    Bad PT100 board?
    539
    • ShadowXundefined
      ShadowX
      I have a DuetWifi V1.0 board. Everything was running fine last week. When I turn it on today, it does not sense my extruder temperature. If I try to turn on my heaters, it generates a very loud pitched noise.
      The first thing I suspect was a bad connection. I measured the resistance at the RTD1 terminals with the machine off and it was around 120 ohms. I checked all the connections and it seems fine.
      Unfortunately, while working, the terminal on the board broke off. Since RTD2 was not used, I moved the wires to those terminals and changed my M308 to use "spi.cs2". I was not able to read any temperature on the RTD2 port either.
      Just as a sanity check, I unplugged the wires and put in a 100 ohm resistor in the terminals shown with red arrows. I can't read 0 degrees on my PanelDue or web interface. There is no temperature display for the extruder.
      I'm just wondering if the board went bad or if its a bad setting. Its hard to say its a bad setting when everything was working fine last week.
      Does anyone have suggestions? I haven't probed the PT100 board yet or hooked it up to a logic analyzer. It just seems like its an upward battle since I migrated to RRF3.
      ; Configuration file for Duet WiFi
      ; ---------------------------- General Settings ------------------------------------
      M111 S0 		; Debugging off
      G21 			; Work in millimeters
      G90 			; Send absolute coordinates...
      M83 			; ...but relative extruder moves
      M555 P1 		; Set firmware compatibility to look like RepRapFirmare
      ; ---------------------------- Printer Bed Settings ------------------------------------
      ; Rod length settings for reference:
      ; L = Ideal Length / Measured_length * Original Delta Rod Length
      ; Larger Number = Smaller part size
      ; Smaller Number = Larger part size
      ; Delta Radius setting for reference:
      ; Lower number  - Middle get looser
      ; Higher number - Middle get tighter
      ; MANUAL CALIBRATION DATA
      M665 L438.000 R264 H424.75 B150 				; M665 - Set delta radius, diagonal rod length, printable radius and homed height, B = safe printing radius
      M666 X0 Y0 Z0									; M666 - Put your endstop adjustments here, or let auto calibration find them
      ; ---------------------------- Motor and Extruder Settings ------------------------------------
      ; Motor Settings
      M569 P0 S1 										; Drive 0 (S0 = Backwards; S1 = Forwards)  X-Axis
      M569 P1 S1 										; Drive 1 (S0 = Backwards; S1 = Forwards)  Y-Axis
      M569 P2 S1 										; Drive 2 (S0 = Backwards; S1 = Forwards)  Z-Axis
      M569 P3 S0 										; Drive 3 (S0 = Backwards; S1 = Forwards)  Extruder
      M350 X16 X16 X16 X16 I1 						; Configure microstepping without interpolation
      M906 X1000 Y1000 Z1000 E600 I30 				; Set motor currents (mA) and motor idle factor in per cent
      M84 S30 										; Set motor idle timeout
      ; Acceleration, Jerk and speed
      M566 X1000 Y1000 Z900 E170 						; Jerk - Set maximum instantaneous speed changes (mm/min)
      M201 X2000 Y2000 Z2000 E200 					; Set accelerations (mm/s^2)
      M203 X20000 Y20000 Z20000 E5000 				; Set maximum speeds (mm/min)
      ; Extruder
      M92 X80 Y80 Z80 E2680 							; Set steps per mm; E value is in mm/minute    E2715
      M572 D0 S0.18  									; Extruder pressure advance
      ; ---------------------------- End Stops ------------------------------------
      M574 X2 S1 P"xstop" 							; Configure active-high endstop for high end on X via pin xstop
      M574 Y2 S1 P"ystop" 							; Configure active-high endstop for high end on Y via pin ystop
      M574 Z2 S1 P"zstop" 							; Configure active-high endstop for high end on Z via pin zstop
      ; ---------------------------- Bed Level and Probe Settings ------------------------------------
      ; Grid Mesh
      M557 X5:205 Y5:165 S20 								; Define mesh grid
