      Background

      My machine has a mains powered bed heater. The bed itself is 10mm thick aluminium with 12mm of semi rigid insulation underneath, so once up to temperature it takes a long time to cool. Despite the fact that it's a large machine, without the bed heater it takes very little electrical power to run. Because it is a large machine, I print large objects which can take days rather than hours to complete. Power outages are rare where I live but when they do happen, it gets costly in both time and filament. So I am thinking of adding some sort of UPS.

      Solution 1

      It occurs to me that with Duet 3, I could utilise the RPi to interface with the UPS such that when power is interrupted and the UPS starts to run on battery power the RPi could turn off the bed heater and other non-essential items such as lights, and maybe even disable my third load balancing gantry to lengthen the run time. After a pre-determined period of time, the RPi could then instigate an orderly shutdown/resume.

      Alternative ideas

      I might still go down that route but another thought occurs to me. A UPS uses an inverter to convert DC voltage to AC voltage at an efficiency of say 85%. The 24V PSU then uses that AC voltage and converts it back to DC at a similar level of efficiency. Which all seems a bit daft and I could be losing 30% of the available run time simply through the process of converting DC to AC and then from AC back to DC.

      I suspect the answer to the following question is a big NO NO but what would happen if I simply connect a big 24V deep cycle leisure battery in parallel with the 24V PSU? This would automatically turn off the bed heater in the event of a power failure because that runs off the mains.

      If the answer to the above is big NO NO, could it be done with some simple circuitry? Would feeding 24 into the output terminals of at PSU cause damage to the PSU? If so could a diode mitigate that? What happens when the battery runs low and power is then restored. Will the 24 PSU charge the battery or will it "fry" either the battery of the PSU? If so, could something be done to limit the current going back into the battery? What else have I not thought about and how could it be mitigated?

      Over to you clever people.......

      Ian
      https://somei3deas.wordpress.com/
      https://www.youtube.com/@deckingman

      DocTruckerundefined A Former User? 2 Replies Last reply Reply Quote 0
      • DocTruckerundefined
        DocTrucker @deckingman
        last edited by DocTrucker

        @deckingman Morning!

        Firstly you would need your PSU at around 13.5V (or I'm guessing about 27V for two in series?) as I think even the leisure batteries charge at that.

        Secondly fuses in the supply are essential. Lead acid and gel batteries have huge cranking amps, around 500A is not unusual, again this is the main rather than leisure batteries but I would have thought they are capable of the same.

        Finally, perhaps you could run a charger on the leisure battery a DC regulator to drop from the charging voltage to the machines 24V, not sure how the charger would react to the loading of the machine, but seeing as my charger has a jump start mode that's spun over my Rover V8 with 8 injectors with coils some of them must be reasonably robust!

        Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

        deckingmanundefined 1 Reply Last reply Reply Quote 0
        • deckingmanundefined
          deckingman @DocTrucker
          last edited by

          @DocTrucker Morning Wes.

          PSU is 24V. I'm showing VIn as being 23.7 so a little low. Too low to recharge a battery I'd guess so for sure I'd need an external charger. Do you know if you can get 24V leisure batteries or are they all 12v so I'd need 2 in series?

          Ian
          https://somei3deas.wordpress.com/
          https://www.youtube.com/@deckingman

          DocTruckerundefined 1 Reply Last reply Reply Quote 0
          • samlogan87undefined
            samlogan87
            last edited by

            We use Phoenix Contact Power supplies and 24vdc ups’s for our pump station controllers. They have to continue to power the modem and RTU for compliance reasons for up to 30 days. The batteries are 2x standard 12v lead acid batteries connected in series. They would be your best option. They are tidy wee din rail mount units. If you get the Quint version they have various comms expansion cards that you can get all sorts of information out. They do also have various io on them such as battery mode that you can set up as an input into the RPi. The trio is an integrated power supply and ups version that is slightly cheaper also by Phoenix contact.

            Regards
            Sam

            Custom Core-XY

            1 Reply Last reply Reply Quote 0
            • samlogan87undefined
              samlogan87
              last edited by

              10A Quint (you can use your current power supply as they are 24in 24 out)

              https://www.phoenixcontact.com/online/portal/nz?uri=pxc-oc-itemdetail:pid=2320225&library=nzen&tab=1

              Custom Core-XY

              1 Reply Last reply Reply Quote 0
              • DocTruckerundefined
                DocTrucker @deckingman
                last edited by

                @deckingman I've found 12v planet a gold mine of information for the truck.

                https://www.12voltplanet.co.uk/

                Winch and starter currents can creep and make you fastidious in lesser wiring! 😄

                Running 3 P3Steel with Duet 2. Duet 3 on the shelf looking for a suitable machine. One first generation Duet in a Logo/Turtle style robot!

