Issues with Homing Delta on RRF3
  • I just upgraded to 3.x and I am having issues homing. Once home begins all axis start to travel towards the endstops as expected. However it seems that 2 of the 3 delta axis reaches the end stop and one does not. All axis then start to jitter significantly around the endstops. If I manually use my figure to depress the endstop on the axis that was not reached the homing completes.
    ; Homing file for RepRapFirmware on RostockMaxc
    G91							; use relative positioning
    G1 H1 X550 Y550 Z550 F5000	; move all carriages up 320mm, stopping at the endstops
    G1 H2 X-3 Y-3 Z-3 			; move all carriages down 3mm
    G1 H1 X6 Y6 Z6 F250			; move carriages slowly up 6mm, stopping at the endstops
    G1 Z-5 F2000				; down a few mm so that we can centre the head
    G90							; back to absolute positioning
    G1 X0 Y0 F2000				; centre the head and
  • @aerouta
    Hi ,
    Have you checked that it work properly?
    Are they optical? Or mechanical?
    Web Control > Settings > Machine Specific > on the right you should see "Endstop". All are not in triggered status if they are not interrupted (or activated if mechanical).
    Can you manually interrupt (or activate) the endstop (the one problematic) and verify in the WC that the signal is properly passed?
    Do your endstop section in config.g look ike this?
    M574 X2 S1 P"xstop" ; Set active high endstops
    M574 Y2 S1 P"ystop"
    M574 Z2 S1 P"zstop"
    Did you already checked the conversion guide?
    https://duet3d.dozuki.com/Wiki/RepRapFirmware_3_overview#Section_M574
  • **@giostark said in Issues with Homing Delta on RRF3:
    @aerouta
    Hi ,
    M574 Y2 S1 P"ystop"
    M574 Z2 S1 P"zstop"
    https://duet3d.dozuki.com/Wiki/RepRapFirmware_3_overview#Section_M574**
    Yes, they seem to be working properly, they are mechanical switches. I just checked them on the WC and they all trigger and toggle status correctly. The issue is not a single tower but which every tower is first to reach the end stop starts to chatter.
    Here is my old M574 command
    M574 X2 Y2 Z2 S1  ; set endstop configuration (all endstops at high end, active high)
    Here is the new M574 command
    M574 X2 S1 P"xstop"
    M574 Y2 S1 P"ystop"
    M574 Z2 S1 P"zstop"			; set endstop configuration (all endstops at high end, active high)
    I have uploaded some videos showing the issue.
    Homing Fail 1
    Homing Fail 2
    Please post your complete config.g file.
    Also, try running M98 P"config.g" to see if there are any error messages.
  • @dc42 said in Issues with Homing Delta on RRF3:
    M98 P"config.g"
    Here are the results from the M98 command...
    M98 P"config.g"
    RepRap name: My Duet
    Warning: Heater 0 appears to be over-powered. If left on at full power, its temperature is predicted to reach 224C
    Warning: Heater 1 appears to be over-powered. If left on at full power, its temperature is predicted to reach 554C
    Error: in file macro line 88 column 10: M92: array too long, max length = 1
    And here is my current config file...
    ; Configuration file for Rostock Max early V1
    ; Communication and general
    M111 S0                             	; Debug off
    M550 RostockMax							; Machine name and Netbios name (can be anything you like)
    M551 Preprap                        	; Machine password (used for FTP)
    ;*** If you have more than one Duet on your network, they must all have different MAC addresses, so change the last digits
    M540 P0xBE:0xEF:0xDE:0xAD:0xFE:0xED 	; MAC Address
    ;*** Wifi Networking
    M552 S1									; Enable WiFi
    M555 P2                           		; Set output to look like Marlin
    ; Axis and motor configuration
    M569 P0 S1				; Drive 0 goes forwards
    M569 P1 S1				; Drive 1 goes forwards
    M569 P2 S1				; Drive 2 goes forwards
    M569 P3 S1				; Drive 3 goes forwards
    M569 P4 S1				; Drive 4 goes forwards
    M574 X2 S1 P"xstop"
    M574 Y2 S1 P"ystop"
    ;*** The homed height is deliberately set too high in the following - you will adjust it during calibration
    ;M665 R144.96 L291 B150 H375.532 	; set delta radius, diagonal rod length, printable radius and homed height
    M665 R144.96 L300.15 B140 H367.532 	; set delta radius, diagonal rod length, printable radius and homed height
    ;M666 X-0.48 Y1.11 Z-0.63			; put your endstop adjustments here, or let auto calibration find them
    M350 X16 Y16 E16 I1    				; Set 16x microstepping with interpolation
    M92 X106.667 Y106.667 Z106.667		; Set axis steps/mm
    M906 X1000 Y1000 Z1000 E800 I60		; Set motor currents (mA) and increase idle current to 60%
    M201 X1500 Y1500 Z1500 E1500		; Accelerations (mm/s^2)
    M203 X20000 Y20000 Z20000 E3600		; Maximum speeds (mm/min)
    M566 X1200 Y1200 Z1200 E1200		; Maximum instant speed changes mm/minute
    G21                                 ; Work in millimetres
    G90                                	; Send absolute coordinates...
