    Wiring a Duet 3 Scanning Z-Probe v1.0 to a Toolboard v1.3
    1.9k
    • WOPR73undefined
      WOPR73 @jay_s_uk
      @jay_s_uk Yeah, thanks. I figured that would be the case. Running a bunch of CAN wires from the hotend seems like such a waste. One for the Toolboard and another for the Z-Probe. I hope that will be it... because the lack of my due diligence seems to be costing me in the end. Welp! I guess I will have to either run multiple CAN lines to the distribution board or just configure an inductive probe and attach that to the tool board... and on a 500x500mm heat bed that will take a while. lol Well thank you for your help it means a lot. 👍
      gloomyandyundefined 1 Reply Last reply Reply Quote 1
      • WOPR73undefined
        WOPR73 @WOPR73
        @WOPR73 yeah, the toolboard only has the "in" if you will for the CAN to control the rest of the items connected to it. the board doesnt have an "out" for additional CAN connections. The distribution board does have 3 more CAN connections. So, there is that if you do not mind running multiple CAN wires from the same location back to the distro board.
        gloomyandyundefined 1 Reply Last reply Reply Quote 0
        • gloomyandyundefined
          gloomyandy @WOPR73
          @WOPR73 You do not need to run multiple CAN wires to the toolhead nor do you need to replace the boards you already have. Please re-read the posts above. The solution provided by jay offers the simplest solution and requires just 4 wires (two CAN wires plus power) from your mainboard to the 1LC and then four wires from the 1LC to the SZP.
          The second solution I provided will require the standard distribution board wiring to the 1LC (so 4 CAN wires in a loop plus power) then an additional 4 wires (two can plus power) wires to the SZP the CAN wires to the SZP would be spliced on to the CAN wires close to the 1LC.
          I don't have access to a drawing program at the moment to provide a diagram of the above, perhams some that does can provide something that will help explain the proposed solutions.
            gloomyandy @WOPR73
            @WOPR73 said in Wiring a Duet 3 Scanning Z-Probe v1.0 to a Toolboard v1.3:
            The 1LC toolboard has two pairs of can wires to allow the CANBUS to be looped through it
            854d1b61-1406-4efe-b988-5b064c487fee-image.png <img src="blob:chrome-untrusted://media-app/4cf83316-03f3-41a1-8da0-dcd169dcd8fb" alt="Screenshot 2024-04-13 08.46.42.png"/>
            These can also be used as described by Jay above to connect to the SZP board.
            WOPR73undefined 1 Reply Last reply Reply Quote 0
            • WOPR73undefined
              WOPR73 @gloomyandy
              @gloomyandy So if I understand this correctly. From the Distribution Board run CAN and Power to the 1LC, But only use 1) CAN_L and 2) CAN_H to control the 1LC. Then use 3) CAN_L and 4) CAN_H from the Distribution Board for connecting to the SZP and pull +v5 and GND from the 1LC. Correct? Is this because 3) CAN_L and 4) CAN_H are not use due to 1LC not having a CAN_OUT?
              dc42undefined WOPR73undefined 2 Replies Last reply Reply Quote 0
                dc42 administrators @WOPR73
                No, like this.
                • From the distribution board run a single pair of CAN wires from CAN1_L and CAN1_H (see https://docs.duet3d.com/duet_boards/duet_3_can_expansion/duet_3_tool_distribution_board_v0.5_wiring.png) to one pair of the the tool board CAN_L and CAN_H connections
                • Connect the other pair of tool board CAN_L and CAN_H connections to the CAN_L and CAN_H connections of the SZP
                • Connect +5V and GND of the tool board IO0 connector to +5V and GND on the SZP.
