.000000 heatingRate 0.753922
    Sample 1 dHigh 2250.000000 tOff 36000.000000 coolingRate 0.165439
    tOn 9250±0, tOff 36000±0, dHigh 2250±0, dLow 750±0, R 0.754±0.000, C 0.165±0.000, V 0.0±0.0, cycles 1
    Sample 2 dLow 1000.000000 tOn 9250.000000 heatingRate 0.727826
    Sample 2 dHigh 2250.000000 tOff 40250.000000 coolingRate 0.155488
    tOn 9250±0, tOff 38125±2125, dHigh 2250±0, dLow 875±125, R 0.741±0.013, C 0.160±0.005, V 0.0±0.0, cycles 2
    Auto tune starting phase 3, fan off
    Sample 1 dLow 1000.000000 tOn 9500.000000 heatingRate 0.699097
    Sample 1 dHigh 2500.000000 tOff 43500.000000 coolingRate 0.141769
    tOn 9500±0, tOff 43500±0, dHigh 2500±0, dLow 1000±0, R 0.699±0.000, C 0.142±0.000, V 0.0±0.0, cycles 1
    Sample 2 dLow 1250.000000 tOn 8750.000000 heatingRate 0.769238
    Sample 2 dHigh 2500.000000 tOff 46250.000000 coolingRate 0.132351
    tOn 9125±375, tOff 44875±1375, dHigh 2500±0, dLow 1125±125, R 0.734±0.035, C 0.137±0.005, V 0.0±0.0, cycles 2
    Sample 3 dLow 750.000000 tOn 8750.000000 heatingRate 0.763718
    Sample 3 dHigh 2750.000000 tOff 50750.000000 coolingRate 0.126651
    tOn 9000±354, tOff 46833±2988, dHigh 2583±118, dLow 1000±204, R 0.744±0.032, C 0.134±0.006, V 0.0±0.0, cycles 3
    Sample 4 dLow 1250.000000 tOn 8500.000000 heatingRate 0.800977
    Sample 4 dHigh 3500.000000 tOff 53500.000000 coolingRate 0.115505
    tOn 8875±375, tOff 48500±3877, dHigh 2812±410, dLow 1062±207, R 0.758±0.037, C 0.129±0.010, V 0.0±0.0, cycles 4
    Sample 5 dLow 1250.000000 tOn 8500.000000 heatingRate 0.761442
    Sample 5 dHigh 3500.000000 tOff 56250.000000 coolingRate 0.110297
    tOn 8800±367, tOff 50050±4651, dHigh 2950±458, dLow 1100±200, R 0.759±0.033, C 0.125±0.011, V 0.0±0.0, cycles 5
    tOn 8800±367, tOff 50050±4651, dHigh 2950±458, dLow 1100±200, R 0.759±0.033, C 0.125±0.011, V 0.0±0.0, cycles 5
    Auto tuning heater 0 completed after 5 cycles in 460 seconds. This heater needs the following M307 command:
    M307 H0 R0.895 C267.3 D2.67 S1.00 V0.0
    Edit the M307 H0 command in config.g to match this.
    Heater 0 switched off

    I suspect that the relatively large thermal mass means that as the full bed heats up it is impacting the heating/cooling times of the test cycle. But there also seems to be something a little odd going on with the "dLow" values as these are sometimes zero.

    It may well be that I need to add an additional thermistor (perhaps embedded in the edge of the bed) to get more accurate readings of the actual bed temperature. However I don't think the setup I have is that unusual so I thought the data might be of interest to you.

    undefined 1 Reply Last reply 19 Nov 2020, 08:44 Reply Quote 0
    • undefined
      Zhang Jianyu
      last edited by 16 Nov 2020, 22:34

      The new auto-tune is working well for me on Duet 2 board. Thanks for your work on this 🙂

      1 Reply Last reply Reply Quote 0
      • undefined
        Exerqtor
        last edited by Exerqtor 17 Nov 2020, 06:38

        Working great here to! Took good over an hour to tune a 330x330x4mm 24v alu heated bed with a 4mm glass surface and cork insulation underneith for 60C tho 😂

        1 Reply Last reply Reply Quote 0
        • undefined
          gloomyandy
          last edited by 17 Nov 2020, 08:32

          @Exerqtor How many cycles did it take to tune your 330x300x4mm bed?

          undefined 1 Reply Last reply 17 Nov 2020, 13:41 Reply Quote 0
          • undefined
            oliof
            last edited by oliof 17 Nov 2020, 09:16

            My 300x300x4mm bed took seven or eight cycles. 220V AC bed to 80C

            <>RatRig V-Minion Fly Super5Pro RRF<> V-Core 3.1 IDEX k*****r <> RatRig V-Minion SKR 2 Marlin<>

            1 Reply Last reply Reply Quote 0
            • undefined
              Exerqtor @gloomyandy
              last edited by Exerqtor 17 Nov 2020, 13:41

              @gloomyandy said in New heater tuning algorithm:

              @Exerqtor How many cycles did it take to tune your 330x300x4mm bed?

