    [feature] Adaptive / Feedforward Temperature setpoint
    Firmware developers
    8
    51
    3.5k
    • timschneiderundefined
      timschneider @droftarts
      @droftarts
      Hi @droftarts
      I use the following tuning method:
      • determine the lowest possible temperatur Temp_base for the filament, e.g. extrude with F30 (0.5 mm/sec Speed_base) so that the filament is melting and will bond to each other
      • define your desired extrusion rate, e.g. 35 mm³/sec -> calculate the required extrusion speed -> around 5.5 mm/sec (Speed_desired) for 2.85mm filament -> F330
      • Extrude the filament with the desired speed + 20% and increase the temperature of the hotend till you are able to extrude at the desired speed. Note the needed temperature for that speed Temp_required. The extrusion length should be at least two times your hotend length. The 20% increase is some kind of error margin for non linear extrusion and when the fan is on.
      • calculate the needed temperature boost with Temp_boost = (Temp_required - Temp_base) / (Speed_desired - Speed_base)
      For Example PLA
      Temp_base = 190
      Temp_required = 230
      Speed_base = 0.5 mm/s
      Speed_desired = 5.5 mm/s
      Temp_boost = 40 / 5 => 8 => T8
      Edit: Temp_base will be the temperature you set in your slicer for that material.
      timschneiderundefined 1 Reply Last reply Reply Quote 1
        timschneider @timschneider
        @droftarts
        I have updated the description so that it hopefully becomes clearer how much material has to be extruded and why you should aim for a 20% plus error margin and that you should use the temp_base for slicing.
        timschneiderundefined 1 Reply Last reply Reply Quote 0
          thank you for implementing the temperature feedforward.
          It took me a while to get it installed on a machine and test it, unfortunately I was not able to get it working. Maybe its a pure display thing, but I do not see the temperature increase I was expecting.
          I set M309 P0 S0.06 T8 A100 and was extruding at 245°C with 0.6mm/sec, so I was expecting an temperature increase of 4.8°C but the temperature in DWC was still at 245°C.
          the following chart is showing the print process and a pretty stable temperature without the increase and decrease of the temperature feed forward.
          The printer is on
            The problem is the A100 - without the A param it works.
            What is the purpose of the A param - I thought it is kind of a look a head and will set the temp increase in advance.
            But it will not work for short moves.
            To reproduce:
            G28 X Y
            M568 P0 R160 S230
            T0
            G91
            echo "will not work"
            M309 P0 S0.05 T8 A100
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G4 S5
            echo "will work"
            M309 P0 S0.05 T8 A0
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
            G1 X1 E1 F120
              dc42 administrators @timschneider
              @timschneider we knew that large A values will not work correctly, because there need to be enough moves in the queue that have been committed in order to look that far ahead. I think A40 should generally work: can you try that?
              Trietundefined timschneiderundefined 2 Replies Last reply Reply Quote 1
              • Trietundefined
                Triet @dc42
                I dared to try 😊
                Using firmware version 3.6.0-beta.4 and with following command in my config.g:
                M309 P0 S0.06 T10 A40
                I can confirm that temperature modulation based on flow rate works.
                I used the small model below as a preliminary experiment, printed at a nominal temperature of 190 deg C. (usually I print this material at 212 deg C).
                Remarks:
                During the first layer the temperature jumped to over 220 deg C but with the bed at 45 deg C this was unnecessarily high to achieve bed adhesion. To avoid such surprises I managed to disable this feature for the first layer alone using
                the macro command
                M309 P0 S{(layer_num == 0 ? 0 : 0.06)} T{(layer_num == 0 ? 0 : 10)} A{(layer_num == 0 ? 0 : 40)}
                which yields M309 P0 S0 T0 A0 for ths 1st layer only; then the temperature set for the 1st layer in the slicer is used unchanged.
                I needed several retries because I was getting a heater fault error right at the 1st layer. The increase was too sudden I guess. Only after I reconfigured the heater fault detection I could continue the print:
                M570 H1 P15 T20 ; wait 15 sec, allow 20C deviation
                The maximum temperature increase happened at the widest height of the model and was about 5 degrees, but only a short time.
                Most of the time the print temperature stayed around 192C, that is, only 2 degrees higher than set. Although the speeds were set up to 300 mm/sec, due to a layer time limitation and weak cooling fan, the print went quite slow with 20-35 mm/sec.
