    [feature] Adaptive / Feedforward Temperature setpoint

    Scheduled Pinned Locked Moved
    Firmware developers
    8
    51
    3.3k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • timschneiderundefined
      timschneider
      last edited by timschneider

      Hi,
      I remember this being mentioned somewhere before, maybe someone here can help where that was.

      It's about raising the temperature depending on the extrusion speed.
      i first implemented the idea as a daemon script a few months ago https://forum.duet3d.com/post/338055

      The problem with increased temperature is, that the filament will burn while printing slow speed areas like top surface, outer perimeter, bridges and so on. This limits the ability to crank up the temperature e.g. for PLA you can start at 180 °C up you can not expect much performance unless you have a very long melt zone.

      If you want to go fast with your normal setup you need to increase the temperature to compensate for the reduced time of the filament in the melt zone. But if you increase the temperature too much, you will burn your filament while printing slow, e.g. printing PLA at 280°C is totally fine if the time in the melt zone is below 2-3 sec.

      I have found that feedforward temperature setpoint allows significantly higher extrusion rates without burning the filament.
      For example, for PLA, with a 0.8mm nozzle and 220°C nozzle temperature, I achieve a maximum of 180 mm/min or 19.14 mm³/sec with 2.85mm² filament and a standard deviation of less than 0.01 -> 1%.

      ; max F180.0 mm/min or 19.14mm³/s
      ; temp: 220 °C
      ; mean error: 0.0253076 -> 2.53076%
      ; min error: 0.0178955 -> 1.78955%
      ; max error: 0.0349438 -> 3.49438%
      ; standard deviation: 0.0014118 -> 0.14118%
      

      With the dynamic temperature increase with a factor of feedforward = 8, I achieve a maximum of 330 mm/min or 35.09 mm³/sec. with a comparable standard deviation.
      The formula is: new_target_temp = target_temp + avg_extrusion_speed * feedforward

      ; max F330.0 mm/min or 35.09mm³/s
      ; temp: 220 °C
      ; mean error: 0.0090234 -> 0.90234 %
      ; min error: -0.0016260 -> -0.16260 % 
      ; max error: 0.0218506 -> 2.18506 %
      ; standard deviation: 0.0038675 -> 0.38675%
      

      56065bd9-329c-41f1-9ccf-62589ece4061-grafik.png

      5a20c588-42af-4491-9f7e-d7369b86e2a3-grafik.png

      dcf2c685-589b-4ee8-93d0-9dbd95e2eaa4-grafik.png

      as you can see, I've misused the heater feedforward for my implementaion.

      What dou you think about it?

      Surprisingly, I have found that a factor of 8 is suitable for different FIlaments e.g. PLA, PETG, PA6. Maybe someone with a deeper understanding can explain this? I am thinking of @dc42 ?

      Btw. these are the non linear extrusion parameters

      M592 D0 A-0.0039865 B0.0029572 L0.2
      

      As you can see, this will also reduce the NLE values

      droftartsundefined dc42undefined 2 Replies Last reply Reply Quote 1
      • droftartsundefined
        droftarts administrators @timschneider
        last edited by

        @timschneider Interesting! There is a discussion in the OrcaSlicer community about this, see https://github.com/SoftFever/OrcaSlicer/discussions/5057, and an implementation as a post-slicing app here https://github.com/sb53systems/G-Code-Flow-Temperature-Controller

        I think while it could be firmware controlled, a slicer implementation might be more desirable.

        Ian

        Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

        timschneiderundefined Tinchusundefined 2 Replies Last reply Reply Quote 2
        • dc42undefined
          dc42 administrators @timschneider
          last edited by dc42

          @timschneider interesting! This could be implemented as an extension to M309, https://docs.duet3d.com/User_manual/Reference/Gcodes#m309-set-or-report-heater-feedforward, perhaps by adding a T parameter to specify the temperature increase(s) per unit of extrusion speed.

