    Auto tune failed due to bad curve fit

    Scheduled Pinned Locked Moved
    Tuning and tweaking
    4
    16
    1.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • Phaedruxundefined
      Phaedrux Moderator @fcwilt
      last edited by

      @fcwilt said in Auto tune failed due to bad curve fit:

      Could you, as a test, connect those parts to the 6HC and see if it works there?

      This would be an interesting test.

      Z-Bot CoreXY Build | Thingiverse Profile

      Frederikundefined 1 Reply Last reply Reply Quote 0
      • Frederikundefined
        Frederik @Phaedrux
        last edited by Frederik

        @Phaedrux @fcwilt
        good morning,
        Yes, I can test that
        The wiring is complete new from sensor and heater + the sensors itself.
        It shows the correct room temperature.

        Its a 65W heater and the slice engineering rtd pt1000 sensor. Perhaps with 8cm of cable lenght from sensor to toolboard

        This Pic is shit from the transition tool fan off to on

        IMG_20210304_095252.jpg

        1 Reply Last reply Reply Quote 0
        • dc42undefined
          dc42 administrators @Frederik
          last edited by dc42

          @Frederik said in Auto tune failed due to bad curve fit:

          Hello,

          i got the following message when i try to PID Tune Tool0 with the slice engineering PT1000 Sensor on on a Toolboard LC1.

          
          Auto tune failed due to bad curve fit (R=1.946, 1/C=0.0048:0.0036, D=11.6)
          
          Warning: heater behaviour was not consistent during tuning
          ...
          RRF3.3beta1
          Duet3 Mainbord + sbc + Toolboard
          
          The Tuning works optical perfect, every time the same curve, even when the fan tuning starts , the temp is cycling without any big difference in the same range
          
          and after around one hour i got this error message
          
          what could that be ?
          

          The reason it's failing is that the measured cooling rate with the fan on is actually lower than with the fan off:

           1/C=0.0048:0.0036
          

          The second figure should be higher than the first one, unless there is a mechanism I haven't thought of whereby turning on the print cooling fan actually reduces the cooling of the hot end. Assuming that the print cooling fan is configured correctly, it seems that turning on the print cooling fan has negligible cooling effect on your hot end, and there is sufficient variability in the measurements that the second cooling rate measurement is lower than the first one.

          I suggest you tune that hot end using M303 with H parameter instead of with T parameter, so that it doesn't tune it with fan off and then with fan on.

          What type of hot end is it?

          EDIT: you published your temperature graph as I was composing that message. That graph does show that turning on the fan has an effect.

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          Frederikundefined 1 Reply Last reply Reply Quote 0
          • Frederikundefined
            Frederik @dc42
            last edited by Frederik

            @dc42 it's a original mosquito magnum with a 65W heater and the white thermal insulation ring installed. Nozzle is nickel plated copper.

            But I am running it with a 40mm fan instead of the 25mm one at around 25%

            The picture above was a pid tune at 300°C with all fans at 100%

            Another pid tu e I tried was 400°C with the tool fan at 40% and the part cooling fan at 35% with the same results.

            This is my Printhead with cabling and fan duct out of PC

            IMG_20210304_101735.jpg
            IMG_20210304_101704.jpg
            IMG_20210304_101638.jpg

            1 Reply Last reply Reply Quote 0
            • dc42undefined
              dc42 administrators
              last edited by dc42

              Thanks. I will check how the cooling rate with fan on is calculated from the data. In your temperature graph, it looks like the cooling segments have much the same lengths with fan on as with fan off, however the heating segments are much longer with fan on.

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              Frederikundefined 1 Reply Last reply Reply Quote 0
              • Frederikundefined
                Frederik @dc42
                last edited by

                @dc42 I will try a tune with a lower temperature and a tune with the heater and sensor connected to the mainboard

                dc42undefined 1 Reply Last reply Reply Quote 0
                • dc42undefined
                  dc42 administrators @Frederik
                  last edited by

                  @Frederik said in Auto tune failed due to bad curve fit:

                  @dc42 I will try a tune with a lower temperature and a tune with the heater and sensor connected to the mainboard

                  When you tune it with it connected to the main board, please use the same temperature as you did before, so that I can compare the results directly.

                  Duet WiFi hardware designer and firmware engineer
                  Please do not ask me for Duet support via PM or email, use the forum
                  http://www.escher3d.com, https://miscsolutions.wordpress.com

                  Frederikundefined 2 Replies Last reply Reply Quote 0
                  • Frederikundefined
                    Frederik @dc42
                    last edited by

                    @dc42 ok, I will test it as soon as I am back from work

                    1 Reply Last reply Reply Quote 0
                    • Frederikundefined
                      Frederik @dc42
                      last edited by Frederik

                      @dc42
                      Hello,

                      Today i had time to test the PID Tuning with the sensors connected to the duet 3 Mainboard.

                      The Tuning completed succesfully wih the following message:

                      
                      Auto tuning heater 1 completed after 4 idle and 21 tuning cycles in
                      1540 seconds. This heater needs the following M307 command:
                      M307 H1 R2.420 C186.9:181.7 D9.54 S1.00 V24.0
                      
                      

                      I made a new photo at the moment from tuning with fan off, to fan on
                      All other parameters where the same
                      M303 T0 300

                      IMG_20210308_120643.jpg

                      1 Reply Last reply Reply Quote 0
                      • dc42undefined
                        dc42 administrators
                        last edited by dc42

                        Thanks! I can see that this time it measured a slightly higher cooling rate with the fan on (which is why tuning worked), however the temperature graph shows that the temperature rises much more slowly with the fan on, indicating that the fan has a substantial effect. I will review how RRF measures the cooling rate.

                        Duet WiFi hardware designer and firmware engineer
                        Please do not ask me for Duet support via PM or email, use the forum
                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                        Frederikundefined 1 Reply Last reply Reply Quote 0
                        • Frederikundefined
                          Frederik @dc42
                          last edited by

                          @dc42 Ok, Thank you

                          The Part Fan is one 5015 Blower and the Hotend cooling Fan a 40mm Sunon that is running for testing between 40 and 100 %