    Temperature offset?
    746
    • DIY-O-Sphereundefined
      DIY-O-Sphere @Queevix
      @Queevix
      If you can reach the connector on the board, you can disconnect the sensor and measure the resistance directly with an ohmmeter.
      At 20°C you should measure about 1077Ohm.
      You can also do this with the replacement.
      (UTC+1)
      Queevixundefined 1 Reply Last reply Reply Quote 0
      • Queevixundefined
        Queevix @DIY-O-Sphere
        @DIY-O-Sphere
        The spare measures 1.070 Kohm at about 18°C, the problematic PT1000 gives me 1.069 Kohm. I feel like this difference would be tolerable, or am I wrong?
        achrnundefined 1 Reply Last reply Reply Quote 0
        • achrnundefined
          achrn @Queevix
          @Queevix https://www.sterlingsensors.co.uk/pt1000-resistance-table
          1069 is just under 18C, so no you're not wrong.
          • Queevixundefined
            Queevix @achrn
            @achrn @DIY-O-Sphere
            So why am I still getting a reading of -12.4°C in DWC?
            achrnundefined infiniteloopundefined 2 Replies Last reply Reply Quote 0
            • achrnundefined
              achrn @Queevix
              @Queevix I have no idea, because the direction it's going implies the resistance the Duet is seeing is slightly lower than what you're measuring - if it was a poor connection I'd expect it to be increasing resistance, which would show as a too high reading, and if it was a short you'd see a reading that's miles off. I don't know what manifests as a slightly too low reading.
              • infiniteloopundefined
                infiniteloop @Queevix
                @Queevix
                Does that change if you heat the sensor with a something like hair dryer?
                • Queevixundefined
                  Queevix @infiniteloop
                  @infiniteloop
                  It sure does, it also changes if I set the hotend to any temperature.
                  The problem (I assume) is that the reading I get from my sensor is about 30 degrees lower than the temperature it's actually at.
                  so if I heat it up to 160degrees, it would actually be about 190°C
                    @Queevix
                    So I assume the PT1000 to be working properly.
                    For a PT1000, such an offset is uncommon. Maybe you got some parasitic resistance along the lines and/or connectors? As you have a second PT1000, try to connect that directly to the board: does it tell the same readings at room temperature as the one you've built-in?
                      Can you post your full config.g and config-override.g?
                      Also post the results of M122 and M98 P"config.g"
                      Queevixundefined 3 Replies Last reply Reply Quote 0
                      • Queevixundefined
                        @infiniteloop
                        The spare gives me more or less the same result (difference of about half a degree), also with the other connector lead.
                        • Queevixundefined
                          Queevix @Phaedrux
                          @Phaedrux
                          Here's my full config file. I do not seem to have a config-override on this printer. Could that be a problem?
                          ; Configuration file for Duet 3 Mini 5+ (firmware version 3.3)
                          ; generated by RepRapFirmware Configuration Tool v3.3.10 on Sat Jan 22 2022 15:24:14 GMT+0100 (Central European Standard Time)
                          M575 P1 S1 B57600                            ; enable support for PanelDue
                          G90                                          ; send absolute coordinates...
                          M83                                          ; ...but relative extruder moves
                          M550 P"BigBitch"                             ; set printer name
                          M552 S1                                      ; enable network
                          M586 P0 S1                                   ; enable HTTP
                          M586 P1 S0                                   ; disable FTP
                          M586 P2 S0                                   ; disable Telnet
                          M569 P0.0 S1                                 ; physical drive 0.0 goes forwards
                          M569 P0.1 S0                                 ; physical drive 0.1 goes forwards
                          M569 P0.2 S1                                 ; physical drive 0.2 goes forwards
                          M569 P0.3 S1                                 ; physical drive 0.3 goes forwards
                          M584 X0.0 Y0.1 Z0.2 E0.3                     ; set drive mapping
                          M350 X16 Y16 Z16 E16 I1                      ; configure microstepping with interpolation
                          M92 X80.00 Y80.00 Z400.00 E409.00            ; set steps per mm
                          M566 X900.00 Y900.00 Z60.00 E120.00          ; set maximum instantaneous speed changes (mm/min)
                          M203 X6000.00 Y6000.00 Z180.00 E1200.00      ; set maximum speeds (mm/min)
                          M201 X500.00 Y500.00 Z20.00 E250.00          ; set accelerations (mm/s^2)
                          M906 X800 Y800 Z800 E800 I30                 ; set motor currents (mA) and motor idle factor in per cent
                          M84 S30                                      ; Set idle timeout
                          M208 X0 Y0 Z0 S1                             ; set axis minima
                          M208 X475 Y465 Z450 S0                       ; set axis maxima
                          M574 X1 S1 P"io5.in"                         ; configure switch-type (e.g. microswitch) endstop for low end on X via pin io5.in
                          M574 Y1 S1 P"io6.in"                         ; configure switch-type (e.g. microswitch) endstop for low end on Y via pin io6.in