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          timschneiderundefined 1 Reply Last reply Reply Quote 1
          • timschneiderundefined
            timschneider @droftarts
            last edited by

            @droftarts said in [feature] Adaptive / Feedforward Temperature setpoint:

            @timschneider Interesting! There is a discussion in the OrcaSlicer community about this, see https://github.com/SoftFever/OrcaSlicer/discussions/5057, and an implementation as a post-slicing app here https://github.com/sb53systems/G-Code-Flow-Temperature-Controller

            I think while it could be firmware controlled, a slicer implementation might be more desirable.

            Ian

            hey cool - yes i though that a slicer implementaion is even better, but the problem is the calibration of it, it takes ages to calibrate the PA and NLE for every setpoint and since we can automatically calculate the NLE in the printer as a macro, we can also tune the adaptive temp control with it, automatically.

            1 Reply Last reply Reply Quote 0
            • timschneiderundefined
              timschneider @dc42
              last edited by timschneider

              @dc42
              do you mean something like the following:

              From 83be8a6fac88110fc62f6e105f522ef601164b69 Mon Sep 17 00:00:00 2001
              From: Tim Schneider <tim@schneider.engineering>
              Date: Wed, 21 Aug 2024 14:22:41 +0200
              Subject: [PATCH] - M309: added T parameter to specify the temperature
               increase(s) per unit of extrusion speed
              
              ---
               src/Heating/Heat.cpp        |  4 ++--
               src/Heating/Heat.h          |  2 +-
               src/Heating/Heater.h        |  2 +-
               src/Heating/LocalHeater.cpp | 17 +++++++++++++----
               src/Heating/LocalHeater.h   |  4 +++-
               src/Heating/RemoteHeater.h  |  2 +-
               src/Tools/Tool.cpp          | 15 +++++++++++++--
               src/Tools/Tool.h            |  1 +
               8 files changed, 35 insertions(+), 12 deletions(-)
              
              diff --git a/src/Heating/Heat.cpp b/src/Heating/Heat.cpp
              index 397c25bd..cd4cb7d0 100644
              --- a/src/Heating/Heat.cpp
              +++ b/src/Heating/Heat.cpp
              @@ -876,14 +876,14 @@ void Heat::FeedForwardAdjustment(unsigned int heater, float fanPwmChange, float
               }
               
               // This one is called from an ISR so we must not get a lock
              -void Heat::SetExtrusionFeedForward(unsigned int heater, float pwm) const noexcept
              +void Heat::SetExtrusionFeedForward(unsigned int heater, float pwm, float degree) const noexcept
               {
               	if (heater < MaxHeaters)
               	{
               		Heater * const h = heaters[heater];
               		if (h != nullptr)
               		{
              -			h->SetExtrusionFeedForward(pwm);
              +			h->SetExtrusionFeedForward(pwm, degree);
               		}
               	}
               }
              diff --git a/src/Heating/Heat.h b/src/Heating/Heat.h
              index 7ca1e5e4..5e49680b 100644
              --- a/src/Heating/Heat.h
              +++ b/src/Heating/Heat.h
              @@ -128,7 +128,7 @@ public:
               	GCodeResult SetActiveOrStandby(int heater, const Tool *tool, bool active, const StringRef& reply) noexcept;	// Turn a heater on
               	void SwitchOff(int heater) noexcept;								// Turn off a specific heater
               	void FeedForwardAdjustment(unsigned int heater, float fanPwmChange, float extrusionChange) const noexcept;
              -	void SetExtrusionFeedForward(unsigned int heater, float pwm) const noexcept;
              +	void SetExtrusionFeedForward(unsigned int heater, float pwm, float degree) const noexcept;
               
               #if HAS_MASS_STORAGE || HAS_SBC_INTERFACE
               	bool WriteModelParameters(FileStore *f) const noexcept;				// Write heater model parameters to file returning true if no error
              diff --git a/src/Heating/Heater.h b/src/Heating/Heater.h
              index 64f61666..b71f3405 100644
              --- a/src/Heating/Heater.h
              +++ b/src/Heating/Heater.h
              @@ -57,7 +57,7 @@ public:
               	virtual void Suspend(bool sus) noexcept = 0;						// Suspend the heater to conserve power or while doing Z probing
               	virtual float GetAccumulator() const noexcept = 0;					// Get the inertial term accumulator
               	virtual void FeedForwardAdjustment(float fanPwmChange, float extrusionChange) noexcept = 0;
              -	virtual void SetExtrusionFeedForward(float pwm) noexcept = 0;
              +	virtual void SetExtrusionFeedForward(float pwm, float degree) noexcept = 0;
               
