Bed Temperature ERROR
-
Did that same issue that is I swapped them same readings
-
Could you post a photo of the Duet with both thermistors connected, please?
-
Here you go I hope….
-
Did that same issue that is I swapped them same readings
Just to confirm: with the bed thermistor plugged into the E0 thermistor connector and the hot end thermistor plugged into the bed thermistor connector, you still get -273 in the current bed temperature box?
Please run M305 P0 and verify that the values it reports are as in your M305 P0 command in config.g.
-
T:100000.0 B:3950.0 C:0.00e+00 R:4700.0 L:0 H:0 X:0 from command sent
M305 P0 T100000 B3950 C0 R4700 ; Set thermistor + ADC parameters for heater 0 from configso what is the next step?
-
Anyone???
-
Did that same issue that is I swapped them same readings
Just to confirm: with the bed thermistor plugged into the E0 thermistor connector and the hot end thermistor plugged into the bed thermistor connector, you still get -273 in the current bed temperature box?
Please can you answer this question.
-
Bed temperature stays the same regardless of what thermistor is plugged in. The only way I was able to effect a change to the reading was to use T value 1 in that case it reads 2000 degrees.
-
Also the -273 is on the display, the web app reads ERROR
-
Looks like there is an issue with the bed temp channel. Please contact your supplier.