                          M574 Z1 S2                                   ; configure Z-probe endstop for low end on Z
                          M950 S0 C"io2.out" 							 ; Duet 3 Mini 5+
                          M558 P9 C"io2.in" H10 F120 T6000 A3          ; set Z probe type to modulated and the dive height + speeds
                          G31 P1000 X-39 Y2 Z3.1 S21 H2 T0.02          ; Nozzle offset - Powder Coated Sheet with temperature compensation (0.02mm/°C)
                          M574 Z1 S2                          		 ; set Z probe trigger value, offset and trigger height
                          M557 X5:435 Y5:465 P10:10                   ; define mesh grid
                          M376 H5										 ; Fade height 5mm
                          M308 S0 P"temp0" Y"thermistor" T100000 B4138 ; configure sensor 0 as thermistor on pin temp0
                          M950 H0 C"out0" T0                           ; create bed heater output on out0 and map it to sensor 0
                          M307 H0 B0 R0.213 C666.6 D8.13 S1.00 V24.1                            ;
                          M140 H0                                      ; map heated bed to heater 0
                          M143 H0 S80                                  ; set temperature limit for heater 0 to 80C
                          M308 S1 P"temp1" Y"pt1000"   ; configure sensor 1 as thermistor on pin temp1
                          M950 H1 C"out1" T1                           ; create nozzle heater output on out1 and map it to sensor 1
                          M307 H1 R1.350 K0.244:0.000 D5.89 E1.35 S1.00 B0                            ; disable bang-bang mode for heater  and set PWM limit
                          M143 H1 S280                                 ; set temperature limit for heater 1 to 280C
                          M950 F0 C"out3" Q500                         ; create fan 0 on pin out3 and set its frequency
                          M106 P0 S0 H-1                               ; set fan 0 value. Thermostatic control is turned off
                          M950 F1 C"out4" Q500                         ; create fan 1 on pin out4 and set its frequency
                          M106 P1 S1 H1 T45                            ; set fan 1 value. Thermostatic control is turned on
                          M563 P0 D0 H1 F0                             ; define tool 0
                          G10 P0 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P0 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P1 D0 H1 F0                             ; define tool 0
                          G10 P1 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P1 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P2 D0 H1 F0                             ; define tool 0
                          G10 P2 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P2 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P3 D0 H1 F0                             ; define tool 0
                          G10 P3 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P3 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P4 D0 H1 F0                             ; define tool 0
                          G10 P4 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P4 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P5 D0 H1 F0                             ; define tool 0
                          G10 P5 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P5 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P6 D0 H1 F0                             ; define tool 0
                          G10 P6 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P6 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          M563 P7 D0 H1 F0                             ; define tool 0
                          G10 P7 X0 Y0 Z0                              ; set tool 0 axis offsets
                          G10 P7 R0 S0                                 ; set initial tool 0 active and standby temperatures to 0C
                          M572 D0 S0.06
                          • Queevixundefined
                            Queevix @Phaedrux
                            @Phaedrux
                            M122
                            M122
                            RepRapFirmware for Duet 3 Mini 5+ version 3.4.1 (2022-06-01 21:06:56) running on Duet 3 Mini5plus WiFi (standalone mode)
                            Board ID: URV2B-M396U-D65J0-40KMY-1H03Z-72JMX
                            Used output buffers: 3 of 40 (27 max)
                            Static ram: 103684
                            Dynamic ram: 111512 of which 0 recycled
                            Never used RAM 26516, free system stack 196 words
                            Tasks: NETWORK(ready,14.4%,253) HEAT(notifyWait,0.0%,358) Move(notifyWait,0.0%,363) CanReceiv(notifyWait,0.0%,942) CanSender(notifyWait,0.0%,372) CanClock(delaying,0.0%,339) TMC(notifyWait,0.7%,114) MAIN(running,84.0%,426) IDLE(ready,0.1%,29) AIN(delaying,0.8%,273), total 100.0%
                            Owned mutexes: WiFi(NETWORK)
                            Last reset 00:05:29 ago, cause: power up
                            Last software reset at 2023-02-26 13:21, reason: User, GCodes spinning, available RAM 23252, slot 0
                            Software reset code 0x0003 HFSR 0x00000000 CFSR 0x00000000 ICSR 0x00000000 BFAR 0xe000ed38 SP 0x00000000 Task MAIN Freestk 0 n/a
                            Error status: 0x00
                            Aux0 errors 0,0,0
                            MCU revision 3, ADC conversions started 330081, completed 330080, timed out 0, errs 0
                            Step timer max interval 1490
                            MCU temperature: min 23.5, current 28.0, max 28.0
                            Supply voltage: min 24.0, current 24.1, max 24.1, under voltage events: 0, over voltage events: 0, power good: yes
                            Events: 0 queued, 0 completed
