    Heater Temperature Excursion
    1.8k
    • BoAundefined
      BoA
      Had similar issue. Could not reproduce it by moving wires (at the beginning) but it was a broken heatbed thermistor wire (in Your case hotend thermistor wire). It started as a "noise" on temperature reading and finished with open circuit in about 2 weeks.
      • Leavundefined
        Leav
        I tried reproducing by extruding material, and was inexplicably able to reproduce the bed heater noise flickering:
        @BoA The fact that it's happening on two different thermistors "at the same time" is suspicious to me (i.e. less likely to be a thermistor fault), don't you think?
        BoAundefined 1 Reply Last reply Reply Quote 0
          How is your wiring for the thermistors ran?
          The graph in your first photo is clearly signal noise. It thinks the temp is dropping and increases power to maintain temp, but then it gets a real reading and sees the temp is actually hotter than expected and triggers the fault.
          I would be inclined to replace the thermistor and wiring entirely.
          Leavundefined 1 Reply Last reply Reply Quote 1
          • Leavundefined
            Leav @Phaedrux
            @Phaedrux said in Heater Temperature Excursion:
            Thanks for the tip @Phaedrux, in my delta I have 3 wiring harnesses (one in each tower) and the hotend thermistor was running along side the hot end fan for a long distance.
            I moved the fan to a different harness and was able to print without errors again, though the noise was significantly higher in the bed thermistor for some reason. (does not go through that harness at all).
            I can't really understand why this issue suddenly popped up, and I can't say that I feel like I solved it since the temperature readings for the bed were so noisy in the beginning (but became completely smooth after the bed was up to temp).
            Is there perhaps a way to filter transients in the temperature probe? (I meam physically, like a ferrite or a capacitor)
              Phaedrux Moderator @Leav
              @Leav said in Heater Temperature Excursion:
              Not sure about that.
              Twisted pair and/or shielded cable can help avoid picking up noise. A PT100 in 4 wire mode is a good choice in this situation as it is designed to reject noise.
              • BoAundefined
                BoA @Leav
                @Leav For heatbed this looks like a noise, but honestly... 50*C drop for about 60 seconds? That is not a noise. That looks like poor connection to heater.
                  Phaedrux Moderator @BoA
                  @BoA said in Heater Temperature Excursion:
                  If it was actually losing connection it would show open circuit and temp would shoot to 2000c to trigger fault.
                  • BoAundefined
                    BoA @Phaedrux
                    @Phaedrux It would show open circuit in case of problem with thermistor, but on second pic it looks like bad connection to heater.
                    • Leavundefined
                      Leav
                      I'm bringing up this old thread since I am still chasing heater faults...
                      This happened ~3 hours into a print, after the following changes to the system:
                      • Changed heater cartridge (new)
                      • Changed to thermistor in cartridge form factor
                      • Added silicone sock (even though there is no
                      • Tuned the new heater configuration
                      Unfortunately I was not near the printer at the time so the temperature graph was lost to the sands of time, but it was and is smooth when I look at it now.
                      Are there any ideas or suggestions for other things to look for that could cause this? quite annoying to have what looks to be a solid setup interrupted by inexplicable random hiccups like this.
                      Looking at M122 response, I found this line:
                      Slowest loop: 581.48ms; fastest: 0.12ms
                      === Network ===
                      Slowest loop: 581.68ms; fastest: 0.00ms
                      WiFi signal strength -72dBm, reconnections 0, sleep mode modem
                      That looks like a suspiciously long loop time to me, and could also perhaps explain minor hiccups/stuttering i've been noticing in the delta motion?
                      The correlation to the network loop time is too close to be coincidental...
                      Is this abnormal?
                      I added the Signal strength since atheory has already been brewing in my head that:
                      Weak signal -> Network Lags -> CPU lags -> heater control loop losing control -> temperature excursion...
                      What do you think?
                      Thanks for your time and ideas!
                      Full M122:
                      M122
                      RepRapFirmware for Duet 2 WiFi/Ethernet version 3.1.1 running on Duet WiFi 1.02 or later
                      Board ID: 0JD0M-9K662-MGPSS-6J1FD-3S46N-TVU6Y
                      Used output buffers: 3 of 24 (18 max)
                      Static ram: 27980
                      Dynamic ram: 93124 of which 48 recycled
                      Exception stack ram used: 592
                      Never used ram: 9328
                      Tasks: NETWORK(ready,308) HEAT(blocked,768) MAIN(running,1732) IDLE(ready,80)
                      Owned mutexes: WiFi(NETWORK)
                      Last reset 06:06:23 ago, cause: software
                      Last software reset at 2020-10-10 13:09, reason: User, spinning module GCodes, available RAM 9424 bytes (slot 2)
                      Software reset code 0x0003 HFSR 0x00000000 CFSR 0x00000000 ICSR 0x0441f000 BFAR 0xe000ed38 SP 0xffffffff Task MAIN
                      Error status: 0
                      MCU temperature: min 29.3, current 38.1, max 43.7
                      Supply voltage: min 23.7, current 24.1, max 24.3, under voltage events: 0, over voltage events: 0, power good: yes
                      Driver 0: standstill, SG min/max 2/423
                      Driver 1: standstill, SG min/max 13/423
                      Driver 2: standstill, SG min/max 41/408
                      Date/time: 2020-10-10 19:16:18
                      === Storage ===
                      Free file entries: 10
                      SD card longest read time 2.9ms, write time 62.5ms, max retries 0
                      Hiccups: 0(0), FreeDm: 169, MinFreeDm: 137, MaxWait: 6600918ms
                      === MainDDARing ===
                      Scheduled moves: 2, completed moves: 2, StepErrors: 0, LaErrors: 0, Underruns: 0, 0  CDDA state: -1
                      === AuxDDARing ===
                      Heater 0 is on, I-accum = 0.0
                      Segments left: 0
                      Movement lock held by null
                      HTTP is idle in state(s) 0
                      Telnet is idle in state(s) 0
                      File is idle in state(s) 0
                      USB is idle in state(s) 0
                      Aux is idle in state(s) 0
                      Trigger is idle in state(s) 0
                      Queue is idle in state(s) 0
                      Daemon is idle in state(s) 0
                      Code queue is empty.