              I didn't look at it tbh! After 45minutes i went downstairs and watched a movie lmao. Just sent a M500 before i went to bed when i saw it was done, then turned off the printer without thinking more about it 😂😂 i just saw it said 4700 something seconds.

              1 Reply Last reply Reply Quote 0
              • undefined
                gloomyandy
                last edited by 17 Nov 2020, 13:49

                No problem, sounds like it ran for a fair number of cycles!

                1 Reply Last reply Reply Quote 0
                • undefined
                  Exerqtor
                  last edited by Exerqtor 17 Nov 2020, 13:56

                  Don't quote me on it, but I THINK it was 11 for the bed. And 7 for the hotend (std Mosquito with a silicone sock, 40mm fan and 50w/12v heater).

                  1 Reply Last reply Reply Quote 0
                  • undefined
                    dc42 administrators @gloomyandy
                    last edited by 19 Nov 2020, 08:44

                    @gloomyandy said in New heater tuning algorithm:

                    I originally posted by mistake in 3.2-beta3.2 thread, but I think it is better here...

                    I've been testing the new algorithm on my printer and have seen some strange results when tuning the bed heater. My bed is a 310x310x6mm aluminium plate with a magnetically attached steel sheet on top. The heater is a mains powered 250x250mm 500W Silicon pad (with the thermistor embedded in it). When tuning my target temperature is 60 degrees. Ambient temperature is around 21 degrees. This combination is probably not ideal as there is a lot of lag between the pad thermistor and the actual bed plate temperature.

                    If I run the tuning from cold then it always seems to run for the full 30 cycles. However if I run it when it has cooled (from 60) to say 30 degrees (using the A parameter to specify the ambient temperature) then it will complete after 5 cycles. To try and understand what is going on I have added some additional debug to the tuning process. Here is the output from the first case:
                    I suspect that the relatively large thermal mass means that as the full bed heats up it is impacting the heating/cooling times of the test cycle. But there also seems to be something a little odd going on with the "dLow" values as these are sometimes zero.
                    ...
                    It may well be that I need to add an additional thermistor (perhaps embedded in the edge of the bed) to get more accurate readings of the actual bed temperature. However I don't think the setup I have is that unusual so I thought the data might be of interest to you.

                    I think I know what is going on. My theory is that systems such as yours behave somewhat like a FOPDT (first order process plus dead time) plus a thermal reservoir that is somewhat weakly coupled to it. When heating from cold, the temperature of the reservoir lags the temperature of the heating element and temperature sensor. It is only when it has heated up to their average temperatures that the behaviour during the tuning cycles becomes stable.

                    This phenomenon also occurs with hot ends to some extent, which is why the tuning algorithm does two heating/cooling cycles before is starts collecting data. It's clear that with bed heaters like yours, more of these dummy cycles are needed.

                    I too have a bed heater that behaves in this way, however in my case the thermistor readings have become noisy, so it is not surprising that it always goes the full 30 cycles.

                    Any solution must not only solve the problem you encountered but also handle noisy thermistors reasonably well, by continuing to average over a reasonably large number of cycles. One option would be to check the consistency after 5 cycles, and if it is poor then throw the data away and start again. So instead of doing 2 dummy cycles and up to 30 real cycles, it would do 7 dummy cycles and up to 25 real cycles. Do you think this would work for your heater?

                    Duet WiFi hardware designer and firmware engineer
                    Please do not ask me for Duet support via PM or email, use the forum
                    http://www.escher3d.com, https://miscsolutions.wordpress.com

                    undefined 1 Reply Last reply 19 Nov 2020, 09:00 Reply Quote 0
                    • undefined
                      gloomyandy @dc42
                      last edited by 19 Nov 2020, 09:00

                      @dc42 said in New heater tuning algorithm:

                      Any solution must not only solve the problem you encountered but also handle noisy thermistors reasonably well, by continuing to average over a reasonably large number of cycles. One option would be to check the consistency after 5 cycles, and if it is poor then throw the data away and start again. So instead of doing 2 dummy cycles and up to 30 real cycles, it would do 7 dummy cycles and up to 25 real cycles. Do you think this would work for your heater?

