      @barbarossa-cologne said in Heated bed 2500 Watt + Duet3 6hc:

      @theruttmeister
      yes, of course PSU. sry
      Rigth. I´m in cologne. So it´s 220v.
      So when I understand it rigth, I should buy a second power supply with more volts for connecting the SSR and the heater?

      Is it a 220V AC bed heater? If it is, then you don't need a PSU for it. If it isn't, then you have the wrong SSR and we need to know what voltage it is.

      Tom Sanladerer posted a video on using SSRs to control AC mains bed heaters here https://www.youtube.com/watch?v=TiEwNf1H_Tc.

      Duet WiFi hardware designer and firmware engineer
      Please do not ask me for Duet support via PM or email, use the forum
      http://www.escher3d.com, https://miscsolutions.wordpress.com

      duttiundefined 1 Reply Last reply Reply Quote 0
      • duttiundefined
        dutti @dc42
        last edited by dutti

        This post is deleted!
        1 Reply Last reply Reply Quote 0
        • duttiundefined
          dutti
          last edited by

          correct?

          theruttmeisterundefined 1 Reply Last reply Reply Quote 0
          • theruttmeisterundefined
            theruttmeister @dutti
            last edited by

            @barbarossa-cologne

            An SSR is just a switch. The control side only needs to be 24V (actually anything from 3-48V is common, the SSR will be marked), the PSU is powering just the switching of the SSR, which uses a very small amount of power.
            The whole point of using an SSR is that the other side of the switch can be for much higher voltages and can carry lots of current.

            So your wall socket can supply up to 13A, your SSR can carry 25A and the bed only draws 11A. Everything is good.

            The PSU is not powering the bed in any way at all. Its just controlling the switch.

            Isolate, substitute, verify.

            duttiundefined 1 Reply Last reply Reply Quote 1
            • duttiundefined
              dutti @theruttmeister
              last edited by

              @dc42
              It's a 220v heater.
              Thanks for the video link.
              I think @theruttmeister
              thanks a lot
              It's working but heating up needs a lot of time. How can I change this?
              23 to 60 degree needs 10 or more minutes
              Thanks

              theruttmeisterundefined Phaedruxundefined 2 Replies Last reply Reply Quote 0
              • theruttmeisterundefined
                theruttmeister @dutti
                last edited by

                @barbarossa-cologne

                If you haven't already, insulate the back of the heater. That can make a huge difference.

                All the other options are lots more difficult: More powerful heater (needs a non-standard wall socket, unless you have a 16A or 32A Ceeform?), smaller bed (that 85x85cm is huge). Thinner bed... which given the size might well warp.

                Best bet is insulation, if you don't have any right now, half the heater output is heating the air.

                Isolate, substitute, verify.

                1 Reply Last reply Reply Quote 0
                • jens55undefined
                  jens55
                  last edited by

                  Do you have the means to measure voltage and current ?
                  The time required for heatup doesn't make sense if everything is hooked up correctly.

                  1 Reply Last reply Reply Quote 0
                  • Phaedruxundefined
                    Phaedrux Moderator @dutti
                    last edited by

                    @barbarossa-cologne said in Heated bed 2500 Watt + Duet3 6hc:

                    It's working but heating up needs a lot of time. How can I change this?
                    23 to 60 degree needs 10 or more minutes

                    Have you PID tuned the heaters and saved the results?
                    https://duet3d.dozuki.com/Wiki/Tuning_the_heater_temperature_control

                    Z-Bot CoreXY Build | Thingiverse Profile

                    1 Reply Last reply Reply Quote 0
                    • duttiundefined
                      dutti
                      last edited by dutti

                      @Phaedrux
                      I started 3D print 3 months ago. So I´m sorry when I don´t understand some code etc.
                      Is this picture helpful?
                      thanks for all

                      PID.jpeg

                      I have to say that this morning it was heating up a bit faster. I disconnected other things from the socket. But it is still slow.... SSR isn´t warm.
                      the house is about 70 years old... maybe it is not enough power on the socket??