      ;Precision Piezo Settings
      M558 P1 C"zprobe.in" H1 F400 T10000 R0.5 S0.1 A6  	; R- Recoverty Time before probing start; A - max times to probe each point; S - tolerance with each probe
      G31 P500 X0 Y0 Z0.08 								; Set Z probe trigger value, offset and trigger height  (increasing z makes nozzle go lower)
      ;Bed Heater
      M308 S0 P"bed_temp" Y"thermistor" T100000 B3950 R4700 L0 H9		; Define bed temperature sensor
      M950 H0 C"bed_heat" T0 											; Heater 0 uses the bed_heat pin, sensor 0
      M307 H0 A366.5 C667.4 D11.7 S1.00 V0.0 B1 						; Bed heater setting
      M140 H0															; Map heated bed to heater 0
      M143 S100 														; Set maximum heater temperature to 100C
      M570 S200 														; Set maximum heating time to 200s
      ;Extruder Heater
      ;M308 S1 P"spi.cs1" Y"rtd-max31865" F60	A"RTD1"					; Define E0 temperature sensor, RTD1
      M308 S1 P"spi.cs2" Y"rtd-max31865" F60 A"RTD2"	    			; Define E0 temperature sensor, RTD2
      M950 H1 C"e0heat" T1 											; Heater 1 uses the e0heat pin and sensor 1
      M307 H1 A347.2 C180.2 D4.8 S1.00 V12.0 B0 						; Hot End heater setting
      ; ---------------------------- Fan Settings ------------------------------------
      ; Fan mapping
      M950 F0 C"fan0" Q500		; Map Fan 0 to P0
      M950 F1 C"fan1" Q500		; Map Fan 1 to P1
      M950 F2 C"fan2" Q500		; Map Fan 2 to P2
      ; Fan Settings
      M106 P0 B0 S0 H-1 			; Set fan 0 value, Thermostatic control is turned off
      M106 P1 B0 S0 H-1 			; Set fan 1 value, Thermostatic control is turned off
      M106 P2 B0 S0 H-1 			; Set fan 2 value, Thermostatic control is turned off
      ; ---------------------------- Tool Settings ------------------------------------
      M563 P0 D0 H1 				; Define tool 0
      G10 P0 X0 Y0 Z0 			; Set tool 0 axis offsets
      G10 P0 R175 S190			; Set initial tool 0 active and standby temperatures.  R= standby S= active
      ; ---------------------------- Network Settings ------------------------------------
      M552 S1 					; Enable network and acquire dynamic address via DHCP
      M575 S1 P1 B57600			; Set the Serial Communication parameters
      Board: Duet 2 WiFi (2WiFi)
      Firmware: RepRapFirmware for Duet 2 WiFi/Ethernet 3.3 (2021-06-15)
      Duet WiFi Server Version: 1.26
      Phaedruxundefined dc42undefined 2 Replies Last reply Reply Quote 0
        Phaedrux Moderator @ShadowX
        @shadowx said in Bad PT100 board?:
        I don't know if this is intentional, but you're setting the microstepping for the X axis 4 times in a row here but not the other axis.
        As for your PT100 problems, have you tried reseating the board in it's connector yet?
        Can you measure the resistance of R1 and R2 resistors? They should read ~400 ohms.
        What exactly does it display for a temperature?
        Finally, can you send M98 P"config.g" just to check for any syntax errors in your config?
          dc42 administrators @ShadowX
          @shadowx with that board revision, when using a 2-wire connection or testing with the resistor, you need to add a link wire between terminals 1 and 2 and another between 3 and 4 (with the resistor fitted between terminals 2 and 3 as you have indicated), or alternatively put solder bridges across the pads provided.
          ShadowXundefined 1 Reply Last reply Reply Quote 0
          • ShadowXundefined
            ShadowX
            @phaedrux said in Bad PT100 board?:
            That is an error on my part. The error has been there since 2018 and earlier that I overlooked. I have fixed the setting as shown in the results on the bottom of this reply.
            I reseated the board multiple times. I took the board in and out at least 5 times.
            They are both about 400.1-400.5 ohms
            What exactly does it display for a temperature? The PanelDue screen does not show temperature for the extrude and the web interface shows the bottom image.
