    Feature Request - workpiece angle compensation CNC
    Firmware wishlist
    11
    54
    2.9k
    • CanDo415undefined
      CanDo415 @Exerqtor
      @Exerqtor
      i tried this before in another case... everything unter the 2nd if wasnt done if the if doesn't match.
      the problem of the missing end if
      Exerqtorundefined jay_s_ukundefined 2 Replies Last reply Reply Quote 0
      • Exerqtorundefined
        Exerqtor @CanDo415
        @CanDo415
        Then you simply must have done something wrong in the other case you're mentioning.
        As reference to conditional construct have look at this.
          jay_s_uk @CanDo415
          @CanDo415 as @Exerqtor said, there's no end if.
          Things have to be indented to be part of the if
            dc42 administrators @CanDo415
            @CanDo415 you also need to replace SIN by sin, COS by cos, ARCTAN by atan etc. See https://docs.duet3d.com/User_manual/Reference/Gcode_meta_commands#functions.
            CanDo415undefined 1 Reply Last reply Reply Quote 1
            • CanDo415undefined
              CanDo415 @dc42
              thanks so far.
              Error promt is:
              M292 S3
              Error: Bad command: If (var.y_2) >= (var.y_3)
              Error: in file macro line 179 column 8: meta command: expected "'"
              Makro:
              G68 A0 B0 R0
              var y_1 = 0
              var x_1 = 0
              var x_2 = 0
              var x_3 = 0
              var x_4 = 0
              var x_5 = 0
              var delta_x = 0
              var y_2 = 0
              var y_3 = 0
              var y_4 = 0
              var y_5 = 0
              var delta_y = 0
              var z0 = 0
              var d_probe = 0
              var z_probe = 0
              var m_1 = 0
              var m_2 = 0
              var m_1_rads = 0
              var m_1_deg = 0
              var buff1 = 0
              var buff2 = 0
              var buff3 = 0
              var speed = 1500
              M291 P"probe Diameter" R"enter diameter of probe" S5 							; Pop up box asking for operator input diameter of
              set var.d_probe = input															; set the diameter of the probe
              M291 P"probe size in z" R"enter z-size of probe" S5 							; Pop up box asking for operator input diameter of
              set var.z_probe = input															; set the size of the probe in z-direction (mostly same as diameter, for plate probes 0)
              M291 P"position probe over front left corner of workpiece" S2 X1 Y1 Z1			; Pop up box asking for operator input
              M558 F{var.speed/5}																; Set the initial movement speed
              G38.2 Z-10 P0 K0																; Probe the material on top
              M558 F50																		; Set the final probing speed
              G38.4 Z50 P0 K0																	; Move away from workpiece in Z
              M400																			; Make sure all movement is complete
              set var.z0 = move.axes[2].machinePosition										; Record the stop position z_first_measurement
              M400																			; Make sure all data recording is complete
              G1 Z{move.axes[2].machinePosition+5}											; Lift probe 5mm
              G1 X{move.axes[0].machinePosition-20} Y{move.axes[1].machinePosition+5}			; Move 20mm to the left of the initial point and 5mm deeper into the material direction
              G1 Z{var.z0 - 1 - var.z_probe / 2}												; Move to probe depth
              M558 F{var.speed}																; Set the initial movement speed
              G38.2 X1000 P0 K0																; Probe the material as a first pass
              G38.4 X-10 P0 K0																; Move away from workpiece in X
              set var.y_1 = move.axes[1].machinePosition										; Record the stop position y_first_measurement
              set var.x_1 = move.axes[0].machinePosition										; Record the stop position x_first_measurement
              G1 X{move.axes[0].machinePosition-5}											; Move 5mm away from the material