                      On my test build I cleared the data every 5 cycles and continued on up to a max of 30 cycles in total. So basically I tuned in groups of 5 cycles. In my case this resulted in the tuning completing after 10 cycles total. So yes I'm pretty sure that your proposal would work in my case (though I'm not sure if it would in the case of even bigger/thicker beds as they might take even longer to heat up). I wonder if there is any way to differentiate between a noisy reading (which will benefit from more readings) and a lagging reading (which probably needs a restart)? But yes I'm pretty sure that being able to extend the dummy cycles would help.

                      1 Reply Last reply Reply Quote 0
                      • undefined
                        dc42 administrators
                        last edited by 19 Nov 2020, 09:22

                        Some other solutions come to mind:

                        1. We could store the last 5 readings instead of just the mean and standard deviation; then we could check whether the last 5 readings are good enough. I am reluctant to do this because of the additional RAM that would be needed. One of the goals of the new algorithm was to use minimal RAM so that it can be implemented on the Duet 3 tool board.

                        2. We could monitor the ratio of heating time to cycle time, and continue doing dummy cycles until this stabilises or has the appearance of being noise rather than a trend. For example, wait for the ratio of heating time to cycle time to be at least 95% of the value in the previous cycle.

                        Your thoughts?

                        Duet WiFi hardware designer and firmware engineer
                        Please do not ask me for Duet support via PM or email, use the forum
                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                        1 Reply Last reply Reply Quote 0
                        • undefined
                          gloomyandy
                          last edited by 19 Nov 2020, 09:55

                          I agree that it would be a pity not to be able to use the same mechanism for the tool boards. On my system the way that the cooling time gets longer and heating time shorter is very noticeable so yes perhaps that could be used to indicate that things have not stabilised. I'm not show how much noise impacts those readings though?

                          Oh and I think there may be a bug in the code that determines the dLow time. In the data I posted above this is sometimes 0 which I don't think is correct. I added some extra code to my experimental version which I think fixes it. I'm not at home at the moment so will post more details later. But I think the problem was that sometimes we fail to detect a "low point" correctly after the heater has been turned on and it is using time values from the previous cycle.

                          undefined 1 Reply Last reply 19 Nov 2020, 10:34 Reply Quote 0
                          • undefined
                            dc42 administrators @gloomyandy
                            last edited by dc42 19 Nov 2020, 10:34

                            @gloomyandy said in New heater tuning algorithm:

                            I agree that it would be a pity not to be able to use the same mechanism for the tool boards. On my system the way that the cooling time gets longer and heating time shorter is very noticeable so yes perhaps that could be used to indicate that things have not stabilised. I'm not show how much noise impacts those readings though?

                            If the temperature readings are noisy then sooner or later the heating time will be at least 95% of the heating time in the last cycle, which would trigger the start of data collection for tuning. So the effect of noise may be to suggest that stabilisation has occurred sooner than it actually has. I am not concerned by this, because we can't expect good results from noisy temperature readings anyway.

                            Oh and I think there may be a bug in the code that determines the dLow time. In the data I posted above this is sometimes 0 which I don't think is correct. I added some extra code to my experimental version which I think fixes it. I'm not at home at the moment so will post more details later. But I think the problem was that sometimes we fail to detect a "low point" correctly after the heater has been turned on and it is using time values from the previous cycle.

                            Thanks, I'll wait for the detail from you.

                            Duet WiFi hardware designer and firmware engineer
                            Please do not ask me for Duet support via PM or email, use the forum
                            http://www.escher3d.com, https://miscsolutions.wordpress.com

                            1 Reply Last reply Reply Quote 0
                            • undefined
                              gloomyandy
                              last edited by gloomyandy 19 Nov 2020, 17:38

                              Hi @dc42 , sorry that took a little longer then I expected!

                              So the problem I was seeing was that when the bed was hot, occasionally when the tuning code switched from heater off to heater on the temperature would not drop below the temperature recorded in peakTemp, or rather it had already heated to be above that temperature by the next time that the tuning code runs. This resulted in new values for peakTemp, afterPeakTemp, peakTime and afterPeakTime not being captured which in turn resulted in the later if statement:

                              else if (afterPeakTime == peakTime && temperature - tuningTargetTemp >= TuningPeakTempDrop - TuningHysteresis)
                              {
                              afterPeakTime = now;
                              afterPeakTemp = temperature;
                              }

                              never being executed. This then gives an odd value for heatingRate as the calculation used the times and values from the previous cooling cycle for afterPeakTime and afterPeakTemp.

                              I've made some changes to my test branch which seem to help with this (but this may not be the best fix). You can see the changes here:
                              https://github.com/gloomyandy/RepRapFirmware/commit/1726cdf3647ecf812400cded0b04d295a30420fc

                              Let me know if any of that makes sense!