               #if SUPPORT_CAN_EXPANSION
               	virtual bool IsLocal() const noexcept = 0;
              diff --git a/src/Heating/LocalHeater.cpp b/src/Heating/LocalHeater.cpp
              index 9059d7f2..eaff1314 100644
              --- a/src/Heating/LocalHeater.cpp
              +++ b/src/Heating/LocalHeater.cpp
              @@ -86,7 +86,7 @@ void LocalHeater::ResetHeater() noexcept
               	mode = HeaterMode::off;
               	previousTemperaturesGood = 0;
               	previousTemperatureIndex = 0;
              -	iAccumulator = extrusionBoost = 0.0;
              +	iAccumulator = extrusionBoost = extrusionTemperatureBoost = lastExtrusionTemperatureBoost = 0.0;
               	badTemperatureCount = 0;
               	averagePWM = lastPwm = 0.0;
               	heatingFaultCount = 0;
              @@ -189,7 +189,7 @@ GCodeResult LocalHeater::SwitchOn(const StringRef& reply) noexcept
               		return GCodeResult::error;
               	}
               
              -	const float target = GetTargetTemperature();
              +	const float target = min<float>(GetTargetTemperature() + extrusionTemperatureBoost, GetHighestTemperatureLimit());
               	const HeaterMode newMode = (temperature + TemperatureCloseEnough < target) ? HeaterMode::heating
               								: (temperature > target + TemperatureCloseEnough) ? HeaterMode::cooling
               									: HeaterMode::stable;
              @@ -282,9 +282,17 @@ void LocalHeater::Spin() noexcept
               		if (GetModel().IsEnabled())
               		{
               			// Get the target temperature and the error
              -			const float targetTemperature = GetTargetTemperature();
              +			const float targetTemperature = min<float>(GetTargetTemperature() + extrusionTemperatureBoost, GetHighestTemperatureLimit());
               			const float error = targetTemperature - temperature;
               
              +			if (extrusionTemperatureBoost != 0.0 || lastExtrusionTemperatureBoost != extrusionTemperatureBoost)
              +			{
              +				// calculate new heater mode to prevent heater fault due to exceededAllowedExcursion
              +				String<1> dummy;
              +				(void)SwitchOn(dummy.GetRef());
              +			}
              +			lastExtrusionTemperatureBoost = extrusionTemperatureBoost;
              +
               			// Do the heating checks
               			switch(mode)
               			{
              @@ -570,9 +578,10 @@ void LocalHeater::FeedForwardAdjustment(float fanPwmChange, float extrusionChang
               }
               
               // Set extrusion feedforward. This is called from an ISR.
              -void LocalHeater::SetExtrusionFeedForward(float pwm) noexcept
              +void LocalHeater::SetExtrusionFeedForward(float pwm, float degree) noexcept
               {
               	extrusionBoost = pwm;
              +	extrusionTemperatureBoost = degree;
               }
               