            Here are the error messages that came back. This is after fixing the M350 command to:
            M350 X16 Y16 Z16 E16 I1
            M98 P"config.g"
            Error: in file macro line 31 column 19: M350: array too long, max length = 0
            Error: in file macro line 32 column 25: M906: array too long, max length = 0
            Error: in file macro line 36 column 24: M566: array too long, max length = 0
            Error: in file macro line 37 column 25: M201: array too long, max length = 0
            Error: in file macro line 38 column 28: M203: array too long, max length = 0
            Error: in file macro line 41 column 18: M92: array too long, max length = 0
            Error: Invalid extruder number '0'
            Error: bad drive number
            Error: Tool 0 not found
            At first, after fixing the M350 command, the whining noise was gone and the PanelDue shows "Tool 0 not found". The macro turns on the bed heater bed, but I get the "tool 0 not found" error message. I thought fixing the M350 solved the noise issue at the time.
            However, if I shut off the printer and restart it, the noise is back if I run the heater macro right away. After I home the printer, the noise is gone when I start my heater. I guess that noise is related to the motors and homing the printer first before I turn on the heater stopped that noise from happening. Note, when the motors where whining, I did not get a tool error on the panelDue, however, I had to use the stop button or that noise would not stop. After the printer homed, I had no more noise and that tool error message popped right up.
            G10 P0 R0 S190  ; Set standby and extruder temp to 200C
            M140 S65 H0 	; Set heated bed initial value to 65C
            T0 				;  Select Tool 0 to turn on the extruder to active
            Thanks for all your help.
            • ShadowXundefined
              ShadowX @dc42
              @dc42 said in Bad PT100 board?:
              I use a 4 wire system on my printer. My measurement between the two middle terminal (2 &3) is around 120 ohms. Between connection 1&2, I get around 1.1 ohms and 3&4, I get 1.2 ohms.
              On the 100 ohm resistor test, I attached a short jumper cable between 1&2 and 3&4 and still had the same results. The jumper wires measured around 0.7 or 0.8 ohms. Note, these measurements are on the top screws of the terminals on the PWB boards. I wasn't able to probe the bottom solder pads unless I remove the boards.
              I just hope it wasn't something stupid I did on the configuration file like left out a semi colon somewhere or added an extra space. I don't believe I changed anything, but its been a least a week since my last print.
              I compared it to my last backup in June and I don't see any differences in the extruder heater or tool settings.
                Those measurements sound good. Does the second channel on the PT100 board behave in the same way when you test using the 100 ohm resistor?
                • ShadowXundefined
                  ShadowX @dc42
                  Yes. I was only able to test the second channel since the terminals on the RTD1 broke off. I can solder the wires or a connector to the RTD1 solder pads to test.
                  I have a Kingst LA1010 logic analyzer. Is there certain pins I can connect to on the board to check if I get the proper signals from the RTD board? I recall there was a schematic available somewhere but don't have the links to them anymore. I guess the basic checks is for power first to the board and then any output signals from the SPI interface.
                  Thanks for you help.
                    There are some issues with your config.g perhaps from the manual transition to RRF3. Here's a clean basic config.g I created in the config tool you can use to start with and modify with your specifics. I tried to copy over as much as I could.
                    I think part of the problem for those errors is that you lack an M584 command to define the drivers and axis. The whining noise may be due to incorrect defaults being applied for the drivers.
                    ; generated by RepRapFirmware Configuration Tool v3.3.0 on Fri Aug 06 2021 12:30:20 GMT-0600 (Central Standard Time)
                    M575 P1 S1 B57600                              ; enable support for PanelDue
                    G90                                            ; send absolute coordinates...