                The deviation between target and actual temperatures can't be assessed during the print, because the increase introduced by this feature is done in the firmware - this is as expected, but raises the need of a plug-in in DWC to preview the effect.
                Manually overriding the extrusion speed live during the print (or perhaps using M220) did cause a corresponding increase in temperature, as it should be.
                It is unclear to me whether extrusion rate increases caused by non-linear extrusion configuration (M592) also cause temperature increases. In theory, his could lead to a vicious circle, because a temperature increase by itself also promotes a higher extrusion.
                I learned that this feature works only increasing the temperature, never decreasing it. That means that one is compelled to choose a nominal printing temperature (the one set in the slicer) that should be low enough that no decrease is necessary due to a smallish flow. This could happen to be inconvenient, depending on the average flow and temperature range needed. This method is suitable to adapt temperature in regions with higher flows, overcoming potential bottlenecks.
                A better approach would have been (in my opinion) to consider the nominal temperature to correspond to the average flow rate, allowing both increases and decreases. In most cases no special tests or calibrations would be needed with this method; for example, setting 205C for PLA, thus allowing a range of +/- 15C=30C. Flow rate "spikes" would be still accounted for. This way, small details and overhangs would benefit too (a more common concern than printing at very high speeds, if quality is important).
                In other words, as it is implemented, you would set for a benchy a nominal temperature corresponding to the chimney top - suboptimal I think.
                Print details:
                Duet 2 WiFi + 0.4 nozzle, PLA, 0.12 mm layer height, 0.3 mm layer width, one wall only (to challenge the operation!)
                And I got this result:
                The print was quite good in my opition, and was not worst than a good one done without the feature under same conditions. Still learning.
                I have gathered some experience using the post-processing script mentioned above. It is difficult to believe how felicitous that script manages the temperature/flow relationship. That solution works differently though: It controls speeds in such a way that the flow matches the temperature when the temperature can't be changed fast enough; it also smoothes the flow rate - sounds dangerous, but works surprisingly well. Unfortunately, it is only a post-processing script with the respective disadvantages. The author was told that such feature belongs to the firmware realm - here we have it.
                I think this feature of the version 3.6.0 will be vastly underestimated. I consider it a big jump, really.
                By the way, the description in the documentation of M309 should be corrected. It states:
                "This feature is intended for high flow hot ends or pellet extruders. It's not normally needed on regular hot ends with a 0.4mm or similar size nozzle where the temperature drop caused by extrusion is less than 1C."
                The feature may be inteded as described, but it is not limited to mere anticipation of temperature fluctuation of the nozzle due to changing flow. In fact, it contributes to a much better control of a key parameter, namely temperature. I myself will be using it quite often, I think.
                Hope I helped a bit.
                  timschneider @dc42
                  ok, A40 is working - but shouldn't A100 act like A0 if A100 can not be maintained? Instead it was acting like T0.
                  @Triet
                  thanks for you tests! You can maybe increase the layer height to increase the volumetric flow rate, as the T parameter from M309 is multiplied by the speed in mm/s of the filament (extruder) - not the movement speed of the X and Y axis. Your absolute maximum flow rate is about 5.44 mm³/s which is about 2.26 mm/sec for 1.75mm or 0.85 mm/sec for 2.85mm filament, which corresponds to 227.6°C or 213.5°C. Thats a steep increase, unless you have a powerfull heater, your printer will not be able to follow. I use T8 with an 60W heater and 2.85mm filament. I run my prints with 25 - 40 mm ³/s.
                  Trietundefined dc42undefined 4 Replies Last reply Reply Quote 0
                  • Trietundefined
                    Triet @timschneider
                    @timschneider said in [feature] Adaptive / Feedforward Temperature setpoint:
                    0
                    This was a test I spontaneously decided to do without planning, but it turned out unsuitable for the purpose of temperature modulation. The maximum flow rate of 5.44 mm3/s (using a 1.75 mm filament) happened very shortly and was not representative at all. I did notice the jump though - causing a heater fault at my first try.
                    I also use a 60 W heater, in a copper block (E3D style) and an original CHT nozzle. It can achieve a 25C increase faster that one would think, but certainly not fast enough if the model consist of parts with disparate flow rates in succession. And that is exactly the test case I am printing right now:
                    As you can recognize here:
                    The temperature is set at 195C but settles at around 199C +/-2C, it can't follow as you say. The range would be much wider if it could. But there are some layers with predominantly high flow, I am waiting to see how the temperature behaves then (I am staring at the display).