               /* Notes on the auto tune algorithm
              diff --git a/src/Heating/LocalHeater.h b/src/Heating/LocalHeater.h
              index cf0840c5..d5a18221 100644
              --- a/src/Heating/LocalHeater.h
              +++ b/src/Heating/LocalHeater.h
              @@ -39,7 +39,7 @@ public:
               	float GetAccumulator() const noexcept override;							// Return the integral accumulator
               	void Suspend(bool sus) noexcept override;								// Suspend the heater to conserve power or while doing Z probing
               	void FeedForwardAdjustment(float fanPwmChange, float extrusionChange) noexcept override;
              -	void SetExtrusionFeedForward(float pwm) noexcept override;				// Set extrusion feedforward
              +	void SetExtrusionFeedForward(float pwm, float degree) noexcept override;	// Set extrusion feedforward
               #if SUPPORT_CAN_EXPANSION
               	bool IsLocal() const noexcept override { return true; }
               	void UpdateRemoteStatus(CanAddress src, const CanHeaterReport& report) noexcept override { }
              @@ -76,6 +76,8 @@ private:
               	float lastPwm;											// The last PWM value set for this heater
               	float averagePWM;										// The running average of the PWM, after scaling.
               	volatile float extrusionBoost;							// The amount of extrusion feedforward to apply
              +	volatile float extrusionTemperatureBoost;				// The amount of extrusion feedforward to apply
              +	float lastExtrusionTemperatureBoost;					// The amount of extrusion feedforward to apply
               	float lastTemperatureValue;								// the last temperature we recorded while heating up
               	uint32_t lastTemperatureMillis;							// when we recorded the last temperature
               	uint32_t timeSetHeating;								// When we turned on the heater
              diff --git a/src/Heating/RemoteHeater.h b/src/Heating/RemoteHeater.h
              index a6c09029..a30872d7 100644
              --- a/src/Heating/RemoteHeater.h
              +++ b/src/Heating/RemoteHeater.h
              @@ -30,7 +30,7 @@ public:
               	float GetAccumulator() const noexcept override;							// Return the integral accumulator
               	void Suspend(bool sus) noexcept override;								// Suspend the heater to conserve power or while doing Z probing
               	void FeedForwardAdjustment(float fanPwmChange, float extrusionChange) noexcept override;
              -	void SetExtrusionFeedForward(float pwm) noexcept override { }			// We can't yet set feedforward on remote heaters because this is called from an ISR
              +	void SetExtrusionFeedForward(float pwm, float degree) noexcept override { }			// We can't yet set feedforward on remote heaters because this is called from an ISR
               	bool IsLocal() const noexcept override { return false; }
               	void UpdateRemoteStatus(CanAddress src, const CanHeaterReport& report) noexcept override;
               	void UpdateHeaterTuning(CanAddress src, const CanMessageHeaterTuningReport& msg) noexcept override;
              diff --git a/src/Tools/Tool.cpp b/src/Tools/Tool.cpp
              index c0676b8f..b41174c9 100644
              --- a/src/Tools/Tool.cpp
              +++ b/src/Tools/Tool.cpp
              @@ -946,6 +946,12 @@ GCodeResult Tool::GetSetFeedForward(GCodeBuffer& gb, const StringRef& reply) THR
               		gb.GetFloatArray(heaterFeedForward, numValues, false);
               		ToolUpdated();
               	}
              +	else if (gb.Seen('T'))
              +	{
              +		size_t numValues = heaterCount;
              +		gb.GetFloatArray(temperatureFeedForward, numValues, false);
              +		ToolUpdated();
              +	}
               	else
               	{
               		reply.printf("Tool %u heater feedforward:", myNumber);
              @@ -953,6 +959,11 @@ GCodeResult Tool::GetSetFeedForward(GCodeBuffer& gb, const StringRef& reply) THR
               		{
               			reply.catf(" %.3f", (double)heaterFeedForward[i]);
               		}
              +		reply.printf("Tool %u temperature feedforward:", myNumber);
              +		for (size_t i = 0; i < heaterCount; ++i)
              +		{
              +			reply.catf(" %.3f", (double)temperatureFeedForward[i]);
              +		}
               	}
               
               	return GCodeResult::ok;
              @@ -964,7 +975,7 @@ void Tool::ApplyFeedForward(float extrusionSpeed) const noexcept
               	Heat& heat = reprap.GetHeat();
               	for (size_t i = 0; i < heaterCount; ++i)
               	{
              -		heat.SetExtrusionFeedForward(heaters[i], extrusionSpeed * heaterFeedForward[i]);
              +		heat.SetExtrusionFeedForward(heaters[i], extrusionSpeed * heaterFeedForward[i], extrusionSpeed * temperatureFeedForward[i]);
               	}
               }
               