                • Make sure that the termination resistor is enabled on the SZP, and disabled on the tool board.
                gloomyandyundefined WOPR73undefined 2 Replies Last reply Reply Quote 0
                  gloomyandy @dc42
                  @dc42 Does the OP need to remove the optional terminator from the distribution board in this configuration?
                    dc42 administrators @gloomyandy
                    @gloomyandy the CAN bus won't proceed beyond the first of the four tool outputs on the distribution board if it is wired like this, so it doesn't matter whether the termination jumper is fitted or not,
                    • WOPR73undefined
                      WOPR73 @WOPR73
                      This post is deleted!
                      • WOPR73undefined
                        WOPR73 @dc42
                        @dc42 So, I can do all of this from Tool 0 CAN-FD on the distro board(remove jumpers). I am just splitting the two pairs of CAN, One to the Toolboard and the other pair to SZP.
                          @WOPR73 yes that's correct. The CAN bus will run from the main board to the distribution board, from that to the tool board, and from the tool board to the SZP. It will be terminated with 120 ohm resistors at both ends i.e. at the Duet 3 Mini and the SZP.
                          • WOPR73undefined
                            WOPR73 @WOPR73
                            @WOPR73 wait. what? 120 ohm resistors at both ends? Duet 3 mini? Mini what?
                              droftarts administrators @WOPR73
                              @WOPR73 I think you have a 6HC, not a Mini 5+. The mainboard has built in 120ohm resistor for termination, so you don't have to worry about terminating that end. At the other end of the CAN bus, the SZP provides the termination.
                              • WOPR73undefined
                                WOPR73 @droftarts
                                @droftarts yeah, I have a 6HC. I bought the distribution board after I saw that in one of the documents stating I would have to use a resistor in able to connect them. One would think that Duet would have some kind of unified standard of conformity for the connection between components that they have created. I am new to wiring up my own 3D printer and have to research a lot of this stuff to make sure I don't make a mistake. This is by no means close to plug-and-play. Welp, lesson learned I guess.
                                The Tool Distribution Board came with 4 premade CAN wires. I am not sure what would be easier or cleaner.
                                1. Using 2 premade CAN wires running back to the Tool Distribution board. One from the SZP and the other one from the 1LC, both being plugged in at the Distribution board.
                                  or
                                2. trying to undo one pair of the wires on the 1LC CAN connection and run it to the SZP.
                                Would have been nice to just have a CAN out on the 1LC. Either way I still need to take the 5v+ and GND from the tool board so it wont be clean looking. I really wish I would have seen this coming. 😞
                                Any thoughts?
                                • WOPR73undefined
                                  WOPR73 @dc42
                                  @dc42 Sorry, But I have a 6HC and a Tool Distribution board. So, I should not need the resistor. With splitting the CAN pair from the Distribution board and one pair going to the 1LC and the other pair going to the SZP. Still unable to M115 or M122 to either. And yes I do have the jumper removed on the distribution board. Using the same connection on the 24v power supply that is being used on the 6HC. Then running power from the distribution board to the 1LC and a blue light is on. But, no response.
                                  4/25/2024, 10:41:36 PM M122 B121
                                  CAN response timeout: board 121, req type 6024, RID 8
                                  4/25/2024, 10:41:11 PM M115 B121
                                  CAN response timeout: board 121, req type 6024, RID 7
                                  i've tried B20, B21 B10, etc; as referred to in some of the duet documents. I went back to the basics and I'm just using the 6HC, Tool Distribution Board and 1LC with supplied CAN cables that came with the Tool Distribution Board. Plus a default config from the RFF config tool.
                                  I was able to upgrade to latest:
                                  Duet Web Control 3.5.1
                                  Panel Due 7i 3.4.1
                                  config.g
                                    Can you share some photos of your wiring setup?
                                    • WOPR73undefined
                                      WOPR73 @Phaedrux
                                      @Phaedrux Sure, Not the best lighting... but, it should do. I have just tried stand alone without a Pi4 and still can not talk to the 1LC.