                            Driver 0: standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 17318, writes 9, timeouts 0, DMA errors 0, CC errors 0
                            Driver 1: standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 17317, writes 9, timeouts 0, DMA errors 0, CC errors 0
                            Driver 2: standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 17317, writes 9, timeouts 0, DMA errors 0, CC errors 0
                            Driver 3: standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 17317, writes 9, timeouts 0, DMA errors 0, CC errors 0
                            Driver 4: standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 17318, writes 9, timeouts 0, DMA errors 0, CC errors 0
                            Driver 5: not present
                            Driver 6: not present
                            Date/time: 2023-02-27 07:12:12
                            Cache data hit count 636420885
                            Slowest loop: 33.38ms; fastest: 0.13ms
                            === Storage ===
                            Free file entries: 10
                            SD card longest read time 1.5ms, write time 8.5ms, max retries 0
                            DMs created 83, segments created 0, maxWait 0ms, bed compensation in use: none, comp offset 0.000
                            === MainDDARing ===
                            === AuxDDARing ===
                            Segments left: 0
                            Movement lock held by null
                            HTTP is idle in state(s) 0
                            Telnet is idle in state(s) 0
                            File is idle in state(s) 0
                            USB is idle in state(s) 0
                            Aux is idle in state(s) 0
                            Trigger is idle in state(s) 0
                            Queue is idle in state(s) 0
                            LCD is idle in state(s) 0
                            SBC is idle in state(s) 0
                            Daemon is idle in state(s) 0
                            Aux2 is idle in state(s) 0
                            Code queue is empty
                            === CAN ===
                            Messages queued 2964, received 0, lost 0, boc 0
                            Longest wait 0ms for reply type 0, peak Tx sync delay 0, free buffers 18 (min 18), ts 1648/0/0
                            Tx timeouts 0,0,1647,0,0,1315 last cancelled message type 4514 dest 127
                            === Network ===
                            Slowest loop: 33.48ms; fastest: 0.00ms
                            HTTP sessions: 1 of 8
                            - WiFi -
                            Network state is active
                            WiFi firmware version 1.26
                            WiFi MAC address d8:bf:c0:15:0b:d5
                            WiFi Vcc 3.38, reset reason Power up
                            WiFi flash size 2097152, free heap 25464
                            WiFi IP address 192.168.1.33
                            WiFi signal strength -70dBm, mode 802.11n, reconnections 0, sleep mode modem
                            Clock register 00002002
                            • Queevixundefined
                              Queevix @Phaedrux
                              @Phaedrux
                              M98 P"config.g"
                              M98 P"config.g"
                              HTTP is enabled on port 80
                              FTP is disabled
                              TELNET is disabled
                              Warning: Temperature coefficients ignored due to invalid sensor number 2
                              • achrnundefined
                                achrn @Queevix
                                @Queevix said in Temperature offset?:
                                That warning is because you've put temperature compensation using sensor 2 in the probe definition, but you don't have a sensor 2. I don't think it's relevant to the fault under discussion though.
                                The warning would go if you took the S21 H2 T0.02 out of your G31 line.
                                • Queevixundefined
                                  Queevix @achrn
                                  @achrn
                                  I'll try that this evening. Thanks!
                                  • mendenmhundefined
                                    mendenmh
                                    Try moving the sensor to a different input. It is possible you have a bad ADC channel.
                                    Queevixundefined 1 Reply Last reply Reply Quote 1
                                    • Queevixundefined
                                      Queevix @mendenmh
                                      @mendenmh @achrn @Phaedrux @DIY-O-Sphere @infiniteloop
                                      So yeah, I connected the sensor to temp2 instead of temp1, and get normal temperatures now. Does this mean my temp1 connection is shot on this board? I wouldn't be very happy about that...
                                      Also, what is an ADC channel?
                                      Anyway, I can print again now, So I guess I'll get started on that 🙂 Thanks everyone!
                                        Phaedrux Moderator @Queevix
                                        Analog Digital Conversion. It's the part that takes the analog signal from the temp sensor and converts it to a digital representation.
                                        When and where did you get the board?
                                        Can you try updating your firmware by uploading this zip file to the system tab in DWC? Just in case.
                                        https://github.com/Duet3D/RepRapFirmware/releases/download/3.4.5/Duet2and3Firmware-3.4.5.zip