              @@ -974,7 +985,7 @@ void Tool::StopFeedForward() const noexcept
               	Heat& heat = reprap.GetHeat();
               	for (size_t i = 0; i < heaterCount; ++i)
               	{
              -		heat.SetExtrusionFeedForward(heaters[i], 0.0);
              +		heat.SetExtrusionFeedForward(heaters[i], 0.0, 0.0);
               	}
               }
               
              diff --git a/src/Tools/Tool.h b/src/Tools/Tool.h
              index 2c2e5afb..e071000b 100644
              --- a/src/Tools/Tool.h
              +++ b/src/Tools/Tool.h
              @@ -188,6 +188,7 @@ private:
               	float activeTemperatures[MaxHeatersPerTool];
               	float standbyTemperatures[MaxHeatersPerTool];
               	float heaterFeedForward[MaxHeatersPerTool];
              +	float temperatureFeedForward[MaxHeatersPerTool];
               
               	// Firmware retraction settings
               	float retractLength, retractExtra;			// retraction length and extra length to un-retract
              -- 
              2.39.2.windows.1
              
              
              

              f3a08b7b-6d14-438c-9bb6-822038e5c019-grafik.png

              I'm not sure about the change of the method interface and so on but if it is heading in the right direction I can prepare a merge request.

              Update
              The implementation will not fit into Duet2 due to too less rom.
              It will fit if the wifi is compiled without W5500 and the ethernet without WIFI
              or both without FTP and Telnet support

              1 Reply Last reply Reply Quote 0
              • droftartsundefined droftarts referenced this topic
              • Tinchusundefined
                Tinchus @droftarts
                last edited by

                @droftarts I was just about to post a question regarding feed forward till I found this post.
                I think the feedforwwar tool doesnt cover all the issue. As mentioned here, you can print perfectly PLA at 180 degrees with excelent quality, BUT you will be restricted on how fast you can print. On the other hand, you can print PLA at 150 mm/s on a 0.8 nozzle only if you go up in your temp to 230 degrees oir little more, but as soon as you slow down you quality goes to the trash bin because of that excesive temp.

                The feedforward config at least to me has not solved this in my prints, I have to either choose print really fast and hot or normal/slow and "cold". My question was going to be if the feedforward command could add some type of algorithm to take into account the cubic mms being extruded instead of the printing speed, in that way you would be covering all nozzle spectrum and printing speed at the same time.

                And regarding where: I think the oposite. It should be the formware the one in charge of that because the slicer never knows the real speed of a path. Final real speed is decided by firmware, the slciewr never knows the real printing speed (and that is the reason why the time calculation on slicer are allways really off)

                timschneiderundefined 1 Reply Last reply Reply Quote 0
                • timschneiderundefined
                  timschneider @Tinchus
                  last edited by

                  @Tinchus said in [feature] Adaptive / Feedforward Temperature setpoint:

                  And regarding where: I think the oposite. It should be the formware the one in charge of that because the slicer never knows the real speed of a path. Final real speed is decided by firmware, the slciewr never knows the real printing speed (and that is the reason why the time calculation on slicer are allways really off)

                  Thats a good point!

                  I made a PR for this https://github.com/Duet3D/RepRapFirmware/pull/1036

                  But due to memory contrains, it will not fit in the ROM of a regular Duet2 combined firmware. You need to disable other not important features to make it work e.g. Telnet and FTP.

                  timschneider opened this pull request in Duet3D/RepRapFirmware

                  closed [WIP] M309: add T parameter to specify the temperature increase(s) per … #1036

                  Tinchusundefined 1 Reply Last reply Reply Quote 0
                  • Tinchusundefined
                    Tinchus @timschneider
                    last edited by

                    @timschneider I wonder if temp increase VS speed will be ok when you change to a bigger noozle and you go slow; in that situation you would have a potential huge increment of mm3/s but a lower speed. Example: 100 MM/s speed with a 0.4 noozle . The you switch to a 0.8 nozzle and go to 80 mm/s

                    timschneiderundefined 1 Reply Last reply Reply Quote 0
                    • timschneiderundefined
                      timschneider @Tinchus
                      last edited by timschneider

                      @Tinchus it is extruder speed e.g. movement of filament per sec, not travel speed so it is accounting for that. I print with 0.8mm to 1.2mm nozzles.

