    Bed heater crashing Duet WiFi at set point
    666
    • Adarackundefined
      Adarack @SIam
      @siam said in Bed heater crashing Duet WiFi at set point:
      @adarack does M98 P"configt.g" throw any errors? Which command did you use to PID tune the Bed? What kind of Bed Heater you are using (24V / 230V how much Watts) Is it directly connected to the duet or did you use a SSR?
      Thank you for the reply!
      M98 P"config.g" shows no errors.
      M98 P"config.g"
      HTTP is enabled on port 80
      FTP is enabled on port 21
      TELNET is enabled on port 23
      Warning: Heater 2 appears to be over-powered. If left on at full power, its temperature is predicted to reach 365C
      The bed is 24v directly connected to the Duet. Not sure of the wattage but I would guess it's the same bed Creality uses of the Ender 3 Pro which is 220W .
      The power supply is a 350W Meanwell 24v.
      EDIT.
      The command I used for the PID tune was M303 H0 S100
      • Adarackundefined
        Adarack
        Decided to try a PID temp of 90c. So entered M303 H0 S90. It completed but with an error.
        Warning: heater behaviour was not consistent during tuning
        Auto tuning heater 0 completed after 3 idle and 25 tuning cycles in 2939 seconds. This heater needs the following M307 command:
         M307 H0 B0 R0.279 C670.9 D3.01 S1.00 V23.8
        Send M500 to save this command in config-override.g
        After a M500 I tried to set the heater to 90c and the board reset as soon as it reached the setpoint.
        M122 after board reset
        RepRapFirmware for Duet 2 WiFi/Ethernet version 3.3 (2021-06-15 21:44:54) running on Duet WiFi 1.02 or later
        Board ID: 08DJM-9178L-L2MS8-6JKDD-3S06Q-98HYP
        Used output buffers: 3 of 24 (11 max)
        Static ram: 23876
        Dynamic ram: 75452 of which 0 recycled
        Never used RAM 15088, free system stack 184 words
        Tasks: NETWORK(ready,12.7%,244) HEAT(delaying,0.0%,330) Move(notifyWait,0.1%,364) MAIN(running,83.6%,461) IDLE(ready,3.6%,29), total 100.0%
        Owned mutexes: WiFi(NETWORK)
        Last reset 00:00:25 ago, cause: software
        Last software reset at 2021-09-06 09:03, reason: HardFault undefInstr, GCodes spinning, available RAM 15088, slot 2
        Software reset code 0x4063 HFSR 0x40000000 CFSR 0x00010000 ICSR 0x0041f803 BFAR 0xe000ed38 SP 0x200033d8 Task NETW Freestk 476 ok
        Stack: 20005cb0 20002c10 20000154 00000030 ffffffff 0045b80d 0045a172 610f0000 00000000 00000000 4204f625 3edbc06f 3331bb4c 40000000 b5ddd98d 388ab355 bb360b61 3e2aaaab 3f800000 00000000 42034a49 4354c416 7f7fffff 00000000 80000010 00000001 e000e000
        Error status: 0x00
        Step timer max interval 0
        MCU temperature: min 32.4, current 33.2, max 33.5
        Supply voltage: min 24.0, current 24.2, max 24.3, under voltage events: 0, over voltage events: 0, power good: yes
        Driver 0: position 0, standstill, SG min/max not available
        Driver 1: position 0, standstill, SG min/max not available
        Driver 2: position 0, standstill, SG min/max not available
        Driver 3: position 0, standstill, SG min/max not available
        Driver 4: position 0, standstill, SG min/max not available
        Driver 5: position 0
        Driver 6: position 0
        Driver 7: position 0
        Driver 8: position 0
        Driver 9: position 0
        Driver 10: position 0
        Driver 11: position 0
        Date/time: 2021-09-06 09:04:05
        Cache data hit count 948703290
        Slowest loop: 3.68ms; fastest: 0.17ms
        === Storage ===
        Free file entries: 10
        SD card longest read time 2.3ms, write time 0.0ms, max retries 0
        === MainDDARing ===
        === AuxDDARing ===
        Bed heaters = 0 -1 -1 -1, chamberHeaters = 2 -1 -1 -1
        Segments left: 0
        Movement lock held by null
        HTTP is idle in state(s) 0
        Telnet is idle in state(s) 0
        File is idle in state(s) 0
        USB is idle in state(s) 0
        Aux is idle in state(s) 0
        Trigger is idle in state(s) 0
        Queue is idle in state(s) 0
        LCD is idle in state(s) 0
        Daemon is idle in state(s) 0
        Code queue is empty.