                1 Reply Last reply Reply Quote 0
                • fmaundefined
                  fma
                  last edited by

                  Ian, if you cool down the bed, your parts may warp and pop off... For PLA, I don't heat the bed anymore: I have a LockBuild surface, and it sticks very well with hair spray. I already printed 300x300 parts without issue.

                  About 24V PSU, I have one of these Quint stuff (a bigger one), and plan to use it with two 12V batteries. We used them at work, and it works fine.

                  Frédéric

                  deckingmanundefined 1 Reply Last reply Reply Quote 0
                  • deckingmanundefined
                    deckingman @fma
                    last edited by

                    @fma As per my OP, it takes an awfully long time for the bed temp to drop to the point where parts might fall off - longer than a UPS could reasonably be expected to run the rest of the printer.

                    Ian
                    https://somei3deas.wordpress.com/
                    https://www.youtube.com/@deckingman

                    Dougal1957undefined 1 Reply Last reply Reply Quote 1
                    • A Former User?
                      A Former User @deckingman
                      last edited by

                      @deckingman said in UPS/Battery backup thoughts and questions:

                      I suspect the answer to the following question is a big NO NO but what would happen if I simply connect a big 24V deep cycle leisure battery in parallel with the 24V PSU?

                      as hinted to you'd only utilize part of the capacity of the batteries as the full charge voltage is a few volts over the nominal voltage. however you could run the duet at full charge voltage of up to 28.8v and have full use of the battery. but it would charge just fine back to 24v if used with 24v psu - the catch is a fraction of the capacity

                      meanwell makes psu's with built in battery backup, but you'll still be using the cell voltage not regulated to nominal voltage. i use a few of them with 12v access controll setups, cheap and works well and even din rail mounting.

                      deckingmanundefined 1 Reply Last reply Reply Quote 0
                      • Dougal1957undefined
                        Dougal1957 @deckingman
                        last edited by

                        @deckingman You could always look into surplus Cell site backup systems where you have 24V Rectifiers that supply a float charge to the batteries and the batteries run the equipment we used to use 24V Systems and there are still a few in service even now.

                        Suppliers I know have are POWEC, Inverses, Harmer and Simmonds and Erskine.

                        Trouble is that they tend to be bulky.

                        deckingmanundefined 1 Reply Last reply Reply Quote 0
                        • deckingmanundefined
                          deckingman @A Former User
                          last edited by

                          @bearer Thanks and that makes sense about a fraction of the battery capacity. But doesn't a the inverter in a UPS suffer the same limitation?

                          Ian
                          https://somei3deas.wordpress.com/
                          https://www.youtube.com/@deckingman

                          1 Reply Last reply Reply Quote 0
                          • deckingmanundefined
                            deckingman @Dougal1957
                            last edited by

                            @Dougal1957 Cheers Doug. I'm not too worried about bulk. The plan is that I'd instigate this after I've first moved the printer into my garage so I'll have more room and it won't matter what it looks like.

                            Ian
                            https://somei3deas.wordpress.com/
                            https://www.youtube.com/@deckingman

                            Dougal1957undefined 1 Reply Last reply Reply Quote 0
                            • Dougal1957undefined
                              Dougal1957 @deckingman
                              last edited by

                              @deckingman Next time I see any on site I'll take a pic or 2 for you

                              1 Reply Last reply Reply Quote 0
                              • fcwiltundefined
                                fcwilt
                                last edited by

                                Hi,

                                The simplest approach would be a UPS of needed capacity to handle the outages.

                                Is that just too expensive?

                                Frederick

                                Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                                deckingmanundefined 1 Reply Last reply Reply Quote 0
                                • deckingmanundefined
                                  deckingman @fcwilt
                                  last edited by deckingman

                                  @fcwilt said in UPS/Battery backup thoughts and questions:

                                  Hi,

                                  The simplest approach would be a UPS of needed capacity to handle the outages.

                                  Is that just too expensive?

                                  Frederick

                                  As per my OP if you read it, you'll see that is the solution I put forward. But it just seems a bit daft to have an inverter converting from DC to 220V AC at around 85% efficiency, then a PSU converting that AC back to 24v DC with another loss due to efficiency. Why not cut out the "middle men" and just have DC backup?