                      Tinchusundefined 1 Reply Last reply Reply Quote 0
                      • Tinchusundefined
                        Tinchus @timschneider
                        last edited by

                        @timschneider that is what I meant. May be Im wrong so please clarify: the push request is using the new requested T parameter in terms of extrusion speed or volumentric speed? Because the firmeware actually never knows what size of nozzle you are using: if slicer request a 10 mm/s extrusion move and you are using a 0.8 nozzle volumen and needed temperature will be quite dfifferent if the slicer request the same speed but you are using a 0.4 nozzle. am I wrong?

                        timschneiderundefined 1 Reply Last reply Reply Quote 0
                        • timschneiderundefined
                          timschneider @Tinchus
                          last edited by

                          @Tinchus, it's the extrusion speed. So I use 2.85 mm filament and if I use an extrusion speed of 1 mm/s, for example, it is about 6.38 mm³/s, regardless of the nozzle size. The only difference between extrusion speed and volume speed is the area of the filament, e.g. for 2.85 mm filament 6.38 mm² and thus only a factor.

                          droftartsundefined 2 Replies Last reply Reply Quote 0
                          • droftartsundefined
                            droftarts administrators @timschneider
                            last edited by

                            @timschneider said in [feature] Adaptive / Feedforward Temperature setpoint:

                            So I use 2.85 mm filament

                            I thought it was just me using up everyone else's 2.85mm filament! If I ever get my Trident-ish machine finished, I've got a Titan extruder with volcano CHT nozzles (probably 1mm nozzle dia) tool earmarked for it, to get through all the old stock (after it's spent time in the filament dryer), and print big things fast! So some form of temperature feedforward would be good.

                            Ian

                            Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                            1 Reply Last reply Reply Quote 0
                            • droftartsundefined
                              droftarts administrators @timschneider
                              last edited by

                              @timschneider As this feature has been added (https://github.com/Duet3D/RepRapFirmware/commit/b300085b44b2fe403d231a674b3b29f702c6b66f), have you got any suggestions for the tuning method that I could add to the feedforward documentation?

                              M309 in the Gcode dictionary has been updated to say:

                              Parameters
                              ...
                              Tddd:eee:fff... Feedforward temperature increase coefficients. The number of coefficients provided must equal the number of heaters configured for the tool when it was created (see M563). Supported in RRF 3.6.0-beta.2 and later.
                              Aggg Feedforward advance time in milliseconds, maximum 100. RRF will attempt to apply the temperature and PWM adjustment this time in advance of the start of the corresponding move. This advance time may not always be achieved, for example when commencing movement from standstill. Supported in RRF 3.6.0-beta.2 and later.

                              Notes
                              ...
                              The units of T are degrees Celsius per mm/sec of filament forward movement.

                              No notes on the A parameter.

                              Ian

                              0 dc42 committed to Duet3D/RepRapFirmware
                              Refactored heater feedforward implementation, added T and A parameters

                              Bed-slinger - Mini5+ WiFi/1LC | RRP Fisher v1 - D2 WiFi | Polargraph - D2 WiFi | TronXY X5S - 6HC/Roto | CNC router - 6HC | Tractus3D T1250 - D2 Eth

                              timschneiderundefined 1 Reply Last reply Reply Quote 0
                              • timschneiderundefined
                                timschneider @droftarts
                                last edited by timschneider

                                @droftarts
                                Hi @droftarts
                                I use the following tuning method:

                                • determine the lowest possible temperatur Temp_base for the filament, e.g. extrude with F30 (0.5 mm/sec Speed_base) so that the filament is melting and will bond to each other
                                • define your desired extrusion rate, e.g. 35 mm³/sec -> calculate the required extrusion speed -> around 5.5 mm/sec (Speed_desired) for 2.85mm filament -> F330
                                • Extrude the filament with the desired speed + 20% and increase the temperature of the hotend till you are able to extrude at the desired speed. Note the needed temperature for that speed Temp_required. The extrusion length should be at least two times your hotend length. The 20% increase is some kind of error margin for non linear extrusion and when the fan is on.
                                • calculate the needed temperature boost with Temp_boost = (Temp_required - Temp_base) / (Speed_desired - Speed_base)

                                For Example PLA

                                Temp_base = 190
                                Temp_required = 230
                                Speed_base = 0.5 mm/s
                                Speed_desired = 5.5 mm/s
                                Temp_boost = 40 / 5 => 8 => T8
                                

                                Edit: Temp_base will be the temperature you set in your slicer for that material.

