      I have a 4 wires PT100 (E3D 2 wires modified to 4 wires as per DC42 blog) which works fine but some times I get a random spikes in the temp graph that I am unable to reproduce.
      Touching and bending the cables does not produce that effect.
      All wrings are shielded except the last 30cm that goes into the effector as they are too stiff with the shielding while the pt100 4 wire cable is not shielded at all.

      Tonight the printer stopped after many hours with the following message:

      06:50:48 Printing paused
      06:50:45 Warning: Tool 0 was not driven because its heater temperatures were not high enough or it has a heater fault
      06:50:45 Error: Temperature reading fault on heater 1: sensor short to other wiring Resume-after-power-fail state saved
      
      • Is there a way to see / save the full temperature logs from the beginning of a print session ?

      • Can a shielded 4 wires cable solve the problem ?

      • Where the shielding should be connected ?

      • It will not be possible to make the shielding goes all thru the pt100 probe as I need to solder the 4 wires of the cable to the 2 wires, so at least the first 4/5 cm after the probe will be unshielded where passing near the heating cartridge wires.
        I am worried that this can mak the whole shielding useless, any thoughts ?

      • One user in the forum solved this problem by changing the PWM frequency of the fans to 10khz, I done this for the layer fans which were off during the last print that gave an error so now I want to do this for the always on fan (the hotend cooling fan)
        How to change the PWM of the always on fans ?

      thx!

      0_1527416865529_spike.jpg

      1 Reply Last reply Reply Quote 0
      • dc42undefined
        dc42 administrators
        last edited by

        @paboman said in Heater fault, spurious spikes:

        sensor short to other wiring

        That suggests it is not a noise issue. Check that there is no way for the PT100 cartridge wires to short to the heater block.

        Duet WiFi hardware designer and firmware engineer
        Please do not ask me for Duet support via PM or email, use the forum
        http://www.escher3d.com, https://miscsolutions.wordpress.com

        pabomanundefined 3 Replies Last reply Reply Quote 0
        • pabomanundefined
          paboman @dc42
          last edited by

          @dc42
          that is quite impossible, maybe is the pt100 damaged somehow (but i dont think so), wires are well insulated.

          Can this spikes be caused by an intermittent connection in the connectors?
          one is the DuPont on the daughterboard, then I have a second one along one of the towers, which is a 4 pole mini xlr (http://www.switchcraft.com/Category.aspx?Parent=806)

          Moving them does not produce any spikes at all

          1 Reply Last reply Reply Quote 0
          • pabomanundefined
            paboman @dc42
            last edited by

            @dc42 just checked again, none of the sensor wires touches the heater block

            1 Reply Last reply Reply Quote 0
            • deckingmanundefined
              deckingman
              last edited by

              As a work around, you could "de-sensitise" the fault anomaly detection by increasing the P and/or T parameters in M570 https://duet3d.dozuki.com/Wiki/GCode#Section_M570_Configure_heater_fault_detection

              Ian
              https://somei3deas.wordpress.com/
              https://www.youtube.com/@deckingman

              pabomanundefined 1 Reply Last reply Reply Quote 0
              • pabomanundefined
                paboman @deckingman
                last edited by

                @deckingman
                thank you!

                now I have changed the 4 wires cable of the pt100 with a shielded one as this is the only thing I can do.
                My plan is to run the printer and later check if random spikes are still there but i cant look at the graph forever so i would like to record the temperature graph somehow.
                I know repetier host has a nice interface for the temps but how to connect the duet wifi to repetier ? what is the ip port ?

                1 Reply Last reply Reply Quote 0
                • sonderzugundefined
                  sonderzug
                  last edited by

                  Hi all,
                  I've had a somewhat related issue with both PT100 and Type K sensors, leaving me unable to print at the temperatures neccessary for the materials I use. I've documented this in another thread, unfortunately without a working fix at this moment (https://forum.duet3d.com/topic/4966/highly-erratic-temperature-readings-above-certain-temperature). It seems that the insulation inside the sensor cartridges is not stable at higher temperatures (>300°C). While this doesn't really apply to you (you're printing at pretty standard temperatures as it seems), a failing cartridge insulation and short to the heater block might still be the case?

                  Best regards, Niklas

                  1 Reply Last reply Reply Quote 0
                  • pabomanundefined
                    paboman @dc42
                    last edited by paboman

                    @dc42 I have changed the pt100 cable with a shielded one but I am still missing something...

                    I am sure the PT100 cable is picking up estruder noise as the temperature graph became noisy as soon as E motors is energized

                    Routing the cable externally to the printer also makes the graph look clean but I cant route the cables in a different way.
                    Cant understand this behavior as all my cables are shielded, steppers cables are twisted and shielded....what am I doing wrong ?

                    0_1527502524918_noise.jpg
                    Look only at the noise, the temperature was raising and falling because of me turning on/off the heater to see if it has any correlation but it hasn't

                    Shield of the extruder stepper is connected to the extruder motor case and to nothing on the other end
                    The shielding of the PT100 is connected to nothing on both ends

                    dc42undefined 1 Reply Last reply Reply Quote 0
                    • dc42undefined
                      dc42 administrators @paboman
                      last edited by

                      @paboman, try connecting the shield of the PT100 cable to ground. There is a ground pin on the daughter board OUTPUT connector, it's the corner pin of that connector closest to the INPUT legend.

                      Duet WiFi hardware designer and firmware engineer
                      Please do not ask me for Duet support via PM or email, use the forum
                      http://www.escher3d.com, https://miscsolutions.wordpress.com

                      pabomanundefined 2 Replies Last reply Reply Quote 0
                      • pabomanundefined
                        paboman @dc42
                        last edited by paboman

                        @dc42

                        Can I use the negative terminal of the main input ?
                        I mean the GND on the big green connector

                        thx!

                        1 Reply Last reply Reply Quote 0
                        • pabomanundefined
                          paboman @dc42
                          last edited by paboman

                          @dc42

                          Now its better but still jumping up and down in the 2°C range
                          I will run the printer to see if it spikes again

                          Is there any way to filter / flatten the readings even more or this is the best I can achieve ?

                          0_1527522022512_pt100-ground.jpg

                          thanks again David!

                          1 Reply Last reply Reply Quote 0
                          • pabomanundefined
                            paboman
                            last edited by paboman

                            UPDATE:
                            SOLVED
                            I made better connection at the shield line and now my temps are within 1°C

                            0_1527546780008_pt100-ok.jpg