                    Based on my experience using the postprocessing script mentioned above, the maximum temperature lag was about 5C, in most cases only 3C - but that script uses a different method, where the flow rate is adapted (smoothed) to match the predicted temperature, very clever in my opinion. The temperature/flow rate relationship is defined there by entering three points of desired temperature at the given flow rates, quite easy. I could envision that a similar method is implemented in the firmware. But even this T-Parameter is a thing as it is now. I have learned to appreciate the value of temperature control and am quite excited about it.
                    More tests following.
                    • Trietundefined
                      Triet @timschneider
                      @timschneider That model (I would call it "the "mother of hinges"), went well - all hinges were moving free without play (after forcingly "unfreezing" them the first time). I can infer then than the temperature variation does not pose a danger in maintaining correct dimensions, in this case at least.
                      Now I am choosing a more representative test model with an ample variation of flow rate, which at the same time allows us to assess artifacts, without being excessive large or long to print.
                      This JUN - the Jungle Queen (visual benchy) has a plethora of details and is not too small.
                      Results:
                      Printing with at 195 C, 0.2 mm layerheight, (0.4 mm nozzle), solid infill with 0.6 mm layer width, and sparse infill speed set at 300 mm/sec (but not reached) and still using M309 P0 S0.06 T10 A40, Orca Slicer was showing a flow rate up to 29 mm3/s, but that is not true. The real maximum is about 20 mm3/s, enough of a range. Extrusion rate smoothing was set to 90 mm3/s to avoid abrupt transitions.
                      The temperature occassionally reached >240 C in the high flow areas. In very slow areas, it was decreased (!) down to 190 C. Most of the time, is was about 200C.
                      The print shows very crisp details, reminding me of previous cases using the postprocessing script. This is obviously the result of printing the small details with a suiting lower temperature.
                      Despite some suboptimal slicer settings (happens when printing in a hurry), the print went well and it looks better than in the picture.
                      Remarks:
                      I noticed that right at the begin of the print the temperature is higher than it should be (although I disabled this temperature modulation feature for the first layer), but immediately begins to fall as the print of the 1st layer progresses. My suspicion is that the firmware looks at the flow of the movements in the print queue in advance, but ignoring the command disabling the feature. But the command it is there:
                      and when it is processed, the temperature fails again to the nominal 195C. It looks like a slip to me.
                      Furthermore, I still got heater faults (even after releasing the check conditions), but strangely, this happened at a moment where the temperature was quite stable after having significantly changed before. So it looks to me like the firmware notes a temperature deviation, but does not update that deviation timely as the temperature has changed and stabilized. Perhaps that part of the firmware should be revised.
                      This time, a decrease in temperature compared to the nominally set print temperature (195 C in this case) took place at some point. So I withdraw the objection I made before, although I don't quite understand how this is controlled in detail. I assume that the T parameter defines a slope determined by changes of temperature in relation to changes in flow, but where we are in that characteristic curve, I don't know.
                      Summarizing, I am very pleased with this enhancement. I still stand on my prediction that this feature will stay extremely underrated. I recommend to try it out.
                      • Trietundefined Triet referenced this topic
                      • Trietundefined
                        Triet @timschneider
                        @timschneider In case you are interested, this video offers insight to flow modulated temperature control:
                        Variable Temperature 3D Printing – The FUTURE of 3D Printing?
                        • Adrian52undefined
                          Adrian52
                          I am finding this feature really interesting. For pla and a 0.4 nozzle, I find
                          M309 p0 S0.06 T6 A40
                          works ok. I use a base temperature of 200, and first layer temperature of 215. First layer prints at 220-225, as I use 20mmsec for perimeter and 40mm/sec for infill. Using a revo 40watt heater and revo cht nozzle, temperatures change quite quickly (low thermal mass). Experimenting with higher speeds, inner perimeters and infill print fine at 140mm/sec (DWC reports about 22cumm/sec) - accurate weighing of resulting print showed that there was no under extrusion. I am not currently using non-linear extrusion. I have a single nozzle delta, so sometimes change filament mid print to get a multicolour effect. The adaptive feed forward is good for this as the base temperature is high enough to load and prime the new filament, but there is little oozing so you get a clean change. This is what a manual filament change looks like
                          The print quality with adaptive feed forward seems excellent, and still finding the limits of how fast one can go.