                                timschneiderundefined 1 Reply Last reply Reply Quote 1
                                • timschneiderundefined
                                  timschneider @timschneider
                                  last edited by

                                  @droftarts
                                  I have updated the description so that it hopefully becomes clearer how much material has to be extruded and why you should aim for a 20% plus error margin and that you should use the temp_base for slicing.

                                  timschneiderundefined 1 Reply Last reply Reply Quote 0
                                  • timschneiderundefined
                                    timschneider @timschneider
                                    last edited by timschneider

                                    @dc42
                                    thank you for implementing the temperature feedforward.
                                    It took me a while to get it installed on a machine and test it, unfortunately I was not able to get it working. Maybe its a pure display thing, but I do not see the temperature increase I was expecting.

                                    I set M309 P0 S0.06 T8 A100 and was extruding at 245°C with 0.6mm/sec, so I was expecting an temperature increase of 4.8°C but the temperature in DWC was still at 245°C.

                                    the following chart is showing the print process and a pretty stable temperature without the increase and decrease of the temperature feed forward.
                                    82a58459-15b3-43ad-b950-66ba4e771906-grafik.png

                                    The printer is on
                                    017f3a63-baa7-47aa-a23e-43b93d78818f-grafik.png

                                    timschneiderundefined 1 Reply Last reply Reply Quote 0
                                    • timschneiderundefined
                                      timschneider @timschneider
                                      last edited by timschneider

                                      @dc42
                                      The problem is the A100 - without the A param it works.
                                      What is the purpose of the A param - I thought it is kind of a look a head and will set the temp increase in advance.
                                      But it will not work for short moves.

                                      To reproduce:

                                      G28 X Y
                                      M568 P0 R160 S230
                                      T0
                                      G91
                                      echo "will not work"
                                      M309 P0 S0.05 T8 A100
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      
                                      G4 S5
                                      echo "will work"
                                      M309 P0 S0.05 T8 A0
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      G1 X1 E1 F120
                                      
                                      dc42undefined 1 Reply Last reply Reply Quote 0
                                      • dc42undefined
                                        dc42 administrators @timschneider
                                        last edited by

                                        @timschneider we knew that large A values will not work correctly, because there need to be enough moves in the queue that have been committed in order to look that far ahead. I think A40 should generally work: can you try that?

                                        Duet WiFi hardware designer and firmware engineer
                                        Please do not ask me for Duet support via PM or email, use the forum
                                        http://www.escher3d.com, https://miscsolutions.wordpress.com

                                        Trietundefined timschneiderundefined 2 Replies Last reply Reply Quote 1
                                        • Trietundefined
                                          Triet @dc42
                                          last edited by

                                          @dc42
                                          I dared to try 😊

                                          Using firmware version 3.6.0-beta.4 and with following command in my config.g:
                                          M309 P0 S0.06 T10 A40
                                          I can confirm that temperature modulation based on flow rate works.

                                          I used the small model below as a preliminary experiment, printed at a nominal temperature of 190 deg C. (usually I print this material at 212 deg C).

                                          Remarks:
                                          During the first layer the temperature jumped to over 220 deg C but with the bed at 45 deg C this was unnecessarily high to achieve bed adhesion. To avoid such surprises I managed to disable this feature for the first layer alone using
                                          the macro command
                                          M309 P0 S{(layer_num == 0 ? 0 : 0.06)} T{(layer_num == 0 ? 0 : 10)} A{(layer_num == 0 ? 0 : 40)}
                                          which yields M309 P0 S0 T0 A0 for ths 1st layer only; then the temperature set for the 1st layer in the slicer is used unchanged.

                                          I needed several retries because I was getting a heater fault error right at the 1st layer. The increase was too sudden I guess. Only after I reconfigured the heater fault detection I could continue the print:
                                          M570 H1 P15 T20 ; wait 15 sec, allow 20C deviation

                                          The maximum temperature increase happened at the widest height of the model and was about 5 degrees, but only a short time.
                                          Most of the time the print temperature stayed around 192C, that is, only 2 degrees higher than set. Although the speeds were set up to 300 mm/sec, due to a layer time limitation and weak cooling fan, the print went quite slow with 20-35 mm/sec.

