    [feature] Adaptive / Feedforward Temperature setpoint
    Firmware developers
    8
    51
    5.0k
    • Trietundefined
      Triet @timschneider
      @timschneider said in [feature] Adaptive / Feedforward Temperature setpoint:
      0
      This was a test I spontaneously decided to do without planning, but it turned out unsuitable for the purpose of temperature modulation. The maximum flow rate of 5.44 mm3/s (using a 1.75 mm filament) happened very shortly and was not representative at all. I did notice the jump though - causing a heater fault at my first try.
      I also use a 60 W heater, in a copper block (E3D style) and an original CHT nozzle. It can achieve a 25C increase faster that one would think, but certainly not fast enough if the model consist of parts with disparate flow rates in succession. And that is exactly the test case I am printing right now:
      As you can recognize here:
      The temperature is set at 195C but settles at around 199C +/-2C, it can't follow as you say. The range would be much wider if it could. But there are some layers with predominantly high flow, I am waiting to see how the temperature behaves then (I am staring at the display).
      Based on my experience using the postprocessing script mentioned above, the maximum temperature lag was about 5C, in most cases only 3C - but that script uses a different method, where the flow rate is adapted (smoothed) to match the predicted temperature, very clever in my opinion. The temperature/flow rate relationship is defined there by entering three points of desired temperature at the given flow rates, quite easy. I could envision that a similar method is implemented in the firmware. But even this T-Parameter is a thing as it is now. I have learned to appreciate the value of temperature control and am quite excited about it.
      More tests following.
      • Trietundefined
        Triet @timschneider
        @timschneider That model (I would call it "the "mother of hinges"), went well - all hinges were moving free without play (after forcingly "unfreezing" them the first time). I can infer then than the temperature variation does not pose a danger in maintaining correct dimensions, in this case at least.
        Now I am choosing a more representative test model with an ample variation of flow rate, which at the same time allows us to assess artifacts, without being excessive large or long to print.
        This JUN - the Jungle Queen (visual benchy) has a plethora of details and is not too small.
        Results:
        Printing with at 195 C, 0.2 mm layerheight, (0.4 mm nozzle), solid infill with 0.6 mm layer width, and sparse infill speed set at 300 mm/sec (but not reached) and still using M309 P0 S0.06 T10 A40, Orca Slicer was showing a flow rate up to 29 mm3/s, but that is not true. The real maximum is about 20 mm3/s, enough of a range. Extrusion rate smoothing was set to 90 mm3/s to avoid abrupt transitions.
        The temperature occassionally reached >240 C in the high flow areas. In very slow areas, it was decreased (!) down to 190 C. Most of the time, is was about 200C.
        The print shows very crisp details, reminding me of previous cases using the postprocessing script. This is obviously the result of printing the small details with a suiting lower temperature.
        Despite some suboptimal slicer settings (happens when printing in a hurry), the print went well and it looks better than in the picture.
        Remarks:
        I noticed that right at the begin of the print the temperature is higher than it should be (although I disabled this temperature modulation feature for the first layer), but immediately begins to fall as the print of the 1st layer progresses. My suspicion is that the firmware looks at the flow of the movements in the print queue in advance, but ignoring the command disabling the feature. But the command it is there:
        and when it is processed, the temperature fails again to the nominal 195C. It looks like a slip to me.
        Furthermore, I still got heater faults (even after releasing the check conditions), but strangely, this happened at a moment where the temperature was quite stable after having significantly changed before. So it looks to me like the firmware notes a temperature deviation, but does not update that deviation timely as the temperature has changed and stabilized. Perhaps that part of the firmware should be revised.
        This time, a decrease in temperature compared to the nominally set print temperature (195 C in this case) took place at some point. So I withdraw the objection I made before, although I don't quite understand how this is controlled in detail. I assume that the T parameter defines a slope determined by changes of temperature in relation to changes in flow, but where we are in that characteristic curve, I don't know.
        Summarizing, I am very pleased with this enhancement. I still stand on my prediction that this feature will stay extremely underrated. I recommend to try it out.