                      === Network ===
                      Responder states: HTTP(2) HTTP(0) HTTP(0) HTTP(0) FTP(0) Telnet(0), 0 sessions
                      HTTP sessions: 1 of 8
                      - WiFi -
                      Network state is active
                      WiFi firmware version 1.23
                      WiFi MAC address 24:62:ab:15:71:64
                      WiFi Vcc 3.39, reset reason Unknown
                      WiFi flash size 4194304, free heap 22440
                      WiFi IP address 192.168.1.6
                      Socket states: 0 4 0 0 0 0 0 0
                        When do you see stutters in motion? Can you post your full config.g? Your M122 doesn't indicate any actual hiccup interruptions, but maybe it was gathered after a reboot?
                        I think this is still an issue of thermistor interference/noise.
                        Leavundefined 2 Replies Last reply Reply Quote 0
                        • Leavundefined
                          Leav @Phaedrux
                          @Phaedrux Config files below.
                          Regarding wiring issue... it could be, I do understand that wiring issues can be tricky to replicate, but for the record I did try to heat up the extruder and jiggle the wires to see if I can create any noise, and no dice.
                          Config.g
                          ; generated by RepRapFirmware Configuration Tool v3.1.4 on Sun Jul 19 2020 22:30:32 GMT+0300 (Israel Daylight Time)
                          G90                                            ; send absolute coordinates...
                          M83                                            ; ...but relative extruder moves
                          M550 P"Goliath"                                ; set printer name
                          M665 R172.66 L511.07 B150 H329.8                 ; Set delta radius, diagonal rod length, printable radius and homed height
                          M666 X0 Y0 Z0                                  ; put your endstop adjustments here, or let auto calibration find them
                          M552 S1                                        ; enable network
                          M586 P0 S1                                     ; enable HTTP
                          M586 P1 S0                                     ; disable FTP
                          M586 P2 S0                                     ; disable Telnet
                          M569 P0 S0                                     ; physical drive 0 goes backwards
                          M569 P1 S1                                     ; physical drive 1 goes forwards
                          M569 P2 S0                                     ; physical drive 2 goes backwards
                          M569 P3 S1                                     ; physical drive 3 goes forwards
                          M584 X0 Y1 Z2 E3                               ; set drive mapping
                          M350 X16 Y16 Z16 E16 I1                        ; configure microstepping with interpolation
                          M92 X100.00 Y100.00 Z100.00 E137.82            ; set steps per mm (E is 430 for bondtech, 137.82 for creality)
                          M566 X600.00 Y600.00 Z600.00 E1200.00          ; set maximum instantaneous speed changes (mm/min) (was [x,y,z]=1200)
                          M203 X9000.00 Y9000.00 Z9000.00 E1200.00       ; set maximum speeds (mm/min) (was [x,y,z]=18000)
                          M201 X500.00 Y500.00 Z500.00 E1000.00       ; set accelerations (mm/s^2) (was [x,y,z]=1000)
                          M906 X1000 Y1000 Z1000 E1500 I30                ; set motor currents (mA) and motor idle factor in per cent
                          M84 S30                                        ; Set idle timeout
                          M208 Z0 S1                                     ; set minimum Z
                          M574 X2 S1 P"!xstop"                           ; configure active-high endstop for high end on X via pin !xstop
                          M574 Y2 S1 P"!ystop"                           ; configure active-high endstop for high end on Y via pin !ystop
                          M574 Z2 S1 P"!zstop"                           ; configure active-high endstop for high end on Z via pin !zstop
                          M558 P5 C"!zprobe.in" H5 F250 T6000 ;A3 S0.01   ; set Z probe type to switch and the dive height + speeds (was 120mm/sec)
                          G31 P500 X30.31 Y17.5 Z2.44                    ; set Z probe trigger value, offset and trigger height (z probe is at a circle with radius 35mm from extruder)
                          M557 R160 S20									;Set probing radius to 160mm with a probe spacing of 20mm
                          M308 S0 P"bedtemp" Y"thermistor" T100000 B4725 C7.060000e-8 ; configure sensor 0 as thermistor on pin bedtemp
                          M950 H0 C"bedheat" T0                          ; create bed heater output on bedheat and map it to sensor 0
                          M307 H0 B1 S1.00                               ; enable bang-bang mode for the bed heater and set PWM limit
                          M140 H0                                        ; map heated bed to heater 0
                          M143 H0 S135                                   ; set temperature limit for heater 0 to 135C