              G1 Z{var.z0+5}																	; Move 5mm above material
              G1 X{move.axes[0].machinePosition+15} Y{move.axes[1].machinePosition-20}		; Move to point 2
              G38.2 Y1000 P0 K0																; Probe the material as a first pass
              G38.4 Y-10 P0 K0																; Probe the material again
              set var.y_2 = move.axes[1].machinePosition										; Record the stop position y_second_measurement
              set var.x_2 = move.axes[0].machinePosition										; Record the stop position x_second_measurement
              G1 Y{move.axes[1].machinePosition-20}											; Move 10mm away from the material
              G1 X{move.axes[0].machinePosition+50}											; Move 50mm along the workpiece in X
              set var.y_3 = move.axes[1].machinePosition										; Record the stop position y_third_measurement
              set var.x_3 = move.axes[0].machinePosition										; Record the stop position x_third_measurement
              ;calculation
              set var.delta_y = {var.y_3-var.y_2}
              set var.delta_x = {var.x_3-var.x_2}
              set var.m_1 = {var.delta_y/var.delta_x}											; m of the staight P2-P3
              set var.m_2 = {(-var.delta_x)/var.delta_y}										; m of perpendicilar to straight P2-P3
              set var.m_1_rads = atan(var.m_1)												; workpiece rotation in rad
              set var.m_1_deg = degrees(var.m_1_rads)											; workpiece rotation in degrees
              ;calc the corner of workpiece
              ;set var.x_4 = {((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))}
              ;set var.y_4 = {(-(var.x_3-var.x_2)/(var.y_3-var.y_2))<>*((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))<>/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))+(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)}
              set var.buff1 = {var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1}
              set var.buff2 = {var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)}
              set var.buff3 = {((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))}
              set var.x_4 = {(var.buff1-var.buff2)/var.buff3}
              set var.buff1 = {(-(var.x_3-var.x_2)/(var.y_3-var.y_2))}
              set var.buff2 = {((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))}
              set var.buff3 = {(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))+(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)}
              set var.y_4 = {var.buff1*var.buff2/var.buff3}
              If (var.y_2) >= (var.y_3)																; workpiece Zero coordinates
              set var.x_5 = {var.x_4+(cos(atan(var.m_1))+cos(atan(var.m_2)))*var.d_probe/2}
              set var.y_5 = {var.y_4+(sin(atan(var.m_1))+sin(atan(var.m_2)))*var.d_probe/2}
              echo 'X= '{var.x_5}', Y= '{var.y_5}
              If (var.y_2) < (var.y_3)
              set var.x_5 = {var.x_4+(cos(atan(var.m_1))-cos(atan(var.m_2)))*var.d_probe/2}
              set var.y_5 = {var.y_4+(sin(atan(var.m_1))-sin(atan(var.m_2)))*var.d_probe/2}
              ;echo X= {var.x_5}, Y= {var.y_5}
              ;move above workpiece zero and set tool x&y to 0
              G1 Y{move.axes[1].machinePosition-1}											; Move 1mm away from the material
              G1 Z{var.z0 + 5}																; Move above workpiece
              G1 X{var.x_5} Y{var.y_5}														; go to Zero
              G10 X0 Y0																		; set x&y to Zero
              G68 A0 B0 R{-var.m_1_deg}														; set Rotation
              X seems to be working, on a psitive angle.
              Y is getting some wrong outputs
                @CanDo415 replace all If by if.
                • CanDo415undefined
                  CanDo415 @dc42
                  i don't know why. sometimes it works. sometimes it fails.
                  getting Error: line 89 column 20: meta command: unknown value 'atan'
                  i have no idea.