        • Trietundefined Triet referenced this topic
        • Trietundefined
          Triet @timschneider
          @timschneider In case you are interested, this video offers insight to flow modulated temperature control:
          Variable Temperature 3D Printing – The FUTURE of 3D Printing?
          • Adrian52undefined
            Adrian52
            I am finding this feature really interesting. For pla and a 0.4 nozzle, I find
            M309 p0 S0.06 T6 A40
            works ok. I use a base temperature of 200, and first layer temperature of 215. First layer prints at 220-225, as I use 20mmsec for perimeter and 40mm/sec for infill. Using a revo 40watt heater and revo cht nozzle, temperatures change quite quickly (low thermal mass). Experimenting with higher speeds, inner perimeters and infill print fine at 140mm/sec (DWC reports about 22cumm/sec) - accurate weighing of resulting print showed that there was no under extrusion. I am not currently using non-linear extrusion. I have a single nozzle delta, so sometimes change filament mid print to get a multicolour effect. The adaptive feed forward is good for this as the base temperature is high enough to load and prime the new filament, but there is little oozing so you get a clean change. This is what a manual filament change looks like
            The print quality with adaptive feed forward seems excellent, and still finding the limits of how fast one can go.
            Trietundefined 1 Reply Last reply Reply Quote 3
            • Trietundefined
              Triet @Adrian52
              @Adrian52 I found that the active (=target) temperature is not updated, either in DWC or in the Paneldue. It is impossible to know how far the current temperature deviation is.
              Besides, I had to increase the S Parameter to about 0.3 to get a quicker change of temperature. Nontheless, I get heater faults from time to time, although I have loosened the check using the command M570 H1 P100 T45, which is incredibly forgiving, as it allows a deviation of 45 C deg to persist for up to 100 sec...
              Adrian52undefined 1 Reply Last reply Reply Quote 0
              • Adrian52undefined
                Adrian52 @Triet
                @Triet I guess if one is using the feedforward in the way intended, the temperature shown is the target temperature. I have been playing with the parameters, trying to understand how they work. I am trying out a 0.25mm nozzle, which has an extrusion rate of about 8.8cumm/sec with 0.125mm layers at 140mm/sec, which is think corresponds to about 3.6mm/sec for 1.75 filament. A T parameter of 12 seems to give the expected increase of just greater than 40deg over the base temperature. I think there is a bit of under extrusion at this speed with the 0.25 nozzle, but checking that out. For my standard 0.4 cht nozzle, 0.2 layers give about 22cumm/sec at 140 mm/sec, that is about 9mm/sec filament. Using T5, this gives the expected increase of about 45deg above base temperature. I dont think the cht nozzle is underextruding under these conditions. I have just started using an S parameter of 1.0, and this seems to work fine with the 0.25 nozzle - not tried with the 0.4 nozzle yet. Tried increasing the A parameter to 50, and the feed forward stops working.
                I have been using M570 H1 P15 T45, and not been getting heater faults. The revo nozzle setup I am using has a low thermal mass, and seems to be controlled very well by the duet.
                  dc42 administrators @timschneider
                  ok, A40 is working - but shouldn't A100 act like A0 if A100 can not be maintained? Instead it was acting like T0.
                  I've reduced the maximum allowed from A100 to A50 in rc2, which I think should work.
                  [EDIT: Adrian's post above suggests that it doesn't.]
                  Adrian52undefined 1 Reply Last reply Reply Quote 1
                    dc42 administrators @Adrian52
                    @Adrian52 said in [feature] Adaptive / Feedforward Temperature setpoint:
                    That's correct, the target (as displayed by DWC and PanelDue) remains the same but the feedforward correction is added to it internally.
                    @Triet said in [feature] Adaptive / Feedforward Temperature setpoint:
                    I'll look at adding the current feedforward boost to the object model.
                    EDIT: I've added the boost parameters to the OM.
