Tuning stall detection
I would like to use stall detection to detect skipped steps on my big Delta Printer (Modified Tevo Little Monster). I use:
Board: Duet2 Ethernet (Standalone)
Firmware: RRF3.4.4
Tower Motors: 3x Nema17 0.9° "17HM19-2004S1" (Product page incl. specs)In a first step I want to determine the right values for F, H and S. Currently I use
M915 P0:1:2 S3 R1
That gives me lots and lots of false positives. Thus I have to tune my arguments, starting with H. In the docs there is a formula to calculate this. It says:
Hmin = full_steps_per_rev * rated_current * actual_current/(sqrt(2) * pi * rated_holding_torque)
Looking into my
config.g
and the stepper motor's data sheet I use:full_steps_per_rev = 400
rated_current (A)= 2
actual_current (A) = 1.5
rated_holding_torque (Nm) = 0.46That gives me 587.163 mm/s as lower speed limit. That seems very wrong.
I might have made a mistake, but I do not see it. Could someone please explain what is wrong or why I have such a high minimum speed value?
Thanks in Advance.
@justus2342 said in Tuning stall detection:
Nevertheless, I would like to have at least a reasonable value for the H-parameter.
I'd say H is less critical.
Hnnn (optional) Minimum motor full steps per second for stall detection to be considered reliable, default 200 (try 400 for 0.9deg motors)
Try 400 and tune sensitivity.
@justus2342 FYI the general consensus is stall detection isn't accurate enough for delta printers
@jay_s_uk We are not talking about sensorless homing, right? What could be a better option to detect skipped steps on a delta printer?
@justus2342 oh, i read that wrong. ignore me then
Does your motor have a spec sheet that shows a torque curve? You may find the rated holding torque to be quite a bit lower.
When doing stall detection homing the current is usually lowered, so that helps with the speed as well. During a print though, you're not going to be using lowered current.
Have you tried adjusting the sensitivity yet?If you're getting lots of false positives that's where I would start.
@Phaedrux said in Tuning stall detection:
Yes, here you go:
https://www.omc-stepperonline.com/download/17HM19-2004S1_Torque_Curve.pdfIt seems indeed a little lower, but since the formula has it in the denominator, smaller values do even raise my minimum speed. That's the wrong direction.
Yes, I played around with it a little. It seems the truth lies somewhere between 3 and 10. I will have to figure it out by trial and error. (It would be really nice to see the trigger value in the warning log-message by the way. )
@Phaedrux Thank you for citing the docs to me. No irony here. I absolutely overlooked that the value for the H parameter is in stepper steps and not in mm/s.
Thus there is no problem and my value is way less off than i thought.
I consider this problem solved now.
undefined justus2342 has marked this topic as solved