        === Network ===
        Slowest loop: 79.17ms; fastest: 0.00ms
        HTTP sessions: 3 of 8
        - WiFi -
        Network state is active
        WiFi firmware version 1.26
        WiFi MAC address dc:4f:22:6e:e2:40
        WiFi Vcc 3.44, reset reason Turned on by main processor
        WiFi flash size 4194304, free heap 22728
        WiFi IP address 10.10.2.85
        WiFi signal strength -37dBm, mode 802.11n, reconnections 0, sleep mode modem
        Clock register 00002002
        Thank you for looking
        SIamundefined 1 Reply Last reply Reply Quote 0
        • o_lampeundefined
          o_lampe @Adarack
          @adarack said in Bed heater crashing Duet WiFi at set point:
          Now however anytime I try to PID tune the bed the Duet crashes. Shortly after "Auto tune starting phase 3, heating system settling" shows in the console the board will reset.
          It's a far fetch, but it might be possible your part cooling fan shorts the onboard power.
          Phase 3 of PID tuning is related to part cooling fan...
          • SIamundefined
            SIam @Adarack
            @adarack Try to load the new settings with M501 and head up the bed again does your Duet restart if you heat only to 80 c°
            Hypercube-Evolution-Hybrid, Piezo Orion, Orbiter
            Duet WiFi 1.02 or later + DueX5
            RepRapFirmware for Duet 2 WiFi/Ethernet 3.4.0beta4 (2021-09-27 11:30:36)
            Duet WiFi Server: 1.26
            Duet Web Control 3.4.0beta4 (2021-09-27)
            Adarackundefined 1 Reply Last reply Reply Quote 0
            • Adarackundefined
              Adarack @SIam
              @o_lampe
              Tried with all fans unplugged and it's the same. Thank you for the idea though
              @siam
              Gave that a shot. I can get the PID tune done at 90c. It seems if I set the heater to any value it will reset once it's near the setpoint. So I'm starting to think that something is buggy with the PID on my board.
              Might have to erase the firmware and reflash. Might just go back to 2.05, with the old config, and see if it still works as it used to.
              M122 with H0 set at 70c
              Static ram: 23876
              Tasks: NETWORK(ready,11.2%,227) HEAT(delaying,0.0%,330) Move(notifyWait,0.1%,364) MAIN(running,83.8%,461) IDLE(ready,4.9%,29), total 100.0%
              Last reset 00:00:18 ago, cause: software
              Last software reset at 2021-09-06 17:01, reason: HardFault undefInstr, Platform spinning, available RAM 15088, slot 0
              Software reset code 0x4060 HFSR 0x40000000 CFSR 0x00010000 ICSR 0x0041f803 BFAR 0xe000ed38 SP 0x20002730 Task MAIN Freestk 1021 ok
              Stack: 200016e0 00000000 00000000 00000000 0042a6e1 004581d3 004581e6 410f0000 00000000 0045a75d 00000000 00000000 8200001b ffffffff a5a5a5a5 200013c4 200016e0 20004c8c 004658bb 8100001b a5a5a5a5 200080c8 200080c8 a5a5a5a5 0b4d23ad 0040a0b7 6136496e
              Error status: 0x00
              MCU temperature: min 29.0, current 30.0, max 30.1
              Date/time: 2021-09-06 17:01:54
              Cache data hit count 705265869
              Slowest loop: 3.67ms; fastest: 0.17ms
              === Storage ===
              SD card longest read time 2.5ms, write time 0.0ms, max retries 0
              === MainDDARing ===
              === AuxDDARing ===
              Segments left: 0
              === Network ===
              Slowest loop: 79.15ms; fastest: 0.00ms
              - WiFi -
              WiFi flash size 4194304, free heap 22888
              WiFi signal strength -36dBm, mode 802.11n, reconnections 0, sleep mode modem
                Phaedrux Moderator @Adarack
                That may be an interesting test to at least narrow down if it's firmware related or electrically related.