                    M550 P"My Printer"                             ; set printer name
                    M665 R105.6 L215 B85 H250                      ; Set delta radius, diagonal rod length, printable radius and homed height
                    M666 X0 Y0 Z0                                  ; put your endstop adjustments here, or let auto calibration find them
                    M552 S1                                        ; enable network
                    M586 P0 S1                                     ; enable HTTP
                    M586 P1 S0                                     ; disable FTP
                    M586 P2 S0                                     ; disable Telnet
                    M569 P0 S1                                     ; physical drive 0 goes forwards
                    M569 P1 S1                                     ; physical drive 1 goes forwards
                    M569 P2 S1                                     ; physical drive 2 goes forwards
                    M569 P3 S0                                     ; physical drive 3 goes backwards
                    M584 X0 Y1 Z2 E3                               ; set drive mapping
                    M350 X16 Y16 Z16 E16 I1                        ; configure microstepping with interpolation
                    M92 X80.00 Y80.00 Z80.00 E2680.00              ; set steps per mm
                    M566 X900.00 Y900.00 Z900.00 E1200.00          ; set maximum instantaneous speed changes (mm/min)
                    M203 X18000.00 Y18000.00 Z18000.00 E3000.00    ; set maximum speeds (mm/min)
                    M201 X2000.00 Y2000.00 Z2000.00 E3000.00       ; set accelerations (mm/s^2)
                    M906 X1000 Y1000 Z1000 E800 I30                ; set motor currents (mA) and motor idle factor in per cent
                    M84 S30                                        ; Set idle timeout
                    M208 Z0 S1                                     ; set minimum Z
                    M574 X2 S1 P"xstop"                            ; configure active-high endstop for high end on X via pin xstop
                    M574 Y2 S1 P"ystop"                            ; configure active-high endstop for high end on Y via pin ystop
                    M574 Z2 S1 P"zstop"                            ; configure active-high endstop for high end on Z via pin zstop
                    M558 P1 C"zprobe.in" H5 F480 T6000             ; set Z probe type to unmodulated and the dive height + speeds
                    G31 P500 X0 Y0 Z0.08                           ; set Z probe trigger value, offset and trigger height
                    M557 R85 S20                                   ; define mesh grid
                    M308 S0 P"bedtemp" Y"thermistor" T100000 B3950 ; configure sensor 0 as thermistor on pin bedtemp
                    M950 H0 C"bedheat" T0                          ; create bed heater output on bedheat and map it to sensor 0
                    M307 H0 B0 S1.00                               ; disable bang-bang mode for the bed heater and set PWM limit
                    M140 H0                                        ; map heated bed to heater 0
                    M143 H0 S120                                   ; set temperature limit for heater 0 to 120C
                    M308 S1 P"spi.cs2" Y"rtd-max31865"             ; configure sensor 1 as thermocouple via CS pin spi.cs2
                    M950 H1 C"e0heat" T1                           ; create nozzle heater output on e0heat and map it to sensor 1
                    M307 H1 B0 S1.00                               ; disable bang-bang mode for heater  and set PWM limit
                    M143 H1 S280                                   ; set temperature limit for heater 1 to 280C
                    M950 F0 C"fan0" Q500                           ; create fan 0 on pin fan0 and set its frequency
                    M106 P0 S0 H-1                                 ; set fan 0 value. Thermostatic control is turned off
                    M950 F1 C"fan1" Q500                           ; create fan 1 on pin fan1 and set its frequency
                    M106 P1 S0 H-1                                 ; set fan 1 value. Thermostatic control is turned off
                    M950 F2 C"fan2" Q500                           ; create fan 2 on pin fan2 and set its frequency
                    M106 P2 S0 H-1                                 ; set fan 2 value. Thermostatic control is turned off
                    M563 P0 D0 H1 F0                               ; define tool 0
                    G10 P0 X0 Y0 Z0                                ; set tool 0 axis offsets
                    G10 P0 R0 S0                                   ; set initial tool 0 active and standby temperatures to 0C
                    M501                                           ; load saved parameters from non-volatile memory
                    T0                                             ; select first tool
                      If you send command M308 S# (where #s the sensor number) with no additional parameters, what is the response? I am assuming you are running RRF 3.
                      How did the terminals of RTD1 break off? If that was caused by physical damage, perhaps you should just buy another daughter board? They are not expensive, and judging by the version in the photo you attached I suspect you have had that one for several years.
                        Phaedrux Moderator @dc42
                        @dc42 I think the photo he has in his first post is just the photo used from the wiki page for the PT100 board, not his own board, so not indicative of the version he has.
                        https://duet3d.dozuki.com/Wiki/Connecting_PT100_temperature_sensors
                          dc42 administrators @Phaedrux
                          @phaedrux thanks, I didn't consider that.