                                      4/26/2024, 12:05:11 AM M122 B121
                                      CAN response timeout: board 121, req type 6024, RID 6
                                      4/26/2024, 12:05:07 AM M122 B120
                                      CAN response timeout: board 120, req type 6024, RID 5
                                      4/26/2024, 12:05:01 AM M115 B120
                                      CAN response timeout: board 120, req type 6024, RID 4
                                      4/26/2024, 12:04:50 AM M115 B121
                                      CAN response timeout: board 121, req type 6024, RID 3
                                        @WOPR73 from your pictures, I can see that you need to remove the bypass jumpers on the distribution board under the 1LC connection.
                                        Are you having problems connecting to the 1LC on its own? Have you ever been able to connect? I can’t see the SZP wired in in your pictures, looks like just the 1LC is wired in at the moment to the distribution board. In this configuration (I can’t see the SZP connected) the termination jumper should be fitted on the distribution board too.
                                        If you still can’t connect, check that your CAN cable from 6HC to distribution board is correct; flat cables like you have are often wired incorrectly for CAN, see https://docs.duet3d.com/en/User_manual/Machine_configuration/CAN_connection#example-of-a-good-cable
                                        Then check your wiring; that the wire from the distribution board CAN_H goes to CAN_H on the toolboard, and so on.
                                        As others have said, if you’re only ever going to run a 1LC and SZP, the distribution board is a bit redundant. You can take two wires from the 6HC (to the 1LC CAN in, then two wires from the 1LC CAN out to the SZP. Set the SZP to provide termination.
                                        If you plan to add more tools, the distribution board makes sense, though the tool with the SZP will still need to be the last on the CAN bus.
                                        • WOPR73undefined
                                          WOPR73 @droftarts
                                          @droftarts Those pictures are when I started over to troubleshoot and I was just trying to talk to the 1LC by itself... without the SZP. I ended up going though the entire chain and finding out that the main power "OUT 0 Power in" and "OUT 0 (out)" was not working even know it was showing correct voltage on a meter and the 1LC had a blue light on. So, I direct connected the Tool Distribution Board to the mains power "power in". After that I had to grab the "Duet2and3Firmware-3.5.1.zip" and install that. Using the RRF Config Tool zip seems to have conflicting versions of DWC vs 6HC Duet3Firmware_MB6HC.bin file in the download zip. Even after getting each 3.5.1 file from github it still complained after many reboots and reinstalls. So, I ripped out all the files started fresh with the "Duet2and3Firmware-3.5.1.zip" and the 1LC is able to be talked to.
                                          5/2/2024, 6:18:27 PM M122 b121
                                          Diagnostics for board 121:
                                          Duet TOOL1LC rev 1.1 or later firmware version 3.5.1 (2024-04-19 14:42:41)
                                          Bootloader ID: SAMC21 bootloader version 2.4 (2021-12-10)
                                          All averaging filters OK
                                          Never used RAM 4152, free system stack 132 words
                                          Tasks: Move(3,nWait 7,0.0%,129) HEAT(2,nWait 6,0.2%,129) CanAsync(5,nWait 4,0.0%,55) CanRecv(3,nWait 1,0.0%,71) CanClock(5,nWait 1,0.0%,67) ACCEL(3,nWait 6,0.0%,53) TMC(2,delaying,3.4%,53) MAIN(1,running,91.8%,315) IDLE(0,ready,0.0%,27) AIN(2,delaying,4.5%,112), total 100.0%
                                          Owned mutexes:
                                          Last reset 00:00:22 ago, cause: power up
                                          Last software reset data not available
                                          Driver 0: pos 0, 80.0 steps/mm, standstill, SG min 0, read errors 0, write errors 0, ifcnt 9, reads 11282, writes 9, timeouts 0, DMA errors 0, CC errors 0, steps req 0 done 0
                                          Moves scheduled 0, completed 0, in progress 0, hiccups 0, segs 0, step errors 0, maxLate 0 maxPrep 0, maxOverdue 0, maxInc 0, mcErrs 0, gcmErrs 0, ebfmin 0.00 max 0.00