                The easiest way to switch between versions is to simply upload the complete zip file package for the version you wish to use in the system tab of DWC.
                https://github.com/Duet3D/RepRapFirmware/releases/download/3.0/Duet2and3Firmware-3.0.zip
                https://github.com/Duet3D/RepRapFirmware/releases/download/3.3/Duet2and3Firmware-3.3.zip
                • Adarackundefined
                  Adarack @Phaedrux
                  @phaedrux
                  I ended up erasing the flash and using bossa to reflash it. It seems to have worked.
                  So I'm at a loss at this point. There are a couple of possibilities I can think of.
                  1. I had a bad flash. I didn't test anything when 3.0 was installed, just went straight to 3.3. So I followed the guide and did 2.05 -> 3.0 -> 3.3 and reworked the config.
                  2. Something is electrically wrong (a very real possibility) and 3.3 has an issue with it whereas 2.05 ignores it.
                  The wiring on this printer is quite old now and it defiantly could use some attention. Especially with all the ABS that has been pushed through it. Also, this board is getting a little old as well and it's on its second printer.
                  It is odd that it only seems to happen when the PID begins to do its work. It will heat fine till it gets close to the setpoint then crash with a hard fault. It only fails on the bed, hotend, and chamber heater work fine.
                  Thank you to everyone who chimed in. I think I will leave it on 2.05 for the immediate future and check all the wiring before attempting the upgrade again.
                  SIamundefined droftartsundefined 2 Replies Last reply Reply Quote 0
                  • SIamundefined
                    SIam @Adarack
                    @adarack you say your board is old, how old and can you see on the duet board the Hardware Version ?
                      @adarack have you checked that the VIN terminal screws are still tight? Also check the bed heater terminal screws. High currents can cause the wires to creep over time, especially if you didn't use ferrules.
                        droftarts administrators @Adarack
                        @adarack Can you post your RRF2 config.g? Maybe you're using bang-bang control. I'd suspect that using PID (or a high switching rate) is causing your PSU problems, though your M122 reports show 'HardFault invState' once and 'HardFault undefInstr' twice as the reason for the software reset. One for @dc42 to look at.
                        • Adarackundefined
                          Adarack @droftarts
                          @siam
                          I can't easily see the board where it is in the printer. I'm pretty sure it says 1.04 something.
                          It has been probably about 2 years since I did anything with the wiring on this printer. Loose connections are possible. I used crimp on terminals and ferrules at a all points though. The main concern is that a lot of the wiring isn't motion rated. It's highly possible that some of the copper strands have begun breaking in the jacket.
                          @droftarts said in Bed heater crashing Duet WiFi at set point:
                          Those 2 faults were from different operations. I was attempting to PID tune the bed at one point. Then after getting a successful tune I tried to heat it. Not sure if that matters though.
                          The config for 2.05
                          ; generated by RepRapFirmware Configuration Tool v3.1.4 on Sat Jul 18 2020 11:04:36 GMT-0400 (Eastern Daylight Time)
                          G90                                     ; send absolute coordinates...