                      1 Reply Last reply Reply Quote 0
                      • jens55undefined
                        jens55
                        last edited by

                        Ahhhhh .... the guilty party is the PWM setting. You have set the heat pad to effectively be 250W!
                        Calibration voltage 0.0V ???

                        duttiundefined 1 Reply Last reply Reply Quote 0
                        • duttiundefined
                          dutti @jens55
                          last edited by

                          @jens55
                          Ok. Do you mean 2500 watt?
                          How can I change this parameters ?

                          1 Reply Last reply Reply Quote 0
                          • jens55undefined
                            jens55
                            last edited by jens55

                            Remove the portion of your M307 command in config.g that says "S0.1"
                            Run heater tuning again.
                            The way you have things configured at the moment is that your heat pad is effectively 250W!

                            duttiundefined 1 Reply Last reply Reply Quote 0
                            • duttiundefined
                              dutti @jens55
                              last edited by

                              @jens55
                              ok I understand.... with S1 or S0.5 its heating much fast,but it comes to a fault. ``temperatur rising much slowly than expected. 1.3.C /sec. (with S0.5 its 0.7c/ sec.)

                              1 Reply Last reply Reply Quote 0
                              • jens55undefined
                                jens55
                                last edited by

                                Default is S1 so just remove the portion that specifies 'S' or replace it with S1.0. You will want full power.
                                You need to run heater tuning again in order to get rid of the warning message. You probably will see a message talking about being over - powered but that is expected. You need to understand what that means nad be aware of it but it's not a show stopper.

                                1 Reply Last reply Reply Quote 0
                                • jens55undefined
                                  jens55
                                  last edited by jens55

                                  What is the command you give to start the tune ?

                                  Stephen6309undefined duttiundefined 2 Replies Last reply Reply Quote 0
                                  • Stephen6309undefined
                                    Stephen6309 @jens55
                                    last edited by Stephen6309

                                    https://duet3d.dozuki.com/Wiki/Gcode#Section_M303_Run_heater_tuning

                                    duttiundefined 1 Reply Last reply Reply Quote 0
                                    • duttiundefined
                                      dutti @jens55
                                      last edited by

                                      @jens55
                                      With S.1 or nothing in the config.g the always comes to a warning:
                                      ``temperatur rising much slowly than expected. 1.3.C /sec"

                                      I mean I can skip the warning and start again. A few times and it's hot enough. So there are 2 options.

                                      S0.1 = heating slow BUT NO warning ``temperatur rising much slowly than expected. 1.3.C /sec"

                                      S1.0 or nothing: temperature rising fast but it comes to the warning:
                                      ``temperatur rising much slowly than expected. 1.3.C /sec"

                                      I use the button in the web control. I mean I used the configuration tool to setup heater etc.

                                      1 Reply Last reply Reply Quote 0
                                      • jens55undefined
                                        jens55
                                        last edited by

                                        It is of course up to you if you use S0.1 or S1.0, you need to decide while keeping in mind the speed of warmup (and maximum temperature).
                                        Forget about the warning message for now!

                                        duttiundefined 1 Reply Last reply Reply Quote 0
                                        • jens55undefined
                                          jens55
                                          last edited by

                                          It's been a while since I have done tuning so maybe someone else can chime in to give you details about how to get rid of the warning message.
                                          Also, if the warning message results in the heater stopping to heat, then there is a problem. Again, I am not the right person to help out with that.

                                          duttiundefined 1 Reply Last reply Reply Quote 0
                                          • duttiundefined
                                            dutti @jens55
                                            last edited by

                                            @jens55
                                            Ok.. but why does it come to a warning when it is faster? The warning tells its rising to slow..
                                            Why does it care about it? Haha
                                            Can I skip this warning forever or change the value for " it's to slow"?
                                            THANKS

                                            1 Reply Last reply Reply Quote 0