                          Trietundefined 1 Reply Last reply Reply Quote 3
                          • Trietundefined
                            Triet @Adrian52
                            @Adrian52 I found that the active (=target) temperature is not updated, either in DWC or in the Paneldue. It is impossible to know how far the current temperature deviation is.
                            Besides, I had to increase the S Parameter to about 0.3 to get a quicker change of temperature. Nontheless, I get heater faults from time to time, although I have loosened the check using the command M570 H1 P100 T45, which is incredibly forgiving, as it allows a deviation of 45 C deg to persist for up to 100 sec...
                            Adrian52undefined 1 Reply Last reply Reply Quote 0
                            • Adrian52undefined
                              Adrian52 @Triet
                              @Triet I guess if one is using the feedforward in the way intended, the temperature shown is the target temperature. I have been playing with the parameters, trying to understand how they work. I am trying out a 0.25mm nozzle, which has an extrusion rate of about 8.8cumm/sec with 0.125mm layers at 140mm/sec, which is think corresponds to about 3.6mm/sec for 1.75 filament. A T parameter of 12 seems to give the expected increase of just greater than 40deg over the base temperature. I think there is a bit of under extrusion at this speed with the 0.25 nozzle, but checking that out. For my standard 0.4 cht nozzle, 0.2 layers give about 22cumm/sec at 140 mm/sec, that is about 9mm/sec filament. Using T5, this gives the expected increase of about 45deg above base temperature. I dont think the cht nozzle is underextruding under these conditions. I have just started using an S parameter of 1.0, and this seems to work fine with the 0.25 nozzle - not tried with the 0.4 nozzle yet. Tried increasing the A parameter to 50, and the feed forward stops working.
                              I have been using M570 H1 P15 T45, and not been getting heater faults. The revo nozzle setup I am using has a low thermal mass, and seems to be controlled very well by the duet.
                                I've reduced the maximum allowed from A100 to A50 in rc2, which I think should work.
                                [EDIT: Adrian's post above suggests that it doesn't.]
                                Adrian52undefined 1 Reply Last reply Reply Quote 1
                                  dc42 administrators @Adrian52
                                  @Adrian52 said in [feature] Adaptive / Feedforward Temperature setpoint:
                                  That's correct, the target (as displayed by DWC and PanelDue) remains the same but the feedforward correction is added to it internally.
                                  @Triet said in [feature] Adaptive / Feedforward Temperature setpoint:
                                  I'll look at adding the current feedforward boost to the object model.
                                  EDIT: I've added the boost parameters to the OM.
                                  • Adrian52undefined
                                    Adrian52 @dc42
                                    @dc42 On my system, the highest A value that works is 48
                                    • Adrian52undefined
                                      Adrian52
                                      To see if I could get the hotend to follow the forward temperature more closely, I tried removing the silicone sock from the revo heater, to see if I could get faster cooling. I redid the pid tune without the sock, and this is the plot printing a 100mmx20mm cube that has three small cylinders attached to one end. The cube walls print at 140mm/sec, and the cylinders around 20mm/sec. The cube has no fill or top, but the initial part shows printing the bottom infill
                                      It then cycles between the fast cube walls and the slow cylinder walls. I was suprised how well controlled the temperature is under these conditions. The print weighed exactly the amount predicted by the slicer, so no underextrusion. The cube walls were printing at 22cumm/sec (o.4 nozzle, 0.2layers). The S parameter was set to 1
                                      Would be interesting to plot the feed forward boosted temperature on the temperature chart - is this possible?
                                      jay_s_ukundefined Trietundefined 2 Replies Last reply Reply Quote 0
                                        jay_s_uk @Adrian52
                                        @Adrian52 you could plot it with BtnCmd if its in the object model
                                        • Trietundefined
                                          Triet @Adrian52
                                          @Adrian52 Wouln't you need to repeat the same print (with/without silicon sock) to properly quantify the effect? What are you comparing to?
                                          • Adrian52undefined
                                            Adrian52 @Triet
                                            @Triet Indeed - I was just looking at the feasibility of leaving off the sock. I was concerned that it would make temperature control unstable, but this doesn't seem to be the case. I thought a next step would be to plot the boosted temperature against the actual temperature, but waiting for an update that has the boosted temperature in the OM. On a learning curve with btncmd too - not used it before. Will aim to do a more formal comparison, including maximum speed and print quality.
                                            Trietundefined 1 Reply Last reply Reply Quote 0