    Relais to power of the Printer

    Scheduled Pinned Locked Moved
    Duet Hardware and wiring
    power management power supply relay
    4
    13
    623
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • MauriceMundefined
      MauriceM
      last edited by MauriceM

      Hey, I would like to be able to switch my printer on and off via a relay.
      I already have the relay here, it needs 5V and GRND which I would take from the exp header.
      Also use a Duex5 so all pins on the bar are omitted.

      Which pin can I use to tell the relay to always send a signal as long as the board is on (to keep the relay open) and if any error message comes in, to stop the signal to make the relay close.

      BoAundefined 1 Reply Last reply Reply Quote 0
      • BoAundefined
        BoA @MauriceM
        last edited by

        @MauriceM PS_ON can be used for that.

        1 Reply Last reply Reply Quote 0
        • MauriceMundefined
          MauriceM
          last edited by

          Thanks 🙂

          how do I configure the pin that does this, maybe someone can explain it to me

          1 Reply Last reply Reply Quote 0
          • alankilianundefined
            alankilian
            last edited by alankilian

            This page talks about using the PS_ON signal and an external relay:

            https://duet3d.dozuki.com/Wiki/Power_Wiring

            If the main PSU supports an ATX-style PS_ON pin (power supply on when pin is connected to ground),
            the Duet 2 can enable and disable the main power as needed. Obviously this will not work if the only source of 5V
            is the 12/24V circuit you are switching; you must either supply USB power or use the 5V in pin from a supply
            that is not shut down when the 12/24V supply is. On an ATX power supply which provides this function.
            
            If you are using an external relay to control mains power to the PSU, you can wire either the +5v or +3.3v
            (depending on what your relay requires) outputs from the duet in to the positive terminal of the relay, and wire
            the ground terminal of the relay to the PS_ON output on the duet. If you are using a mechanical relay and it
            does not include a flyback diode of some sort, you will need to wire one in parallel with the relay signal.
            

            SeemeCNC Rostock Max V3 converted to V3.2 with a Duet2 Ethernet Firmware 3.2 and SE300

            1 Reply Last reply Reply Quote 0
            • MauriceMundefined
              MauriceM
              last edited by

              sry i expressed myself a little wrong, i know how to wire this, otherwise i would not do this 😄
              But my question is more like writing a script or something, that the PS On Pin is always on as long as the board has power and goes off when any error comes in

              engikeneerundefined 1 Reply Last reply Reply Quote 0
              • engikeneerundefined
                engikeneer @MauriceM
                last edited by

                @MauriceM You'll probably be wanting the A parameter in M143:

                https://duet3d.dozuki.com/Wiki/Gcode#Section_M143_Maximum_heater_temperature

                Going for A1 will trip the PS_ON if it gets a fault (I believe but haven't yet tested myself). You'll need to set this for each heater.

                Not sure if there are any other errors that you would want to kill power for?

                E3D TC with D3Mini and Toolboards.
                Home-built CoreXY, Duet Wifi, Chimera direct drive, 2x BMG, 300x300x300 build volume
                i3 clone with a bunch of mods

                1 Reply Last reply Reply Quote 0
                • MauriceMundefined
                  MauriceM
                  last edited by

                  na only the heater error, or short to ground in case a cable breaks inside the cable chain or something... but i thunk that the heater faults are enough.

                  1 Reply Last reply Reply Quote 0
                  • MauriceMundefined
                    MauriceM
                    last edited by

                    ah ok that makes sense also i think A3 will work also ...
                    I will try it

                    1 Reply Last reply Reply Quote 0
                    • MauriceMundefined
                      MauriceM
                      last edited by

                      ok this works fine, i will do that for all heaters, now i have to figure out how to do this, for example when a thermistor wire breaks,...
                      Even if the printer is cooling down i want to shut off the Power

                      BoAundefined 1 Reply Last reply Reply Quote 0
                      • BoAundefined
                        BoA @MauriceM
                        last edited by

                        @MauriceM Not sure if this is a good option. RRF will shut heater down, but I would prefer to keep cooling, otherwise You can end with melted extruder parts near hotend due to fan turned off.

                        1 Reply Last reply Reply Quote 0
                        • MauriceMundefined
                          MauriceM
                          last edited by

                          there is everything printed out of PA12+cF15, i dont think that this will melt.
                          I rather have a safe printer.
                          But i think this should be enough at first, i only cant get to shut off the printer via the chamber heater... but i think the other 3 will be enough

                          BoAundefined 1 Reply Last reply Reply Quote 0
                          • BoAundefined
                            BoA @MauriceM
                            last edited by

                            @MauriceM Well... if You turn off cooling on hotend that has 280*C... I am not sure... PA12+CF15 can hold something like... 150 - 160 *C?

                            1 Reply Last reply Reply Quote 0
                            • MauriceMundefined
                              MauriceM
                              last edited by

                              ah i thought about the fan ducts and not about the heat creap, yeah that could be not so nice....

                              1 Reply Last reply Reply Quote 0