                              Oh and one final thought. With a hot bed we can end up with some very short times in dLow (I've seen values as low as 250mS or 500ms and occasionally 0). With the sample time being 250mS any "jitter" from say 1000 to 750 or 1250 can result in a pretty big impact on the standard deviation and so on the stability test.

                              0 gloomyandy committed 19 Nov 2020, 17:11 to gloomyandy/RepRapFirmware
                              Experimental fix for when temperature drop is not detected with heaters
                              on
                              1 Reply Last reply Reply Quote 0
                              • undefined
                                dc42 administrators
                                last edited by 20 Nov 2020, 09:21

                                Thanks Andy, I agree with your fix and I have committed it.

                                We may need to reduce the heat sample time to handle heaters with very short dead times. It's on my work list to make it variable again.

                                Duet WiFi hardware designer and firmware engineer
                                Please do not ask me for Duet support via PM or email, use the forum
                                http://www.escher3d.com, https://miscsolutions.wordpress.com

                                1 Reply Last reply Reply Quote 0
                                • undefined
                                  jay_s_uk
                                  last edited by 22 Nov 2020, 23:07

                                  @chrishamm
                                  The new heater tuning output doesn't get saved using M500 when a duet is connected to an SBC.
                                  They save fine when in standalone mode

                                  Owns various duet boards and is the main wiki maintainer for the Teamgloomy LPC/STM32 port of RRF. Assume I'm running whatever the latest beta/stable build is

                                  undefined 1 Reply Last reply 23 Nov 2020, 10:13 Reply Quote 0
                                  • undefined
                                    chrishamm administrators @jay_s_uk
                                    last edited by 23 Nov 2020, 10:13

                                    @jay_s_uk This is known and it will be addressed in 3.2-b4. DSF 3.2-b3 doesn't have the new object model properties either, so it cannot save them yet.

                                    Duet software engineer

                                    undefined 1 Reply Last reply 23 Nov 2020, 10:16 Reply Quote 1
                                    • undefined
                                      jay_s_uk @chrishamm
                                      last edited by 23 Nov 2020, 10:16

                                      @chrishamm good. Just wanted to make sure it was known

                                      Owns various duet boards and is the main wiki maintainer for the Teamgloomy LPC/STM32 port of RRF. Assume I'm running whatever the latest beta/stable build is

                                      1 Reply Last reply Reply Quote 0
                                      • undefined
                                        jay_s_uk
                                        last edited by 23 Nov 2020, 10:39

                                        @dc42
                                        unknown.png
                                        Here is a snapshot of the bed tuning being carried out on a my duet 3 in standalone mode.
                                        As you can see, the cool down period takes longer and longer as the bed heats up.
                                        I have a 500x500x10 aluminium bed with a 2kW 240v silicone heater with a thermocouple embedded in it.
                                        These were my results.

                                        Warning: heater behaviour was not consistent during tuning
                                        Auto tuning heater 0 completed after 30 cycles in 1047 seconds. This heater needs the following M307 command:
                                        M307 H0 R1.489 C145.3 D2.44 S1.00 V27.0
                                        Send M500 to save this command in config-override.g

                                        Owns various duet boards and is the main wiki maintainer for the Teamgloomy LPC/STM32 port of RRF. Assume I'm running whatever the latest beta/stable build is

                                        1 Reply Last reply Reply Quote 0
                                        • undefined
                                          gloomyandy
                                          last edited by 23 Nov 2020, 15:56

                                          @dc42 Hi David,
                                          I've been taking another look at this and have implemented your suggestion:
                                          "One option would be to check the consistency after 5 cycles, and if it is poor then throw the data away and start again. So instead of doing 2 dummy cycles and up to 30 real cycles, it would do 7 dummy cycles and up to 25 real cycles."

                                          Though in my case it will actually still run up to 30 real cycles after the 7 dummy ones. I basically added a new phase to insert the extra dummy cycles. I've been testing it and it works fine for me and the results it produces are pretty consistent. You can see the changes I made here: https://github.com/gloomyandy/RepRapFirmware/commit/868993b6e534e985bf5fe689a76ed33ce4ddb9a1

                                          I've also been running a number of tests using the results from the new tuning code on both my bed and hot end heaters and so far it looks pretty good. I see very stable temperatures both with and without the cooling fan. The initial overshoot is pretty low (approx 2 degrees on the hotend and less than 1 degree on the bed).

                                          0 gloomyandy committed 23 Nov 2020, 13:25 to gloomyandy/RepRapFirmware
                                          Run extra 5 tuning cycles if readings are not stable
                                          undefined 1 Reply Last reply 24 Nov 2020, 21:30 Reply Quote 0