                    • Adrian52undefined
                      Adrian52 @dc42
                      @dc42 On my system, the highest A value that works is 48
                      • Adrian52undefined
                        Adrian52
                        To see if I could get the hotend to follow the forward temperature more closely, I tried removing the silicone sock from the revo heater, to see if I could get faster cooling. I redid the pid tune without the sock, and this is the plot printing a 100mmx20mm cube that has three small cylinders attached to one end. The cube walls print at 140mm/sec, and the cylinders around 20mm/sec. The cube has no fill or top, but the initial part shows printing the bottom infill
                        It then cycles between the fast cube walls and the slow cylinder walls. I was suprised how well controlled the temperature is under these conditions. The print weighed exactly the amount predicted by the slicer, so no underextrusion. The cube walls were printing at 22cumm/sec (o.4 nozzle, 0.2layers). The S parameter was set to 1
                        Would be interesting to plot the feed forward boosted temperature on the temperature chart - is this possible?
                        jay_s_ukundefined Trietundefined 2 Replies Last reply Reply Quote 0
                          jay_s_uk @Adrian52
                          @Adrian52 you could plot it with BtnCmd if its in the object model
                          • Trietundefined
                            Triet @Adrian52
                            @Adrian52 Wouln't you need to repeat the same print (with/without silicon sock) to properly quantify the effect? What are you comparing to?
                            • Adrian52undefined
                              Adrian52 @Triet
                              @Triet Indeed - I was just looking at the feasibility of leaving off the sock. I was concerned that it would make temperature control unstable, but this doesn't seem to be the case. I thought a next step would be to plot the boosted temperature against the actual temperature, but waiting for an update that has the boosted temperature in the OM. On a learning curve with btncmd too - not used it before. Will aim to do a more formal comparison, including maximum speed and print quality.
                              Trietundefined 1 Reply Last reply Reply Quote 0
                              • Trietundefined
                                Triet @Adrian52
                                @Adrian52 I share the same interest. If I get somewhere customizing DWC to show the temperature deviation I will post my findings.
                                By the way, removing the silicon sock to facilitate better temperature control is a brilliant idea.
                                  dc42 administrators @Triet
                                  Even better would be to replace the hot end by one with much lower thermal mass and heating/cooling times, such as the E3D Revo.
                                  Adrian52undefined Trietundefined 3 Replies Last reply Reply Quote 0
                                  • Adrian52undefined
                                    Adrian52 @dc42
                                    @dc42 I am in fact using a revo micro on my delta, and just ordered a 60w heater, to see if it shortens the heating time. Hope it doesn't melt my part cooling duct!
                                    • Trietundefined
                                      Triet @dc42
                                      @dc42 The thoroughgoing extrapolation of this idea would be an
                                      INo Trident
                                      • Adrian52undefined
                                        Adrian52
                                        Another experiment, with a 60W e3d revo heater, and no socks. The print is a 20x100mm cube, and a set of 6 8mm diameter cylinders. The cylinders print quite slowly and the cube at 140mm/sec.
                                        This is an excel graph of csv data captured by btncmd (not worked out how to plot calculated values in btncmd).
                                        I added the active temp to the boost (a+b) to compare to the actual temp(current). You can see there is a bit of a lag on both the heating and cooling phases.
                                        I also plot the extrusion volume, and you can see that the boost anticipates the increase in extrusion, although not by enough to align with the current temperature. I plotted extrusion+active temp(e+a) to move the extrusion line up to the area of the current temp line.
                                        Not quite sure why the active +boost is below the current temperature in the initial phase - this is the relatively slow printing of the first layer.
                                        Trietundefined 1 Reply Last reply Reply Quote 1
                                        • Trietundefined
                                          Triet @Adrian52
                                          @Adrian52 If the command would allow an option to limit the extrusion (=speed) to match the actual temperature, it would be much better, as layer adhesion would be optimal. Delamination and sudden breaks under mechanical load would be a thing of the past.
                                          • Adrian52undefined
                                            Adrian52 @dc42
                                            @dc42 the 60w heater on the revo seems to work fine, albeit with a tendency to overshoot a bit. The heat /cool curve (current) is not too bad, but lags the extrusion /boost curves by about 6 seconds. I tried increasing the queue size to 120, which is probably near the limit for my old duet2wifi. The A parameter at 50 works then. Is there any way to adjust for the lag?