                          M83                                     ; ...but relative extruder moves
                          M550 P"Ender 5 Duet"                         ; set printer name
                          ;M918 P1 E4 F2000000                    ; configure direct-connect display
                          M552 S1                                 ; enable network
                          M586 P0 S1                              ; enable HTTP
                          M586 P1 S1                              ; enable FTP
                          M586 P2 S1                              ; enable Telnet
                          M569 P0 S1                              ; physical drive 0 goes forwards
                          M569 P1 S1                              ; physical drive 1 goes forwards
                          M569 P2 S0                              ; physical drive 2 goes backwards
                          M569 P3 S0                              ; physical drive 3 goes backwards
                          M584 X0 Y1 Z2 E3                        ; set drive mapping
                          M350 X16 Y16 Z16 E16 I1                 ; configure microstepping with interpolation
                          M92 X80.00 Y80.00 Z1600.00 E830.1      ; set steps per mm
                          M566 X900.00 Y900.00 Z120.00 E300.00    ; set maximum instantaneous speed changes (mm/min)
                          M203 X6000.00 Y6000.00 Z180.00 E6000.00 ; set maximum speeds (mm/min)
                          M201 X500.00 Y500.00 Z100.00 E5000.00   ; set accelerations (mm/s^2)
                          M906 X700 Y700 Z800 E700 I30          ; set motor currents (mA) and motor idle factor in per cent
                          M84 S30                                 ; Set idle timeout
                          ;Pressure Advance
                          ;M572 D0 S0.2                            ; pressure advance for Bondtech set to 0.2
                          M574 X1 Y1 Z0 S1                        ; set axis minima
                          M208 X230 Y225 Z300 S0                  ; set axis maxima
                          M574 X1 Y1 Z0 S1                         ; set active high endstops
                          M574 Z1 S2                               ; set endstops controlled by probe
                          ;M591 D0 P2 C3 S1
                          M307 H3 A-1 C-1 D-1                     ; disable heater on PWM channel for BLTouch
                          M307 H4 A-1 C-1 D-1                     ; disable heater on PWM channel for BLTouch
                          ;M558 P9 H10 F120 T4000
                          M558 P9 H5 F100 R0.2 A5 T6000           ; set Z probe type to bltouch and the dive height + speeds
                          G31 P500 X55 Y32 Z2.10                  ; Set Z probe trigger value, offset and trigger height
                          M557 X0:200 Y0:210 S20                  ; define mesh grid
                          ;Bed
                          M307 H0 B0 S1.00                        ; disable bang-bang mode for the bed heater and set PWM limit
                          M305 P0 T100000 B4092 R4700             ; set thermistor + ADC parameters for heater 0
                          M143 H0 S120                            ; set temperature limit for heater 0 to 150C
                          ; Hotend
                          M305 P1 T100000 B4092 R4700             ; set thermistor + ADC parameters for heater 1
                          M143 H1 S275                            ; set temperature limit for heater 1 to 275C
                          ; Chamber
                          ;M950 H2 T2
                          M141 H2 P0                              ; assign chamber heater to heater 2
                          M570 H2 S240                           ; Set heater 2 to 120s fault delay
                          M307 H2 D240 B1             ; Set heater 2 to bang-bang mode and deadtime to 60sec
                          M305 P2 X200                            ; configure PT100 for heater 2
                          M143 H2 S70                            ; set temperature limit for heater 2 to 60C Chamber
                          M106 P0 S0 I0 F500 H-1                  ; set fan 0 value, PWM signal inversion and frequency. Thermostatic control is turned off
                          M106 P1 S1 I0 F500 H1 T45               ; set fan 1 value, PWM signal inversion and frequency. Thermostatic control is turned on
                          M106 P2 S1 I0 F500 H1:0 T45             ; set fan 2 value, PWM signal inversion and frequency. Thermostatic control is turned on
                          M563 P0 D0 H1 F0                        ; define tool 0
                          G10 P0 X0 Y0 Z0                         ; set tool 0 axis offsets
                          G10 P0 R0 S0                            ; set initial tool 0 active and standby temperatures to 0C
                          M929                                    ; Enable Logging
                          M501                                    ; load saved parameters from non-volatile memory
                          • Adarackundefined
                            Adarack
                            Just wanted to give a little update.
                            Finally had some time to get into the printer and check the connections. They all felt tight but I loosened and retightened them. Then went through the upgrade process to 3.3 again.
                            Now it works! Not sure what it was exactly but in any case it's heating and not crashing for now.
                            Still want to make a new wire loom for the hotend and have some wire on
                            order. If there are any electrical issues hiding in there somewhere hopefully that will straighten them out.
                            Thank you all for you help!
                            kb58undefined 1 Reply Last reply Reply Quote 1
                            • kb58undefined
                              kb58 @Adarack
                              @adarack Glad that it's fixed. My money is on a poor connection such that as it approaches the temperature setpoint and shuts off the heater, there's a good size voltage spike that resetting the board. If it starts doing it again, I'd suspect the power supply, Meanwell or not.
                              Scratch-built 350mmx350mm coreXY, linear rails, ballscrews, 3 Z axis, Duet3 6HC, v3.3, Tool Board v1.1, BondTech LGX + Mosquito hot end
                              • Adarackundefined
                                Adarack @kb58
                                @kb58
                                Very true. Power supplies can and will fail at some point. I'll order a spare in the near future to have on hand.