                                  Ian
                                  https://somei3deas.wordpress.com/
                                  https://www.youtube.com/@deckingman

                                  Danalundefined fcwiltundefined samlogan87undefined 3 Replies Last reply Reply Quote 0
                                  • Danalundefined
                                    Danal
                                    last edited by

                                    Unless I missed it, we are missing a key fact from this discussion: What is the pattern of outages at your printing site?

                                    For example, at my house, I have a fair number of mains outages that last less than 3 minutes. Often just a few seconds. In the three years I've lived here, outages that last more than a few minutes have only happened twice. And both of those were 8+ hours. A UPS that could keep my 1300+ watt mains bed heater for 8+ hours is certainly physically possible, but it is more bulk and expense than I desire.

                                    Therefore...

                                    I've elected to put my smaller, 12 or 24 volt bed, printers on a small UPS. My printer that is big enough to have a mains bed, the logic (and motors and so forth) are on another small UPS, the bed is not UPS, it is mains only. Obviously, the printer has to have to power cords.

                                    This has worked very well. All short outages have been perfectly covered, and I've not had a long outage during a long print. Maybe someday I will; if it happens, Cest La Vie.

                                    So let's ask it as a question: What is the typical pattern that you are trying to mitigate? Have you considered covering only the "90th percentile" (using that term very loosely) outage occurrences ?

                                    Delta / Kossel printer fanatic

                                    1 Reply Last reply Reply Quote 0
                                    • Danalundefined
                                      Danal @deckingman
                                      last edited by Danal

                                      @deckingman said in UPS/Battery backup thoughts and questions:

                                      As per my OP if you read it, you'll see that is the solution I put forward. But it just seems a bit daft to have an inverter converting from DC to 220V AC at around 85% efficiency, then a PSU converting that AC back to 24v DC with another loss due to efficiency. Why not cut out the "middle men" and just have DC backup?

                                      There is engineering elegance to do it directly, bypassing the 220V stages. There is operational elegance, and robustness, in purchasing a totally "off the shelf" solution and just plugging it in and having it work.

                                      Me, personally, on a 'backup' system, I'm going to go for operational elegance & robustness every time.

                                      Having said that, Telcos have done this for ages. They run ALL THE TIME on 24V from batteries (or is it 48V? I don't remember) and their incoming utility and power distribution keeps those batteries charged.

                                      Assuming that Lead Acid batteries are used, "simple parallel" at 24V is NOT a good strategy. Lead Acid batteries will lose capacity rapidly if held at their nominal voltage for long periods of time. They will not "be there when you need them" in terms of ability to deep discharge.

                                      Instead, they need a battery charger designed for lead acid batteries. One that will 'charge' vs. 'float' at proper voltages. These voltages are all within the operating range of a Duet. So a three way connection of battery charger, batteries, Duet should work just fine.

                                      With one caveat: Some battery chargers are also "maintainers" or "de-sulfate" devices. These put out very short spikes of voltage WAY WAY above charge/float, to stop (or even remove) plate sulfation. Obviously, such spikes should not go into a duet.

                                      Summary: I, personally, would not worry about the losses and would just use off the shelf components. If you do choose to go 24V battery, it seems OK to connect charger/battery/duet all in parallel. Pick a charger that does NOT de-sulfate.

                                      Delta / Kossel printer fanatic

                                      Dougal1957undefined 1 Reply Last reply Reply Quote 0
                                      • Dougal1957undefined
                                        Dougal1957 @Danal
                                        last edited by

                                        @Danal most telco stuff now is -48Volt supply but in the earlier days of Cell sites it was +24V and there are still some of the kit around the batteries tend to be deep discharge Gell type cells and the control systems are designed to disconnect the batteries from the output when they fall to a certain voltage to save the cells (They can be expensive to replace)

                                        Doug

                                        1 Reply Last reply Reply Quote 1
                                        • fcwiltundefined
                                          fcwilt @deckingman
                                          last edited by

                                          @deckingman

                                          Hi,

                                          Seems to me I recall seeing UPS devices with DC output.

                                          Frederick

                                          Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                                          1 Reply Last reply Reply Quote 0
                                          • whosrdaddyundefined
                                            whosrdaddy
                                            last edited by whosrdaddy

                                            We run quite a few Harmer & Simmons modules in the field (for 48V telco stuff 🙂 ).
                                            These are quite expensive but last very long (we have some modules older than 20 years).
                                            I would personally go for "operational elegance" as Danal nicely describes because dealing with DC charging and batteries can be dangerous stuff (I've experienced a 24V battery explosion (due to bad maintenance), it was not pretty...)

                                            Dougal1957undefined 1 Reply Last reply Reply Quote 0