    M83                                 ; ...but relative extruder moves
    ; Thermistors and Heaters
    ;RRF 2
    ;M305 P0 T100000 B3950 R4700 H30 L0	; Put your own H and/or L values here to set the bed thermistor ADC correction
    ;M305 P1 T100000 B4267 R4700 H25 L0	; Put your own H and/or L values here to set the first nozzle thermistor ADC correction
    ;M305 P2 T100000 B3974 R4700 H30 L0	; Put your own H and/or L values here to set the second nozzle thermistor ADC correction
    ;RFF 3
    M308 S0 Y"thermistor" P"bedtemp" T100000 B3950
    M308 S1 Y"thermistor" P"e0temp" T100000 B4725 C7.06e-8 A"T_e0"
    M950 H0 C"bedheat" T0
    M950 H1 C"e0heat" T1
    M308 S10 y"mcutemp" a"Mcu"
    M308 S11 y"drivers" a"Drivers"
    M570 S180				; Hot end may be a little slow to heat up so allow it 180 seconds
    ;Heater 0 model: gain 140.9, time constant 634.3, dead time 13.9, max PWM 1.00, mode: PID
    M307 H0 A199.9 C634.4 D13.9 B0		;Values obtained from autotunning
    M307 H1 A529.9 C170.4 D6.3 B0 		;Values obtained from autotunning
    M570 H1 P7 T30
    ;M106 P1 H-1 				; disable thermostatic mode for fan 1
    M950 F0 C"fan0"
    M950 F1 C"fan1"
    M950 F2 C"fan2"
    M106 P1 T45 H1 S1           ;hot end fan
    ; Enable logging after setting the heater models to avoid logging the usual warnings of overpowered heaters
    M929 S1 P"eventlog.txt"
    ; Tool definitions
    M563 P0 D0 H1                       	; Define tool 0
    G10 P0 S0 R0                        	; Set tool 0 operating and standby temperatures
    ;*** If you have a single-nozzle build, comment the next 2 lines
    ;M563 P1 D1 H2                      	; Define tool 1
    ;G10 P1 S0 R0                       	; Set tool 1 operating and standby temperatures
    M140 H0                                 ;Bed Heater
    ;M92 E92.4:92.4                       	; EZextruder Set extruder steps per mm
    M92 E470:470  				;Bondtech Extruder
    ; Z probe and compensation definition
    ;*** If you have a switch instead of an IR probe, change P1 to P4 in the following M558 command
    ;M558 P4 X0 Y0 Z0 H4 F1000			; Z probe is an IR probe and is not used for homing any axes
    M558 P5 C"e0stop" H4 F1000 T3000  ; Z probe connected to E0 endstop input  "T" Travel speed between probe
    G31 X0 Y0 Z-0.588 P500			; Set the zprobe height and threshold (put your own values here)
    ;*** If you are using axis compensation, put the figures in the following command
    ;M556 S78 X0 Y0 Z0                   	; Axis compensation here
    M208 S1 Z-1.5			; set minimum Z
    T0					; select first hot end
    M143 H1 S350				; Raise max temp
    M143 H0 S170				; Raise max temp
  • @aerouta my interpretation of the error message is that M350 has only one E value, but M92 has two E values.
  • Moderator
    Place your M92 E back along with the others and then specify the additional parameters for both extruders.
  • I have updated the config file to correct the error. I am still having the same problems shown in the video links...
    M111 S0                             	; Debug off
    M574 X2 S1 P"xstop"
    M574 Y2 S1 P"ystop"
    ;RRF 2
    ;RFF 3
    M570 H1 P7 T30
    M950 F0 C"fan0"
    M950 F1 C"fan1"
    M950 F2 C"fan2"
    ; Tool definitions
    M140 H0                             ;Bed Heater
    M92 E470				  			;Bondtech Extruder
    M208 S1 Z-1.5						;set minimum Z
    T0									;select first hot end
  • @aerouta I am not used with Delta printers so much, but M350 is missing the microstepping for Z, is this correct or should it be added?