                                          The deviation between target and actual temperatures can't be assessed during the print, because the increase introduced by this feature is done in the firmware - this is as expected, but raises the need of a plug-in in DWC to preview the effect.

                                          Manually overriding the extrusion speed live during the print (or perhaps using M220) did cause a corresponding increase in temperature, as it should be.

                                          It is unclear to me whether extrusion rate increases caused by non-linear extrusion configuration (M592) also cause temperature increases. In theory, his could lead to a vicious circle, because a temperature increase by itself also promotes a higher extrusion.

                                          I learned that this feature works only increasing the temperature, never decreasing it. That means that one is compelled to choose a nominal printing temperature (the one set in the slicer) that should be low enough that no decrease is necessary due to a smallish flow. This could happen to be inconvenient, depending on the average flow and temperature range needed. This method is suitable to adapt temperature in regions with higher flows, overcoming potential bottlenecks.

                                          A better approach would have been (in my opinion) to consider the nominal temperature to correspond to the average flow rate, allowing both increases and decreases. In most cases no special tests or calibrations would be needed with this method; for example, setting 205C for PLA, thus allowing a range of +/- 15C=30C. Flow rate "spikes" would be still accounted for. This way, small details and overhangs would benefit too (a more common concern than printing at very high speeds, if quality is important).

                                          In other words, as it is implemented, you would set for a benchy a nominal temperature corresponding to the chimney top - suboptimal I think.

                                          Print details:
                                          Duet 2 WiFi + 0.4 nozzle, PLA, 0.12 mm layer height, 0.3 mm layer width, one wall only (to challenge the operation!)

                                          e0a8ceed-9e67-409b-a9c0-4b6371f6e37d-image.png

                                          And I got this result:
                                          dce88bc0-2579-4ec9-8327-d77db4974289-image.png
                                          The print was quite good in my opition, and was not worst than a good one done without the feature under same conditions. Still learning.

                                          I have gathered some experience using the post-processing script mentioned above. It is difficult to believe how felicitous that script manages the temperature/flow relationship. That solution works differently though: It controls speeds in such a way that the flow matches the temperature when the temperature can't be changed fast enough; it also smoothes the flow rate - sounds dangerous, but works surprisingly well. Unfortunately, it is only a post-processing script with the respective disadvantages. The author was told that such feature belongs to the firmware realm - here we have it.

                                          I think this feature of the version 3.6.0 will be vastly underestimated. I consider it a big jump, really.

                                          By the way, the description in the documentation of M309 should be corrected. It states:
                                          "This feature is intended for high flow hot ends or pellet extruders. It's not normally needed on regular hot ends with a 0.4mm or similar size nozzle where the temperature drop caused by extrusion is less than 1C."
                                          The feature may be inteded as described, but it is not limited to mere anticipation of temperature fluctuation of the nozzle due to changing flow. In fact, it contributes to a much better control of a key parameter, namely temperature. I myself will be using it quite often, I think.

                                          Hope I helped a bit.

                                          1 Reply Last reply Reply Quote 3
                                          • timschneiderundefined
                                            timschneider @dc42
                                            last edited by timschneider

                                            @dc42

                                            ok, A40 is working - but shouldn't A100 act like A0 if A100 can not be maintained? Instead it was acting like T0.

                                            @Triet
                                            thanks for you tests! You can maybe increase the layer height to increase the volumetric flow rate, as the T parameter from M309 is multiplied by the speed in mm/s of the filament (extruder) - not the movement speed of the X and Y axis. Your absolute maximum flow rate is about 5.44 mm³/s which is about 2.26 mm/sec for 1.75mm or 0.85 mm/sec for 2.85mm filament, which corresponds to 227.6°C or 213.5°C. Thats a steep increase, unless you have a powerfull heater, your printer will not be able to follow. I use T8 with an 60W heater and 2.85mm filament. I run my prints with 25 - 40 mm ³/s.