                                          Peak sync jitter 5/9, peak Rx sync delay 197, resyncs 0/0, no timer interrupt scheduled
                                          VIN voltage: min 24.7, current 24.7, max 24.7
                                          MCU temperature: min 35.1C, current 35.6C, max 35.6C
                                          Last sensors broadcast 0x00000002 found 1 101 ticks ago, 0 ordering errs, loop time 0
                                          CAN messages queued 427, send timeouts 0, received 201, lost 0, errs 1, boc 0, free buffers 18, min 18, error reg 20000
                                          dup 0, oos 0/0/0/0, bm 0, wbm 0, rxMotionDelay 0
                                          Accelerometer: LIS3DH, status: 00
                                          I2C bus errors 0, naks 3, contentions 0, other errors 0
                                          Now its on to figuring out the SZP. I have a fast blinking red light not in sync with the main board or 1LC. It will not respond to the reset button on the SZP other than a quick green light, then back to flashing fast red. The SZP is/was fastened to the backside of the 3d printed part that the 1LC was on. I'll try to explain the connections I've made hopefully I have it correct. BTW. I bought the Tool Distribution board to avoid the janky resistor that I would have to use if I didn't buy it. Plus who knows what I might add later, right?
                                          From the Tool Distribution Board using Tool 0, 4) CAN1_H and 3) CAN1_L I have connected to the 1LC and able to communicate with.
                                          From the Tool Distribution Board Using Tool 0, 2) CAN_H 0-1 and 1) CAN_L_0-1 going to the SZP.
                                          The SZP does have the solderable jumper on the back of the SZP to set the termination resistor.
                                          The Tool Distribution Board does have all the default jumper on except for the two jumpers on "Tool 0 CAN - FD".
                                          See Photos: IMG_5322.jpg IMG_5323.jpg
                                          So, I am going back to reread the info on Duet and CAN to see what I missed and how I can get the SZP to talk... and then flash with new firmware. I assuming that is what the fast red blinking means. Any help would be great. Thanks!
                                          Oh, yeah, the CAN cables are bought are from Filastruder on in the Duet section of the store. They're not home made looks like the good cable on that link... just black. But, I have made RJ11 and RJ45 cables before.
                                          Now... I found this: "Only one Type 2 probe can be configured, and if using Duet 3 then it must be connected to the Duet 3 main board, not to a CAN-connected expansion or tool board."
                                          M558: Set Z probe type
                                          why? umm. what is the point of the 1LC... more limitations than it worth. Am I missing something?
                                            @WOPR73 Fast flashing red light on the SZP means no CAN connection, which is because you have wired the CAN incorrectly. You can't wire the SZP to the green and white wires from the Tool Distribution board (TDB from now on). If you just had a 1LC, they are the wire that would return from the 1LC to the TDB, to loop on to the next tool (ie the T1 output on the TDB).
                                            From the TDB, the black and white wires should connect to the 1LC. Where these enter the 1LC, there should be another wire pair, that would normally return to the TDB. In your case, they should go to the SZP, and then back to the TDB, like this:
                                            The SZP will actually be on a 'spur' from the CAN bus. Doing it this way will mean the TDB will provide termination to the CAN bus, so you don't have to terminate either the 1LC or the SZP.
                                            Regarding the M558 probe limitation, it has nothing to do with the SZP. The SZP is an entirely separate toolboard from the 1LC. Yes, it's a limitation of the 1LC that not all types of probe can be connected to it. But most probes are encompassed by the types supported by the 1LC. A type 2 probe is a modulated analogue IR probe, which barely anyone uses any more. See https://docs.duet3d.com/en/User_manual/Connecting_hardware/Z_probe_connecting#z-probe-modes-selectable-in-firmware
                                            Probes connected to Duet 3 expansion or tool boards are limited to types 8 and 9. Firmware 3.5 also supports type 11.