                  the calculation seems to be correct. but using G10 moves the tool right down to Y=0
                  G68 A0 B0 R0
                  var y_1 = 0
                  var x_1 = 0
                  var x_2 = 0
                  var x_3 = 0
                  var x_4 = 0
                  var x_5 = 0
                  var delta_x = 0
                  var y_2 = 0
                  var y_3 = 0
                  var y_4 = 0
                  var y_5 = 0
                  var delta_y = 0
                  var z0 = 0
                  var d_probe = 0
                  var z_probe = 0
                  var m_1 = 0
                  var m_2 = 0
                  var m_1_rads = 0
                  var m_1_deg = 0
                  var m_2_rads = 0
                  var m_2_deg = 0
                  var buff1 = 0
                  var buff2 = 0
                  var buff3 = 0
                  var speed = 1500
                  ;calculation
                  set var.m_2 = {-(var.delta_x/var.delta_y)}										; m of perpendicilar to straight P2-P3
                  set var.m_2_rads = atan(var.m_2)												; workpiece rotation in rad
                  set var.m_2_deg = degrees(var.m_2_rads)											; workpiece rotation in degrees
                  var a = 0
                  set var.a= {var.y_3-var.y_2}
                  ;if var.a >= 0														            	; workpiece Zero coordinates
                  set var.x_5 = {var.x_4+(cos(var.m_1_deg)+cos(var.m_2_deg))*var.d_probe/2}
                  set var.y_5 = {var.y_4+(sin(var.m_1_deg)+sin(var.m_2_deg))*var.d_probe/2}
                  ;echo 'X= '{var.x_5}', Y= '{var.y_5}
                  ;if var.a < 0
                  ;set var.x_5 = {var.x_4+(cos(atan(var.m_1))-cos(atan(var.m_2)))*var.d_probe/2}
                  ;set var.y_5 = {var.y_4+(sin(atan(var.m_1))-sin(atan(var.m_2)))*var.d_probe/2}
                  G1 X{var.x_5}
                  G1 Y{var.y_5}														            ; go to Zero
                  ;G10 L20 X0 Y0																	; set x&y to Zero
                  ;G68 A0 B0 R{-var.m_1_deg}														; set Rotation
                  • infiniteloopundefined
                    infiniteloop @CanDo415
                    @CanDo415
                    @Exerqtor already pointed you at the proper doc - better read it completely. In the section Expressions, it says:
                    … when RepRapFirmware is running in CNC mode, any use of ( ) to enclose a subexpression or function parameter list must be within an expression enclosed in { }
                    Within your macro, you apply the curly braces inconsistently, Instead of
                    set var.m_1_rads = atan(var.m_1) ;  may not work in CNC mode, (var.m_1) is regarded as a comment
                    write
                    set var.m_1_rads = {atan(var.m_1)}
                    Same is true for other function calls like degrees().
                    In general, if writing macros, you should study the GCode meta commands completely and in-depth.
                    • CanDo415undefined
                      CanDo415 @infiniteloop
                      thank you all. finally it works as inteded.
                      G68 A0 B0 R0
                      G10 L20 X{move.axes[0].machinePosition} Y{move.axes[1].machinePosition} Z{move.axes[2].machinePosition}
                      var y_1 = 0
                      var x_1 = 0
                      var x_2 = 0
                      var x_3 = 0
                      var x_4 = 0
                      var x_5 = 0
                      var delta_x = 0
                      var y_2 = 0
                      var y_3 = 0
                      var y_4 = 0
                      var y_5 = 0
                      var delta_y = 0
                      var z0 = 0
                      var d_probe = 0
                      var z_probe = 0
                      var m_1 = 0
                      var m_2 = 0
                      var m_1_rads = 0
                      var m_1_deg = 0
                      var m_2_rads = 0
                      var m_2_deg = 0
                      var buff1 = 0
                      var buff2 = 0
                      var buff3 = 0
                      var buff4 = 0
                      var speed = 1500
                      G1 X{move.axes[0].machinePosition-20-var.d_probe/2} Y{move.axes[1].machinePosition+5}           	; Move 20mm to the left of the initial point and 5mm deeper into the material direction
                      G1 X{move.axes[0].machinePosition+15+var.d_probe/2} Y{move.axes[1].machinePosition-20-var.d_probe/2}	; Move to point 2
                      ;calculation
                      set var.m_1_rads = {atan(var.m_1)}								    	            			; workpiece rotation in rad
                      set var.m_1_deg = {degrees(var.m_1_rads)}	            										; workpiece rotation in degrees
                      set var.m_2_rads = {atan(var.m_2)}						            			    			; workpiece rotation in rad
                      set var.m_2_deg = {degrees(var.m_2_rads)}							            				; workpiece rotation in degrees
                      set var.buff3 = {(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))}
                      set var.buff4 = {(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)}
                      set var.y_4 = {var.buff1*var.buff2/var.buff3+var.buff4}
                      var a = 0
                      if var.a < 0														            	            ; workpiece Zero coordinates
                      if var.a > 0
                      if var.a =0
                          set var.x_5 = {var.x_1+var.d_probe/2}
                          set var.y_5 = {var.y_2+var.d_probe/2}
                      echo "ZERO X = ", var.x_5," ; Y = ", var.y_5
                      M400
                        @CanDo415 the reason is that standard CNC GCode uses ( and ) to enclose comments, which is an unfortunate choice. In order to be compatible with this, RRF does the same when in CNC mode unless the ( ) are themselves inside { }.