                          M308 S1 P"e0temp" Y"thermistor" T100000 B4725 C7.060000e-8  ; configure sensor 1 as thermistor on pin e0temp
                          M950 H1 C"e0heat" T1                           ; create nozzle heater output on e0heat and map it to sensor 1
                          M307 H1 B0 S1.00                               ; disable bang-bang mode for heater  and set PWM limit
                          M308 S2 P"e1temp" Y"thermistor" T100000 B4725 C7.060000e-8  ; configure sensor 2 as thermistor on pin e1temp (chamber thermistor)
                          M950 F0 C"fan0" Q100                           ; create fan 0 on pin fan0 and set its frequency
                          M106 P0 X1 H1 T45                            ; set fan H1 (was 0.25) value. Thermostatic control is turned on
                          M563 P0 S"Extruder0" D0 H1 F0                  ; define tool 0
                          G10 P0 X0 Y0 Z0                                ; set tool 0 axis offsets
                          G10 P0 R0 S0                                   ; set initial tool 0 active and standby temperatures to 0C
                          ; Lighting
                          M950 P0 C"e1heat"							   ; create output port 0 attached to heater 1\
                          M42 P0 S0.1									; Turn on Case light 10%
                          ; Load Custom settings
                          M501
                          Config-override.g
                          ; config-override.g file generated in response to M500 at 2020-10-08 22:54
                          ; Delta parameters
                          M665 L511.070:511.070:511.070 R173.652 H337.845 B160.0 X0.728 Y1.338 Z0.000
                          M666 X-1.091 Y-0.667 Z1.759 A0.00 B0.00
                          ; Heater model parameters
                          M307 H0 A340.0 C200.0 D5.5 S1.00 V0.0 B1
                          M307 H1 A561.3 C290.3 D4.1 S1.00 V24.0 B0
                          ; Workplace coordinates
                          G10 L2 P1 X0.00 Y0.00 Z0.00
                          G10 L2 P2 X0.00 Y0.00 Z0.00
                          G10 L2 P3 X0.00 Y0.00 Z0.00
                          G10 L2 P4 X0.00 Y0.00 Z0.00
                          G10 L2 P5 X0.00 Y0.00 Z0.00
                          G10 L2 P6 X0.00 Y0.00 Z0.00
                          G10 L2 P7 X0.00 Y0.00 Z0.00
                          G10 L2 P8 X0.00 Y0.00 Z0.00
                          G10 L2 P9 X0.00 Y0.00 Z0.00
                            Is this a direct drive extruder setup? As in, do the motor wires run along with the heater and thermistor and fan wiring?
                            • Vetiundefined
                              Veti @Phaedrux
                              @Phaedrux
                              it looks like a delta.
                              please post a picture of the printer
                              • Leavundefined
                                Leav
                                @Phaedrux @Veti
                                Here's the beast I call Goliath, a labor of blood, sweat and love
                                I've added some annotations to help understand how the wiring is handled. generally I tried to avoid putting sensor wires next to potentially noisy power wires, where possible.
                                • Leavundefined
                                  Leav @Phaedrux
                                  Forgot to answer this. Usually during long sweeping curves I will see the printer pause for a fraction of a second and continue.
                                  I thought perhaps the CPU is getting overloaded...
                                    When you notice it doing that check the m122 for hiccups. Though that's usually only when using microsteps higher than 16 which you are not. Curves with small segments could do it. What slicer do you use? s3d has been known to do that.
                                    Low e jerk and pressure advance could be another possibility.
                                    Do you use mesh compensation? Low z jerk can sometimes cause stutters in xy but you've got a delta so all jerk is the same on xyz so I don't think that's what's going on here.
                                    Leavundefined 1 Reply Last reply Reply Quote 0
                                    • Leavundefined
                                      Leav @Phaedrux
                                      I use PrusaSlicer, will do the M122 when I notice the hiccups.
                                      Interesting, I don't use pressure advance but I can see why the low E jerk could cause that.
                                      Yes I'm definitely a mesh user. I see how that could cause issues for cartesian users, but I agree probably unrelated for me on a delta.
                                      If I may re-ask the question from a few posts ago: what do you make of the "slowest loop" statistic? Is that not concerning?
                                        Unsure of the slowest loop stat. @dc42 would have to comment.
                                        • Leavundefined
                                          Leav
                                          I hope this isn't bad form, but it seems this question slipped by so I'm tagging @dc42 again...
                                            No that's fine. Keeps us from forgetting. Thanks for giving it a couple days. 🙂