  • @JoergS5 These commands were brought over from a properly functioning RRF2 config. I have tried adding "Z16". There was no improvement in homing..
  • @aerouta what does happen when you only home one axis? Does the stepper stop correctly when reaching end position? (all 3 steppers tested separately)
    E.g. G91 and G1 H1 X550 F5000 only.
    Testing whether every stepper has it's correct endstop assigned. Because the two videos could be explained by steppers trying to move on but not stopped because the endstop belonging to this stepper was not reached yet.
    My interpretation of the first video is: the left stepper is at the endstop, but endstop is not activated, so it tries to move on, the belt slipping over the pulley (so jitter), the vibrations propagate to the middle arm also. But the middle arm is IMHO not at the end position. You could validate by pressing the endstop before it reaches the end position. (lower speed to have more time...)
  • @JoergS5 The videos show that the first axis to reach the endstop begins the jitter. I tested each axis one at a time and confirmed what is seen on the video. Attempting to home one axis begins the jitter on that axis.
    Is there any changes from board V1.01 to V1.04 that could cause this? This was another change that was made. My v1.01 board developed an intermintate failure that resulted in both thermocouples to fault. I then purchased the .04 board and upgraded to RRF3. This is my first attempt to use the new .04 board.
  • @aerouta I have also a 1.04 board.
    The release history is here: https://duet3d.dozuki.com/Wiki/Hardware_Overview#Section_PCB_revision_history
    I cannot see something related to your problem, but check also.
    My last idea is that you have an endstop type which now needs the ! in the syntax, according to https://duet3d.dozuki.com/Wiki/Gcode#Section_M574_RepRapFirmware_Num_3
    M574 X2 S1 P"!xstop"
    etc.
    Do you have your old config, did it use M574 S0? This would be S1 with ! now.
    You can also recheck the RRF3 upgrade checklist in https://duet3d.dozuki.com/Wiki/RepRapFirmware_3_overview
  • @JoergS5 @dc42
    Old config...
  • Moderator
    @aerouta said in Issues with Homing Delta on RRF3:
    Does this error still show up when you send M98 Pconfig.g?
    Can you verify your firmware version by sending M115. It should be 3.1.1
    And please share your newly changed config.g
    Can you test your endstops by hand and watch the DWC machine page for the endstops. When looking at the front of the printer, the X tower is on the left, the Y tower is on the right and the Z tower is at the back. +X movement is to the right and +Y movement is towards the rear. Verify that when you press the X tower endstop the X endstop triggers, etc.
    I wonder if maybe an endstop plug is swapped or not working.
  • @Phaedrux I conducted the test you suggested. Endstop index 0, 1, 2 triggered on towers X, Y, Z respectively.
    I no longer get the M92 error during the M98 command and my firmware version is confirmed to be 3.1.1
    M111 S0									; Debug off
    M574 X2 S1 P"xstop"
    M574 Y2 S1 P"ystop"
    ;RRF 2
    ;RFF 3
    M307 H0 A199.9 C634.4 D13.9 B0		; Values obtained from autotunning
    M307 H1 A529.9 C170.4 D6.3 B0 		; Values obtained from autotunning
    M570 H1 P7 T30
    M950 F0 C"fan0"
    M950 F1 C"fan1"
    M950 F2 C"fan2"
    M106 P1 T45 H1 S1					; hot end fan
    ; Tool definitions
    M140 H0								;Bed Heater
    M92 E470							; Bondtech Extruder
  • Moderator
    Can you alter your M350 and M92 lines to include the Z and E axis respectively? And lets include an explicit M584 to map the drivers to their respective axis.
    You have:
    Change it to:
    M584 X0 Y1 Z2 E3 ; Driver 0 controls the X motor, 1 controls Y, 2 controls Z motor, 3 control E motor
    M350 X16 Y16 Z16 E16 I1    				; Set 16x microstepping with interpolation
    M92 X106.667 Y106.667 Z106.667 E470		; Set axis steps/mm
    Then you can remove the M92 E470 that occurs lower down in the config.
    Also, I'm not sure it matters, but when comparing to a fresh delta config from the web tool, the M665 delta commands are placed higher in the config.g file near the top before all the drive commands.
    Here it is for comparison:
    ; generated by RepRapFirmware Configuration Tool v3.1.3 on Tue Jun 23 2020 20:26:57 GMT-0600 (Central Standard Time)
    G90                                            ; send absolute coordinates...
    M550 P"My Printer"                             ; set printer name
    M665 R105.6 L215 B85 H250                      ; Set delta radius, diagonal rod length, printable radius and homed height
    M666 X0 Y0 Z0                                  ; put your endstop adjustments here, or let auto calibration find them
    M552 S1                                        ; enable network
    M586 P0 S1                                     ; enable HTTP
    M586 P1 S0                                     ; disable FTP
    M586 P2 S0                                     ; disable Telnet
    M569 P0 S1                                     ; physical drive 0 goes forwards
    M569 P1 S1                                     ; physical drive 1 goes forwards
    M569 P2 S1                                     ; physical drive 2 goes forwards
    M569 P3 S1                                     ; physical drive 3 goes forwards
    M584 X0 Y1 Z2 E3                               ; set drive mapping
    M350 X16 Y16 Z16 E16 I1                        ; configure microstepping with interpolation
    M92 X80.00 Y80.00 Z80.00 E663.00               ; set steps per mm
    M566 X1200.00 Y1200.00 Z1200.00 E1200.00       ; set maximum instantaneous speed changes (mm/min)
    M203 X18000.00 Y18000.00 Z18000.00 E1200.00    ; set maximum speeds (mm/min)
    M201 X1000.00 Y1000.00 Z1000.00 E1000.00       ; set accelerations (mm/s^2)
    M906 X1000 Y1000 Z1000 E800 I30                ; set motor currents (mA) and motor idle factor in per cent
    M84 S30                                        ; Set idle timeout
    M208 Z0 S1                                     ; set minimum Z
    M574 X2 S1 P"xstop"                            ; configure active-high endstop for high end on X via pin xstop
    M574 Y2 S1 P"ystop"                            ; configure active-high endstop for high end on Y via pin ystop
    M574 Z2 S1 P"zstop"                            ; configure active-high endstop for high end on Z via pin zstop
    M558 P0 H5 F120 T6000                          ; disable Z probe but set dive height, probe speed and travel speed
    M557 R85 S20                                   ; define mesh grid
    M950 H0 C"bedheat" T0                          ; create bed heater output on bedheat and map it to sensor 0
    M307 H0 B1 S1.00                               ; enable bang-bang mode for the bed heater and set PWM limit
    M140 H0                                        ; map heated bed to heater 0
    M143 H0 S120                                   ; set temperature limit for heater 0 to 120C
    M308 S1 P"e0temp" Y"thermistor" T100000 B4138  ; configure sensor 1 as thermistor on pin e0temp
    M950 H1 C"e0heat" T1                           ; create nozzle heater output on e0heat and map it to sensor 1
    M307 H1 B0 S1.00                               ; disable bang-bang mode for heater  and set PWM limit
    M950 F0 C"fan0" Q500                           ; create fan 0 on pin fan0 and set its frequency
    M106 P0 S0 H-1                                 ; set fan 0 value. Thermostatic control is turned off
    M950 F1 C"fan1" Q500                           ; create fan 1 on pin fan1 and set its frequency
    M106 P1 S1 H1 T45                              ; set fan 1 value. Thermostatic control is turned on
    M563 P0 D0 H1 F0                               ; define tool 0
    G10 P0 X0 Y0 Z0                                ; set tool 0 axis offsets
    G10 P0 R0 S0                                   ; set initial tool 0 active and standby temperatures to 0C
  • Here is my new config file with suggested changes. Same machine response...
    M574 X2 S1 P"xstop"
    M574 Y2 S1 P"ystop"
    ;RRF 2
    ;RFF 3
    M570 H1 P7 T30
    M950 F0 C"fan0"
    M950 F1 C"fan1"
    M950 F2 C"fan2"
    ; Tool definitions
    M140 H0								;Bed Heater
  • Moderator
    @aerouta config.g looks okay, except there's an extra M92 at line 82, but as it's the same as the earlier one, it shouldn't cause a problem.
    Did you disconnect any motors or endstops, or rewire the machine? Because it really sound like two of the endstops (or motors) have been swapped, so are not related to the correct axis. That's why 2 of the 3 axes reach the endstop; one correctly hits the endstop and stops, one hits the endstop and stops the third, but continues to move, as the third hasn't hit the switch that would stop the second, until you press it with your finger.
    Move each motor individually so you know which tower is which, by sending G1 H2 X10 F100 (which will move just the X axis). Then press the switch on that tower, and check it activates the X endstop (send M119 to check status or check in DWC > Machine-Specific > Endstops). Repeat for the Y and Z towers.
  • @droftarts Yes, I did switch from a 1.01 to a 1.04 board. I will recheck all my motor and endstop connections.
  • @droftarts the motor connects were switched! good catch!